Steve,
It would be appropriate for the GFDI to have 80-amp rated contacts that
do not have an over-current trip mechanism. IMHO, the fact that they can
trip on over-current and unnecessarily interrupt the dc system bond is a
serious design flaw.
Kent Osterberg
Blue Mountain Solar, Inc.
www.bluemountainsolar.com
On 5/23/2012 9:27 AM, Steve Higgins wrote:
Bob,
Be careful with that GFDI... It's most likely wired on the output of
the controllers, on the battery side.
This can trip if a ground fault is occurring, or if you are exceeding
80 amps of current. With 8, 3 module strings, an edge of cloud event
you could have the 80amp portion of that breaker tripping rather than
the GFDI.
Steve Higgins
Sales Application Engineering Mgr
Direct 360-618-4313
Outback Power Technologies
5917 195th Street NE Arlington, Washington 98223
------------------------------------------------------------------------
*From:* re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Bob
Clark
*Sent:* Tuesday, May 22, 2012 7:37 PM
*To:* re-wrenches@lists.re-wrenches.org
*Subject:* [RE-wrenches] Finding ground faults
Wrenches:
Sorry to bring up this situation again, but I could not find a
previous discussion thread that talked about step-by-step procedures
for tracking down ground faults (I believe it was John Berdner who
provided the bulk of the writing in that regard and it related to high
voltage strings---not that 75-85 volts per string is all that low).
We have an Outback FLEXpower Two system with 8, 3-module strings
(Silicon Energy 190W, 25.3Vmp, 7.5 Imp) combined in a Midnite Solar
MNPV12 combiner with breakers. The cables from the array are routed
to two different Wiley 4-string pass-through boxes (located under the
two center strings) and then off of the roof and into the PV combiner.
Up until this week the system has seen several weeks of awesome power
production. Yesterday, the rains came and the GFDI breaker tripped.
Every time it rains, the little green breaker on the GFDI trips off.
That tells me that the ground fault is occurring in a place where at
least one of the conductors on one of the strings (possibly more) is
getting wet and conducting current to ground.
It would seem to me that the most likely place for moisture to cause a
ground fault to occur in this system would be in the pass-through
boxes. This would mean removing the central modules to access the
pass-through boxes.
Any of you who have mounted the Silicon Energy modules know that the
cables are contained in trays along the side of the modules until they
are routed through conduit to the pass-through boxes. So, if there is
current going to ground from any of these cables, it could even be
occurring in any of the 9 trays along side of the modules. I do not
like the idea of tracking down a ground fault in one of these trays as
they are all interconnected.
How best (and safely) to track down where the ground fault is
occurring? Any advice as to the best and safest way to track down the
ground fault(s) would be greatly appreciated.
*Bob Clark*
*/SolarWind Energy Systems, LLC/*
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options& settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules& etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org