Re: [AFMUG] Battery backup at large sites
Magnum inverters have an AC input cutoff where if it dips below, they invert and cancel charge. Very, very good rugged units. American made with good warranties. On Dec 27, 2016 11:55 AM, "Ken Hohhof" <af...@kwisp.com> wrote: > I’ve never used the Tripp Lite APC series, but I believe their main > purpose is emergency vehicles, RVs, boats, etc. where they switch > automatically between battery and shore power. Using similar units in the > past, I have found one thing to look for is how low the shore (commercial) > power has to be for the transfer switch to switch to batteries. They may > just use a relay, assuming commercial power is either there or it isn’t. > But we get a lot of partial voltage situations like 60 or 80 volts, and a > lot of our electronics won’t run on that. It’s very frustrating to drive > out to a site that is down, and find a fully charged battery string that > isn’t being used because the ATS thinks 80 volts is plenty. > > > > > > *From:* Af [mailto:af-boun...@afmug.com] *On Behalf Of *Josh Corson > *Sent:* Tuesday, December 27, 2016 11:48 AM > *To:* af@afmug.com > *Subject:* Re: [AFMUG] Battery backup at large sites > > > > How about a APC750 or APC1250 tripplite inverter/charger? > > Also I wanted to have a way to monitor how long of runtime the batteries > have remaining...like the APC smart UPS units. > > > On Dec 27, 2016, at 2:52 AM, Forrest Christian (List Account) < > li...@packetflux.com> wrote: > > The tool you're looking for in relation to the monitoring is a packetflux > sitemonitor base unit. > > > > Others can point you toward the chargers. > > > > On Dec 26, 2016 11:36 PM, "Josh Corson" <j...@bluebitnetworks.com> wrote: > > What is everyone using as a battery backup at sites that cannot use a > standard off the shelve UPS? > The site in mention is probably using 500 watts max. The battery side > of things is a no brainer - calculate run time, determine your bank, > buy batteries. > However, what are you using for: > > 1. Inverter / charger > 2. Network monitoring capability when AC goes out with SNMP. > > The hardest challenge I've found is sourcing something for network > monitoring that isn't an all in one charger/inverter like the ICT > models at 1k. > > Always wondered if you could rig a APC network card to work in a battery > bank... > > If anyone could share the layout of their system I'd appreciate it! > > Josh > > Sent from my iPhone > >
Re: [AFMUG] Battery backup at large sites
I’ve never used the Tripp Lite APC series, but I believe their main purpose is emergency vehicles, RVs, boats, etc. where they switch automatically between battery and shore power. Using similar units in the past, I have found one thing to look for is how low the shore (commercial) power has to be for the transfer switch to switch to batteries. They may just use a relay, assuming commercial power is either there or it isn’t. But we get a lot of partial voltage situations like 60 or 80 volts, and a lot of our electronics won’t run on that. It’s very frustrating to drive out to a site that is down, and find a fully charged battery string that isn’t being used because the ATS thinks 80 volts is plenty. From: Af [mailto:af-boun...@afmug.com] On Behalf Of Josh Corson Sent: Tuesday, December 27, 2016 11:48 AM To: af@afmug.com Subject: Re: [AFMUG] Battery backup at large sites How about a APC750 or APC1250 tripplite inverter/charger? Also I wanted to have a way to monitor how long of runtime the batteries have remaining...like the APC smart UPS units. On Dec 27, 2016, at 2:52 AM, Forrest Christian (List Account) <li...@packetflux.com <mailto:li...@packetflux.com> > wrote: The tool you're looking for in relation to the monitoring is a packetflux sitemonitor base unit. Others can point you toward the chargers. On Dec 26, 2016 11:36 PM, "Josh Corson" <j...@bluebitnetworks.com <mailto:j...@bluebitnetworks.com> > wrote: What is everyone using as a battery backup at sites that cannot use a standard off the shelve UPS? The site in mention is probably using 500 watts max. The battery side of things is a no brainer - calculate run time, determine your bank, buy batteries. However, what are you using for: 1. Inverter / charger 2. Network monitoring capability when AC goes out with SNMP. The hardest challenge I've found is sourcing something for network monitoring that isn't an all in one charger/inverter like the ICT models at 1k. Always wondered if you could rig a APC network card to work in a battery bank... If anyone could share the layout of their system I'd appreciate it! Josh Sent from my iPhone
Re: [AFMUG] Battery backup at large sites
How about a APC750 or APC1250 tripplite inverter/charger? Also I wanted to have a way to monitor how long of runtime the batteries have remaining...like the APC smart UPS units. On Dec 27, 2016, at 2:52 AM, Forrest Christian (List Account) < li...@packetflux.com> wrote: The tool you're looking for in relation to the monitoring is a packetflux sitemonitor base unit. Others can point you toward the chargers. On Dec 26, 2016 11:36 PM, "Josh Corson"wrote: > What is everyone using as a battery backup at sites that cannot use a > standard off the shelve UPS? > The site in mention is probably using 500 watts max. The battery side > of things is a no brainer - calculate run time, determine your bank, > buy batteries. > However, what are you using for: > > 1. Inverter / charger > 2. Network monitoring capability when AC goes out with SNMP. > > The hardest challenge I've found is sourcing something for network > monitoring that isn't an all in one charger/inverter like the ICT > models at 1k. > > Always wondered if you could rig a APC network card to work in a battery > bank... > > If anyone could share the layout of their system I'd appreciate it! > > Josh > > Sent from my iPhone >
