nches.org> wrote:Hi Jay,This is a new issue, but I don’t believe it’s generator related. Without CC comms plugged in, generator is steadily charging. It was serviced recently and has solid voltage and frequency under load. I am all for leaving the comms disconnected, but unfortunately there is no scre
Hi Chris,
Is this new or has it been always like this?
jay
> On Nov 8, 2024, at 1:42 PM, Chris Sparadeo via RE-wrenches
> wrote:
>
> Hey wrenchers,
>
> I have an off-grid customer with a pair of VFX 3648 inverters, a FM 100
> charge controller and two eVault
On Nov 8, 2024, at 1:58 PM, Dave Angelini Offgrid Solar via RE-wrenches wrote:
Sounds like a basic generator issue. Use another gen for test !
Dave Angelini Offgrid Solar
"we go where powerlines don't"
https://offgridsolar1.com/
e-mail offgridso...@sti.net
text 209 813 0060
On 2024-11-08
Check out Sunwize. On Nov 8, 2024, at 11:52 AM, Chris Daum via RE-wrenches wrote:Hi folks: We’re working on a system for a job off of the east coast; requirements include hurricane toughness and goods that can survive a saline marine environment. Does anyone even make powder-coated racks anymore
Hi Jeremy
When I’ve watched eg4 inverter/battery closed loop do its thing, it spends
seconds at top voltage setting.
Depending on what CC settings you have, just a few minutes is all you need.
Jay
> On Nov 7, 2024, at 6:31 AM, Jeremy Rodriguez via RE-wrenches
> wrote:
>
&g
Hi Chris,
Outback wasn’t purchased by EG4 or signature solar but it was purchased by 1
owner of EG4/Signature solar and 1 from Big battery if my info is right.
> On Nov 6, 2024, at 7:41 AM, Chris Schaefer via RE-wrenches
> wrote:
>
> Just for fun I visited the EG4 website to see if they s
It would be interesting to see if there is power there. Like put a low wattage 120v incandescent light bulb on it. If it was static wouldn’t the meter drain the volts? JayOn Oct 28, 2024, at 7:31 AM, rick--- via RE-wrenches wrote:An update on this “issue”. Sol-Ark Tech Support said that the high
in advance,
jay
___
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cg
did connect wouldn’t it be
possible for the inverter to try to sell to the generator? If you didn’t have
to change grid to Gen?
Jay
> On Oct 23, 2024, at 8:47 PM, Jeremy Rodriguez via RE-wrenches
> wrote:
>
>
> Wrenches,
> We have a client that has brought utility power
On Oct 24, 2024, at 4:40 PM, Jay wrote:That one cell you have a picture of sure looks suspicious to me. Especially given the good IR picture. It looks it’s physically broken, right about where a hard hat would rest while moving it. That level of hot spot can’t be good. There are two kinds of
co-Gen power.Dave PalumboHyde Park, Vermont802-371-8678 voice or text-- next part --An HTML attachment was scrubbed...URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20241021/6799f15c/attachment-0001.htm>----
Hi williamYou cannot use the balancing xformer with the A version. They also need the mate3S and new hub. 10.1?On Oct 21, 2024, at 1:59 PM, William Miller via RE-wrenches wrote:Friends: I am completely unable to reach Outback tech support so I am wondering if you can answer a question: I am repla
Hi David
I’ve never had an issue with any electronic washer with an Outback, that’s the
best I can say.
Jay
> On Oct 21, 2024, at 9:12 AM, David Palumbo via RE-wrenches
> wrote:
>
>
> Wrenches,
>
> I need to replace a front load washer in my off grid rental house.
instead of selling it?
Drake Chamberlin
Athens Electric LLC
Ohio Electrical Contractor’s License 44810
NABCEP Certified PV Installation Professional
---
On 2024-10-17 18:51, Jay via RE-wrenches wrote:
I just saw the news that magnum has closed its doors
I just saw the news that magnum has closed its doors.
Jay
___
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
Hi Todd
That’s creative for sure!
Not sure how I’d do that on the fm 100.
Jay
> On Oct 14, 2024, at 4:36 PM, Todd Cory via RE-wrenches
> wrote:
>
>
> This works too.
>
> Todd
>
>
>
> On Monday, October 14, 2024 12:55pm, "jay via RE-wrenches&
don’t know if I’ll ever get anyone from OB on the phone.
thanks
jay
___
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & sett
age to the
> array.
