We had one Sunny Island system go totally dead years ago. The only way to
get it running again was to charge the batteries, which we did in groups of
two (6 volt batteries each) with a heavy duty 12 VDC automotive charger. It
took about a week to charge all the batteries. Jerry, it's good to know
that there are 48 VDC chargers out there. Do you have a model you like?

William, once the battery bank voltage goes really low (I can't recall the
cutoff voltage) the Sunny Island displays indeed turn completely off.

We stopped installing Sunny Islands about 3 or 4 years ago. It is a solid
product, but definitely part of the older generation of battery inverters
that take a lot of skill to install and program properly to set the project
up for success. The Sunny Portal at the time could give the owner a little
insight into their battery state of charge, but I don't think it sends push
notifications in real time. I think it will send error event notifications
but they are delayed. You might check with SMA about the potential there.

August


On Thu, Dec 17, 2020 at 12:12 PM Jerry Shafer <jerrysgarag...@gmail.com>
wrote:

> Wrenches
> This is why AC coupling is not the best solution but
> you can program the SI to protect low voltage so if this happens you still
> have headroom to reboot the system, also program the GT inverters not to
> wait 300 sec to start. I would also suggest having a 48 vdc charger wired
> directly to the gen set as a fail safe charger to wake up everything.
> Jerry
>
> On Thu, Dec 17, 2020, 11:55 AM William Miller <will...@millersolar.com>
> wrote:
>
>> Friends:
>>
>>
>>
>> I have a client living off-grid with a Sunny Island system AC coupled to
>> Sunny Boy inverters.  They returned from being away to find the system
>> entirely shutdown due to cloudy weather, a dead generator cranking battery
>> and a water leak which ran two booster pumps continuously over a period of
>> time.  The displays on the Sunny Islands were blank and therefore the
>> inverters would not start.
>>
>>
>>
>> We put a new cranking battery into the generator and got it started, but
>> with no life in the Sunny Islands, neither the generator nor the Sunny Boys
>> had any possibility of reviving the discharged 6,000 amp-hour lead acid
>> battery array.  Fortunately after disconnecting the batteries for ten
>> minutes, the voltage rebounded just enough to start the Sunny Islands which
>> allowed the generator to connect and we were back in operation.
>>
>>
>>
>> I am not sure why the displays went dead on the Sunny Islands.  I am on
>> my way back out to download and examine the SD card logs.  I have developed
>> an Excel tool to help me tabulate the data.  Maybe there is some clue in
>> those files.
>>
>>
>>
>> In the meantime I have these questions that those of you with more Sunny
>> Island experience might be able to answer:
>>
>>
>>
>> 1.   Is it normal for the display screens on the Sunny Islands to go
>> blank after shutting off due to low battery voltage?
>>
>>
>>
>> 2.   Is there an up-to-date option for remote monitoring that will send
>> an email if certain error conditions occur?
>>
>>
>>
>> 3.   What would you do with a 6k AH battery bank with a voltage too low
>> to start a battery inverter or solar charge controller?
>>
>>
>>
>> Thanks in advance.  The wrenches hive-mind is a huge asset.
>>
>>
>>
>> William Miller
>>
>> Miller Solar
>>
>> 17395 Oak Road, Atascadero, CA 93422
>>
>> 805-438-5600
>>
>> www.millersolar.com
>>
>> CA Lic. 773985
>>
>>
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to