Follow up to Bill's point.

For Micros I've installed a disconnect on the roof, but never a breaker or fuse
Why install a breaker?

jay

peltz power
On Apr 29, 2014, at 9:43 AM, Bill Hoffer wrote:

> Dave
> 
> I agree, in the case of microinverters, you already have a main PV System 
> disconnect at the Load Panel to shut down the system that is readily 
> accesible.  I would consider the disconnect on the roof as a supplemental 
> disconnect for the purposes of maintenance by authorized personal that only 
> needs to be accessible.  
> 
> Bill
> 
> 
> On Tue, Apr 29, 2014 at 8:44 AM, Dave Click <davecl...@fsec.ucf.edu> wrote:
> I think 240.24(A)(4) allows the installation of the inverter OCPDs in the 
> SolaDeck hidden under a module.
> 
> 240.24 Location in or on Premises.
> (A) Accessibility. Overcurrent devices shall be readily accessible and shall 
> be installed so that the center of the grip of the operating handle of the 
> switch or circuit breaker, when in its highest position, is not more than 2.0 
> m (6 ft 7 in.) above the floor or working platform, unless one of the 
> following applies:
> ...
> (4) For overcurrent devices adjacent to utilization equipment that they 
> supply, access shall be permitted to be by portable means.
> 
> 
> And if panelboards / fused safety switches are allowed to have screwed-down 
> covers over the OCPDs, I'd think that installing a removable module over 
> these OCPDs would meet NEC. I guess an AHJ could argue that this requires TWO 
> covers be removed, unlike a panelboard or a switch.
> 
> DKC
> 
> 
> On 2014/4/29, 11:15, Jason Szumlanski wrote:
>> 690.9(D) is not applicable to the original discussion because we were 
>> talking about an Inverter output circuit, not a PV Source or Output circuit.
>> 
>> 690.34 may apply if you call a SolaDeck with breakers a junction box, but I 
>> can see that being a stretch in the mind of many. 
>> 
>> My and Ray's question about the screws on the SolaDeck cover itself 
>> requiring a tool to render it accessible is still an issue if the breakers 
>> themselves need to be "readily accessible," but that would also apply to a 
>> Midnite MNPV, which also has a cover with a screw.
>> 
>> 
>> Jason Szumlanski
>> 
>> 
>> On 4/28/2014 5:57 PM, Bill Brooks wrote:
>>> Read 690.9(D) and 690.34. Not sure where this “hysteria—run for the border” 
>>> sentiment is coming from.
>>> 
>>>  
>>> 690.9(D) Photovoltaic Source and Output Circuits. Listed PV
>>> 
>>> overcurrent devices shall be required to provide overcurrent
>>> 
>>> protection in PV source and output circuits. The overcurrent
>>> 
>>> devices shall be accessible but shall not be required to
>>> 
>>> be readily accessible.
>>> 
>>>  
>>> 690.34 Access to Boxes. Junction, pull, and outlet boxes
>>> 
>>> located behind modules or panels shall be so installed that
>>> 
>>> the wiring contained in them can be rendered accessible
>>> 
>>> directly or by displacement of a module(s) or panel(s) secured
>>> 
>>> by removable fasteners and connected by a flexible
>>> 
>>> wiring system.
>>> 
>>>  
>>> This is not a change. Please help me understand the concern.
>>> 
>>>  
>>> Bill Brooks.
>>> 
>>>  
>>>  
>>> From: re-wrenches-boun...@lists.re-wrenches.org 
>>> [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Ray Walters
>>> Sent: Monday, April 28, 2014 2:23 PM
>>> To: RE-wrenches
>>> Subject: Re: [RE-wrenches] (no subject)
>>> 
>>>  
>>> Interesting so does "require a tool" include taking a screw off the cover 
>>> plate of the combiner box, too?
>>> What a game changer.  I'm going to Mexico for my next project; I'll 
>>> actually enjoy even more being the sole AHJ on the project.  
>>> 
>>> R.Ray Walters
>>> CTO, Solarray, Inc
>>> Nabcep Certified PV Installer, 
>>> Licensed Master Electrician
>>> Solar Design Engineer
>>> 303 505-8760
>>> On 4/28/2014 2:52 PM, Michael Morningstar wrote:
>>> 
>>> Readily accessible is now defined in the 2014 NEC. Installing OCPD’s 
>>> underneath a module is a major faux paux, and I can’t imagine any AHJ 
>>> thinking otherwise. Having to remove a module in order to reset a breaker, 
>>> what a drag.
>>> 
>>>  
>>> "Capable of being reached quickly for operation, renewal or inspection 
>>> without requiring those concerned to use a tool, to climb over, remove 
>>> obstacle or other.”
>>> 
>>>  
>>> Michael
>>> 
>>>  
>>>  
>>>  
>>> 
>>> 
>>> 
>>> On Apr 28, 2014, at 10:29 AM, William Miller <will...@millersolar.com> 
>>> wrote:
>>> 
>>> 
>>> 
>>> You call it a solar panel, I call it a glass j-box cover plate. 
>>> 
>>> William
>>> 
>>> Miller Solar
>>> 
>>> 
>>> On Apr 28, 2014, at 9:21 AM, Jason Szumlanski <ja...@fafcosolar.com> wrote:
>>> 
>>> If that is the interpretation,
>>> I don't see how the breakers are "readily accessible" in a SolaDeck
>>> mounted anywhere, regardless of whether it is under a module. It
>>> requires removal of four screws (using a tool) to access the breakers
>>> inside the enclosure. It's all up to the AHJ. It has not been an issue
>>> locally here. I can see how other jurisdictions may not
>>> concur.
>>> 
>> 
>> 
>> _______________________________________________
>> List sponsored by Home Power magazine
>> 
>> List Address: RE-wrenches@lists.re-wrenches.org
>> 
>> Change email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: 
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out participant bios:
>> www.members.re-wrenches.org
>> 
>> 
>> 
>> 
>> 
>> _______________________________________________
>> List sponsored by Home Power magazine
>> 
>> List Address: RE-wrenches@lists.re-wrenches.org
>> 
>> Change email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: 
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out participant bios:
>> www.members.re-wrenches.org
>> 
> 
> 
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 
> 
> 
> 
> 
> -- 
> William Hoffer 
> 161 SE Fourth Ave
> P.O. Box 1823
> White Salmon, WA 98672-1823
> suneng...@gmail.com
> 
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to