Jason,

This isn’t an AC coupled system is it? There is a very common issue that can 
occur when you AC couple XWs on lithium batteries.

If this is AC coupled, I’ll go into more detail on what I think your problem 
might be. Also, let us know if you got it fixed.

Thanks,
Kienan
maxfieldso...@hotmail.com<mailto:maxfieldso...@hotmail.com>
(801) 631-5584



On Mar 27, 2019, at 9:42 AM, Sandra Herrera 
<sandra.herr...@se.com<mailto:sandra.herr...@se.com>> wrote:

Jason,

Lets connect off-list direct email, I will need to send you a file.

Also, this can only be done using the Cofig Tool.

sandra.herr...@se.com<mailto:sandra.herr...@se.com>

From: RE-wrenches 
<re-wrenches-boun...@lists.re-wrenches.org<mailto:re-wrenches-boun...@lists.re-wrenches.org>>
 On Behalf Of Jason Szumlanski
Sent: Wednesday, March 27, 2019 8:32 AM
To: RE-wrenches 
<re-wrenches@lists.re-wrenches.org<mailto:re-wrenches@lists.re-wrenches.org>>
Subject: Re: [RE-wrenches] Xantrex XW6048 (quad) blowing past setpoints


[External email: Use caution with links and attachments]

________________________________


[https://mailtrack.io/trace/mail/72c426fd7ef4b53eb1e42228450b27719ee791db.png?u=1613865]
I can't even get 1 hour of charging. The voltage rises too quickly and the 
battery management systems disconnect the battery.

What is the calibration process?

I still plan to disable the chargers that are reporting the wrong (lower) 
voltage and see if the others (individually) still ignore the setpoints. It's a 
very remote location, so diagnostics are extremely difficult.





On Tue, Mar 26, 2019 at 9:00 AM Sandra Herrera 
<sandra.herr...@se.com<mailto:sandra.herr...@se.com>> wrote:
Jason,

The Battery daily summary from the ComBox is information on one day at a time, 
this is not part of the logs, and it should be available even if you have 1 
hour or charging.

However, based on your discovery of different DC voltages from the inverter, my 
recommendation is to calibrate them.

Sandra


From: RE-wrenches 
<re-wrenches-boun...@lists.re-wrenches.org<mailto:re-wrenches-boun...@lists.re-wrenches.org>>
 On Behalf Of Jason Szumlanski
Sent: Monday, March 25, 2019 4:18 PM
To: RE-wrenches 
<re-wrenches@lists.re-wrenches.org<mailto:re-wrenches@lists.re-wrenches.org>>
Subject: Re: [RE-wrenches] Xantrex XW6048 (quad) blowing past setpoints


[External email: Use caution with links and attachments]

________________________________


[X]
This is a newly commissioned Lithionic LiPo battery on an old system that has 
been out of commission for over a year. 51V nominal battery. Logs are not 
possible. This happens within minutes of bulk charging initiation. There is no 
spike. It's a steady rise.

Jason





On Mon, Mar 25, 2019 at 4:41 PM Sandra Herrera 
<sandra.herr...@se.com<mailto:sandra.herr...@se.com>> wrote:
Jason,

Can you share the Battery Daily Summary from the ComBox? Only select the 
battery voltage so it is easier to see where the 0.8V jump is occurring.

Also, what battery are you using?

Thanks

Sandra Herrera

From: RE-wrenches 
<re-wrenches-boun...@lists.re-wrenches.org<mailto:re-wrenches-boun...@lists.re-wrenches.org>>
 On Behalf Of Jason Szumlanski
Sent: Monday, March 25, 2019 1:36 PM
To: RE-wrenches 
<re-wrenches@lists.re-wrenches.org<mailto:re-wrenches@lists.re-wrenches.org>>
Subject: [RE-wrenches] Xantrex XW6048 (quad) blowing past setpoints


[External email: Use caution with links and attachments]

________________________________


I have four inverter/chargers (master and 3 slaves) that are blowing past their 
57.6V setpoint that I programmed and confirmed via the Context Combox. They are 
hitting 58.4V and tripping the battery management units on a set of Lithium 
Batts. Any ideas why this would happen? I can disable chargers on individual 
units, so I know the settings are getting uploaded via the Combox.