>
> Jason Szumlanski
> Principal Solar Designer | Florida Solar Design Group
> NABCEP Certified Solar Professional (PVIP)
> Florida State Certified Solar Contractor CVC56956
> Florida Certified Electrical Contractor EC13013208
>
>
> On Thu, Oct 10
Jason
What’s the possibllity it was a lighting strike?
Jay
> On Oct 10, 2024, at 2:57 PM, Jason Szumlanski via RE-wrenches
> wrote:
>
>
> We have been talking a lot recently about all-in-ones. I just had a massive
> fail during Hurricane Milton with a quad Sol-Ark 15K of
Good question for midnite. JayOn Oct 10, 2024, at 3:35 PM, Dave Tedeyan via RE-wrenches wrote:Yikes! I cannot speak to the AIO's in general. However, I do still always install some sort of inverter bypass in battery based systems. Then in case of a failure like this you can at least continue to p
HI Michael,
Thats good news.
Can you monitor the individual battery cells volts/temp from the app or
inverter? I can’t get an answer on that one.
jay
> On Oct 10, 2024, at 1:33 PM, Michael Morningstar via RE-wrenches
> wrote:
>
> Just installed an AIO/Pflo16. The build
ir, I haven't had any problems and the capacity claims seem legitimate. The value proposition can't be ignored. Jason Szumlanski Florida Solar Design GroupOn Wed, Oct 9, 2024, 7:29 PM jay <jay.pe...@gmail.com> wrote:Thats all super helpful, appreciate the advice everyone. I’ve not used
95560www.greenwired.com Leave a review! On Wed, 09 Oct 2024 16:29:20 -0700 jay via RE-wrenches wrote ---Thats all super helpful, appreciate the advice everyone. I’ve not used the sol ark 15 and just wanted to make sure I wasn’t missing anything about battery options.And specifically the ones
Thats all super helpful, appreciate the advice everyone.
I’ve not used the sol ark 15 and just wanted to make sure I wasn’t missing
anything about battery options.
And specifically the ones that don’t seem to play well.
Jay
> On Oct 9, 2024, at 2:56 PM, Jason Szumlanski via RE-wrenc
HI All
Wondering what people are using for lithium battery and sol ark?
And no, LA is not a option for this system.
Outdoor rated would be preferred, heated isn’t needed.
thanks in advance
jay
___
List sponsored by Redwood Alliance
Pay
Hi David.
That is quite odd. I’ve used dozens of iotas over the years and have not seen
this issue.
Is it a newer on that uses the IQ adapter?
For an alternative you can try powermax.
I’ve had good luck with those too.
Jay
> On Oct 8, 2024, at 7:40 PM, David Palumbo via RE-wrenc
I have done in the past VFX and FX.
I haven not done VFRX snd FXR but it should be ok.
newest firmware is master.
jay
> On Oct 8, 2024, at 12:21 PM, William Miller via RE-wrenches
> wrote:
>
> I’m in the field with a dead VXR3048. Will the FXR play nice with the VFXR?
>
Hi DaveI bet there is no way to install a temp sensor?Question about the 7 hrs absorb time. Where did you come up with that figure. Is the 5% adjustable or the adjustment is in the battery capacity?ThxJayOn Oct 4, 2024, at 8:30 AM, Dave Tedeyan via RE-wrenches wrote:Hi All, I have inherited and d
not that easy when I tried it and that seems necessary, so I am looking for hints on your process. William Miller Solar17395 Oak Road, Atascadero, CA 93422805-438-5600www.millersolar.comCA Lic. 773985 From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jay via RE
Hi JimI recommend a laser level. Can be just a line laser or can be a multi line level. Brightness is key. Much easier, faster and accurate than using string. Also makes it much easier to keep everything straight JayOn Oct 3, 2024, at 7:44 PM, William Miller via RE-wrenches wrote:Good question, J
.
jay
> On Sep 30, 2024, at 5:51 PM, Wayne Irwin via RE-wrenches
> wrote:
>
> Hurricane Helene has taught us the hard way that Enphase batteries with
> anything other than IQ8's won't restart.
> The issue is that when the batteries try to restart (at the non-programmab
I would contact GNB and find out what testing products they recommend and testing procedures. JayOn Sep 26, 2024, at 4:38 PM, Glenn Burt via RE-wrenches wrote:
West Mountain Radio makes a Computerized Battery Analyzer that would perform testing.-GlennSent from my 'smart'phone, so ple
is 16-60v MPPT
range on its micro, 3.75X
Always lots to consider even with a micro.