Re: [AFMUG] Battery backup at large sites
Sent from my iPhone On Dec 27, 2016, at 2:52 AM, Forrest Christian (List Account) < li...@packetflux.com> wrote: The tool you're looking for in relation to the monitoring is a packetflux sitemonitor base unit. Others can point you toward the chargers. On Dec 26, 2016 11:36 PM, "Josh Corson"wrote: > What is everyone using as a battery backup at sites that cannot use a > standard off the shelve UPS? > The site in mention is probably using 500 watts max. The battery side > of things is a no brainer - calculate run time, determine your bank, > buy batteries. > However, what are you using for: > > 1. Inverter / charger > 2. Network monitoring capability when AC goes out with SNMP. > > The hardest challenge I've found is sourcing something for network > monitoring that isn't an all in one charger/inverter like the ICT > models at 1k. > > Always wondered if you could rig a APC network card to work in a battery > bank... > > If anyone could share the layout of their system I'd appreciate it! > > Josh > > Sent from my iPhone >
Re: [AFMUG] Battery backup at large sites
Alpha FXM or Tripplite APS. On 12/27/2016 10:24 AM, Ken Hohhof wrote: http://www.tripplite.com/snmp-web-management-accessory-card-smartpro-smartonline-ups-systems~SNMPWEBCARD/ <http://www.tripplite.com/snmp-web-management-accessory-card-smartpro-smartonline-ups-systems%7ESNMPWEBCARD/> *From:*Af [mailto:af-boun...@afmug.com] *On Behalf Of *Gino Villarini *Sent:* Tuesday, December 27, 2016 10:09 AM *To:* af@afmug.com *Subject:* Re: [AFMUG] Battery backup at large sites Only downside to tripp lite gear is they have no way of remotely monitor them� *From: *Af <af-boun...@afmug.com <mailto:af-boun...@afmug.com>> on behalf of "Jim Bouse [Brazos WiFi]" <j...@brazoswifi.com <mailto:j...@brazoswifi.com>> *Reply-To: *"af@afmug.com <mailto:af@afmug.com>" <af@afmug.com <mailto:af@afmug.com>> *Date: *Tuesday, December 27, 2016 at 11:59 AM *To: *"af@afmug.com <mailto:af@afmug.com>" <af@afmug.com <mailto:af@afmug.com>> *Subject: *Re: [AFMUG] Battery backup at large sites We have been using Tripp Lite APS700HF on many of the sites coupled with 2x 100AH AGM. This gives AC out with very extended runtimes. If we have to add juice we can do it with jumpercables from a truck or a generator. Running a 12v system keeps it simple. Don�t forget the fuses. Jim Bouse Owner Mobile IT Pro - Brazos WiFi 979-985-5912 j...@brazoswifi.com <mailto:j...@brazoswifi.com> *From:*Af [mailto:af-boun...@afmug.com] *On Behalf Of *Josh Baird *Sent:* Tuesday, December 27, 2016 9:39 AM *To:* af@afmug.com <mailto:af@afmug.com> *Subject:* Re: [AFMUG] Battery backup at large sites excessups.com <http://excessups.com> /*Gino Villarini*/ President Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968 On Tue, Dec 27, 2016 at 10:20 AM, Gino Villarini <g...@aeronetpr.com <mailto:g...@aeronetpr.com>> wrote: Where are you sourcing your apc 750XLs from ? *From: *Af <af-boun...@afmug.com <mailto:af-boun...@afmug.com>> on behalf of Josh Luthman <j...@imaginenetworksllc.com <mailto:j...@imaginenetworksllc.com>> *Reply-To: *"af@afmug.com <mailto:af@afmug.com>" <af@afmug.com <mailto:af@afmug.com>> *Date: *Tuesday, December 27, 2016 at 11:06 AM *To: *"af@afmug.com <mailto:af@afmug.com>" <af@afmug.com <mailto:af@afmug.com>> *Subject: *Re: [AFMUG] Battery backup at large sites Old sites we replace/use an APC 750 XL with big batteries from Batteries Plus. We get some good deals on them. New sites or anything we can replace and do DC (24vdc) we'll use Meanwell AD-155B (IIRC) and DR40. From this point forward we'll probably be deploying Netonix switches. If you need sync on the Ethernet ports you'll have to go with Packetflux. Josh Luthman Office: 937-552-2340 <tel:%28937%29%20552-2340> Direct: 937-552-2343 <tel:%28937%29%20552-2343> 1100 Wayne St Suite 1337 Troy, OH 45373 /*Gino Villarini*/ President Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968 On Tue, Dec 27, 2016 at 9:21 AM, Ken Hohhof <af...@kwisp.com <mailto:af...@kwisp.com>> wrote: I�m a little unclear, are you looking for an AC UPS, or to run everything off DC? You mention inverter so I�m thinking you want an AC system? Also, is this going in a controlled environment like a NOC, or will it be in an outdoor temperature environment? And what is your budget? Sounds like you are finding $1,000 too expensive? If you are looking for an AC UPS that you attach your own battery bank to, that is spec�d for outdoor temps, and that has all the features built in, look at Alpha FXM series. Crossover Distribution can get you quotes. FXM650 would meet your power requirements, but I�d look at FXM1100 as long as you�re OK with a 48V battery string. *From:*Af [mailto:af-boun...@afmug.com <mailto:af-boun...@afmug.com>] *On Behalf Of *Gino Villarini *Sent:* Tuesday, December 27, 2016 4:42 AM *To:* af@afmug.com <mailto:af@afmug.com> *Subject:* Re: [AFMUG] Battery backup at large sites Eltek or Emerson Rectifier system On 12/27/16, 2:36 AM, "Af on behalf of Josh Corson" <af-boun...@afmug.com <mailto:af-boun...@afmug.com> /*Gino Villarini*/ President Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968 on behalf of j...@bluebitnetworks.com <mailto:j...@bluebitnetworks.com>> wrote: >What is everyone using as a battery backup at sites that cannot use a >standard off the shelve UPS? >The site in mention is probably using 500 watts max. The battery side >of things is a no brainer - calculate run time, determine your bank, >buy batteries. >However, what are you using for: > >1. Inverter / charger >2. Network monitoring capability when AC goes out with SNMP. > >The hardest challenge I've found is sourcing something for network >monitoring that isn't an all in one charger/inverter like the ICT >models at 1k. > >Always wondered if you could rig a APC network card to work in a battery >bank... > >If anyone could share the layout of their system I'd appreciate it! > >Josh > >Sent from my iPhone