Jason Szumlanski

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
_______________________________________________
List sponsored by Redwood Alliance

List Address: 
RE-wrenches@lists.re-wrenches.org<mailto:RE-wrenches@lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fmailtrack.io%2Ftrace%2Flink%2F18cba8599d23d6d99bcbe44f3ec46d60f0c4d90e%3Furl%3Dhttps%253A%252F%252Feur02.safelinks.protection.outlook.com%252F%253Furl%253Dhttps%25253A%25252F%25252Fmailtrack.io%25252Ftrace%25252Flink%25252F8d9e12ac10c579b7810fd6e15594017b4395543d%25253Furl%25253Dhttp%2525253A%2525252F%2525252Flists.re-wrenches.org%2525252Foptions.cgi%2525252Fre-wrenches-re-wrenches.org%252526userId%25253D1613865%252526signature%25253Dff64cebca7b2a8fe%2526data%253D02%25257C01%25257Csandra.herrera%252540se.com%25257C29357b33ca254f5c0b0508d6b1781e9c%25257C6e51e1adc54b4b39b5980ffe9ae68fef%25257C0%25257C0%25257C636891526800151601%2526sdata%253Dej4W%25252FA0RbNrDhRy5Y%25252FU4rx6NEPf87CEOBUTInVUMfq4%25253D%2526reserved%253D0%26userId%3D1613865%26signature%3Db1ee2a5091a592df&data=02%7C01%7Csandra.herrera%40se.com%7C090af5434b7c4c0bd91a08d6b2c97154%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C636892975595675889&sdata=VZgn%2BYgLWYwy8tNVgSfqpri7OidwjWTVl8CyxTni7f4%3D&reserved=0>

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fmailtrack.io%2Ftrace%2Flink%2Fe28e6a185e7da9eaa3d1dc625605218dc2cc373d%3Furl%3Dhttp%253A%252F%252Fwww.mail-archive.com%252Fre-wrenches%2540lists.re-wrenches.org%252Fmaillist.html%26userId%3D1613865%26signature%3D0b2c152acef4d3a8&data=02%7C01%7Csandra.herrera%40se.com%7C090af5434b7c4c0bd91a08d6b2c97154%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C636892975595685894&sdata=3X3itC8zZ3hT1ziCwU%2FqVIgsb149C4N5QUYI2bFqEyk%3D&reserved=0>

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fmailtrack.io%2Ftrace%2Flink%2F7a33632c4c87da9837c960e385230c617a913cb8%3Furl%3Dhttps%253A%252F%252Feur02.safelinks.protection.outlook.com%252F%253Furl%253Dhttps%25253A%25252F%25252Fmailtrack.io%25252Ftrace%25252Flink%25252F58c2621c30bb36ba8f1b7bc660c2029c0d7b170d%25253Furl%25253Dhttp%2525253A%2525252F%2525252Fwww.re-wrenches.org%2525252Fetiquette.htm%252526userId%25253D1613865%252526signature%25253D43f1391ecbe9e76f%2526data%253D02%25257C01%25257Csandra.herrera%252540se.com%25257C29357b33ca254f5c0b0508d6b1781e9c%25257C6e51e1adc54b4b39b5980ffe9ae68fef%25257C0%25257C0%25257C636891526800161610%2526sdata%253DiymCQe2Js%25252BbEuTPZxj3qtQX%25252FuIFDsiF0AabIXSIsh0k%25253D%2526reserved%253D0%26userId%3D1613865%26signature%3D62e3763c879d975f&data=02%7C01%7Csandra.herrera%40se.com%7C090af5434b7c4c0bd91a08d6b2c97154%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C636892975595695903&sdata=s0rqr7uz7fna2QYgshZM7f3g5uEXbQ2OWKGhrbdhASI%3D&reserved=0>

