690.9(D) is not applicable to the original discussion because we were talking about an Inverter output circuit, not a PV Source or Output circuit..
690.34 may apply if you call a SolaDeck with breakers a junction box, but I can see that being a stretch in the mind of many. My and Ray's question about the screws on the SolaDeck cover itself requiring a tool to render it accessible is still an issue if the breakers themselves need to be "readily accessible," but that would also apply to a Midnite MNPV, which also has a cover with a screw. Jason Szumlanski > > On 4/28/2014 5:57 PM, Bill Brooks wrote: > > Read 690.9(D) and 690.34. Not sure where this “hysteria—run for the > border” sentiment is coming from. > > > > *690.9(D) Photovoltaic Source and Output Circuits. *Listed PV > > overcurrent devices shall be required to provide overcurrent > > protection in PV source and output circuits. The overcurrent > > devices shall be accessible but shall not be required to > > be readily accessible. > > > > *690.34 Access to Boxes. *Junction, pull, and outlet boxes > > located behind modules or panels shall be so installed that > > the wiring contained in them can be rendered accessible > > directly or by displacement of a module(s) or panel(s) secured > > by removable fasteners and connected by a flexible > > wiring system. > > > > This is not a change. Please help me understand the concern. > > > > Bill Brooks. > > > > > > *From:* re-wrenches-boun...@lists.re-wrenches.org [ > mailto:re-wrenches-boun...@lists.re-wrenches.org<re-wrenches-boun...@lists.re-wrenches.org>] > *On Behalf Of *Ray Walters > *Sent:* Monday, April 28, 2014 2:23 PM > *To:* RE-wrenches > *Subject:* Re: [RE-wrenches] (no subject) > > > > Interesting so does "require a tool" include taking a screw off the cover > plate of the combiner box, too? > What a game changer. I'm going to Mexico for my next project; I'll > actually enjoy even more being the sole AHJ on the project. > > R.Ray Walters > > CTO, Solarray, Inc > > Nabcep Certified PV Installer, > > Licensed Master Electrician > > Solar Design Engineer > > 303 505-8760 > > On 4/28/2014 2:52 PM, Michael Morningstar wrote: > > Readily accessible is now defined in the 2014 NEC. Installing OCPD’s > underneath a module is a major faux paux, and I can’t imagine any AHJ > thinking otherwise. Having to remove a module in order to reset a breaker, > what a drag. > > > > "Capable of being reached quickly for operation, renewal or inspection > without requiring those concerned to use a tool, to climb over, remove > obstacle or other.” > > > > Michael > > > > > > > > > > On Apr 28, 2014, at 10:29 AM, William Miller <will...@millersolar.com> > wrote: > > > > You call it a solar panel, I call it a glass j-box cover plate. > > William > > Miller Solar > > > On Apr 28, 2014, at 9:21 AM, Jason Szumlanski <ja...@fafcosolar.com> > wrote: > > If that is the interpretation, > I don't see how the breakers are "readily accessible" in a SolaDeck > mounted anywhere, regardless of whether it is under a module. It > requires removal of four screws (using a tool) to access the breakers > inside the enclosure. It's all up to the AHJ. It has not been an issue > locally here. I can see how other jurisdictions may not > concur. > > > > _______________________________________________ > List sponsored by Home Power magazine > > List Address: RE-wrenches@lists.re-wrenches.org > > Change email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out participant bios: > www.members.re-wrenches.org > > >
_______________________________________________ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org