Chris Freitas is my hero; that was true wrenching, even better that his
mad scientist's experiment is still relevant 20 years later. Here's a
link to the full article I stumbled on to last night:
http://www.ibiblio.org/london/alternative-energy/homepower-magazine/archives/27/27p26.txt
Very cool that William was pulling it from his vault this morning, too.
Chris encased the batteries in concrete or safety, but apparently
nothing happened to them.
Just one note Chris mentioned on the smaller breakers, they would not
see as high a fault current, since they would be wired with #6 or
smaller wire. This added wire resistance would reduce the current at
the breaker. I'm not saying that we depend on that, just that a real
world short is not going to have 4/0 cables protected by a QO breaker.
Also, I found that higher amp class T fuses (601 to 1200 amps) have an
AIC of 100,000 amps DC. SO throwing some of those inline on big systems
might make sense. Now if we could just get an acid proof fuse holder
for them.
I know 240.21H allows OCPDs in the battery box, but I still don't
believe the fuses and holders are listed for the corrosive environment.
R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760
On 4/9/2013 10:54 AM, toddc...@finestplanet.com wrote:
when i hear of current flows like this i cant help but wonder is there
a risk of batteries exploding during these kinds of tests?
todd
On Tuesday, April 9, 2013 7:00am, "William Dorsett"
<wmdors...@sbcglobal.net> said:
This topic comes up often enough that we ought to mention a yellowed
article in Home Power, (1992 Issue 27, pg 26). Christopher Freitas
wrote /Overcurrent Protection for Battery-Powered Systems /where he
describes experiments he did back when he was with Ananda. He put a
2000 A Big Switch to initiate a short (4/0 cable) between the
terminals on a set of four golf cart batteries (2 strings @ 12V). In
series, he put in a 500A Shunt so he could measure current passing and
various fuses and breakers. "For comparison, we decided to directly
short the battery...the meter read 6960 amps peak current (three
seconds) ...during each test the 4/0 cable lifted off the ground 4
inches into the air by the forces generated by the extremely high
current.." They videoed the 250 A ANN buss fuses arc and smoke; the
200A Heinemann Series AM breakers (paralleled ones that maybe Roy
mentioned) went 3 seconds without breaking and the video showed a
flash and blue smoke.
175A ITE breaker with 42,000 AIC "simply tripped...but still allowed a
peak current of 2960 amps
200A Class T Littlefuse "opened promptly with no external signs of
stress...1920 amps peak current"
Christopher's recommendations:
"Every AE system must have overcurrent protection able to interrupt
the maximum current available from the batteries. For most systems,
the main protection should use current limiting high AIC fuses, such
as a Class T or Class R. A disconnect switch which allows the fuse to
be safely changed should be included. A lower cost alternative is to
mount the fuse in a fuse holder without a disconnect. Although the
fuse would always be electrically hot, it normally would not be
changed during the life of the system. The fuse holder should be
mounted outside the battery enclosure. Fuses should not be bolted
directly onto the battery terminal, as they are not designed to handle
the physical stresses that can occur without the protection of a fuse
holder.
Fuses which have exposed elements, such as ANN fuses, should not be
used because they are not current limiting and have only 2500 amps
AIC. They also may be a significant hazard when installed near batteries.
High AIC breakers, like the Heinemann Series CF (25,000 Amps AIC @
65VDC) can provide overcurrent protection for individual items. They
cannot be used to protect lower AIC breakers. This eliminates their
use as a main disconnect in most systems.
Low AIC breakers, like the Heinemann Series AM (5000A AIC @65 VDC) or
the Square-D QO (5000A @ 125 VDC) can be used in load distribution
centers and components, but must be protected by a current limiting
fuse. Using low-AIC breakers alone will not provide sufficient
protection with a battery system and may be a significant hazard
during short circuit situations."
It won't pull up anymore on HP's article search but probably Michael
has a copy he could post for those interested.//
Bill Dorsett
Manhattan, KS
*From:*re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *John
Berdner
*Sent:* Monday, April 08, 2013 7:25 PM
*To:* al...@positiveenergysolar.com; RE-wrenches
*Subject:* Re: [RE-wrenches] Fuse sizing in battery circuits
Allan:
A pretty accurate retention of the Grass Valley / Nevada County
through 2000.
You only missed the Trace to Xantrex "acquisition" that was the start
of the divorce J
Class T fuses provide better protection for battery based inverters --
always been that way.
The move to breakers was a cost reduction issues when Trace introduced
the DC-250.
I still contend that the way the DC-250 did it was a Code violation
when used with PV in the box (current from all sources issue) but that
is history.
For high current applications the Boltswitch Pull outs (the ones we
used in the Power Centers) came in 100A, 200A and 400 A sizes and 1,
2, and 3 pole versions.
I think they are still made today.
Still the best way to do currents above 250 Amps.
You can do a Eaton / GJ1P breaker up to 750 Amps but they are Spin Dee.
As you noted you can use a single pull out to do up to 3 battery strings.
You make a copper "comb" to parallel separate fused inputs to a single
inverter.
If you have more than one inverter you can have "back to back" fuse
blocks with an H-H-H shaped bus bar set up.
The biggest one I recall we did was a 12 400 A battery/PV inputs
going to 8 SW inverters.
