Sorry, per the OP this appears in 690.31(E)...

On Nov 3, 2012, at 11:19 AM, David Brearley wrote:

> FWIW: In the 2011 Code, Section 690.31(D) is changed to include the following:
> 
> "Where dc photovoltaic source or output circuits…are run inside a building or 
> restructure, they shall be contained in metal raceways,Type MC metal-clad 
> cable that complies with 250.118(10), or metal enclosures…"
> 
> 
> On Nov 3, 2012, at 10:41 AM, Nick Vida wrote:
> 
>> Hello wrenches,
>> 
>> wondering if any of you are running into inspectors wanting EMT in the 
>> attics, or allowing flex only if there is a fusible disconnect on the roof. 
>> We have heard this a few time lately and havent yet seen a code reference, 
>> (except 690.31e saying metal raceways are fine- not specifying EMT only). I 
>> am wondering if this is a new wave of inspectors wanting the future now as 
>> informed by an expert seminar, or if there is something I am not aware of. 
>> Any comments are very appreciated.
>> 
>> Thank you,
>> 
>> Nick Vida
>> wrench
>> _______________________________________________
>> List sponsored by Home Power magazine
>> 
>> List Address: RE-wrenches@lists.re-wrenches.org
>> 
>> Options & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: 
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out participant bios:
>> www.members.re-wrenches.org
>> 
> 

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to