Jay I too find this firmware issue questionable. there IS settings on this AGS 
& Inverter for disconnect using voltage AND or  hz.  Again voltage 110/55Hz is 
what I will usually start out with.These additional settings; cool down time 
and spin down time, I set to the lowest setting possible. This being said….. I 
would not be a bit surprised that some bonehead code writer had NO idea what Hz 
was when and IF he set this to 40 Hz.  Happy new year to all! TUMP
> On Dec 31, 2016, at 12:39 PM, jay <jay.pe...@gmail.com> wrote:
> 
> HI Hugh,
> 
> Interesting problem your describe which I've not seen before.
> 
> I’m curious about your comments on Outback.  
> I’ve found them to be quite programable in regards to disconnecting from a 
> generator.  
> You can set voltage and cycles. Default comes in at 60 cycles which is 1 
> second and way too long.  
> Setting it down to around 10 cycles  works with every generator I’ve tried, 
> and from my measurements the inverter seems to be switching on cycles, not 
> voltage.
> But maybe I misunderstood what you were saying?
> 
> But I know in the old days before inverters got so programable ( or poorly 
> programed in the case of the new SW) that out here on the west coast we 
> installed a contactor which was controlled via either AGS or manual remote 
> start.  It shuts the AC off in a hard way yes, and you sure might get a light 
> flicker but you don’t get the voltage/Hz sag being a problem here.
> 
> And I’m not sure but seems to me that some of the older generators used to 
> come with an internal contactor that did this?
> But none that I’m seeing now do. 
> Maybe others can comment on that.
> 
> And finally I’m curious about how important the cool down period is.  
> How I set my generator run times, by the time its told to shut down its not 
> running all that hard, which shouldn’t be a problem.
> But again, I’ll defer to the genny experts here.
> 
> Happy new year 
> 
> jay
> 
> 
> 
> 
> 
> 
> 
>> On Dec 30, 2016, at 1:13 AM, Hugh Piggott <h...@scoraigwind.co.uk 
>> <mailto:h...@scoraigwind.co.uk>> wrote:
>> 
>> hi Lou,
>> 
>> I don’t wish to contradict this version of events but if true then it will 
>> make the inverter unsuitable for most generators.  Here is another scenario 
>> I have seen a few times that looks similar but can be fixed.
>> 
>> The inverter charges the battery etc. and decides to turn off the generator. 
>>  It disconnects.  It may or may not have its own “cool down” time for the 
>> generator.  It then tells the generator to stop.  At this point the 
>> generator control circuit may decide to run a further cool down period.  
>> Meantime incoming AC voltage is still visible to the inverter.  The inverter 
>> may then decide that it is obliged to connect to this running generator.  
>> After any chosen “warm up period” it may go ahead and synch with the running 
>> generator and start to draw power just before and during the point where 
>> fuel is shut off and it dies.  This causes power quality problems and errors 
>> in some inverters.  Maybe better firmware could fix this.  Victron inverters 
>> are designed to disconnect on a falling voltage every time, and they do so 
>> gracefully.  With SMA inverters and Outbacks it’s better avoided.
>> 
>> The best fix for this is to make sure that the generator does not have its 
>> own cool down period.  If you can access and edit this parameter in the 
>> generator this is best.  Another fix is to set a longer warmup time in the 
>> inverter software but this can cause issues where the generator is being 
>> started to meet a high load.  In the case of an SMA inverter you can get a 
>> fix to it using “genman mode”.
>> 
>> I just wonder if you have witnessed the process and checked whether the 
>> generator’s own built-in cool down period could be the cause.
>> 
>> cheers
>> Hugh
>> 
>>> On 30 Dec 2016, at 00:43, Lou Russo <l...@spreesolarsystems.com 
>>> <mailto:l...@spreesolarsystems.com>> wrote:
>>> 
>>> Thanks to all for the input and suggestions, it is much appreciated. Just 
>>> to be clear about the situation, the inverter has already made the AC 
>>> transfer, which goes smoothly. The AC IN light is off. At this point the 
>>> generator is unloaded and there is no battery charging happening. The 
>>> inverter is carrying the loads.  From what Schnieder tells me is that the 
>>> software is telling the inverter to follow the Hertz of the generator until 
>>> it's below 40 Hertz. 
>>> 
>>> I do believe that manual start is best as it keeps the user in tune with 
>>> system. It is what I do at my own home. Unfortunately most clients want the 
>>> autostart and don't want to think about it. This is typically not deal 
>>> breaker for me and I will push a client only so far on it. In this 
>>> particular situation the system is 500 ft away from the home. So the 
>>> autostart is mandatory. 
>>> 
>>> 
>> 
>> _________
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 

> t...@swnl.net 
> <blocked::mailto:t...@swnl.net%22%20%5Co%20%22blocked::mailto:t...@swnl.net>  
>              www.SWNL.net 
> <blocked::http://www.swnl.net/%22%20%5Co%20%22blocked::http://www.swnl.net/>
>                 Solarwinds Northernlights       
>        Serving Mid Coast Maine & Northern California
>                          207-832-7574   Cl. 610-517-8401                      
>         
>                               Blair "TUMP" May
>                ********  MAINE'S CHARTER ********
>                       NABCEP    "Certified PV Installer" 
>    
>               ********  MAINE'S CHARTER ********
>                   Trace Xantrex "Certified" Dealer / Installer"
> 


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings: