William and Wrenches, 

I have pondered situations like this one and wonder the following: If a high 
voltage DC solenoid were placed at the PV array and the coil was controlled by 
an arc fault detector along with a means of manually disconnecting, would that 
not work to satisfy shut down requirements and safety concerns? 

We have been using 350A, 800 volt solenoids from Gigavac in our lithium battery 
system on both the positive and negative terminals (controlled by a CPU) to 
provide 100% disconnect if case of any battery fault. 

Larry



On Sep 23, 2015, at 2:26 PM, William Miller <will...@millersolar.com> wrote:

Dear Fellow Wrenches
 
Below is a design conundrum that may resonate with some of you:
 
We are finalizing a design for an off-grid residential system.  The customer 
insist the PV should be on the roof and pre-installed a 1-1/4” PVC conduit from 
his roof to a crawl space, in anticipation of a solar install.  This created 
real problems, because we all know we can’t pull PV source or output circuits 
in (or now, on)  the envelopes of habitable buildings.
 
There was no practical way to replace the PVC.  We contrived a method to sleeve 
¾” liquid-tight through the 1-1/4” PVC to the crawl space, continuing on with 
EMT.  This is the largest metallic conduit we could fit.  The distance was 
greater than 10 feet so we couldn’t use EMT.  Due to the conduit size 
restriction, we upgraded to Morningstar 600 volt charge controllers, allowing 
us to reduce conductor size.
 
(As a sidebar, although the Morningstar is listed as a 600 volt charge 
controller, we have found no circumstance were we could take advantage of that 
high a voltage.  With the currently available high wattage modules, by the time 
we added enough in series to get to 600 volts, we were well beyond the wattage 
capabilities of the controller.  For sake of design considerations, I suggest 
one regard these units as ~300 volt charge controllers.)
 
We now have plans for 300 volt PV feeders running down an interior wall and 
under the house, with no roof-top disconnecting means.  It is my understanding 
none are required.  I am not comfortable with this.  In this scenario, there is 
no safe way to replace either of the two Morningstar controllers. Should 
someone drill through or damage the EMT in the wall or under the floor, there 
would be no way to turn off the feeder.
 
I don’t like putting HU361RBs on a roof.  They must remain vertical and so they 
stick up too high and are hard to provide mounting for.  Sola-deck units are 
another option, but they require integrating with shingles, not practical on 
this job or many others.  I finally settled on a DC-Sunvolt PV-X16A-4X-RG 
disconnect as a possible solution.  At $216 it is not out of range.  The unit 
will provide means to turn off the feeders for service.  I will report back on 
my impressions of the unit.
 
To distill this scenario, I don’t believe the code requires a disconnect, but I 
feel morally obligated to install one.  I’d be interested in verification of 
the code interpretation and others response to similar situations.
 
I found no other options for rooftop disconnecting means that would be small, 
reasonably priced and not present a high profile.  If there are products I 
don’t know about, I would be most grateful to receive your input.
 
While researching the hardware I stumbled upon this article, linked below.  It 
seems to present a real dilemma, but I am not convinced.  Please remain 
skeptical as you read.  It appears all of the links direct you to the same 
source.
 
https://www.linkedin.com/pulse/greatest-debacle-solar-pv-australias-rooftop-dc-isolator-lucas-sadler
 
<https://www.linkedin.com/pulse/greatest-debacle-solar-pv-australias-rooftop-dc-isolator-lucas-sadler>
 
Thanks again to all of you for helpful advice and expertise.  I learned about 
Sunvolt here, just one of many great suggestions.
 
Sincerely,
 
William Miller
 
 
<image002.jpg>
Lic 773985
millersolar.com <http://www.millersolar.com/>
805-438-5600



_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to