This is a partial backup scenario and the main service panel has a solid
neutral to ground bond. I have not been able to find anywhere else where
there is a bond, but there is always the chance that there is a neutral
wire in a switch box or outlet box somewhere in the house that is touching
an equipment ground or metallic enclosure.



On Wed, Jun 5, 2024, 9:53 AM Mac Lewis <maclew...@gmail.com> wrote:

> Hi Jason,
>
> You should be able to land your PV EGC in the inverter ground bar.  You
> could do a quick resistance check to verify the +, - PV
>
> Is there a bond somewhere (upstream service panel or in the Sol-Ark
> itself) between ground and neutral?  If not, this can cause this fault.
>
> On Wed, Jun 5, 2024 at 7:03 AM Jason Szumlanski via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
>> Can anybody clarify the following instruction from the manual?
>>
>> "GND the panel MOUNTS/FRAMES to any GND outside the circuit via 12AWG
>> wire"
>>
>> Does this mean do not connect the array equipment grounding conductor to
>> the grounding terminal in the inverter? Where would be the suggested place
>> to connect the equipment grounding conductor, and why does it make a
>> difference? It would still be electrically bonded to the grounding terminal
>> in the inverter.
>>
>> I'm asking because I do, in fact, have an equipment grounding conductor
>> from the array connected to the ground terminal in the inverter at a home.
>> I am getting an F08 GFDI fault. The manual doesn't say anything about the
>> DC side with respect to this error. It suggests it is an AC current leakage
>> to ground. But Sol-Ark tech support suggested that I disconnect the PV to
>> rule it out as a source of the fault.
>>
>>
>>
>> Jason Szumlanski
>> Florida Solar Design Group
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>>
>
> --
>
>
>
> Mac Lewis
>
> *"Yo solo sé que no sé nada." -Sócrates*
>
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to