Hi Ray

In my experience I’ve had plenty of hub and component/comm failures but I’ve 
never had it shut down the fndc or charge controllers with OB or Schneider 
equipment. 

I’m wondering if you have?  

Thx

Jay

Peltz power. 



> On May 17, 2020, at 6:21 PM, Ray <r...@solarray.com> wrote:
> 
> 
> I don't connect to the HUB or Mate if I don't have to; both to avoid issues 
> with the customers changing programming, but also to save the customer money. 
>  However, the #1 reason is that when all the equipment is interconnected, it 
> is all dependent.  A failure in a comm cable or single piece of equipment can 
> cause all the controllers to shut down.  I just don't think the benefits of 
> com connection out weigh the loss of redundancy.  I have many systems with 
> multiple charge controllers, and I have seen everything from a bad temp 
> sensor to a single failed controller take the other controllers off line too. 
>  Without the interconnection, a failed controller will just drop the system 
> to half power, not to zero production.  
> 
> This isn't just with Outback, I follow this reasoning with Midnite and Magnum 
> as well.  I often mix equipment (Magnum inverter, Outback Controller) so comm 
> connection isn't a possibility anyway.  We might be missing some bells and 
> whistles, but our systems stay operational in more situations.   Basically 
> I'm not happy enough with any single manufacturer to give them a monopoly 
> with my designs.  I've always built our systems with the best equipment we 
> can get for that particular situation.
> 
> Ray Walters
> Remote Solar
> 303 505-8760
>> On 5/17/20 7:38 AM, Mac Lewis wrote:
>> Hi Ray,
>> 
>> I'm curious, do you avoid have the FM100 on the Hub to avoid clients 
>> changing the programming or have you seen some other issues?  I have some of 
>> them out there and they seem to be solid, all Hub 10.3 connected.
>> 
>> On Fri, May 15, 2020 at 3:48 PM Dave Angelini Offgrid Solar 
>> <offgridso...@sti.net> wrote:
>>> I have little experience with arc fault detection because I do not use them 
>>> offgrid. Could it save one from starting a wildfire? My experience is I 
>>> have never had a ground mount start a wildfire and even a bad panel is 
>>> pretty contained in a failure.
>>> 
>>> I just know that I make a small fortune replacing grid tie inverter AFD's 
>>> that failsafe in the no solar mode. Definitely do not want another way to 
>>> lose power offgrid. There are plenty already:)
>>> 
>>>  
>>> 
>>>  
>>> Dave Angelini Offgrid Solar
>>> "we go where powerlines don't"
>>> http://members.sti.net/offgridsolar/
>>> e-mail  offgridso...@sti.net
>>> text 209 813 0060
>>>> On Fri, 15 May 2020 11:03:11 -0700, Jay <jay.pe...@gmail.com> wrote:
>>>> 
>>>> Hi William,
>>>>  
>>>> that warning isn't on the AFCI one,
>>>>  
>>>> Jay
>>>>  
>>>> Peltz power. 
>>>>  
>>>>  
>>>>  
>>>>  
>>>>  
>>>>  
>>>>  
>>>>  
>>>>  
>>>>  
>>>> 
>>>>> On May 15, 2020, at 10:41 AM, William Miller <will...@millersolar.com> 
>>>>> wrote:
>>>>> 
>>>>> Jay:
>>>>> 
>>>>>  
>>>>> 
>>>>> On the FM100 landing page.  The warning is pasted below.
>>>>> 
>>>>>  
>>>>> 
>>>>> Due to the different voltage ratings, OutBack Power does not recommend 
>>>>> mixing the FM100-300VDC with the FM60 or FM80-150VDC controllers on the 
>>>>> same battery bank.
>>>>> 
>>>>>  
>>>>> 
>>>>> Interestingly the warning is not seen on the FM100 AFCI landing page.
>>>>> 
>>>>>  
>>>>> 
>>>>> I thought I saw this also in one of the Owner's manuals but I looked 
>>>>> today and can't find it there.  Interesting...
>>>>> 
>>>>>  
>>>>> 
>>>>> I have a client that wants to add a fourth PV array to a system with 
>>>>> three FM80s.  This will require a fourth charge controller.  Being able 
>>>>> to run smaller wire in the existing conduits is an attractive 
>>>>> proposition, making the FM100 a desirable approach.  I now have to figure 
>>>>> out if I can add the FM100-AFCI (which is apparently the only version 
>>>>> available) to a system with three FM80s, and if I do, what do I do with 
>>>>> the existing GFDI breaker and how do I arrange the DC bond?  There is a 