Jay
> On Sep 25, 2024, at 7:29 AM, jay wrote:
>
> Hi Vince,
>
> Your math looks correct of course, but I think you left out a variable in
> that the panel won’t be operating at max
operating unless it can’t
even produce enough volts to make that voltage. I’ve never seen a curve of
Enphase MPPT efficiency vs input voltage. Would like to though.
Jay
> On Sep 24, 2024, at 8:38 PM, Vince McClellan via RE-wrenches
> wrote:
>
> Hello Wrenches List
> I
Since Dana brought up OB, does anyone have any updates as to OB?
If they were not at the trade show then that is enough evidence to me they are
gone.
Jay
> On Sep 24, 2024, at 7:02 AM, Dana Orzel via RE-wrenches
> wrote:
>
> As previously mentioned, I am upgrading my h
he
did.
At this point with the cost of LFP vs VRLA and cycle life, availability etc
and all that, LFP is the clear winner for me. With the exception of sub
freezing temperatures.
Just my 2 cents
jay
> On Sep 23, 2024, at 9:23 AM, Maverick Brown via RE-wrenches
>
cells, at around 20-21v LVD ( which is all I
use)
Which every legacy inverter I know of has a higher LBCO set point than that.
Jay
> On Sep 18, 2024, at 7:22 AM, Mac Lewis via RE-wrenches
> wrote:
>
> Hi David,
>
> This upgrade comes up a lot. You are at a point where you
accurate the % meter in the
battery is.
I’m sure you’ll get a whole lot of advice,
good luck
jay
> On Sep 17, 2024, at 9:19 AM, David Palumbo via RE-wrenches
> wrote:
>
> Wrenches,
>
> I have a nice little rental house here in my off-grid neighborhood that after
>
float termination, it links each CC so that the first one to
float causes the others to go into float as well. I’ve never found it to be a
big deal either way.
Charge termination is the other one which I always defeat.
But sounds like it all working.
Jay
> On Sep 9, 2024, at 7:21
It doesn’t make any sense that the controllers would be processing 2800 watts
internally.
It would be so hot you couldn’t touch them. Think of a 1500 watt electric
heater and this would be 2X.
I would put my clamp on to confirm. But I suspect it’s going somewhere
Jay
> On Sep 7, 2
Hi all.
Any issues with the xw 60-150 operating lithium batteries?
Namely that they are fast enough in their regulation
Thx
Jay
___
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE
such data”.
Thankfully the installer kept all his paperwork after he retired and moved so
he was able to provide it to discover.
I also heard that Schneider is discontinuing the XW line.
Jay
___
List sponsored by Redwood Alliance
Pay optional
might be connected.
You might check the charge voltages/time to make sure they are correct and I
can’t remember if the classic has battery sense wire connections.
jay
> On Aug 27, 2024, at 2:51 PM, Ray Walters via RE-wrenches
> wrote:
>
> The SPD was on one of the PV inpu
Hi Drake
What makes you say think it’s a soft start?
3 wire isn’t a soft start. It does have a reduced start load but not soft
start.
I’d go with a grundfos sq.
Jay
> On Aug 27, 2024, at 9:08 AM, Drake Chamberlin via RE-wrenches
> wrote:
>
>
> I am looking at a Red Li
I’ll check this and the control by web out.
Thanks everyone
jay
> On Aug 20, 2024, at 9:28 AM, Mac Lewis via RE-wrenches
> wrote:
>
> Hi Jay,
>
> Regarding Victron, it may still be useful. You can boot up the Cerbo with DC
> power, they have a DC powered cell modem
Commander Remote Power • SunFlow Systems Cathodic Protection maver...@mavericksolar.com512-460-9825On Aug 20, 2024, at 8:15 AM, Jay via RE-wrenches wrote:Hi AllI’ve got a client who has a large ranch and wants to monitor (via a web and or app) and control ( simple on/off dry contact) some pumps and
?
