Hi all, I currently have an off-grid client that has a 120/240VAC 7.5 HP - 40A FLC single phase pool pump. Locked rotor current is around 110 A. I had initially (and naively) thought that two Sol Ark 12k units would be able to handle this load. Due to the lack of a transformer, the unit's just can't output the required inductive startup inrush. Now getting clarification from Sol Ark that max inductive HP output is 2.5 HP per unit. We had installed an amply sized SR35 soft starter, with no avail. The 20 kW generator can start the motor, but it is noticeably shaken with the intense load drop.
I am toying with the idea of installing a VFD and upgrading the pool pump to a three phase motor. Would make for a much smoother ramp and self start. The client is a bit hesitant to upgrade and would like to continue using their clunky, non-self starting single phase motor. My other thought was to implement an autotransformer to add some copper to the equation and help the Sol Ark's get the job done. Has anyone had any experience with the Victron 100A autotransformer for both 120/240 input and output? Any suggestions or relative experience would be greatly appreciated! -Kindly, -Chris -- *Chris Sparadeo * *NABCEP Certified PV Installation Professional **® **# 042919-015652* *NABCEP Certified PV System Inspector **®** # 052920-015652 * *State of Vermont Journeyman Electrician # EJ-07619*
_______________________________________________ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org