Ooops !!  Sorry about that one !!    That was from 1741...

Still applicable of course but NOT   NEC.

That was applicable from 2007 though.

boB




On 5/23/2012 6:34 PM, b...@midnitesolar.com wrote:
On 5/23/2012 4:44 PM, Darryl Thayer wrote:
I sure do not like the way the X brand installed their charge controller, Also the code says that all strings must open if one string is faulted. your breaker does this up to 4 strings.
DT



I think that this is the pertinent part of the code regarding this...

In part...

31.1 Inverters or charge controllers with direct photovoltaic inputs from a grounded photovoltaic array or

arrays shall be provided with a ground-fault detector/interrupter (GFDI). The GFDI shall be capable of

detecting a ground fault, providing an indication of the fault, interrupting the flow of fault current, and either

isolating the faulted array section or disabling the inverter to cease the export of power.



This may very well change in the 2014 NEC from what I understand.

boB



*From:* Steve Higgins <shigg...@outbackpower.com>
*To:* RE-wrenches <re-wrenches@lists.re-wrenches.org>
*Sent:* Wednesday, May 23, 2012 2:18 PM
*Subject:* Re: [RE-wrenches] Finding ground faults

From what I understand, future controllers from Outback Power will incorporate the Ground Fault detection into the controller.
Steve Higgins
Sales Application Engineering Mgr
Direct 360-618-4313
Outback Power Technologies
5917 195th Street NE Arlington, Washington 98223

*From:* re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *William Miller
*Sent:* Wednesday, May 23, 2012 11:22 AM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Finding ground faults

Steve:

IMHO, a brilliant suggestion.

William Miller


At 11:19 AM 5/23/2012, you wrote:
Steve,

It would be appropriate for the GFDI to have 80-amp rated contacts that do not have an over-current trip mechanism. IMHO, the fact that they can trip on over-current and unnecessarily interrupt the dc system bond is a serious design flaw.

Kent Osterberg
Blue Mountain Solar, Inc.
www.bluemountainsolar.com  <http://www.bluemountainsolar.com>


_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to