Re: [AFMUG] Battery backup at large sites
http://www.tripplite.com/snmp-web-management-accessory-card-smartpro-smarton line-ups-systems~SNMPWEBCARD/ From: Af [mailto:af-boun...@afmug.com] On Behalf Of Gino Villarini Sent: Tuesday, December 27, 2016 10:09 AM To: af@afmug.com Subject: Re: [AFMUG] Battery backup at large sites Only downside to tripp lite gear is they have no way of remotely monitor them. From: Af <af-boun...@afmug.com <mailto:af-boun...@afmug.com> > on behalf of "Jim Bouse [Brazos WiFi]" <j...@brazoswifi.com <mailto:j...@brazoswifi.com> > Reply-To: "af@afmug.com <mailto:af@afmug.com> " <af@afmug.com <mailto:af@afmug.com> > Date: Tuesday, December 27, 2016 at 11:59 AM To: "af@afmug.com <mailto:af@afmug.com> " <af@afmug.com <mailto:af@afmug.com> > Subject: Re: [AFMUG] Battery backup at large sites We have been using Tripp Lite APS700HF on many of the sites coupled with 2x 100AH AGM. This gives AC out with very extended runtimes. If we have to add juice we can do it with jumpercables from a truck or a generator. Running a 12v system keeps it simple. Don't forget the fuses. Jim Bouse Owner Mobile IT Pro - Brazos WiFi 979-985-5912 j...@brazoswifi.com <mailto:j...@brazoswifi.com> From: Af [mailto:af-boun...@afmug.com] On Behalf Of Josh Baird Sent: Tuesday, December 27, 2016 9:39 AM To: af@afmug.com <mailto:af@afmug.com> Subject: Re: [AFMUG] Battery backup at large sites excessups.com <http://excessups.com> Gino Villarini President Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968 On Tue, Dec 27, 2016 at 10:20 AM, Gino Villarini <g...@aeronetpr.com <mailto:g...@aeronetpr.com> > wrote: Where are you sourcing your apc 750XLs from ? From: Af <af-boun...@afmug.com <mailto:af-boun...@afmug.com> > on behalf of Josh Luthman <j...@imaginenetworksllc.com <mailto:j...@imaginenetworksllc.com> > Reply-To: "af@afmug.com <mailto:af@afmug.com> " <af@afmug.com <mailto:af@afmug.com> > Date: Tuesday, December 27, 2016 at 11:06 AM To: "af@afmug.com <mailto:af@afmug.com> " <af@afmug.com <mailto:af@afmug.com> > Subject: Re: [AFMUG] Battery backup at large sites Old sites we replace/use an APC 750 XL with big batteries from Batteries Plus. We get some good deals on them. New sites or anything we can replace and do DC (24vdc) we'll use Meanwell AD-155B (IIRC) and DR40. From this point forward we'll probably be deploying Netonix switches. If you need sync on the Ethernet ports you'll have to go with Packetflux. Josh Luthman Office: 937-552-2340 <tel:(937)%20552-2340> Direct: 937-552-2343 <tel:(937)%20552-2343> 1100 Wayne St Suite 1337 Troy, OH 45373 Gino Villarini President Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968 On Tue, Dec 27, 2016 at 9:21 AM, Ken Hohhof <af...@kwisp.com <mailto:af...@kwisp.com> > wrote: I'm a little unclear, are you looking for an AC UPS, or to run everything off DC? You mention inverter so I'm thinking you want an AC system? Also, is this going in a controlled environment like a NOC, or will it be in an outdoor temperature environment? And what is your budget? Sounds like you are finding $1,000 too expensive? If you are looking for an AC UPS that you attach your own battery bank to, that is spec'd for outdoor temps, and that has all the features built in, look at Alpha FXM series. Crossover Distribution can get you quotes. FXM650 would meet your power requirements, but I'd look at FXM1100 as long as you're OK with a 48V battery string. From: Af [mailto:af-boun...@afmug.com <mailto:af-boun...@afmug.com> ] On Behalf Of Gino Villarini Sent: Tuesday, December 27, 2016 4:42 AM To: af@afmug.com <mailto:af@afmug.com> Subject: Re: [AFMUG] Battery backup at large sites Eltek or Emerson Rectifier system On 12/27/16, 2:36 AM, "Af on behalf of Josh Corson" <af-boun...@afmug.com <mailto:af-boun...@afmug.com> Gino Villarini President Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968 on behalf of j...@bluebitnetworks.com <mailto:j...@bluebitnetworks.com> > wrote: >What is everyone using as a battery backup at sites that cannot use a >standard off the shelve UPS? >The site in mention is probably using 500 watts max. The battery side >of things is a no brainer - calculate run time, determine your bank, >buy batteries. >However, what are you using for: > >1. Inverter / charger >2. Network monitoring capability when AC goes out with SNMP. > >The hardest challenge I've found is sourcing something for network >monitoring that isn't an all in one charger/inverter like the ICT >models at 1k. > >Always wondered if you could rig a APC network card to work in a battery >bank... > >If anyone could share the layout of their system I'd appreciate it! > >Josh > >Sent from my iPhone
Re: [AFMUG] Battery backup at large sites