You size the copper bus bars for 1000 A / square inch of cross section
and you are good to go (this is from the UL 508 design guide).
Best Regards,
John Berdner
General Manager, North America
SolarEdge Technologies, Inc.
3347 Gateway Boulevard, Fremont CA 94538 USA */(*Please note of our
new address.)/*
T: 510.498.3200, X 747
M: 530.277.4894
*From:*re-wrenches-boun...@lists.re-wrenches.org
<mailto:re-wrenches-boun...@lists.re-wrenches.org>
[mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of
*Allan Sindelar
*Sent:* Friday, April 05, 2013 9:00 PM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Fuse sizing in battery circuits
William,
For this I went deep into the catacombs of our hardware file cabinet,
and quickly found a 1996 spec sheet from an Ananda Power Technologies
SafeT-Block. For the young'uns, Ananda was a quality company, the
originator of the listed Powercenter - the breaker and terminal block
hardware that is part of every batttery-based system nowadays. Ananda
became APT, then Pulse, then part of Trace (the PC250 and PC500) as
part of a short-lived marriage followed by a messy divorce, the
results of which led, as an act of revenge insurrection, to the
introduction into the U.S. market of the Sunny Boy and AC-coupled
systems, and the rest is even more wacky history. But I digress, after
a run-on sentence bad enough that my high school English teacher is
rolling over in her grave...
I have attached a scan of page two of the spec sheet. In the upper
left corner is a chart of current vs. time for a Class T fuse. Once I
understood this chart I never again worried about nuisance tripping,
as whether described as fast-acting or not, Class T fuses have an
inherent surge capacity of about 2 1/2 times their rating, and thus
can handle surges.
If you put them on individual battery strings, the point is to prevent
overcurrent on one string, which is only likely to occur when either
1) a terminal is corroded sufficiently that one string fails to carry
its share of the load or charge (we have seen this) or 2) one string
fails when the batteries reach end-of-life. When the Class T fuses
blows in that situation it has done its job.
Allan
*Allan Sindelar*
al...@positiveenergysolar.com <mailto:al...@positiveenergysolar.com>
NABCEP Certified Photovoltaic Installer
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder and Chief Technology Officer
*Positive Energy, Inc.*
3209 Richards Lane (note new address)
Santa Fe, New Mexico 87507
*505 424-1112*
www.positiveenergysolar.com <http://www.positiveenergysolar.com/>
image001.png
On 4/5/2013 8:29 PM, William Miller wrote:
Friends:
Good topic. Some questions:
1. Most manufacturer's present an installation guide that shows
one OCPD in the battery circuit and that is in the BOS cabinet.
This means the battery leads are unprotected. Do we need an OPCD
at the battery terminals?
2. Class T fuses are generally recommended for this application.
The data shows them as "fast acting." Is this a problem? Will
they act too fast and open during normal surge loads?
Thanks in advance!
William Miller
Troy,
Overcurrent device size is matched to the conductor size. The
inverse time constant nature of an overcurrent device can
typically handle the surge currents as long as conductor sizing
has truly been done correctly for the conductor. Circuit breakers
are preferred to fuses because they can be reset.
There has been volumes written on this issue. The constant current
at lowest battery voltage should be used, plus the ac ripple
content on the battery circuit. This is usually a much larger
conductor than your average designer will plan for. The best thing
is to look at Midnight, Outback, and Schneider and see what size
overcurrent devices they require for their products. That will
give you a good clue as to how to size the conductor and
overcurrent device.
Bill.
*From:* re-wrenches-boun...@lists.re-wrenches.org
<mailto:re-wrenches-boun...@lists.re-wrenches.org>
[mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of
*Troy Harvey
*Sent:* Friday, April 05, 2013 3:38 PM
*To:* RE-wrenches
*Subject:* [RE-wrenches] Fuse sizing in battery circuits
I've got a question about battery string fusing. Typically we size
the wire from the batteries to the inverter based on continuous
rating procedures (max power/efficiency)*125%.
However a 6kW inverter, can peak at 12kW for 5-10 seconds,
doubling the source current. That is no big deal for the wire,
because it is a short time frame... little heat will be generated.
However, in fusing the sub-strings, you need to account for that
peak surge current so you don't blow fuses all the time. But if
you put a 500-1000 amp fuse on a 4/0 wire, above the max surge
draw of the inverter, the wire will be under-protected for its
ampacity rating. Any thoughts on the catch-22?
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
<mailto:RE-wrenches@lists.re-wrenches.org>
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
<http://www.re-wrenches.org/etiquette.htm>
Check out participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org>
CONFIDENTIALITY NOTICE: This e-mail and its attachments are intended
only for the use of the individual or entity who is the intended
recipient and may contain information that is privileged, confidential
and exempt from disclosure or any type of use under applicable law. If
the reader of this e-mail is not the intended recipient, or the
employee, agent, or representative responsible for delivering the
e-mail to the intended recipient, you are hereby notified that any
dissemination, distribution, copying, or other use of this e-mail is
strictly prohibited. If you have received this e-mail in error, please
reply immediately to the sender.
*P*Please think of the environment before printing this email
Sent from Finest Planet WebMail.
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org