I believe that I was told in a 2005-ish Xantrex GT training that their minimum clearance (~30") requirement came from the need to be above lawn sprinklers. I can't remember offhand seeing this reason given in any recent manual, so any bottom clearances required in the manual may apply to you even if you're inside.

On 2014/10/23 0:59, frenergy wrote:
Bob-O, Peter, Garrison,
I appreciate the responses, will proceed accordingly. I have seen some references to minimum distance to floor in some manuals. Thank you,
Bill
Feather River Solar Electric

    ----- Original Message -----
    *From:* Garrison Riegel <mailto:garri...@solarserviceinc.com>
    *To:* 'RE-wrenches' <mailto:re-wrenches@lists.re-wrenches.org>
    *Sent:* Wednesday, October 22, 2014 11:11 AM
    *Subject:* Re: [RE-wrenches] Mounting height

    Bill,

    See 2011 NEC 690.14(D) or 2014 NEC 690.15(A) Utility-Interactive
    Inverters Mounted in Not Readily Accessible Locations. Basically
    there is no maximum height restriction for inverters but there are
    a number of requirements for AC and DC disconnecting means.  See
    NEC 404.8 for maximum disconnect height of 6’ 7”…although
    exception No. 2 may allow the disconnect to be accessible by
    portable means.  I don’t know of any minimum height requirements
    in the code, although most (all?) string and microinverter
    manufacturers specify a required clearance below the inverter.  I
    suppose that would be the minimum.

    Garrison

    Garrison Riegel

    Project Manager | /Solar Service Inc/
    <http://www.solarserviceinc.com/>

    [p] 847-677-0950 | garri...@solarserviceinc.com
    <mailto:garri...@solarserviceinc.com>

    NABCEP Certified PV Installation Professional™

    *From:*RE-wrenches
    [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of
    *frenergy
    *Sent:* Tuesday, October 21, 2014 11:02 PM
    *To:* RE-wrenches
    *Subject:* [RE-wrenches] Mounting height

    Wrenches,

            I can't seem to find a reference to the heights allowable
    for inverter installs, either minimum or maximum (need both).  For
    that matter, AC combiners, DC discos, any switchgear related to
    the inverter(s).

            Any help appreciated.

    Bill

    Feather River Solar Electric

    solar powered since 1982

    ------------------------------------------------------------------------
    _______________________________________________
    List sponsored by Redwood Alliance

    List Address: RE-wrenches@lists.re-wrenches.org

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive:
    http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm

    Check out or update participant bios:
    www.members.re-wrenches.org



_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to