HI Kevin,

I'd start with a new breaker.
I've had them go bad.

jay

peltz power
On Mar 11, 2015, at 2:19 PM, "Kevin Pegg" <kp...@energyalternatives.ca> wrote:

> Hello Wrenches, 
> 
> Customer in remote location has a strange situation come up on an existing 
> system installed (by others) 6 or so years go. Quad stack VFX3648. 
> 
> Last night gen start was triggered by low voltage - a normal system 
> operation. 
> 
> Approx 1h into charge, they lost 1/2 the circuits in house - L2 de-energized. 
> Caretaker went to check power system and noticed the X240 breakers tripped. 
> Tried to reset but it tripped out right away. So he left it as is and called 
> me in the morning. 
> 
> Here's what I've been able to determine today: 
> 
> - The x240 is installed to bridge L1 & L2 on the load side. 
> - with master inverter on, 3 slaves off, both L1 and L2 energized so suggests 
> x240 is working. 
> - within 10 seconds of generator on and charging, x240 breaker trips (and 
> makes L2 go dark). 
> - loads are minor, ~1,000 w of misc lights and such, isn't all loaded up on 
> one leg. 
> 
> Appreciate any thoughts to remedy. I'm not as familiar with this config as 
> others. 
> 
> Kevin Pegg
> EA Energy Alternatives Ltd. 
> 37471 Hwy 16 E
> Telkwa, BC  V0J 2X2
> 250-846-9888
> Http://www.EnergyAlternatives.ca 
> 
> 
> 
> _

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to