There are good reasons to want to put AC combiners under modules, but some reasons not to want to. An AC breaker is far more likely to trip than a DC string fuse, due to the surge availability. As a PV system is designed to last a minimum of 25 years, the installer might not be the one to sort out problems decades down the line.

A strategy I prefer would be to use a SolaDeck as a junction box. Run small wires to a convenient AC combiner location.


At 12:43 PM 4/29/2014, you wrote:
Dave

I agree, in the case of microinverters, you already have a main PV System disconnect at the Load Panel to shut down the system that is readily accesible. I would consider the disconnect on the roof as a supplemental disconnect for the purposes of maintenance by authorized personal that only needs to be accessible.

Bill


On Tue, Apr 29, 2014 at 8:44 AM, Dave Click <<mailto:davecl...@fsec.ucf.edu>davecl...@fsec.ucf.edu> wrote: I think 240.24(A)(4) allows the installation of the inverter OCPDs in the SolaDeck hidden under a module.

240.24 Location in or on Premises.
(A) Accessibility. Overcurrent devices shall be readily accessible and shall be installed so that the center of the grip of the operating handle of the switch or circuit breaker, when in its highest position, is not more than 2.0 m (6 ft 7 in.) above the floor or working platform, unless one of the following applies:
...
(4) For overcurrent devices adjacent to utilization equipment that they supply, access shall be permitted to be by portable means.


And if panelboards / fused safety switches are allowed to have screwed-down covers over the OCPDs, I'd think that installing a removable module over these OCPDs would meet NEC. I guess an AHJ could argue that this requires TWO covers be removed, unlike a panelboard or a switch.

DKC


On 2014/4/29, 11:15, Jason Szumlanski wrote:
690.9(D) is not applicable to the original discussion because we were talking about an Inverter output circuit, not a PV Source or Output circuit.

690.34 may apply if you call a SolaDeck with breakers a junction box, but I can see that being a stretch in the mind of many.

My and Ray's question about the screws on the SolaDeck cover itself requiring a tool to render it accessible is still an issue if the breakers themselves need to be "readily accessible," but that would also apply to a Midnite MNPV, which also has a cover with a screw.


Jason Szumlanski

On 4/28/2014 5:57 PM, Bill Brooks wrote:

Read 690.9(D) and 690.34. Not sure where this “hysteria­run for the border” sentiment is coming from.



690.9(D) Photovoltaic Source and Output Circuits. Listed PV

overcurrent devices shall be required to provide overcurrent

protection in PV source and output circuits. The overcurrent

devices shall be accessible but shall not be required to

be readily accessible.



690.34 Access to Boxes. Junction, pull, and outlet boxes

located behind modules or panels shall be so installed that

the wiring contained in them can be rendered accessible

directly or by displacement of a module(s) or panel(s) secured

by removable fasteners and connected by a flexible

wiring system.



This is not a change. Please help me understand the concern.



Bill Brooks.





From: <mailto:re-wrenches-boun...@lists.re-wrenches.org>re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Ray Walters
Sent: Monday, April 28, 2014 2:23 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] (no subject)



Interesting so does "require a tool" include taking a screw off the cover plate of the combiner box, too? What a game changer. I'm going to Mexico for my next project; I'll actually enjoy even more being the sole AHJ on the project.


R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
<tel:303%20505-8760>303 505-8760
On 4/28/2014 2:52 PM, Michael Morningstar wrote:

Readily accessible is now defined in the 2014 NEC. Installing OCPD’s underneath a module is a major faux paux, and I can’t imagine any AHJ thinking otherwise. Having to remove a module in order to reset a breaker, what a drag.



"Capable of being reached quickly for operation, renewal or inspection without requiring those concerned to use a tool, to climb over, remove obstacle or other.”



Michael









On Apr 28, 2014, at 10:29 AM, William Miller <<mailto:will...@millersolar.com>will...@millersolar.com> wrote:



You call it a solar panel, I call it a glass j-box cover plate.

William

Miller Solar


On Apr 28, 2014, at 9:21 AM, Jason Szumlanski <<mailto:ja...@fafcosolar.com>ja...@fafcosolar.com> wrote:

If that is the interpretation,
I don't see how the breakers are "readily accessible" in a SolaDeck
mounted anywhere, regardless of whether it is under a module. It
requires removal of four screws (using a tool) to access the breakers
inside the enclosure. It's all up to the AHJ. It has not been an issue
locally here. I can see how other jurisdictions may not
concur.


_______________________________________________
List sponsored by Home Power magazine

List Address: <mailto:RE-wrenches@lists.re-wrenches.org>RE-wrenches@lists.re-wrenches.org

Change email address & settings:
<http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches..org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
<http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm

Check out participant bios:
<http://www.members.re-wrenches.org>www.members.re-wrenches.org






_______________________________________________

List sponsored by Home Power magazine


List Address: <mailto:RE-wrenches@lists.re-wrenches.org>RE-wrenches@lists.re-wrenches.org


Change email address & settings:

<http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org


List-Archive: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org


List rules & etiquette:

<http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm


Check out participant bios:

<http://www.members.re-wrenches.org>www.members.re-wrenches.org



_______________________________________________
List sponsored by Home Power magazine

List Address: <mailto:RE-wrenches@lists.re-wrenches.org>RE-wrenches@lists.re-wrenches.org

Change email address & settings:
<http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
<http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm

Check out participant bios:
<http://www.members.re-wrenches.org>www.members.re-wrenches.org





--
William Hoffer
161 SE Fourth Ave
P.O. Box 1823
White Salmon, WA 98672-1823
<mailto:bhof...@sunergyengineeringservices.com>suneng...@gmail.com

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to