Gary, I have just two methods I use to test all batteries. I do a voltage check of each battery under load with solar input shut off. You will quickly find a battery with a bad cell or two. It is best to do this test when the batteries are already somewhat discharged to see clearer results. When under charge, and even floating or with a light load, a battery with bad cells can look OK in the voltage check. Bad cells can show up as down about 1.5 to 2 volts for each bad cell from normal. I have also seen batteries that not only dropped in voltage but actually changed polarity. Had a 6volt L16 read -2 VDC. That dropped the string by 8 volts!!! Typically bad cell problems will show up after some discharge and if a single string, the string voltage suddenly drops down. In parallel strings the numbers get really random but other batteries in same string will rise high to compensate for the low battery. I have seen a 6 volt go to +9 volts and was boiling violently. (hence why multiple strings are not the best design). If the above checks are OK, batteries still appearing to be weak have reached the twilight of their lives and a plan is needed to retire them. $$$$ 9 years seems about right from my experience to see serious decline in output.
The other quick test for parallel string batteries is to use the DC clamp meter to check each string as being roughly equal in current under load or under full charge rate. This will find bad cells, different aged batteries, and /or bad connections. When you lose a string, that will definitely reduce the coasting time. I don't check specific gravity for two reasons. It is time consuming and moving acid around is not good in my book. I have found individual batteries with low specific gravity readings that went on to work OK for many years, If the batteries pass my voltage and current checks, I call them good to go. John Blittersdorf Solar Guru Rob Stubbins Solar (division of Rob Stubbins Electrical and General Contractors) 280 Quality Lane Rutland, VT 05701 802-775-1484 ext 512 On Thu, Sep 1, 2016 at 8:51 AM, Gary Bassett <g...@hudsonsolar.com> wrote: > We have a grid tied battery backup system that uses 8 Sun Xtender > PVX-2120L batteries, about 9 years old. The grid has been going out > frequently – about 4 times in the past 3 weeks. When the grid goes out, the > battery voltage gets too low and shuts the system down pretty quickly. One > of the times, this happened within 4 hours. We want to test the capacity of > the batteries and we have a testing procedure from Concorde that seems like > it would take a lot of time. Is there a quick way to test the battery > capacity? > > > > Gary > > > > > > _______________________________________________ > List sponsored by Redwood Alliance > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches. > org/maillist.html > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > www.members.re-wrenches.org > > >
_______________________________________________ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org