Thanks, Steve. Parallel operation might be tricky, but I'm sure they have
dealt with this before. I'll check it out.






On Tue, Apr 21, 2020 at 12:45 PM Steve Higgins <st...@surrette.com> wrote:

> Try these guys... Heard Good things.   Not sure how they would work with 4
> in parallel on the same battery bank.
>
> https://quickcharge.com/selct-a-charge-stationary-chargers.html
> <https://mailtrack.io/trace/link/751f313d73ae8c2a19e74ca521cc26c5954fca82?url=https%3A%2F%2Fquickcharge.com%2Fselct-a-charge-stationary-chargers.html&userId=1613865&signature=be80402a587b780f>
>
>
>
>
> <https://mailtrack.io/trace/link/9d59a4c0f4555dc844ecd9c32c427527efad410b?url=http%3A%2F%2Fwww.rollsbattery.com&userId=1613865&signature=28a0634d1190ead5>
> <https://mailtrack.io/trace/link/9d59a4c0f4555dc844ecd9c32c427527efad410b?url=http%3A%2F%2Fwww.rollsbattery.com&userId=1613865&signature=28a0634d1190ead5>
> <https://mailtrack.io/trace/link/9d59a4c0f4555dc844ecd9c32c427527efad410b?url=http%3A%2F%2Fwww.rollsbattery.com&userId=1613865&signature=28a0634d1190ead5>
> <https://mailtrack.io/trace/link/311c611dcf82a7ccde1f887b33e25cc8cf390717?url=http%3A%2F%2Fwww.rollsbattery.com&userId=1613865&signature=65a80bae1bf676eb>
> <https://mailtrack.io/trace/link/311c611dcf82a7ccde1f887b33e25cc8cf390717?url=http%3A%2F%2Fwww.rollsbattery.com&userId=1613865&signature=65a80bae1bf676eb>
> <https://mailtrack.io/trace/link/572cb12db148382620b80edca516e57a5e4f8747?url=http%3A%2F%2Fwww.rollsbattery.com&userId=1613865&signature=0001dea60b254627>
> <https://mailtrack.io/trace/link/572cb12db148382620b80edca516e57a5e4f8747?url=http%3A%2F%2Fwww.rollsbattery.com&userId=1613865&signature=0001dea60b254627>
> <https://mailtrack.io/trace/link/572cb12db148382620b80edca516e57a5e4f8747?url=http%3A%2F%2Fwww.rollsbattery.com&userId=1613865&signature=0001dea60b254627>
> <https://mailtrack.io/trace/link/06c6215df3394febbd1620384b5205ccca740b82?url=http%3A%2F%2Fwww.rollsbattery.com&userId=1613865&signature=6a278595e1af9721>
> <https://mailtrack.io/trace/link/06c6215df3394febbd1620384b5205ccca740b82?url=http%3A%2F%2Fwww.rollsbattery.com&userId=1613865&signature=6a278595e1af9721>
> <https://mailtrack.io/trace/link/06c6215df3394febbd1620384b5205ccca740b82?url=http%3A%2F%2Fwww.rollsbattery.com&userId=1613865&signature=6a278595e1af9721>
> <https://mailtrack.io/trace/link/ff87973987b1bf4c9dea04dd61358f884c7772f7?url=http%3A%2F%2Fwww.rollsbattery.com&userId=1613865&signature=580299cfa4196eaf>
> <https://mailtrack.io/trace/link/ff87973987b1bf4c9dea04dd61358f884c7772f7?url=http%3A%2F%2Fwww.rollsbattery.com&userId=1613865&signature=580299cfa4196eaf>
> <https://mailtrack.io/trace/link/ff87973987b1bf4c9dea04dd61358f884c7772f7?url=http%3A%2F%2Fwww.rollsbattery.com&userId=1613865&signature=580299cfa4196eaf>
> <https://mailtrack.io/trace/link/da85fb0810b828b0ede00e402954f476c444017f?url=http%3A%2F%2Fwww.rollsbattery.com&userId=1613865&signature=5688702baec59913>
> <https://mailtrack.io/trace/link/da85fb0810b828b0ede00e402954f476c444017f?url=http%3A%2F%2Fwww.rollsbattery.com&userId=1613865&signature=5688702baec59913>
> Steve Higgins ⋅ Technical Services Manager
> t +1.902.597.4020  m +1.206.790.5840
> f +1.902.597.8447  e st...@surrette.com
> <#m_3535228063810942375_SignatureSanitizer_SafeHtmlFilter_>
