To elaborate a bit on Ray's accurate suggestion with a bit of history... in the early days the general consensus developed that for general use, 36 cells (given that one cell produces just shy of 1/2 volt, regardless of cell size) was the standard cell count for battery charging. This was based on the understanding that a typical Vmp of 17.1-17.6 for a 36 cell module was necessary to equalize a 12V FLA battery to ~15.5 VDC in hot ambient daytime temperatures after all system losses due to various resistance in wire, connections, controllers, etc., were accounted for. You'll occasionally see early modules with 35, 33, 32 and even 30 cells, tried as "self-regulating" modules - didn't work, as it couldn't account for voltage variations due to temperature. Anyway, 36 cells is the default standard to charge a 12V battery. Extrapolating from this, there's a direct correlation between cell count and voltage in most applications: as 36 cells > 12Vnom, 72 cells > 24V and 60 cells > 20Vnom. Go outside of these rules of thumb only with clear understanding of these limitations.

Three 60 cell modules is a nominal 80V; ideal for a 48 Vnom battery bank, while still below the 150V limit of many standard controllers in record cold temperatures. Three 72 cell modules, or 72 Vnom, is on the ragged edge of voltage compliance in cold winter climates.

Allan

On 9/12/2018 10:30 AM, Ray wrote:

A 2nd option: A pair of 72 cell modules should be enough.

Ray Walters
Remote Solar
303 505-8760
On 9/12/18 9:21 AM, Mac Lewis wrote:
Hi Bill,

I agree with Allen. We get similar peak temps here and two 60 cell modules doesn't charge a 48V battery bank adequately. This effect would become worse over time with voltage degradation. I try to be at least 15% above highest expected battery voltage with Vmp of the strings. With 150V input limit on the Outback controllers, that leaves you with only one option, strings of 3, with our low temps.

On Tue, Sep 11, 2018, 4:24 PM Sindelar Solar <al...@sindelarsolar.com <mailto:al...@sindelarsolar.com>> wrote:

    Bill, I wouldn't, especially with FLAs. I have seen this
    situation here, where the summer highs are similar, with a few
    homeowner/hack installations and no, 60-cell modules will not
    finish the charge in hot weather. Strings of three work just
    about perfect with modern charge controllers, especially in
    winter, as they range high enough but well below 150VDC limits.

    Allan

    On 9/11/2018 4:04 PM, Bill Battagin wrote:

    I've been on hold with OB for about 40 minutes now and I need to
    know if 2 SW PVs with a Voc of 39.9 and a Vmpp of 31.3 will do
    an effective job of charging a 48 volt LA battery especially
    with temps of 95 degrees.  Anybody have experience with this or
    similar,  Appreciate the feedback.  It just seems I'm a little
    low in Vmpp if I want to equalize when its hot.  Will it be even
    more questionable in 10 years as PVs age?

    OB did just pickup only to tell me I need Java for the string
    sizing tool and he can't help me with this configuration.

    Bill

--

    *Allan Sindelar*
    al...@sindelarsolar.com <mailto:al...@sindelarsolar.com>
    NABCEP Certified PV Installation Professional
    New Mexico EE98J Journeyman Electrician
    Founder (Retired), Positive Energy, Inc.
    *505 780-2738 cell*

    _______________________________________________
    List sponsored by Redwood Alliance

    List Address: RE-wrenches@lists.re-wrenches.org
    <mailto:RE-wrenches@lists.re-wrenches.org>

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive:
    http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out or update participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org>



_______________________________________________
List sponsored by Redwood Alliance

List Address:RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

--

*Allan Sindelar*
al...@sindelarsolar.com <mailto:al...@sindelarsolar.com>
NABCEP Certified PV Installation Professional
New Mexico EE98J Journeyman Electrician
Founder (Retired), Positive Energy, Inc.
*505 780-2738 cell*

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to