Maybe it’s a real arc-fault in the system somewhere, and the breaker is trying 
to tell you that.

Tom McCalmont
CEO, Paired Power
pairedpower.com <http://pairedpower.com/> | LinkedIn 
<https://www.linkedin.com/company/paired-power/>
Direct: (669) 877-2931



> On Nov 21, 2025, at 3:32 PM, Kent via RE-wrenches 
> <[email protected]> wrote:
> 
> Fellow Wrenches,
> 
> I have a system that we installed a few weeks ago that is driving us crazy 
> with overload faults. It is a remote cabin with maybe a half dozen circuits 
> being fed by a Little Rosie inverter. Every couple weeks the power system 
> shuts down with the Little Rosie showing an overload for no apparent reason. 
> Client resets the inverter and everything runs fine for a couple weeks or so. 
> The system seems to have no trouble when the Arc Fault (a Siemens arc fault 
> breaker in a 100-A Siemens panel) breaker is turned off. Any of you have 
> similar issues with these breakers? It is weird that the breaker could 
> actually be causing the inverter to trip off.
> 
> Kent Osterberg
> Blue Mountain Solar
> 
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to