Thanks in advance
Jay
___
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cg
Commander Remote Power • SunFlow Systems Cathodic Protection maver...@mavericksolar.com512-460-9825On Aug 18, 2024, at 3:59 PM, Kirk Herander via RE-wrenches wrote:Looks like its only programmable directly on the Mate3s, not in optics RE. Or maybe I haven;t found it yet.On Sun, Aug 18, 2024 at 3:22 PM Jay
There is a setting called FLEXnet dc advanced control. Default is YI always set it to NPg 128 in my manual. JayOn Aug 18, 2024, at 11:11 AM, Kirk Herander via RE-wrenches wrote:Hello All,. I have a Radian 8048 system in service for over 10 years now. It sold back quite normally until the last sev
O 81144sgsrenewables@gmail
On Aug 15, 2024, at 9:49 AM, jay via RE-wrenches wrote:
Hi All,I have an installer buddy where i used to live who's having to try and get a discover lithium warrantied. Its 3 yrs old, 2 years installed.The dealer is closed, and the customer doesn't have t
; If he's not running the generator through a transformer, then he's probably
>> just running 120 vac off one leg of the generator, with no load on the other
>> leg. This imbalance will definitely cause generator failures long term, and
>> not reliably charge the b
issues. Could be settings or an actual board.
Probably not the fet board but could be either the ac or control board.
Jay
> On Aug 15, 2024, at 7:02 PM, Ron Young via RE-wrenches
> wrote:
>
> Hi Wrenches, I have a client who has a 6 year old Outback 3524 inverter. It
> has per
block which makes trying to get info
out of the battery all but impossible as it won’t stay on long enough to
download the info.
Does anyone have a contact who could help my installer/friend with this issue?
thanks
Jay
___
List sponsored by Redwood
HI Michael,
I’d say the AC board on the VFX is suspect. Bad relay.
Yes to #2. That will work just fine.
Good luck
jay
> On Aug 14, 2024, at 4:13 PM, Michael Welch via RE-wrenches
> wrote:
>
> Wrenches. I am hesitant to post here, since I am not really a Wrench. I feel
&g
r, LLC
> Potsdam, NY
> (315) 212-2114 Call/ Text
>
>>> On Aug 13, 2024, at 5:03 PM, Jay via RE-wrenches
>>> wrote:
>>>
>>
>> I hadn’t heard of these. Very ingenious mounting system.
>>
>> Thx
>> Jay
>>
>>>>
I hadn’t heard of these. Very ingenious mounting system.
Thx
Jay
> On Aug 13, 2024, at 2:45 PM, Foxfire Energy via RE-wrenches
> wrote:
>
> We installed a 20kW 48V set in a Grid Tied system in May.. Knowledgeable
> (and friendly) Tech Support.. So far so good.. Certainly
It’s on NAZ solar home page. It didn’t want to link JayOn Aug 13, 2024, at 8:44 AM, Kirpal Khalsa via RE-wrenches wrote:When? Info or link? ThanksKirpalOn Tue, Aug 13, 2024, 6:21 AM Jay via RE-wrenches <re-wrenches@lists.re-wrenches.org> wrote:midnite is having a webinar about the A
midnite is having a webinar about the AIO and batteries.
Sign up.
Jay
___
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address
Since we are asking about that.
Does anyone have any news on Outback?
___
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & setti
connectors included on them are TE PV4-S. i haven't seen those a quite a few years. On Thu, Aug 1, 2024 at 12:15 PM Jay <jay.pe...@gmail.com> wrote:Unfortunately sunpower is about out of business.Warranty might not be possible at this point JayOn Aug 1, 2024, at 10:04 AM, Evan M via RE-
Unfortunately sunpower is about out of business.
Warranty might not be possible at this point
Jay
> On Aug 1, 2024, at 10:04 AM, Evan M via RE-wrenches
> wrote:
>
>
> Anyone happen know the make/model of connectors associated with the Sunpower
> cracking issues a coupl
Sol Ark is definitely not made in america.
Its made by Deye in China.
I don’t know all the rules about what you have to do to call it made in
america, like put a label on it or something, but made in china.
jay
> On Aug 1, 2024, at 6:17 AM, Maverick Brown via RE-wrenches
>
Hi Chad.
Stay away from magnum.
Do you want to keep that 12v or make changes?
Jay
> On Jul 30, 2024, at 5:47 PM, Chad Waits via RE-wrenches
> wrote:
>
>
> Gentlemen,
>
> I ask for this help with the caveat that I have very little knowledge of the
> specifics of
I never did hear why altE folded. Anyone know?On Jul 30, 2024, at 1:50 PM, Richard Nicol via RE-wrenches wrote:Chris Brown of Solampio has purchased the remaining inventory of AltE, including the building. He has extra KV BMS boards for sale as well as some reconditioned batteries, firmware updat
back at some point.
The other thing I just remembered is that there are balancers from a few
companies that I’d recommend ( so does kilovault).
Kilovault and victron are the two that come to mind but are probably others.