> <https://mailtrack.io/trace/link/d5eee52d9bfa637cdf316c5e159ae4066dc03928?url=http%3A%2F%2Fwww.facebook.com%2FRollsBattery&userId=1613865&signature=0b418130a4d439c9>
> <https://mailtrack.io/trace/link/d5eee52d9bfa637cdf316c5e159ae4066dc03928?url=http%3A%2F%2Fwww.facebook.com%2FRollsBattery&userId=1613865&signature=0b418130a4d439c9>
> <https://mailtrack.io/trace/link/0dfb9e8931e70517774c747de01a19b1530fd5c5?url=http%3A%2F%2Fwww.twitter.com%2FRollsBattery&userId=1613865&signature=adf4ceda01370d9d>
> <https://mailtrack.io/trace/link/629c20e61bb07bfa86d9188f5b259a206e1c0890?url=https%3A%2F%2Fwww.youtube.com%2Fuser%2FRollsBattery&userId=1613865&signature=c54c847ba6b4a7e9>
> <https://mailtrack.io/trace/link/c3fa97127acc244f9362f192ec76510265e79182?url=https%3A%2F%2Fwww.linkedin.com%2Fcompany%2Frolls-battery-engineering&userId=1613865&signature=33cbd35918dbe280>
> <https://mailtrack.io/trace/link/6048a007a0795023d574b073fc2774b01d4098d6?url=http%3A%2F%2Fwww.instagram.com%2FRollsBattery&userId=1613865&signature=7f9a70f6407b3c1a>
> <https://mailtrack.io/trace/link/6048a007a0795023d574b073fc2774b01d4098d6?url=http%3A%2F%2Fwww.instagram.com%2FRollsBattery&userId=1613865&signature=7f9a70f6407b3c1a>
> <https://mailtrack.io/trace/link/61f76eb90498c669b2be5c398d809291cd2ee0a3?url=http%3A%2F%2Fwww.instagram.com%2FRollsBattery&userId=1613865&signature=5af1e9622b504276>
>
> ------------------------------
> *Become a Certified PV Professional. Register for* *NABCEP CEC 2020*
> <https://mailtrack.io/trace/link/68744999097695e3cc0c499e6fd69a0e139455f2?url=http%3A%2F%2Frollsbattery.com%2Fnabcep2020&userId=1613865&signature=d1f84e474d5167f7>
>  *using promo code* *20RBE*
> <https://mailtrack.io/trace/link/68744999097695e3cc0c499e6fd69a0e139455f2?url=http%3A%2F%2Frollsbattery.com%2Fnabcep2020&userId=1613865&signature=d1f84e474d5167f7>
> ------------------------------
> CONFIDENTIALITY: The information transmitted herein is intended only for
> the addressee and may contain confidential, proprietary and/or privileged
> material. Any unauthorized review, distribution or other use of or the
> taking of any action in reliance upon this information is prohibited. If
> you receive this email in error, please contact the sender and delete or
> destroy this message and all copies.
> ------------------------------
>
>
> On Tue, Apr 21, 2020 at 9:44 AM RE Ellison <reelli...@gmail.com> wrote:
>
>> Maybe somebody’s already got this thought in here I didn’t look that
>> in-depth
>>
>> Used to be a good suggestion was to get a couple magnums or heart
>> interface inverters and use them strictly as a charger not an inverter
>>
>> So the inverters you have can keep inverting the generator would feed the
>> other inverters that are used strictly as chargers so the transfer switch
>> does not function and you don’t get that instantaneous change when it
>> crosses over with the transfer switch
>>
>> Another advantages is if you have a problem you have inverters on site
>> that you could wire over to to keep things going
>>
>> Just a thought,
>> Bob Ellison
>>
>> On Apr 21, 2020, at 12:32 PM, Jason Szumlanski <
>> ja...@floridasolardesigngroup.com> wrote:
>>
>> I'm not sure I follow. I would disconnect the generator AC2 input from
>> the existing quad XW system and move it to the external chargers. Or, I
>> could just turn the charging off by software config in the XWs.
