Are AC coupled systems with no DC loads exempted from the grounding rules of DC coupled, battery based systems and the rules of DC grounding?


This is from the Sunny Island Manual:
"External grounding of the negative pole of the batteries is possible, because the batteries
and the grid side are galvanically isolated within the Sunny Island.
• Dimenssion the cross‑section of the protective conductor sufficiently. Thus you are ensuring that in the event of a fault the high currents occurring can be discharged with
an external grounding.
• If groounding of the negative pole of the battery is necessary, assemble this outside of
the Sunny Island.

As far as I am aware, the NEC code is kind of vague on grounding battery banks (please correct me if I am wrong), it is more of a AHJ requirement.

There is no reference to ground (DC side) inside the SI.

SMA America, LLC
Steve Jefferson
Supervisor, Service Line
6020 West Oaks Blvd, Suite 300
Rocklin, CA 95765 - 3714
U.S.A.
Tel:  +1 916 625 0870
Fax: +1 916 624-2445
Service Line +1 877 697 6283 (Toll Free)
Email: steve.jeffer...@sma-america.com
<http://www.sma-america.com/>www.SMA-America.com

This email and any attachments thereto may contain SMA America, LLC confidential, privileged and private material for the sole use of the intended recipient. Any review, copying, or distribution of this email (or any attachments thereto) by others is strictly prohibited. If you are not the intended recipient, please contact the sender immediately and permanently delete the original and any copies of this email and any attachments thereto. Thank you.

From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of August Goers
Sent: Wednesday, April 10, 2013 2:13 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Fuse sizing in battery circuits

Steve,

So if we wanted to ground the negative would we literally run a ground wire to one of the battery terminals? Is there anything in the NEC that governs this? What are the deciding factors when deciding to ground the negative or not?

As a separate note, I've noticed that the negative battery terminals measure 0 volts to ground on a Sunny Island setup once everything is connected without any extra grounding added. I thought that there must be some reference to ground happening in the Sunny Island but apparently I'm wrong.

Thanks, August

From: <mailto:re-wrenches-boun...@lists.re-wrenches.org>re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Steve Jefferson
Sent: Wednesday, April 10, 2013 9:56 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Fuse sizing in battery circuits

If the Batt negative is not bonded to ground, then yes SMA recommends fusing both Positive and Negative.

Also, the negative is not bonded to ground internally in the Sunny Island.

SMA America, LLC
Steve Jefferson
Supervisor, Service Line
6020 West Oaks Blvd, Suite 300
Rocklin, CA 95765 - 3714
U.S.A.
Tel:  +1 916 625 0870
Fax: +1 916 624-2445
Service Line +1 877 697 6283 (Toll Free)
Email: <mailto:steve.jeffer...@sma-america.com>steve.jeffer...@sma-america.com
www.SMA-America.com

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to