Valere-Eltek, compact, has telemetry if you buy the BC-2000 unit. They will even do scheduled battery load tests. From: Gino Villarini Sent: Tuesday, December 27, 2016 3:41 AM To: af@afmug.com Subject: Re: [AFMUG] Battery backup at large sites Eltek or Emerson Rectifier system On 12/27/16, 2:36 AM, "Af on behalf of Josh Corson" <af-boun...@afmug.com Gino Villarini President Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968 on behalf of j...@bluebitnetworks.com> wrote: >What is everyone using as a battery backup at sites that cannot use a >standard off the shelve UPS? >The site in mention is probably using 500 watts max. The battery side >of things is a no brainer - calculate run time, determine your bank, >buy batteries. >However, what are you using for: > >1. Inverter / charger >2. Network monitoring capability when AC goes out with SNMP. > >The hardest challenge I've found is sourcing something for network >monitoring that isn't an all in one charger/inverter like the ICT >models at 1k. > >Always wondered if you could rig a APC network card to work in a battery >bank... > >If anyone could share the layout of their system I'd appreciate it! > >Josh > >Sent from my iPhone
Re: [AFMUG] Battery backup at large sites
Only downside to tripp lite gear is they have no way of remotely monitor them… From: Af <af-boun...@afmug.com<mailto:af-boun...@afmug.com>> on behalf of "Jim Bouse [Brazos WiFi]" <j...@brazoswifi.com<mailto:j...@brazoswifi.com>> Reply-To: "af@afmug.com<mailto:af@afmug.com>" <af@afmug.com<mailto:af@afmug.com>> Date: Tuesday, December 27, 2016 at 11:59 AM To: "af@afmug.com<mailto:af@afmug.com>" <af@afmug.com<mailto:af@afmug.com>> Subject: Re: [AFMUG] Battery backup at large sites We have been using Tripp Lite APS700HF on many of the sites coupled with 2x 100AH AGM. This gives AC out with very extended runtimes. If we have to add juice we can do it with jumpercables from a truck or a generator. Running a 12v system keeps it simple. Don’t forget the fuses. Jim Bouse Owner Mobile IT Pro - Brazos WiFi 979-985-5912 j...@brazoswifi.com<mailto:j...@brazoswifi.com> From: Af [mailto:af-boun...@afmug.com] On Behalf Of Josh Baird Sent: Tuesday, December 27, 2016 9:39 AM To: af@afmug.com<mailto:af@afmug.com> Subject: Re: [AFMUG] Battery backup at large sites excessups.com<http://excessups.com> Gino Villarini President Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968 [cid:aeronet-logo_310cfc3e-6691-4f69-bd49-b37b834b9238.png] On Tue, Dec 27, 2016 at 10:20 AM, Gino Villarini <g...@aeronetpr.com<mailto:g...@aeronetpr.com>> wrote: Where are you sourcing your apc 750XLs from ? From: Af <af-boun...@afmug.com<mailto:af-boun...@afmug.com>> on behalf of Josh Luthman <j...@imaginenetworksllc.com<mailto:j...@imaginenetworksllc.com>> Reply-To: "af@afmug.com<mailto:af@afmug.com>" <af@afmug.com<mailto:af@afmug.com>> Date: Tuesday, December 27, 2016 at 11:06 AM To: "af@afmug.com<mailto:af@afmug.com>" <af@afmug.com<mailto:af@afmug.com>> Subject: Re: [AFMUG] Battery backup at large sites Old sites we replace/use an APC 750 XL with big batteries from Batteries Plus. We get some good deals on them. New sites or anything we can replace and do DC (24vdc) we'll use Meanwell AD-155B (IIRC) and DR40. From this point forward we'll probably be deploying Netonix switches. If you need sync on the Ethernet ports you'll have to go with Packetflux. Josh Luthman Office: 937-552-2340<tel:(937)%20552-2340> Direct: 937-552-2343<tel:(937)%20552-2343> 1100 Wayne St Suite 1337 Troy, OH 45373 Gino Villarini President Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968 [cid:image001.png@01D26026.779DF4F0] On Tue, Dec 27, 2016 at 9:21 AM, Ken Hohhof <af...@kwisp.com<mailto:af...@kwisp.com>> wrote: I’m a little unclear, are you looking for an AC UPS, or to run everything off DC? You mention inverter so I’m thinking you want an AC system? Also, is this going in a controlled environment like a NOC, or will it be in an outdoor temperature environment? And what is your budget? Sounds like you are finding $1,000 too expensive? If you are looking for an AC UPS that you attach your own battery bank to, that is spec’d for outdoor temps, and that has all the features built in, look at Alpha FXM series. Crossover Distribution can get you quotes. FXM650 would meet your power requirements, but I’d look at FXM1100 as long as you’re OK with a 48V battery string. From: Af [mailto:af-boun...@afmug.com<mailto:af-boun...@afmug.com>] On Behalf Of Gino Villarini Sent: Tuesday, December 27, 2016 4:42 AM To: af@afmug.com<mailto:af@afmug.com> Subject: Re: [AFMUG] Battery backup at large sites Eltek or Emerson Rectifier system On 12/27/16, 2:36 AM, "Af on behalf of Josh Corson" <af-boun...@afmug.com<mailto:af-boun...@afmug.com> Gino Villarini President Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968 [cid:image003.png@01D26026.779DF4F0] on behalf of j...@bluebitnetworks.com<mailto:j...@bluebitnetworks.com>> wrote: >What is everyone using as a battery backup at sites that cannot use a >standard off the shelve UPS? >The site in mention is probably using 500 watts max. The battery side >of things is a no brainer - calculate run time, determine your bank, >buy batteries. >However, what are you using for: > >1. Inverter / charger >2. Network monitoring capability when AC goes out with SNMP. > >The hardest challenge I've found is sourcing something for network >monitoring that isn't an all in one charger/inverter like the ICT >models at 1k. > >Always wondered if you could rig a APC network card to work in a battery >bank... > >If anyone could share the layout of their system I'd appreciate it! > >Josh > >Sent from my iPhone
Re: [AFMUG] Battery backup at large sites
