I believe that I was told in a 2005-ish Xantrex GT training that their
minimum clearance (~30") requirement came from the need to be above lawn
sprinklers. I can't remember offhand seeing this reason given in any
recent manual, so any bottom clearances required in the manual may apply
to you even if you're inside.
On 2014/10/23 0:59, frenergy wrote:
Bob-O, Peter, Garrison,
I appreciate the responses, will proceed accordingly. I have
seen some references to minimum distance to floor in some manuals.
Thank you,
Bill
Feather River Solar Electric
----- Original Message -----
*From:* Garrison Riegel <mailto:garri...@solarserviceinc.com>
*To:* 'RE-wrenches' <mailto:re-wrenches@lists.re-wrenches.org>
*Sent:* Wednesday, October 22, 2014 11:11 AM
*Subject:* Re: [RE-wrenches] Mounting height
Bill,
See 2011 NEC 690.14(D) or 2014 NEC 690.15(A) Utility-Interactive
Inverters Mounted in Not Readily Accessible Locations. Basically
there is no maximum height restriction for inverters but there are
a number of requirements for AC and DC disconnecting means. See
NEC 404.8 for maximum disconnect height of 6’ 7”…although
exception No. 2 may allow the disconnect to be accessible by
portable means. I don’t know of any minimum height requirements
in the code, although most (all?) string and microinverter
manufacturers specify a required clearance below the inverter. I
suppose that would be the minimum.
Garrison
Garrison Riegel
Project Manager | /Solar Service Inc/
<http://www.solarserviceinc.com/>
[p] 847-677-0950 | garri...@solarserviceinc.com
<mailto:garri...@solarserviceinc.com>
NABCEP Certified PV Installation Professional™
*From:*RE-wrenches
[mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of
*frenergy
*Sent:* Tuesday, October 21, 2014 11:02 PM
*To:* RE-wrenches
*Subject:* [RE-wrenches] Mounting height
Wrenches,
I can't seem to find a reference to the heights allowable
for inverter installs, either minimum or maximum (need both). For
that matter, AC combiners, DC discos, any switchgear related to
the inverter(s).
Any help appreciated.
Bill
Feather River Solar Electric
solar powered since 1982
------------------------------------------------------------------------
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org