Hi Kent,
This is the first we have heard of an issue of this nature but if you can 
please provide the model of breaker and share what loads are connected to that 
circuit with [email protected]<mailto:[email protected]> we would like 
to try to recreate the issue and determine if it is something on our end that 
needs to be addressed.

Sue Stankevitz
MidNite Solar, Inc.<https://www.midnitesolar.com/index.php>
(360) 403-7207 (XT122)
[cid:[email protected]]

From: RE-wrenches <[email protected]> On Behalf Of Kent 
via RE-wrenches
Sent: Friday, November 21, 2025 7:29 PM
To: Tom McCalmont <[email protected]>; RE-wrenches 
<[email protected]>
Cc: Kent <[email protected]>
Subject: Re: [RE-wrenches] Little Rosie vs Arc Fault Breaker?


It is the inverter that trips off not the breaker and nothing needs to be done 
to restore power except to reset the inverter. It isn't unusual for an inverter 
to trip off due to overload faster than a breaker responds. But I wouldn't 
expect the inverter to trip off due to an arc fault.

The electrician has been out there twice looking for a problem with the wiring 
and found nothing.

Kent Osterberg
Blue Mountain Solar


On 11/21/2025 3:35 PM, Tom McCalmont wrote:
Maybe it’s a real arc-fault in the system somewhere, and the breaker is trying 
to tell you that.

Tom McCalmont
CEO, Paired Power
pairedpower.com<http://pairedpower.com> | 
LinkedIn<https://www.linkedin.com/company/paired-power/>
Direct: (669) 877-2931




On Nov 21, 2025, at 3:32 PM, Kent via RE-wrenches 
<[email protected]><mailto:[email protected]> 
wrote:

Fellow Wrenches,

I have a system that we installed a few weeks ago that is driving us crazy with 
overload faults. It is a remote cabin with maybe a half dozen circuits being 
fed by a Little Rosie inverter. Every couple weeks the power system shuts down 
with the Little Rosie showing an overload for no apparent reason. Client resets 
the inverter and everything runs fine for a couple weeks or so. The system 
seems to have no trouble when the Arc Fault (a Siemens arc fault breaker in a 
100-A Siemens panel) breaker is turned off. Any of you have similar issues with 
these breakers? It is weird that the breaker could actually be causing the 
inverter to trip off.

Kent Osterberg
Blue Mountain Solar


_______________________________________________


_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to