We have been using Tripp Lite APS700HF on many of the sites coupled with 2x 100AH AGM. This gives AC out with very extended runtimes. If we have to add juice we can do it with jumpercables from a truck or a generator. Running a 12v system keeps it simple. Don’t forget the fuses. Jim Bouse Owner Mobile IT Pro - Brazos WiFi 979-985-5912 j...@brazoswifi.com From: Af [mailto:af-boun...@afmug.com] On Behalf Of Josh Baird Sent: Tuesday, December 27, 2016 9:39 AM To: af@afmug.com Subject: Re: [AFMUG] Battery backup at large sites excessups.com<http://excessups.com> On Tue, Dec 27, 2016 at 10:20 AM, Gino Villarini <g...@aeronetpr.com<mailto:g...@aeronetpr.com>> wrote: Where are you sourcing your apc 750XLs from ? From: Af <af-boun...@afmug.com<mailto:af-boun...@afmug.com>> on behalf of Josh Luthman <j...@imaginenetworksllc.com<mailto:j...@imaginenetworksllc.com>> Reply-To: "af@afmug.com<mailto:af@afmug.com>" <af@afmug.com<mailto:af@afmug.com>> Date: Tuesday, December 27, 2016 at 11:06 AM To: "af@afmug.com<mailto:af@afmug.com>" <af@afmug.com<mailto:af@afmug.com>> Subject: Re: [AFMUG] Battery backup at large sites Old sites we replace/use an APC 750 XL with big batteries from Batteries Plus. We get some good deals on them. New sites or anything we can replace and do DC (24vdc) we'll use Meanwell AD-155B (IIRC) and DR40. From this point forward we'll probably be deploying Netonix switches. If you need sync on the Ethernet ports you'll have to go with Packetflux. Josh Luthman Office: 937-552-2340<tel:(937)%20552-2340> Direct: 937-552-2343<tel:(937)%20552-2343> 1100 Wayne St Suite 1337 Troy, OH 45373 Gino Villarini President Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968 [cid:image001.png@01D26026.779DF4F0] On Tue, Dec 27, 2016 at 9:21 AM, Ken Hohhof <af...@kwisp.com<mailto:af...@kwisp.com>> wrote: I’m a little unclear, are you looking for an AC UPS, or to run everything off DC? You mention inverter so I’m thinking you want an AC system? Also, is this going in a controlled environment like a NOC, or will it be in an outdoor temperature environment? And what is your budget? Sounds like you are finding $1,000 too expensive? If you are looking for an AC UPS that you attach your own battery bank to, that is spec’d for outdoor temps, and that has all the features built in, look at Alpha FXM series. Crossover Distribution can get you quotes. FXM650 would meet your power requirements, but I’d look at FXM1100 as long as you’re OK with a 48V battery string. From: Af [mailto:af-boun...@afmug.com<mailto:af-boun...@afmug.com>] On Behalf Of Gino Villarini Sent: Tuesday, December 27, 2016 4:42 AM To: af@afmug.com<mailto:af@afmug.com> Subject: Re: [AFMUG] Battery backup at large sites Eltek or Emerson Rectifier system On 12/27/16, 2:36 AM, "Af on behalf of Josh Corson" <af-boun...@afmug.com<mailto:af-boun...@afmug.com> Gino Villarini President Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968 [cid:image003.png@01D26026.779DF4F0] on behalf of j...@bluebitnetworks.com<mailto:j...@bluebitnetworks.com>> wrote: >What is everyone using as a battery backup at sites that cannot use a >standard off the shelve UPS? >The site in mention is probably using 500 watts max. The battery side >of things is a no brainer - calculate run time, determine your bank, >buy batteries. >However, what are you using for: > >1. Inverter / charger >2. Network monitoring capability when AC goes out with SNMP. > >The hardest challenge I've found is sourcing something for network >monitoring that isn't an all in one charger/inverter like the ICT >models at 1k. > >Always wondered if you could rig a APC network card to work in a battery >bank... > >If anyone could share the layout of their system I'd appreciate it! > >Josh > >Sent from my iPhone
Re: [AFMUG] Battery backup at large sites
excessups.com On Tue, Dec 27, 2016 at 10:20 AM, Gino Villarini <g...@aeronetpr.com> wrote: > Where are you sourcing your apc 750XLs from ? > > From: Af <af-boun...@afmug.com> on behalf of Josh Luthman < > j...@imaginenetworksllc.com> > Reply-To: "af@afmug.com" <af@afmug.com> > Date: Tuesday, December 27, 2016 at 11:06 AM > To: "af@afmug.com" <af@afmug.com> > Subject: Re: [AFMUG] Battery backup at large sites > > Old sites we replace/use an APC 750 XL with big batteries from Batteries > Plus. We get some good deals on them. > > New sites or anything we can replace and do DC (24vdc) we'll use Meanwell > AD-155B (IIRC) and DR40. From this point forward we'll probably be > deploying Netonix switches. If you need sync on the Ethernet ports you'll > have to go with Packetflux. > > > Josh Luthman > Office: 937-552-2340 <(937)%20552-2340> > Direct: 937-552-2343 <(937)%20552-2343> > 1100 Wayne St > Suite 1337 > Troy, OH 45373 > > > > *Gino Villarini* > President > Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968 > > On Tue, Dec 27, 2016 at 9:21 AM, Ken Hohhof <af...@kwisp.com> wrote: > >> I’m a little unclear, are you looking for an AC UPS, or to run everything >> off DC? You mention inverter so I’m thinking you want an AC system? >> >> >> >> Also, is this going in a controlled environment like a NOC, or will it be >> in an outdoor temperature environment? >> >> >> >> And what is your budget? Sounds like you are finding $1,000 too >> expensive? >> >> >> >> If you are looking for an AC UPS that you attach your own battery bank >> to, that is spec’d for outdoor temps, and that has all the features built >> in, look at Alpha FXM series. Crossover Distribution can get you quotes. >> FXM650 would meet your power requirements, but I’d look at FXM1100 as long >> as you’re OK with a 48V battery string. >> >> >> >> >> >> *From:* Af [mailto:af-boun...