>>
>> If I were to buy four inverter/chargers to serve as "external" chargers
>> for the battery (any brand, really) I would just connect the generator
>> input to AC2 and the battery to the batt terminals of the four inverters.
>> The AC1 input/output would have no connections. The inverter function would
>> be turned off and the charger function turned on.
>>
>> Again, this would be an expensive solution. I'm sure there are some
>> companies making high output DC chargers. I assume a 48V model will be able
>> to go up to 60V charging output, which would be plenty for my 51V nominal
>> system.
>>
>>
>>
>>
>>
>> On Tue, Apr 21, 2020 at 11:44 AM Dave Angelini Offgrid Solar <
>> offgridso...@sti.net> wrote:
>>
>>> 4 xw's need the external relay contactors not the internals, Right?
>>>
>>> You will destroy the internals relays. If there was warranty still left,
>>> and there is not on 6048, you would need to scrap them for parts. Xw logs
>>> welded relay warnings and faults for warranty on all xw's.
>>>
>>> *Dave Angelini Offgrid Solar
>>> "we go where powerlines don't"
>>> http://members.sti.net/offgridsolar/ 
>>> <https://mailtrack.io/trace/link/1000ae1ce8f2c3b0e4611f7427decfb5b5d40a7a?url=http%3A%2F%2Fmembers.sti.net%2Foffgridsolar%2F&userId=1613865&signature=b1f0d3afa42d4a66>
>>> e-mail  offgridso...@sti.net <offgridso...@sti.net>
>>> text 209 813 0060*
>>>
>>> On Tue, 21 Apr 2020 08:27:53 -0400, Jason Szumlanski <
>>> ja...@floridasolardesigngroup.com> wrote:
>>>
>>> I actually need 400Adc at 51V nominal of total charge rate. I was hoping
>>> to use 100Adc chargers for redundancy, or some combination of 2-8 chargers
>>> to reach the needed current, assuming they can be synced up. I don't think
>>> the charging algorithm needs to be complicated. We are basically bulk
>>> charging the LiPOs to 80% with the battery BMS controlling the generator.
>>> The concept is to get to 80% sometime in the night and solar kicks in
>>> during the day to reach 100% using 2-stage charging from the XW charge
>>> controllers.
>>>
>>> The problem I have is the quad XW6048s in the system run at a pretty
>>> good load typically... often over 50%. This is off-grid with generator
>>> backup. The transfer switches in the XW6048 are causing surges and
>>> brownouts when the switched loads are high, especially smart dimmers and
>>> televisions. I need seamless power for this client. My thought is to
>>> abandon the internal chargers in the XW6048s and just run loads off
>>> inverter power full-time. I would charge the batteries with external
>>> battery chargers. The tricky part is how to adjust the charge rate based on
>>> load, and also based on solar input. I need to limit the net charging
>>> current. Of course, I still need 400Adc of charging current, which I'm
>>> learning might be hard to find. I don't really want to buy four more XWs -
>>> that's a pretty expensive solution.
>>>
>>> Jason Szumlanski
>>> Florida Solar Design Group
>>>
>>>
>>> On Fri, Apr 17, 2020 at 4:26 PM Dave Angelini Offgrid Solar <
>>> offgridso...@sti.net> wrote:
>>>
>>>> I use the CSW 4048. It has a 50 amp charger. A good spare for clients.
>>>> Get 2 of them. Repurpose an old Radian or XW well over 100A. XW+ is 140adc.