Jay
> On Jul 30, 2024, at 12:36 PM, Maverick Brown via RE-wrenc
electronics
thanks in advance
jay
___
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options
anual references. Does anyone have a good, direct number for Fortress tech support that will pick up. I'm getting nothing...Thanks!On Thu, Jul 25, 2024, 7:39 AM Jay via RE-wrenches <re-wrenches@lists.re-wrenches.org> wrote:Hi LewisYes both the 12 and 18 have RSDIt’s a button on the left side
Hi Lewis
Yes both the 12 and 18 have RSD
It’s a button on the left side.
Shuts off AC and PV
Jay
> On Jul 25, 2024, at 7:30 AM, Mac Lewis via RE-wrenches
> wrote:
>
>
> Hello Wrenches,
>
> Does anyone know if the 12kW Envy inverter has remote stop capability?
I don’t know but it’s form factor is very similar to LUX/deye
Handles, door latches, disconnects.
I wonder if it’s a Ali express special?
Jay
> On Jul 24, 2024, at 9:42 AM, Jason Szumlanski via RE-wrenches
> wrote:
>
> Can someone help me identify the inverter in the atta
Hi Drake
What do you mean it off gassed?
Like blew the top off?
> On Jul 24, 2024, at 8:40 AM, Drake Chamberlin via RE-wrenches
> wrote:
>
>
> A severely abused bank of Rolls Surrette batteries had one battery off gas
> heavily on discharge. It seems like the off gassing happens on overcha
y, non UL, no real data ( surprise) super narrow PV window.
Just bizarre what’s out there.
Jay
___
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches@lists.re-wrenches.org
Change list
appreciated
They have a really wide range.
Another brand I’ve worked on is RPS
thanks
jay
> On Jul 22, 2024, at 3:10 PM, Michael Morningstar via RE-wrenches
> wrote:
>
> My pump guy (he's 82 and worked in the business since he was a kid) likes
> them. He tears pum
Does anyone know anything about this company?
https://workhorsepumps.com
I have someone asking me about it.
thanks in advanced.
jay
___
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE
e AIO.
Jay
> On Jul 20, 2024, at 5:24 PM, Dan Fink via RE-wrenches
> wrote:
>
> James Showalter from Signature Solar and Eric Lundgren from Big Battery
> purchased Outback Solar. I have had terrible tech support experiences from
> both of those outfits, they tend to con
HI Howie,
Does the AIO communicate with other brands of batteries?
I concure about using batteries/inverters from same OEM, its my preference.
Jay
> On Jul 20, 2024, at 6:37 PM, Howie Michaelson via RE-wrenches
> wrote:
>
> I have been testing a pre-production model of Midnit
I just checked the OB forums page and there is nothing current. One thing I found says that the new president of OB is the CEO of Big Battery. I don’t know that to be a fact. Which is also somehow related to signature solar/ EG4. My guess is that if/when OB resurfaces it won’t have the same product
directly to see if it reads it, probably
easier with another mate.
It just sucks to not have tech support or anyone on wrenches from some OEMS
Jay
> On Jul 19, 2024, at 10:13 AM, Christopher Warfel via RE-wrenches
> wrote:
>
> This is grid tied system with all firmware upda
Hi jim. WilliamMight be right, but what equipment do you have on this system?Doing a cat 5 unplug,plug back might helpJayOn Jul 18, 2024, at 3:18 PM, William Miller via RE-wrenches wrote:Jim:You may be logged in as a limited access user. Try logging in as installer. William MillerMiller Solar.com
Yes I really like the rack mounts I’m curious about the AES mounts and others that don’t have an enclosure. How does code deal with that? ThxJayOn Jul 17, 2024, at 9:28 AM, Michael Morningstar via RE-wrenches wrote:Because I work mostly alone, I'm digging the rack mounts. Dealing with 200 lb bat
Does anyone have even an crazy idea of why this engineer would say that VFD
drives don’t like generators?
Besides the obvious, IE he doesn’t know what he’s talking about?
thanks everyone
jay
> On Jul 11, 2024, at 11:22 AM, James Jarvis wrote:
>
> There should be no issues. M
Thanks Michael,
Thats what I wanted to confirm.
For some reason the engineer on this project is in way over his head.
OK back to my client
jay
> On Jul 11, 2024, at 11:11 AM, Michael Morningstar via RE-wrenches
> wrote:
>
> I’ve years of experience running vfds on generat
engineer seems to think there is but he won’t say why.
i can’t think of any reason at all?
