This is a fairly complicated issue. I agree that an ungrounded battery system is safer than a grounded one, since the hot wire will not arc to the casing of the enclosure.

If a system has a charge control and an array, the negative wire of the array usually needs to be grounded (or have a fuse in each leg). If there is an MPPT charge control, the voltage will almost certainly be over 50 volts. However, supposedly even a 24 volt system with no MPPT can go over 50 V.

So, in a standard battery system, with a charge control, ground fault protection and an array, the DC system will likely need grounding. If the DC system is grounded, then the battery cables are grounded also. In 250.166 (B) it says the grounding electrode conductor (GEC) shall not be smaller than the largest conductor supplied by the system.

If the battery cables are "supplied by the system" doesn't this imply that the GEC should be the size of the battery cable? This is the logic that has led some inspectors to require a 4/0 copper wire to be bonded to a 1/2" water pipe. This is, of course, technically absurd.

Are a lot of battery based systems now going in with no DC grounding and fuses in both legs? How does a GFP work in this scenario?

The Sunny Island is a different animal, as the DC system in it does not connect to the array. It is AC coupled instead of DC coupled. Therefore, it is connected with AC. The connection to the batteries is isolated. So maybe the issue of DC grounding doesn't apply. The DC system in the Sunny Island will, however, normally operate at over 50 volts, unless the batteries are low.

What is the bottom line here?

At 04:47 PM 4/15/2013, you wrote:
Hi August;

250.162(A) says "operating at greater than 50 v", which a 48 v nominal system operates most of the time at over 50 v, at least when solar charging and/or selling back. We used to get dinged many years ago for using breakers rated at 50v dc on 48 v systems. John Wiles used to insist we use the highest possible voltage (Voc of modules on coldest day) Personally I prefer ungrounded systems, so I'm not saying there's anything wrong from a safety stand point, just that inspectors here don't see it the same way.


R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760On 4/15/2013 2:20 PM, August Goers wrote:
Hi Drake,

The Sunny Island System runs at 48 V nominal so I don't believe 250.162(A) applies. We have some really savvy inspectors in the Bay Area and they were happy for us to be ungrounded since we're operating at 48 V. Yes, the actual voltage might go above 50 V when charging but I believe it is the nominal voltage that the code cares about.

Best,

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to