low power factors are bad -- you pay for the higher VA, but are only 
using the lower watts to do actual work !!

I'm really surprised that USP doesn't have a PFC front end to bring 
everything back into line.

Bob M. wrote:
>
> I have an APC SU2200 (SmartUPS, 2200VA) 3U tall, that I put new 
> batteries in a few months ago. So far it's just sitting, plugged in, 
> turned off, with no load. I got curious as to how much power it was 
> sucking out of the wall outlet, so I plugged the UPS into my 
> Kill-A-Watt device and plugged that into the wall. Here are the 
> numbers I observed:
>
> 122.2 Volts
> 1.48 Amps
> 31 Watts
> 181 Volt-Amps
> 0.17 Power Factor
>
> The values were identical with the unit turned on, also with no load. 
> The only thing running inside the UPS is the battery charger; the 
> inverter is completely bypassed and is not running.
>
> I then ran the UPS into a test cycle, again with no load, but this 
> time the inverter turned on and powered the load, thus disconnecting 
> itself from the commercial AC power. Surprisingly, there was still a 
> little bit of power being used, probably by the transformer and line 
> sampling circuit. Here are the readings I got during the self-test:
>
> 122.4 Volts
> 0.09 Amps
> 0 Watts
> 11 Volt-Amps
> 0.06 Power Factor
>
> As far as I know, the utility's kilowatt-hour meter on the side of my 
> house, which is a rotating aluminum-disc style, measures WATTS, not 
> Volt-Amps. Somehow APC has managed to get their charging circuit to 
> draw a lot of current while keeping the power factor and Wattage power 
> extremely low. I suspect it's highly capacitive.
>
> So here's where you all get to jump in. Is this UPS costing me a lot 
> just to keep the batteries charged (180 VA) or am I only being charged 
> for the wattage it draws?
>
> Bob M.
>
>  

Reply via email to