This generator is only running this one load, the well pump.
jay
___
List sponsored by Redwood Alliance
Pay optional member dues here: http://re
The evault doesn’t see the multiple inputs, just like any battery. The envy % reading via web is working well. And yes it’s a bit weird to the solar from the inverter not add up to the daily charge numbers But it’s working fine If you follow oem charge instructions the open loop voltages are a bit
No problem at all. I just did a system exactly like that. Works fine. JayOn Jun 29, 2024, at 5:49 PM, Kirk Herander via RE-wrenches wrote:All,I'm wondering if there are any precautions if charging a Fortress Evault LFP bank using 1 or more OB charge controllers, in tandem with an Envy inverter P
lines don't"
https://offgridsolar1.com/
e-mail offgridso...@sti.net
text 209 813 0060
On 2024-06-17 2:49 pm, Jay via RE-wrenches wrote:
Is the Outback app working?I can log into my account but not the app?ThxJay___List sponsored by Redw
Is the Outback app working?
I can log into my account but not the app?
Thx
Jay
___
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email
Hi GregHow about this midnite box midnitesolar.comPersonally what I don’t like about single switch A or B is there is an off time. With the midnite box, you switch both on, and turn the off the one you want. That way there is never an off time. Just a thought. JayOn Jun 15, 2024, at 11:19 AM, greg
Call Zonna energy.
It’s most likely 1 of the control boards.
And probably not the power modules.
Not all that uncommon especially for the non A versions.
Jay
> On Jun 9, 2024, at 4:50 PM, Scot Arey via RE-wrenches
> wrote:
>
>
> Longtime Outback user but since the exp
Hi Scot
What a fascinating issue.
I can’t help as to the structural concerns but I like the deck mounts idea to
make sure you don’t have any issues.
Jay
> On May 29, 2024, at 4:17 PM, Scot Arey via RE-wrenches
> wrote:
>
>
> With all our Texas hail storms, we now have roo
type of connector.
Thanks
Jay
___
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches
That is fantastic service! And it also confirms that LFP batteries are actually capable of the same explosive energy ( even more actually) as NMC contrary to the claims made by many that it’s impossible. While I’m using LFP batteries in most systems, it does scare me much more than Lead. JayOn Ma
HI Brad,
Is this off/on grid?
And are the two wells near each other or they just join up at the tank and
float switch?
If you’ve got the power then I’d install just a standard AC centrifugal pump.
Sure uses more power but lasts forever. And is maybe $500 vs $2500
And you’ve said minimal water
HI All
Any recommendations for a off grid installer in Anchorage or SE alaska?
Pls contact me off list
thanks
jay
___
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches@lists.re
Hi JerryWhat equipment are you using to pull steel from that depth?Jay On May 26, 2024, at 3:18 PM, Jerry Shafer via RE-wrenches wrote:Hey wrenchesWater leaks in wells, I just pulled my well pump out at a mere 390 feet, older galvanized 11/4 « steel, where the Water rose and dropped the pipe
And of course using a torch to soften the tubing just enough so that the barb
fitting can insert and then grab into the plastic with the clamps.
For 1” its not needed but helpful. For 1.25”- 2” its needed, or at least I’ve
never been able to get a solid connection without heat.
Jay
> On
aks.
Install the clamps at 120 or 180 degrees from each other is important.
If you want to do it correctly then use a HDPE butt welding machine. I just
never could afford one.
Jay
> On May 26, 2024, at 12:54 PM, Bradley Bassett via RE-wrenches
> wrote:
>
> Just went th
Dave Angelini Offgrid Solar
"we go where powerlines don't"
https://offgridsolar1.com/
e-mail offgridso...@sti.net
text 209 813 0060
On 2024-05-26 4:26 am, Jay via RE-wrenches
wrote:
Hi Brad
With
Hi Brad
With 2 check valves leaking I’d look for a broken pipe or a corroded fitting.
If there is anyway to isolate between the 2 check valves then you could measure
the pressure drop on both sides which should point to the direction of the
leak.
Jay
> On May 25, 2024, at 7:41 PM, Brad
Hi Drake,
What it says to me is that they either fired everyone or said move to tx.
I’ve always joked that if the potential project I’m to work on starts badly it
never gets better.
I still don’t understand why the owners of EG4 would by a legacy inverter
company?
Jay
> On May 24, 2
I was talking to signature solar today.
Signature solar and EG4 are sister companies. I don’t have info if one owns the
other or if they are equal partners?
They did admit they bought OB. But didn’t know if signature or EG4 bought them.
Jay
1 - 100 of 1737 matches