Follow up with Jay,

We thought it might help others to post what we found with Jay's system. This 
was a Magnum MS4024PAE model that is 120/240 split phase input and output. We 
describe this unit as 2-2k units in series inside one unit with a two winding 
transformer basically an autoformer. 

The issue Jay was having was a "Overtemp" fault when charging from generator 
after an hour or so. The first tech suggested turning down the charge rate to 
70% which solved the issue but didn't answer the question of why the unit was 
in "Overtemp". The first suspicion was there was 120v into the inverter which 
will cause the transformer to run on half the windings and overheat at full 
charger output. It is perfectly acceptable to input 120v to the MS-PAE (either 
leg) and it will charge and the output will be 240v but the charge rate should 
be reduced. The voltage measurement to the input terminals was 240v so that 
issue was not suspected anymore. 

What Jay found was one pole of the 240v breaker from the generator was bad. 
What made it hard to troubleshoot and the reason for the post is that the 
MS-PAE will accept 120 or 240 input but always convert to 240 output. When 
measuring the input to a MS-PAE you should remove the wires from the terminal 
block and take the readings on the wires. The sense transformer on the inverter 
input will make the input look like 240v but no current on one leg will 
overheat the transformer. With the wires removed the voltage measurement will 
show there is no 240v available.

Gary

Gary Baxter
Product Manager
Magnum | Dimensions
2211 West Casino Rd.
Everett, WA. 98204
Office 425.353.8833 | Mobile 425.501.0289 | Fax. 425.353.8390

Please Note My New Email Address:

gbax...@sensata.com | www.magnumenergy.com

A Sensata Technologies Business Unit




-----Original Message-----
From: Baxter, Gary 
Sent: Thursday, October 23, 2014 9:50 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] magnum question

Hi Jay,
Sorry you didn't get help. Let me know what you need and I will get you an 
answer.

Gary Baxter
Product Manager
Magnum/Dimensions 

> On Oct 23, 2014, at 9:19 PM, jay peltz <j...@asis.com> wrote:
> 
> HI All,
> 
> Does anyone have a person at Magnum in engineering or higher up than tech 
> support.
> 
> I've got a problem with an inverter that tech support won't or can't help 
> with.
> 
> thanks
> 
> jay
> 
> peltz power
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to