HI Hugh,

Interesting problem your describe which I've not seen before.

I’m curious about your comments on Outback.  
I’ve found them to be quite programable in regards to disconnecting from a 
generator.  
You can set voltage and cycles. Default comes in at 60 cycles which is 1 second 
and way too long.  
Setting it down to around 10 cycles  works with every generator I’ve tried, and 
from my measurements the inverter seems to be switching on cycles, not voltage.
But maybe I misunderstood what you were saying?

But I know in the old days before inverters got so programable ( or poorly 
programed in the case of the new SW) that out here on the west coast we 
installed a contactor which was controlled via either AGS or manual remote 
start.  It shuts the AC off in a hard way yes, and you sure might get a light 
flicker but you don’t get the voltage/Hz sag being a problem here.

And I’m not sure but seems to me that some of the older generators used to come 
with an internal contactor that did this?
But none that I’m seeing now do. 
Maybe others can comment on that.

And finally I’m curious about how important the cool down period is.  
How I set my generator run times, by the time its told to shut down its not 
running all that hard, which shouldn’t be a problem.
But again, I’ll defer to the genny experts here.

Happy new year 

jay







> On Dec 30, 2016, at 1:13 AM, Hugh Piggott <h...@scoraigwind.co.uk> wrote:
> 
> hi Lou,
> 
> I don’t wish to contradict this version of events but if true then it will 
> make the inverter unsuitable for most generators.  Here is another scenario I 
> have seen a few times that looks similar but can be fixed.
> 
> The inverter charges the battery etc. and decides to turn off the generator.  
> It disconnects.  It may or may not have its own “cool down” time for the 
> generator.  It then tells the generator to stop.  At this point the generator 
> control circuit may decide to run a further cool down period.  Meantime 
> incoming AC voltage is still visible to the inverter.  The inverter may then 
> decide that it is obliged to connect to this running generator.  After any 
> chosen “warm up period” it may go ahead and synch with the running generator 
> and start to draw power just before and during the point where fuel is shut 
> off and it dies.  This causes power quality problems and errors in some 
> inverters.  Maybe better firmware could fix this.  Victron inverters are 
> designed to disconnect on a falling voltage every time, and they do so 
> gracefully.  With SMA inverters and Outbacks it’s better avoided.
> 
> The best fix for this is to make sure that the generator does not have its 
> own cool down period.  If you can access and edit this parameter in the 
> generator this is best.  Another fix is to set a longer warmup time in the 
> inverter software but this can cause issues where the generator is being 
> started to meet a high load.  In the case of an SMA inverter you can get a 
> fix to it using “genman mode”.
> 
> I just wonder if you have witnessed the process and checked whether the 
> generator’s own built-in cool down period could be the cause.
> 
> cheers
> Hugh
> 
>> On 30 Dec 2016, at 00:43, Lou Russo <l...@spreesolarsystems.com 
>> <mailto:l...@spreesolarsystems.com>> wrote:
>> 
>> Thanks to all for the input and suggestions, it is much appreciated. Just to 
>> be clear about the situation, the inverter has already made the AC transfer, 
>> which goes smoothly. The AC IN light is off. At this point the generator is 
>> unloaded and there is no battery charging happening. The inverter is 
>> carrying the loads.  From what Schnieder tells me is that the software is 
>> telling the inverter to follow the Hertz of the generator until it's below 
>> 40 Hertz. 
>> 
>> I do believe that manual start is best as it keeps the user in tune with 
>> system. It is what I do at my own home. Unfortunately most clients want the 
>> autostart and don't want to think about it. This is typically not deal 
>> breaker for me and I will push a client only so far on it. In this 
>> particular situation the system is 500 ft away from the home. So the 
>> autostart is mandatory. 
>> 
>> 
> 
> _________

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to