>>>>
>>>> *Dave Angelini Offgrid Solar*
>>>>
>>>> *"we go where powerlines don't"
>>>> http://members.sti.net/offgridsolar/ 
>>>> <https://mailtrack.io/trace/link/15506a57ff1e01606f7be6e8d256e9fc082576bb?url=http%3A%2F%2Fmembers.sti.net%2Foffgridsolar%2F&userId=1613865&signature=fdbbadb371b7cf15>
>>>> e-mail  offgridso...@sti.net <offgridso...@sti.net>
>>>> text 209 813 0060*
>>>>
>>>> On Fri, 17 Apr 2020 14:21:14 -0400, Jason Szumlanski <
>>>> ja...@floridasolardesigngroup.com> wrote:
>>>>
>>>> I'm looking for a standalone 51V nominal battery charger suitable for a
>>>> LiPO battery with 2-stage charging and adjustable setpoints for max current
>>>> and battery voltage. It would require dual chargers with 100A capacity (I
>>>> want dual chargers for redundancy so I have at least 50% capacity if one
>>>> goes bad). Ideally they would sync up so they change stages simultaneously,
>>>> but I'm not sure if that's really important.
>>>>
>>>> Who makes something like that?
>>>>
>>>> Jason Szumlanski
>>>>
>>>>
>>>>
>>>> _______________________________________________
>>>> List sponsored by Redwood Alliance
>>>>
>>>> List Address: RE-wrenches@lists.re-wrenches.org
>>>>
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>> <https://mailtrack.io/trace/link/7f50a0eadda0cb3de5a897432d4ff4ae2b5a5ff6?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=2c5ff46b6702a0b2>
>>>>
>>>> List-Archive:
>>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>> <https://mailtrack.io/trace/link/5bd53fe813189e2266b6538ca606b966ecc72e15?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=7208ccc85f648335>
>>>>
>>>> List rules & etiquette:
>>>> www.re-wrenches.org/etiquette.htm
>>>> <https://mailtrack.io/trace/link/73fed2c336accd5aae78c627844cfeab4bcb8b34?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=267ea0dc715039c6>
>>>>
>>>> Check out or update participant bios:
>>>> www.members.re-wrenches.org
>>>> <https://mailtrack.io/trace/link/bf35649bad2205539bd80d64bd9a0c8b901cc447?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=acc07bfa0f7987b8>
>>>>
>>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> <https://mailtrack.io/trace/link/7f50a0eadda0cb3de5a897432d4ff4ae2b5a5ff6?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=2c5ff46b6702a0b2>
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>> <https://mailtrack.io/trace/link/5bd53fe813189e2266b6538ca606b966ecc72e15?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=7208ccc85f648335>
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> <https://mailtrack.io/trace/link/73fed2c336accd5aae78c627844cfeab4bcb8b34?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=267ea0dc715039c6>
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>> <https://mailtrack.io/trace/link/bf35649bad2205539bd80d64bd9a0c8b901cc447?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=acc07bfa0f7987b8>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> <https://mailtrack.io/trace/link/7f50a0eadda0cb3de5a897432d4ff4ae2b5a5ff6?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=2c5ff46b6702a0b2>
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>> <https://mailtrack.io/trace/link/bb2e604d144b7c4fdbb64042509e0e02c23dfeb5?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=ec08b0018f561de8>
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> <https://mailtrack.io/trace/link/d11092bda7abb595eb518a44690a107f0047a4a3?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=ec4d994f9ae04bd8>
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>> <https://mailtrack.io/trace/link/9b5312442593d331c3b2947013032b83aa186007?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=8b4e74b713ab4eb3>
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/1bf3d25b542479f44193332f39ed5157f2a90830?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=27dade8d004dad21>
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> <https://mailtrack.io/trace/link/bb2e604d144b7c4fdbb64042509e0e02c23dfeb5?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=ec08b0018f561de8>
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> <https://mailtrack.io/trace/link/d11092bda7abb595eb518a44690a107f0047a4a3?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=ec4d994f9ae04bd8>
>
> Check out or update participant bios:
> www.members.re-wrenches.org
> <https://mailtrack.io/trace/link/9b5312442593d331c3b2947013032b83aa186007?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=8b4e74b713ab4eb3>
>
>
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to