@afmug.com] *On Behalf Of *Gino Villarini >> *Sent:* Tuesday, December 27, 2016 4:42 AM >> *To:* af@afmug.com >> *Subject:* Re: [AFMUG] Battery backup at large sites >> >> >> >> Eltek or Emerson Rectifier system >> >> On 12/27/16, 2:36 AM, "Af on behalf of Josh Corson" <af-boun...@afmug.com >> >> >> >> *Gino Villarini* >> >> President >> >> Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968 >> >> on behalf of j...@bluebitnetworks.com> wrote: >> >> >What is everyone using as a battery backup at sites that cannot use a >> >standard off the shelve UPS? >> >The site in mention is probably using 500 watts max. The battery side >> >of things is a no brainer - calculate run time, determine your bank, >> >buy batteries. >> >However, what are you using for: >> > >> >1. Inverter / charger >> >2. Network monitoring capability when AC goes out with SNMP. >> > >> >The hardest challenge I've found is sourcing something for network >> >monitoring that isn't an all in one charger/inverter like the ICT >> >models at 1k. >> > >> >Always wondered if you could rig a APC network card to work in a battery >> >bank... >> > >> >If anyone could share the layout of their system I'd appreciate it! >> > >> >Josh >> > >> >Sent from my iPhone >> > >
Re: [AFMUG] Battery backup at large sites
The old desktop form factor 750xl is no longer made, we have to get refurbished ones now too On Dec 27, 2016 9:25 AM, "Josh Luthman" <j...@imaginenetworksllc.com> wrote: > Online/Google search. Bunch of them from RefurbUPS/ebay. > > > Josh Luthman > Office: 937-552-2340 <(937)%20552-2340> > Direct: 937-552-2343 <(937)%20552-2343> > 1100 Wayne St > Suite 1337 > Troy, OH 45373 > > On Tue, Dec 27, 2016 at 10:20 AM, Gino Villarini <g...@aeronetpr.com> > wrote: > >> Where are you sourcing your apc 750XLs from ? >> >> From: Af <af-boun...@afmug.com> on behalf of Josh Luthman < >> j...@imaginenetworksllc.com> >> Reply-To: "af@afmug.com" <af@afmug.com> >> Date: Tuesday, December 27, 2016 at 11:06 AM >> To: "af@afmug.com" <af@afmug.com> >> Subject: Re: [AFMUG] Battery backup at large sites >> >> Old sites we replace/use an APC 750 XL with big batteries from Batteries >> Plus. We get some good deals on them. >> >> New sites or anything we can replace and do DC (24vdc) we'll use Meanwell >> AD-155B (IIRC) and DR40. From this point forward we'll probably be >> deploying Netonix switches. If you need sync on the Ethernet ports you'll >> have to go with Packetflux. >> >> >> Josh Luthman >> Office: 937-552-2340 <(937)%20552-2340> >> Direct: 937-552-2343 <(937)%20552-2343> >> 1100 Wayne St >> Suite 1337 >> Troy, OH 45373 >> >> >> >> *Gino Villarini* >> President >> Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968 >> >> On Tue, Dec 27, 2016 at 9:21 AM, Ken Hohhof <af...@kwisp.com> wrote: >> >>> I’m a little unclear, are you looking for an AC UPS, or to run >>> everything off DC? You mention inverter so I’m thinking you want an AC >>> system? >>> >>> >>> >>> Also, is this going in a controlled environment like a NOC, or will it >>> be in an outdoor temperature environment? >>> >>> >>> >>> And what is your budget? Sounds like you are finding $1,000 too >>> expensive? >>> >>> >>> >>> If you are looking for an AC UPS that you attach your own battery bank >>> to, that is spec’d for outdoor temps, and that has all the features built >>> in, look at Alpha FXM series. Crossover Distribution can get you quotes. >>> FXM650 would meet your power requirements, but I’d look at FXM1100 as long >>> as you’re OK with a 48V battery string. >>> >>> >>> >>> >>> >>> *From:* Af [mailto:af-boun...@afmug.com] *On Behalf Of *Gino Villarini >>> *Sent:* Tuesday, December 27, 2016 4:42 AM >>> *To:* af@afmug.com >>> *Subject:* Re: [AFMUG] Battery backup at large sites >>> >>> >>> >>> Eltek or Emerson Rectifier system >>> >>> On 12/27/16, 2:36 AM, "Af on behalf of Josh Corson" < >>> af-boun...@afmug.com >>> >>> >>> >>> *Gino Villarini* >>> >>> President >>> >>> Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968 >>> >>> on behalf of j...@bluebitnetworks.com> wrote: >>> >>> >What is everyone using as a battery backup at sites that cannot use a >>> >standard off the shelve UPS? >>> >The site in mention is probably using 500 watts max. The battery side >>> >of things is a no brainer - calculate run time, determine your bank, >>> >buy batteries. >>> >However, what are you using for: >>> > >>> >1. Inverter / charger >>> >2. Network monitoring capability when AC goes out with SNMP. >>> > >>> >The hardest challenge I've found is sourcing something for network >>> >monitoring that isn't an all in one charger/inverter like the ICT >>> >models at 1k. >>> > >>> >Always wondered if you could rig a APC network card to work in a battery >>> >bank... >>> > >>> >If anyone could share the layout of their system I'd appreciate it! >>> > >>> >Josh >>> > >>> >Sent from my iPhone >>> >> >> >
Re: [AFMUG] Battery backup at large sites
