Hi Jay
Hi Larry
The X240 is a 4000 watt transformer it is also available in the PSX-240
Both can be used as a step up, a step down or a balancing xfmr.

Below is a link to the manuals.
https://www.outbackpower.com/resources/documents/product-documentation/item/autotransformer-technical-documentation
 Balancing transformer is not required by the Radian or the FXR inverters.
I was used in the older FX series usually as a step up/balancing Xfmr.
In step up operation it allows a single inverter to be on and will provide a 
second ac voltage of the opposite phase. If 2 inverters L1 and L2 were present  
it would load balance which allowed the least used phase to contribute to the 
most used phase.

   It can still be used as step up with a single FXR inverter meaning a single 
unit and the X240 will provide two phases L1 and  L2 with 180 degrees of phase 
separation.  It will not work as a load balancing xfmr using the FXR inverter. 
With the FXR we lost the load balancing ability. What we gained was the ability 
to sell back in a multi inverter stacked system, the 7 modes available from the 
Radian and Selling with in a 3 phase 120/208 system up to a 9 inverters.
I hope this helps.
Take Care All





From: RE-wrenches <re-wrenches-boun...@lists.re-wrenches.org> On Behalf Of Jay
Sent: Wednesday, February 3, 2021 4:45 PM
To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
Subject: Re: [RE-wrenches] Load imbalance issues with SolArk?

Hi Larry

I’m not so sure about that. The X-240 doesn’t work with the Radian or FXR 
versions. IE it won’t balance the loads so that the inverter sees a balance on 
L1/L2.

It did do this for the older FX versions.

Jay




On Feb 3, 2021, at 2:10 PM, 
la...@starlightsolar.com<mailto:la...@starlightsolar.com> wrote:
Amos,

When using it in balancing mode, as seen in the attached image, the PSX will 
provide 120Vac from either leg and the inverter output should stay balanced. A 
240Vac circuit from the main panel goes to the PSX then to a sub panel and any 
240Vac loads stay on the main panel.


Larry Crutcher
Starlight Solar Power Systems

<Screen Shot 2021-02-03 at 2.00.39 PM.png>


On Feb 3, 2021, at 1:49 PM, Amos Post 
<integrityenergy...@gmail.com<mailto:integrityenergy...@gmail.com>> wrote:

We have had this issue with a recent installation.  It’s a new off-grid house 
build, and so not many loads to speak of yet, except mainly power tools.  The 
Solark 12K will not start any of: portable air compressor, table saw, and 
sometimes struggles with a miter saw, which are each 16amps or less at 120V, 
but I have measured close to 50amps start up for the air compressor and table 
saw.  The air compressor and table saw are 1.5HP each.  What helps is if the 
motors are warmed up, or putting another load on the other leg to balance the 
inverter’s output.

Was thinking we would install a couple of dedicated 120V outlets for 
“high-current” 120V loads with a PSX-240, stepping down the inverter's 240 to 
120.  My understanding is this will solve the issue for starting these loads, 
but not sure if we might run into issues with inbalance down the road...  Would 
be curious to know if there’s another way to balance all of the house loads 
using the PSX-240?..
<IE LOGO 150x78.jpg>

       Amos Post
   Integrity Energy
  W 802.763.7023
   C 802.291.2188
    
ienergyVT.com<https://protect2.fireeye.com/v1/url?k=1446f2de-4bddca0a-1445fb55-860a66ff9d26-4a559e51315323ab&q=1&e=8bda5334-eefc-4426-882f-473bf8f783da&u=http%3A%2F%2Fwww.ienergyvt.com%2F>
        
Facebook<https://protect2.fireeye.com/v1/url?k=4dfa2226-12611af2-4df92bad-860a66ff9d26-6f5b7f95c12f7468&q=1&e=8bda5334-eefc-4426-882f-473bf8f783da&u=https%3A%2F%2Fwww.facebook.com%2Fintegrityenergyllp%3Fref%3Dhl>


On Feb 3, 2021, at 2:41 PM, 
la...@starlightsolar.com<mailto:la...@starlightsolar.com> wrote:

If it turns out to be true, could you simply add the Outback PSX-240 to balance 
the loads?

Larry Crutcher
Starlight Solar Power Systems



On Feb 3, 2021, at 10:52 AM, Nick A Lucchese 
<luccheseso...@me.com<mailto:luccheseso...@me.com>> wrote:

Good morning Wrenches,

I’ve strongly been considering using the SolArk 12K unit for awhile but have 
heard from a few folks that there can be somewhat frequent issues with the 
inverter shutting down from line to line imbalance. As little as 1400 watts? I 
could see where these instances would be minimized with attention to detail on 
balancing all the loads but if’s as little as a delta of 1400 watts that might 
occur with something as innocent as a toaster oven. Seems like it would also be 
less of an issue in a grid back up or AC coupled scenario but for off grid I’d 
be bummed to be getting calls every couple weeks from an off grid client that 
trusted me to offer the right equipment.

How much of an issue is this? Is it getting exaggerated? Those that have NOT 
had this happening was it on a full time off grid site?