Check out or update participant bios:
www.members.re-wrenches.org<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fmailtrack.io%2Ftrace%2Flink%2F5e5882bdb74c6623d91159977445cccc4f582319%3Furl%3Dhttps%253A%252F%252Feur02.safelinks.protection.outlook.com%252F%253Furl%253Dhttps%25253A%25252F%25252Fmailtrack.io%25252Ftrace%25252Flink%25252F9bc2e78bed9b8b94e220a1d9572411cd56c6863b%25253Furl%25253Dhttp%2525253A%2525252F%2525252Fwww.members.re-wrenches.org%252526userId%25253D1613865%252526signature%25253D9e6fdef31370bf88%2526data%253D02%25257C01%25257Csandra.herrera%252540se.com%25257C29357b33ca254f5c0b0508d6b1781e9c%25257C6e51e1adc54b4b39b5980ffe9ae68fef%25257C0%25257C0%25257C636891526800171614%2526sdata%253D4W%25252Ft2RLvs9Uwv2dfgyjW%25252BzAC%25252BtWUX7HoN9BNAvMv3wA%25253D%2526reserved%253D0%26userId%3D1613865%26signature%3Da11ac01d03fd1498&data=02%7C01%7Csandra.herrera%40se.com%7C090af5434b7c4c0bd91a08d6b2c97154%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C636892975595695903&sdata=QlHASRXR69AVP542BIYea1B0mJ%2Be9H1pWNKBdyd5gvM%3D&reserved=0>

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
_______________________________________________
List sponsored by Redwood Alliance

List Address: 
RE-wrenches@lists.re-wrenches.org<mailto:RE-wrenches@lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fmailtrack.io%2Ftrace%2Flink%2F472d17d9be91574dff6d989a837c993215540b7c%3Furl%3Dhttp%253A%252F%252Flists.re-wrenches.org%252Foptions.cgi%252Fre-wrenches-re-wrenches.org%26userId%3D1613865%26signature%3D1ff79895c955d6d1&data=02%7C01%7Csandra.herrera%40se.com%7C090af5434b7c4c0bd91a08d6b2c97154%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C636892975595705917&sdata=7KZZSUXAlGw%2FWXKB5McplMwYlqp9G7anFf3MnHCSCDU%3D&reserved=0>

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fmailtrack.io%2Ftrace%2Flink%2F62e382fbba22bd0322ed491c70013122b32ac337%3Furl%3Dhttp%253A%252F%252Fwww.mail-archive.com%252Fre-wrenches%2540lists.re-wrenches.org%252Fmaillist.html%26userId%3D1613865%26signature%3D459f1c55a0251f6b&data=02%7C01%7Csandra.herrera%40se.com%7C090af5434b7c4c0bd91a08d6b2c97154%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C636892975595715918&sdata=HFPYSGtnqmI4WJDKqpLTTFJTTPTXXvKVbPhK4DtaU7A%3D&reserved=0>

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fmailtrack.io%2Ftrace%2Flink%2F6ccc977170ec9afe7ae227149fe1b7e48fcad269%3Furl%3Dhttp%253A%252F%252Fwww.re-wrenches.org%252Fetiquette.htm%26userId%3D1613865%26signature%3D97660bec94e18d53&data=02%7C01%7Csandra.herrera%40se.com%7C090af5434b7c4c0bd91a08d6b2c97154%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C636892975595715918&sdata=GRpNhIC6OIVxOkt2J3fA4PULlAuO0CHVLwWfv6QkxIo%3D&reserved=0>

Check out or update participant bios:
www.members.re-wrenches.org<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fmailtrack.io%2Ftrace%2Flink%2F73257c2326046c73eafa7a859ff008b50d628ba7%3Furl%3Dhttp%253A%252F%252Fwww.members.re-wrenches.org%26userId%3D1613865%26signature%3D505b9f731c70e5e6&data=02%7C01%7Csandra.herrera%40se.com%7C090af5434b7c4c0bd91a08d6b2c97154%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C636892975595725923&sdata=Dd2hHbwJAtEDIzBWNGLjYIddAOB2QL7%2BP4xZc%2Flr%2FZ0%3D&reserved=0>

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
_______________________________________________
List sponsored by Redwood Alliance

List Address: 
RE-wrenches@lists.re-wrenches.org<mailto:RE-wrenches@lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to