Kevin,

        Not to add any confusion but I recently had to re-program the slave in 
a 2 VFX with Xfrmr system as it was doing the same thing...the 2 pole xfrmr 
breaker was tripping when a moderate load was on.  Granted this was not 
happening during charging though.  I think I changed the slave from OB slave L1 
to OB slave L2 and all was good.  It doesn't seem likely the programming in 
your case would have been messed with having been working well for years prior. 
 Curious to hear though of a solution eventually.

Bill

Feather River Solar Electric
4291 Nelson St.
Taylorsville, CA  95983
530.284.7849 / 6544 fax
  ----- Original Message ----- 
  From: Tump 
  To: RE-wrenches 
  Sent: Monday, March 16, 2015 5:39 AM
  Subject: Re: [RE-wrenches] Outback quad stack X240 breaker tripping


  Have you turned the breaker on the t240 to the off position? One does NOT 
have to have that operational for the system to operate correctly.The old t240 
has about the same parasitic draw as an inverter. Isolate, Isolate, Isolate. If 
the system functions correctly w/ the t240 off and the stacking is correct on 
this q stack disconnect it(the t240). Otherwise I would remove the inverter com 
cables and only connect 1 pair of inverters at a time, reset the mate with the 
correct com cables connected to P1& P2. Sometimes something so simple as 
disconnecting & reconnection the mate can have quite a benefit. Again I would, 
if you are really stuck on having the t240 operational, then try it with each 
inverter as a single unit then try the second set of inverters. Disconnect the 
#s1&2 inverters and do the same; connect #s 3&4 P1 & P2, to see exactly which 
component may be your problem.
  You are more then happy to contact me off list if you choose. contact info 
below. Tump

  On Mar 15, 2015, at 5:04 PM, Jerry Shafer wrote:


     Wrenches
    OK if the X240 blows the fuse which is on the output of the inverter while 
the inverter is charging, excessive current must be passing through from one 
inverter and back to the output of another inverter ( a form of AC coupling 
gone bad). The time delay fits as the inverter ramps up, I would look at the 
contactors in each slave as one may be hanging or ther may be a bad board, easy 
way to test is to isolate each inverter and with a amp meter connected at the 
X240 see if current goes away in the X240 as it should not be doing much with 
light loads on the "House" side of the inverters. The X240 is 25 amps while the 
inverters are 50 amps. Sounds like a interesting one to diagnose.

    Jerry



    On Wed, Mar 11, 2015 at 11:59 AM, Chris Worcester 
<ch...@solarwindworks.com> wrote:

      Hi Kevin, 
      I have seen the  X240's  trip off like this when theyare over loaded. 
When this was happening to us the slave inverters had blown AC  boards and some 
times Control and FET boards too. We had a hard time diagnosing this as their  
green lights were on.  Using a clamp on  amp meter on each inverter's AC IN 
conductor while charging with the gen set allowed us to compare their charging 
currents to each other. Typically the ones with blown  AC boards output would 
be close to zero amps. So the X240's were doing double duty and they will smoke 
too if the inverters aren't delta with. 




      Sincerely, 
      Chris Worcester
      530-448-9692 
       Sent from my Galaxy SĀ®III



      -------- Original message --------
      From: Kevin Pegg 
      Date:03/11/2015 1:19 PM (GMT-08:00) 
      To: RE-wrenches 
      Subject: [RE-wrenches] Outback quad stack X240 breaker tripping 


      Hello Wrenches, 

      Customer in remote location has a strange situation come up on an 
existing system installed (by others) 6 or so years go. Quad stack VFX3648. 

      Last night gen start was triggered by low voltage - a normal system 
operation. 

      Approx 1h into charge, they lost 1/2 the circuits in house - L2 
de-energized. Caretaker went to check power system and noticed the X240 
breakers tripped. Tried to reset but it tripped out right away. So he left it 
as is and called me in the morning. 

      Here's what I've been able to determine today: 

      - The x240 is installed to bridge L1 & L2 on the load side. 
      - with master inverter on, 3 slaves off, both L1 and L2 energized so 
suggests x240 is working. 
      - within 10 seconds of generator on and charging, x240 breaker trips (and 
makes L2 go dark). 
      - loads are minor, ~1,000 w of misc lights and such, isn't all loaded up 
on one leg. 

      Appreciate any thoughts to remedy. I'm not as familiar with this config 
as others. 

      Kevin Pegg
      EA Energy Alternatives Ltd. 
      37471 Hwy 16 E
      Telkwa, BC  V0J 2X2
      250-846-9888
      Http://www.EnergyAlternatives.ca 



      _______________________________________________
      List sponsored by Redwood Alliance

      List Address: RE-wrenches@lists.re-wrenches.org

      Change listserver email address & settings:
      http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

      List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

      List rules & etiquette:
      www.re-wrenches.org/etiquette.htm

      Check out or update participant bios:
      www.members.re-wrenches.org



      _______________________________________________
      List sponsored by Redwood Alliance

      List Address: RE-wrenches@lists.re-wrenches.org

      Change listserver email address & settings:
      http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

      List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

      List rules & etiquette:
      www.re-wrenches.org/etiquette.htm

      Check out or update participant bios:
      www.members.re-wrenches.org





    _______________________________________________
    List sponsored by Redwood Alliance

    List Address: RE-wrenches@lists.re-wrenches.org

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm

    Check out or update participant bios:
    www.members.re-wrenches.org




    t...@swnl.net               www.SWNL.net
                    Solarwinds Northernlights       
           Serving Mid Coast Maine & Northern California
                             207-832-7574   Cl. 610-517-8401                    
          
                                  Blair "TUMP" May
                   ********  MAINE'S CHARTER ********
                          NABCEP    "Certified PV Installer" 
       
                  ********  MAINE'S CHARTER ********
                      Trace Xantrex "Certified" Dealer / Installer"









------------------------------------------------------------------------------


  _______________________________________________
  List sponsored by Redwood Alliance

  List Address: RE-wrenches@lists.re-wrenches.org

  Change listserver email address & settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

  List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

  List rules & etiquette:
  www.re-wrenches.org/etiquette.htm

  Check out or update participant bios:
  www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to