>>>>> lot to consider here.
>>>>> 
>>>>>  
>>>>> 
>>>>> BTW, I was told by a tech support person for an on-line sales firm that 
>>>>> the original FM100 did not have the AFCI but those units have been 
>>>>> discontinued.  Now all FM100s have the AFCI capability.  I am weighing if 
>>>>> I want AFCI if it is not required.  My territory includes central 
>>>>> California wild lands so I suppose I should take advantage of any fire 
>>>>> safety means at my disposal...
>>>>> 
>>>>>  
>>>>> 
>>>>> William
>>>>> 
>>>>>  
>>>>> 
>>>>>  
>>>>> 
>>>>> From: Jay [mailto:jay.pe...@gmail.com] 
>>>>> Sent: Friday, May 15, 2020 7:34 AM
>>>>> To: will...@millersolar.com; RE-wrenches
>>>>> Subject: Re: [RE-wrenches] Outback FM100
>>>>> 
>>>>>  
>>>>> 
>>>>> Hi William
>>>>> 
>>>>>  
>>>>> 
>>>>> Yes downsizing breaker to meet load is no problem. And getting wire that 
>>>>> big into it with 1" KO is a pain. 
>>>>> 
>>>>>  
>>>>> 
>>>>> I'm pretty sure any hub will work, needs 3S mate
>>>>> 
>>>>>  
>>>>> 
>>>>> Where in the manual did you find the "don't mix with other 60/80 
>>>>> controllers?  
>>>>> 
>>>>>  
>>>>> 
>>>>> Jay
>>>>> 
>>>>>  
>>>>> 
>>>>> Peltz power 
>>>>> 
>>>>> 
>>>>> 
>>>>> 
>>>>> On May 15, 2020, at 12:46 AM, William Miller <will...@millersolar.com> 
>>>>> wrote:
>>>>> 
>>>>> Friends:
>>>>> 
>>>>>  
>>>>> 
>>>>> I have occasion to try the FM100 charge controller.  I am wondering of 
>>>>> anyone had found any quirks with implementing this device.  I have a few 
>>>>> specific questions:
>>>>> 
>>>>>  
>>>>> 
>>>>> 1.       I want to avoid AFCI unless mandated.  Will this be defeated if 
>>>>> I don't run the leads through the sense coil? (There is an AFCI and 
>>>>> non-AFCI version but I can't seem to find the non-AFCI version anywhere.)
>>>>> 
>>>>> 2.       I noticed the manual indicates you are not supposed to mix the 
>>>>> FM100 with the FM80 or 60 in the same battery system.  This negates it 
>>>>> for one project I had in mind.  I am curious as to why this is.  Anyone 
>>>>> know?
>>>>> 
>>>>> 3.       Will the FM100 work with a standard hub?
>>>>> 
>>>>> 4.       I suppose this unit requires a 125 amp breaker.  If the PV array 
>>>>> cannot support that full 100 amps I might down-size the OCPD accordingly. 
>>>>>  Anyone contemplate this question?
>>>>> 
>>>>>  
>>>>> 
>>>>> Thanks in advance.
>>>>> 
>>>>> William
>>>>> 
>>>>>  
>>>>> 
>>>>>  
>>>>> 
>>>>> _______________________________________________
>>>>> List sponsored by Redwood Alliance
>>>>> 
>>>>> List Address: RE-wrenches@lists.re-wrenches.org
>>>>> 
>>>>> Change listserver email address & settings:
>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>> 
>>>>> List-Archive: 
>>>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>>> 
>>>>> List rules & etiquette:
>>>>> www.re-wrenches.org/etiquette.htm
>>>>> 
>>>>> Check out or update participant bios:
>>>>> www.members.re-wrenches.org
>>>>> 
>>>>> _______________________________________________
>>>>> List sponsored by Redwood Alliance
>>>>> 
>>>>> List Address: RE-wrenches@lists.re-wrenches.org
>>>>> 
>>>>> Change listserver email address & settings:
>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>> 
>>>>> List-Archive: 
>>>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>>> 
>>>>> List rules & etiquette:
>>>>> www.re-wrenches.org/etiquette.htm
>>>>> 
>>>>> Check out or update participant bios:
>>>>> www.members.re-wrenches.org
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>> 
>>> List Address: RE-wrenches@lists.re-wrenches.org
>>> 
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> 
>>> List-Archive: 
>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>> 
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>> 
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>> 
>> 
>> 
>> -- 
>> 
>> 
>> 
>> Mac Lewis
>> 
>> "Yo solo sé que no sé nada." -Sócrates
>> 
>> 
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> List Address: RE-wrenches@lists.re-wrenches.org
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: 
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to