These are going to be old maybe 10+ years old, and electronics doesn’t live forever. If nothing else, capacitors dry up. I have some 1400 RM XL units still running and they haven’t blown up yet, but at some point we can’t rely on scavenged 20th century equipment to run our networks. It should also be noted these do not have temperature compensated charging and vintage APC equipment is known for overcharging batteries anyway. (Less of a problem with large external batteries) From: Af [mailto:af-boun...@afmug.com] On Behalf Of Josh Luthman Sent: Tuesday, December 27, 2016 9:26 AM To: af@afmug.com Subject: Re: [AFMUG] Battery backup at large sites Online/Google search. Bunch of them from RefurbUPS/ebay. Josh Luthman Office: 937-552-2340 Direct: 937-552-2343 1100 Wayne St Suite 1337 Troy, OH 45373 On Tue, Dec 27, 2016 at 10:20 AM, Gino Villarini <g...@aeronetpr.com <mailto:g...@aeronetpr.com> > wrote: Where are you sourcing your apc 750XLs from ? From: Af <af-boun...@afmug.com <mailto:af-boun...@afmug.com> > on behalf of Josh Luthman <j...@imaginenetworksllc.com <mailto:j...@imaginenetworksllc.com> > Reply-To: "af@afmug.com <mailto:af@afmug.com> " <af@afmug.com <mailto:af@afmug.com> > Date: Tuesday, December 27, 2016 at 11:06 AM To: "af@afmug.com <mailto:af@afmug.com> " <af@afmug.com <mailto:af@afmug.com> > Subject: Re: [AFMUG] Battery backup at large sites Old sites we replace/use an APC 750 XL with big batteries from Batteries Plus. We get some good deals on them. New sites or anything we can replace and do DC (24vdc) we'll use Meanwell AD-155B (IIRC) and DR40. From this point forward we'll probably be deploying Netonix switches. If you need sync on the Ethernet ports you'll have to go with Packetflux. Josh Luthman Office: 937-552-2340 <tel:(937)%20552-2340> Direct: 937-552-2343 <tel:(937)%20552-2343> 1100 Wayne St Suite 1337 Troy, OH 45373 Gino Villarini President Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968 On Tue, Dec 27, 2016 at 9:21 AM, Ken Hohhof <af...@kwisp.com <mailto:af...@kwisp.com> > wrote: I’m a little unclear, are you looking for an AC UPS, or to run everything off DC? You mention inverter so I’m thinking you want an AC system? Also, is this going in a controlled environment like a NOC, or will it be in an outdoor temperature environment? And what is your budget? Sounds like you are finding $1,000 too expensive? If you are looking for an AC UPS that you attach your own battery bank to, that is spec’d for outdoor temps, and that has all the features built in, look at Alpha FXM series. Crossover Distribution can get you quotes. FXM650 would meet your power requirements, but I’d look at FXM1100 as long as you’re OK with a 48V battery string. From: Af [mailto:af-boun...@afmug.com <mailto:af-boun...@afmug.com> ] On Behalf Of Gino Villarini Sent: Tuesday, December 27, 2016 4:42 AM To: af@afmug.com <mailto:af@afmug.com> Subject: Re: [AFMUG] Battery backup at large sites Eltek or Emerson Rectifier system On 12/27/16, 2:36 AM, "Af on behalf of Josh Corson" <af-boun...@afmug.com <mailto:af-boun...@afmug.com> Gino Villarini President Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968 on behalf of j...@bluebitnetworks.com <mailto:j...@bluebitnetworks.com> > wrote: >What is everyone using as a battery backup at sites that cannot use a >standard off the shelve UPS? >The site in mention is probably using 500 watts max. The battery side >of things is a no brainer - calculate run time, determine your bank, >buy batteries. >However, what are you using for: > >1. Inverter / charger >2. Network monitoring capability when AC goes out with SNMP. > >The hardest challenge I've found is sourcing something for network >monitoring that isn't an all in one charger/inverter like the ICT >models at 1k. > >Always wondered if you could rig a APC network card to work in a battery >bank... > >If anyone could share the layout of their system I'd appreciate it! > >Josh > >Sent from my iPhone
Re: [AFMUG] Battery backup at large sites
Online/Google search. Bunch of them from RefurbUPS/ebay. Josh Luthman Office: 937-552-2340 Direct: 937-552-2343 1100 Wayne St Suite 1337 Troy, OH 45373 On Tue, Dec 27, 2016 at 10:20 AM, Gino Villarini <g...@aeronetpr.com> wrote: > Where are you sourcing your apc 750XLs from ? > > From: Af <af-boun...@afmug.com> on behalf of Josh Luthman < > j...@imaginenetworksllc.com> > Reply-To: "af@afmug.com" <af@afmug.com> > Date: Tuesday, December 27, 2016 at 11:06 AM > To: "af@afmug.com" <af@afmug.com> > Subject: Re: [AFMUG] Battery backup at large sites > > Old sites we replace/use an APC 750 XL with big batteries from Batteries > Plus. We get some good deals on them. > > New sites or anything we can replace and do DC (24vdc) we'll use Meanwell > AD-155B (IIRC) and DR40. From this point forward we'll probably be > deploying Netonix switches. If you need sync on the Ethernet ports you'll > have to go with Packetflux. > > > Josh Luthman > Office: 937-552-2340 <(937)%20552-2340> > Direct: 937-552-2343 <(937)%20552-2343> > 1100 Wayne St > Suite 1337 > Troy, OH 45373 > > > > *Gino Villarini* > President > Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968 > > On Tue, Dec 27, 2016 at 9:21 AM, Ken Hohhof <af...@kwisp.com> wrote: > >> I’m a little unclear, are you looking for an AC UPS, or to run everything >> off DC? You mention inverter so I’m thinking you want an AC system? >> >> >> >> Also, is this going in a controlled environment like a NOC, or will it be >> in an outdoor temperature environment? >> >> >> >> And what is your budget? Sounds like you are finding $1,000 too >> expensive? >> >> >> >> If you are looking for an AC UPS that you attach your own battery bank >> to, that is spec’d for outdoor temps, and that has all the features built >> in, look at Alpha FXM series. Crossover Distribution can get you quotes. >> FXM650 would meet your power requirements, but I’d look at FXM1100 as long >> as you’re OK with a 48V battery string. >> >> >> >> >> >> *From:* Af [mailto:af-boun...