Instead of MOVs, how about a gas discharge tube [GDT]. OR Possibly in parallel 
with the MOV. They are small and metal and the specs say they can take quite a 
few discharges and not break down..
Anyone use those?
Thank you for all the replies and info on my subject!..
73

--- In Repeater-Builder@yahoogroups.com, "Jeff DePolo" <j...@...> wrote:
>
> 
> Hmmm.  That's a tougher one.  Mostly I use the Polyphasers (PLDO-120US-15A
> or -20A) at sites that don't have facility-wide protection.  The TrippLite
> Isobar Ultra series is another (ISOBAR8ULTRA et al).  The Isobars also have
> a $50,000 equipment warranty (can't say I've ever had to use it, don't know
> how much red tape there is to go through).  I like the Polyphasers because
> it's designed to mount to a ground panel/bus bar, so I mount it to the bus
> bar that has all of my other arrestors (coax, telco, etc.) on it to provide
> a common-point ground.  The Isobar doesn't have provisions for direct
> grounding - it relies only on the equipment grounding conductor in the AC
> cord, but the TrippLite has arguably better EMI/RFI filtering than the
> Polyphaser.
> 
>                                       --- Jeff WN3A
> 
> 
> > -----Original Message-----
> > From: Repeater-Builder@yahoogroups.com 
> > [mailto:repeater-buil...@yahoogroups.com] On Behalf Of Chuck Kelsey
> > Sent: Tuesday, June 08, 2010 4:48 PM
> > To: Repeater-Builder@yahoogroups.com
> > Subject: Re: [Repeater-Builder] MOVs for power supply primary
> > 
> >   
> > 
> > OK, I should have been more specific. What would be a 
> > reasonable unit for a 
> > repeater site that may have only a couple thousand dollars worth of 
> > equipment inside?
> > 
> > Chuck
> > WB2EDV
> > 
> > ----- Original Message ----- 
> > From: "Jeff DePolo" <j...@... <mailto:jd0%40broadsci.com> >
> > To: <Repeater-Builder@yahoogroups.com 
> > <mailto:Repeater-Builder%40yahoogroups.com> >
> > Sent: Tuesday, June 08, 2010 4:22 PM
> > Subject: RE: [Repeater-Builder] MOVs for power supply primary
> > 
> > >
> > > Probably the ones I've had the most luck with are the 
> > Islatrol series from
> > > Control Concepts. I think they have been bought out by 
> > Emerson or Liebert
> > > or one of the other companies that have power divisions. 
> > Anyway, they 
> > > call
> > > these "active tracking filters". They not only are TVSS's 
> > but also filter
> > > noise, low-amplitude spikes, etc. Right now I'm typing from 
> > a mountaintop
> > > site (broadcast) that we re-built a few years ago. We put 
> > in an Islator
> > > I-2100 (120/240V single-phase). The old equipment shelter 
> > which had been
> > > here since 1990 had the same model unit. In the 15+ years we've been
> > > managing and maintaining the site, we've had zero 
> > surge-related failures,
> > > and this site sticks out like a sore thumb as far as 
> > lightning goes. In 
> > > the
> > > last few years I've used the same series of arrestors for 
> > new site builds 
> > > at
> > > a dozen sites or so and have had no power-related problems.
> > >
> > > Others that make comparable-quality products include 
> > Joslyn, Transtector,
> > > and Innovative Technologies.
> > >
> > > There is one big difference (to me anyway) between TVSS's, 
> > that being
> > > whether they are the series or parallel type. Series type takes the 
> > > utility
> > > service (or transfer switch output if there's a generator 
> > too) as its 
> > > input,
> > > and provides a protected output to feed the panel(s). 
> > Parallel type is
> > > typically connected to a breaker in the panel, which puts 
> > it in parallel
> > > with all of the loads. I much prefer series. Parallel type 
> > can be less
> > > effective because a) there will always be some inductance 
> > and resistance 
> > > in
> > > the wiring between the panel and the protector, b) if the 
> > TVSS conducts,
> > > there's a good chance it will trip the breaker in the 
> > panel, resulting in 
> > > no
> > > protection until the breaker is reset, and c) they are much 
> > less effective
> > > as a noise filter. The upside to parallel type is they can 
> > easily be 
> > > added
> > > at any time just by popping breakers in the panel and feeding the 
> > > arrestor.
> > > Series, on the other hand, are in-line with the service 
> > conductors, so if
> > > you want to add one (or repair one), you have to take the 
> > service down.
> > > Series tends to also be more expensive, especially for 
> > three-phase and
> > > unlike parallel type, the price goes up as the current 
> > rating goes up for
> > > obvious reasons.
> > >
> > > A good 200A single-phase arrestor of the ilk I'm talking 
> > about starts at
> > > about $1000 and goes up quite a ways from there. I think these 
> > > single-phase
> > > I-2100's were in the $2000 range. I recently spec'ed a 
> > 120/208 3-phase
> > > Transtector (parallel type) for another site where I'm much 
> > less concerned
> > > about power-wise, and that was about $1800. No cheap, but 
> > where you're
> > > protecting equipment in the 6 and 7 figure range, it's a 
> > no-brainer. If
> > > you're repeater is a Micor mobile and an Astron, it might be hard to
> > > justify... :-)
> > >
> > > --- Jeff
> > 
> > 
> > 
> > 
> >
>


Reply via email to