Has it happened less on sites using the "Limited to Home” mode? I have an 
upcoming project that was going to be setup with a couple Radians in HBX mode 
and my thought was perhaps it might be an ideal solution there but if the 
continuity of electrical service was going to be provided mainly through 
batteries and inverting and not through the pass through relays the majority of 
the time then the site might likely experience this issue with imbalance 
shutdowns.

There are many attractive features of the SolArk and I really like the thought 
of taking advantage of the 185 amp DC charger versus the Radian’s 115 but I’m 
kind of thinking the risks may outweigh the benefits if these shutdowns occur 
even once every couple of months. Any of you have a long enough history with 
them to chime in with your observations? Are they most reliable for AC coupled 
with backup rather than off grid or the “Limited to Home” mode?

Thanks for your time,
Nick A Lucchese
_______________________________________________
List sponsored by Redwood Alliance

List Address: 
RE-wrenches@lists.re-wrenches.org<mailto:RE-wrenches@lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<https://protect2.fireeye.com/v1/url?k=6acff649-3554ce9d-6accffc2-860a66ff9d26-fb54d0216d063fae&q=1&e=8bda5334-eefc-4426-882f-473bf8f783da&u=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org>

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<https://protect2.fireeye.com/v1/url?k=6ae8ae30-357396e4-6aeba7bb-860a66ff9d26-224c9a2e5676f204&q=1&e=8bda5334-eefc-4426-882f-473bf8f783da&u=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org>

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm<https://protect2.fireeye.com/v1/url?k=f9aaf6b2-a631ce66-f9a9ff39-860a66ff9d26-7609cf657b1370f6&q=1&e=8bda5334-eefc-4426-882f-473bf8f783da&u=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm>

Check out or update participant bios:
http://www.members.re-wrenches.org<https://protect2.fireeye.com/v1/url?k=ab7d80ef-f4e6b83b-ab7e8964-860a66ff9d26-578f30fd629eb461&q=1&e=8bda5334-eefc-4426-882f-473bf8f783da&u=http%3A%2F%2Fwww.members.re-wrenches.org%2F>

_______________________________________________
List sponsored by Redwood Alliance

List Address: 
RE-wrenches@lists.re-wrenches.org<mailto:RE-wrenches@lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<https://protect2.fireeye.com/v1/url?k=19203f4b-46bb079f-192336c0-860a66ff9d26-3db6367be42c7280&q=1&e=8bda5334-eefc-4426-882f-473bf8f783da&u=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org>

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<https://protect2.fireeye.com/v1/url?k=023ee8d9-5da5d00d-023de152-860a66ff9d26-88fd4a8bd5dc5992&q=1&e=8bda5334-eefc-4426-882f-473bf8f783da&u=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org>

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm<https://protect2.fireeye.com/v1/url?k=716e7ce2-2ef54436-716d7569-860a66ff9d26-bafe538620be1ece&q=1&e=8bda5334-eefc-4426-882f-473bf8f783da&u=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm>

Check out or update participant bios:
http://www.members.re-wrenches.org<https://protect2.fireeye.com/v1/url?k=21481a01-7ed322d5-214b138a-860a66ff9d26-2a8eadbc6c92a933&q=1&e=8bda5334-eefc-4426-882f-473bf8f783da&u=http%3A%2F%2Fwww.members.re-wrenches.org%2F>

_______________________________________________
List sponsored by Redwood Alliance

List Address: 
RE-wrenches@lists.re-wrenches.org<mailto:RE-wrenches@lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<https://protect2.fireeye.com/v1/url?k=55525217-0ac96ac3-55515b9c-860a66ff9d26-f148846708994e6c&q=1&e=8bda5334-eefc-4426-882f-473bf8f783da&u=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org>

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<https://protect2.fireeye.com/v1/url?k=b45b9705-ebc0afd1-b4589e8e-860a66ff9d26-721f0940a24c2e65&q=1&e=8bda5334-eefc-4426-882f-473bf8f783da&u=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org>

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm<https://protect2.fireeye.com/v1/url?k=664d5add-39d66209-664e5356-860a66ff9d26-fe5cdce72e74e2b6&q=1&e=8bda5334-eefc-4426-882f-473bf8f783da&u=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm>

Check out or update participant bios:
http://www.members.re-wrenches.org<https://protect2.fireeye.com/v1/url?k=b31ce7eb-ec87df3f-b31fee60-860a66ff9d26-f4f4fffce71fd11a&q=1&e=8bda5334-eefc-4426-882f-473bf8f783da&u=http%3A%2F%2Fwww.members.re-wrenches.org%2F>


This email and any attachments may contain confidential information that is 
intended only for the recipient(s). If you have received this email in error, 
please notify the sender and delete it from your system. Any views or opinions 
presented in this email are solely those of the author and do not necessarily 
represent those of the company or its affiliates. This email does not 
constitute an agreement to conduct transactions by electronic means and does 
not create any legally binding contract or enforceable obligation in the 
absence of a fully signed written contract. The recipient should check this 
email and any attachments for viruses. The company accepts no liability for any 
loss or damage caused by software viruses. If you are the intended recipient 
and you do not wish to receive similar email(s) from us in the future then 
please notify the sender. Please consider the environment before printing.
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to