I’m currently building a similar sized system (a bit larger), so I know what 
the costs are for such scale. Seems like 6-9 SolArks or XWpros for dedicated 
closed loop charging only wouldn’t be unreasonable? 

If an equally sized battery charger exists it would be a monstrosity!



> On Dec 2, 2021, at 7:53 AM, Jay <jay.pe...@gmail.com> wrote:
> 
> Hi all
> 
> Sorry I guess I didn’t explain the clients wants well enough
> 
> 1. 90-100kwh+ 48 vdc lithium battery 
> 2. 208 3 phase AC generator powering 48v nominal battery chargers.
> 208-3phase as that is the house/EE design voltage. 
> 3. AC generator because it’s back up if the inverters fail, so no DC 
> generator. 
> 4. Client doesn’t want any drop outs or have to reset clocks etc during 
> generator/inverter- charging/switchover.
> 5. Inverter size is not decided yet, probably 40-80kw. 
> 6.  Generator size isn’t specified yet, but given the loads 60-125kw 
> probably. 
> Size would be based on battery charging or max ac load which ever is larger. 
> 
> That leads me external chargers. 
> 
> I’m looking for large programmable battery chargers for lithium batteries 
> powered from a 208-3phase ac generator in the 60-125 kw size range. 
> 
> Thanks
> 
> Jay
> 
> 
> 
> 
> 
> 
>> On Dec 2, 2021, at 6:56 AM, MDElectricSolar <mdelectricso...@gmail.com> 
>> wrote:
>> 
>> Maybe a DC output generator, the Wildcat Maverick charges a 48v battery 
>> bank directly and has it’s own controls, independent from the inverter.
>> 
>> https://wildcatpowergen.com/pages/maverick 
>> <https://wildcatpowergen.com/pages/maverick>
>> 
>> Michael D Nelson
>> MD Electric & Solar, Inc.
>> 707-684-0064 mobile
>> 707-884-1862 office
>> www.mdelectricsolar.com
>> www.facebook.com/mdelectricandsolar
>> 
>> 
>>> On Dec 2, 2021, at 6:27 AM, Mac Lewis <maclew...@gmail.com> wrote:
>>> 
>>> 
>>> Hi Jay, 
>>> 
>>> Is the plan to feed DC current (from generator and grid) into the batteries 
>>> and keep the inverters as power source for loads?
>>> 
>>> On Thu, Dec 2, 2021 at 6:30 AM Darryl Thayer <darylsol...@gmail.com 
>>> <mailto:darylsol...@gmail.com>> wrote:
>>> Jay I am confused as usual, what are the loads?  AC or DC?  How are you 
>>> charging the battery from the generator or how is the battery powering the 
>>> loads?   What is the desired current or the size of the generator?  sorry 
>>> if this I dumb question
>>> 
>>> On Wed, Dec 1, 2021 at 2:23 PM Jay <jay.pe...@gmail.com 
>>> <mailto:jay.pe...@gmail.com>> wrote:
>>> I got a call from a colleague that is designing a very large roughly 90-100 
>>> kWh lithium battery at 48v. 
>>> 
>>> He’s looking for large AC chargers to charge this bank. The reason is total 
>>> elimination of switch over delay from inverter to generator and back. 
>>> 
>>> One technique is to use inverters for this, but pretty pricey. 
>>> 
>>> Any recommendations as to equipment, brands etc?  
>>> 
>>> It would be a 208 3 phase AC side powered by a generator. 
>>> 
>>> Thx 
>>> Jay
>>> 
>>> Peltz power. 
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>> 
>>> Pay optional member dues here: http://re-wrenches.org 
>>> <http://re-wrenches.org/>
>>> 
>>> List Address: RE-wrenches@lists.re-wrenches.org 
>>> <mailto:RE-wrenches@lists.re-wrenches.org>
>>> 
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>>> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>>> 
>>> There are two list archives for searching. When one doesn't work, try the 
>>> other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ 
>>> <https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/>
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
>>> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>>> 
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm 
>>> <http://www.re-wrenches.org/etiquette.htm>
>>> 
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>> 
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>> 
>>> Pay optional member dues here: http://re-wrenches.org 
>>> <http://re-wrenches.org/>
>>> 
>>> List Address: RE-wrenches@lists.re-wrenches.org 
>>> <mailto:RE-wrenches@lists.re-wrenches.org>
>>> 
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>>> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>>> 
>>> There are two list archives for searching. When one doesn't work, try the 
>>> other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ 
>>> <https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/>
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
>>> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>>> 
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm 
>>> <http://www.re-wrenches.org/etiquette.htm>
>>> 
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>> 
>>> 
>>> 
>>> -- 
>>> 
>>> 
>>> 
>>> Mac Lewis
>>> 
>>> "Yo solo sé que no sé nada." -Sócrates
>>> 
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>> 
>>> Pay optional member dues here: http://re-wrenches.org
>>> 
>>> List Address: RE-wrenches@lists.re-wrenches.org
>>> 
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> 
>>> There are two list archives for searching. When one doesn't work, try the 
>>> other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>> 
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>> 
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> Pay optional member dues here: http://re-wrenches.org
>> 
>> List Address: RE-wrenches@lists.re-wrenches.org
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> There are two list archives for searching. When one doesn't work, try the 
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 




        Michael Morningstar

        Morningstar Electric
        PO Box 1494
        Mount Shasta, California 96067
        530-921-0560
        CSLB 949635
 
  

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to