@afmug.com] *On Behalf Of *Gino Villarini >> *Sent:* Tuesday, December 27, 2016 4:42 AM >> *To:* af@afmug.com >> *Subject:* Re: [AFMUG] Battery backup at large sites >> >> >> >> Eltek or Emerson Rectifier system >> >> On 12/27/16, 2:36 AM, "Af on behalf of Josh Corson" <af-boun...@afmug.com >> >> >> >> *Gino Villarini* >> >> President >> >> Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968 >> >> on behalf of j...@bluebitnetworks.com> wrote: >> >> >What is everyone using as a battery backup at sites that cannot use a >> >standard off the shelve UPS? >> >The site in mention is probably using 500 watts max. The battery side >> >of things is a no brainer - calculate run time, determine your bank, >> >buy batteries. >> >However, what are you using for: >> > >> >1. Inverter / charger >> >2. Network monitoring capability when AC goes out with SNMP. >> > >> >The hardest challenge I've found is sourcing something for network >> >monitoring that isn't an all in one charger/inverter like the ICT >> >models at 1k. >> > >> >Always wondered if you could rig a APC network card to work in a battery >> >bank... >> > >> >If anyone could share the layout of their system I'd appreciate it! >> > >> >Josh >> > >> >Sent from my iPhone >> > >
Re: [AFMUG] Battery backup at large sites
Where are you sourcing your apc 750XLs from ? From: Af <af-boun...@afmug.com<mailto:af-boun...@afmug.com>> on behalf of Josh Luthman <j...@imaginenetworksllc.com<mailto:j...@imaginenetworksllc.com>> Reply-To: "af@afmug.com<mailto:af@afmug.com>" <af@afmug.com<mailto:af@afmug.com>> Date: Tuesday, December 27, 2016 at 11:06 AM To: "af@afmug.com<mailto:af@afmug.com>" <af@afmug.com<mailto:af@afmug.com>> Subject: Re: [AFMUG] Battery backup at large sites Old sites we replace/use an APC 750 XL with big batteries from Batteries Plus. We get some good deals on them. New sites or anything we can replace and do DC (24vdc) we'll use Meanwell AD-155B (IIRC) and DR40. From this point forward we'll probably be deploying Netonix switches. If you need sync on the Ethernet ports you'll have to go with Packetflux. Josh Luthman Office: 937-552-2340 Direct: 937-552-2343 1100 Wayne St Suite 1337 Troy, OH 45373 Gino Villarini President Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968 [cid:aeronet-logo_310cfc3e-6691-4f69-bd49-b37b834b9238.png] On Tue, Dec 27, 2016 at 9:21 AM, Ken Hohhof <af...@kwisp.com<mailto:af...@kwisp.com>> wrote: I’m a little unclear, are you looking for an AC UPS, or to run everything off DC? You mention inverter so I’m thinking you want an AC system? Also, is this going in a controlled environment like a NOC, or will it be in an outdoor temperature environment? And what is your budget? Sounds like you are finding $1,000 too expensive? If you are looking for an AC UPS that you attach your own battery bank to, that is spec’d for outdoor temps, and that has all the features built in, look at Alpha FXM series. Crossover Distribution can get you quotes. FXM650 would meet your power requirements, but I’d look at FXM1100 as long as you’re OK with a 48V battery string. From: Af [mailto:af-boun...@afmug.com<mailto:af-boun...@afmug.com>] On Behalf Of Gino Villarini Sent: Tuesday, December 27, 2016 4:42 AM To: af@afmug.com<mailto:af@afmug.com> Subject: Re: [AFMUG] Battery backup at large sites Eltek or Emerson Rectifier system On 12/27/16, 2:36 AM, "Af on behalf of Josh Corson" <af-boun...@afmug.com<mailto:af-boun...@afmug.com> Gino Villarini President Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968 [cid:image002.png@01D26019.E81F73F0] on behalf of j...@bluebitnetworks.com<mailto:j...@bluebitnetworks.com>> wrote: >What is everyone using as a battery backup at sites that cannot use a >standard off the shelve UPS? >The site in mention is probably using 500 watts max. The battery side >of things is a no brainer - calculate run time, determine your bank, >buy batteries. >However, what are you using for: > >1. Inverter / charger >2. Network monitoring capability when AC goes out with SNMP. > >The hardest challenge I've found is sourcing something for network >monitoring that isn't an all in one charger/inverter like the ICT >models at 1k. > >Always wondered if you could rig a APC network card to work in a battery >bank... > >If anyone could share the layout of their system I'd appreciate it! > >Josh > >Sent from my iPhone
Re: [AFMUG] Battery backup at large sites
That Alpha FXM looks like a really nice one-and-done type of solution. Unfortunately if you need A/C, then I think every good option is kind of in that price bracket. If you went all DC you'll have a lot more parts and assembly, and when it's all done you might only save a few hundred bucks.. IMO the reason to use all DC is you'll save enclosure space, gain a little efficiency, and you end up with a modular system you can add new features onto like a switchable PoE injector or what-not. I've used an inverter/charger from AIMS power. I think their smallest unit is 2000 watts though, so it might be a waste for only 600 watts. If you do get an inverter/charger, the cheapest thing you can add to tell if your power is on or off is any managed device that you plug into AC and just ping it. You might use (for example) a WiFi AP; which is convenient to have at your site anyway, but doesn't affect service to customers when it goes down. When that device goes down you know your power is off. The second cheapest thing is a Packetflux Site Monitor, and that gives you a lot more options such as the option to add a current shunt in line with your battery. -- Original Message -- From: "Ken Hohhof" <af...@kwisp.com> To: af@afmug.com Sent: 12/27/2016 9:21:32 AM Subject: Re: [AFMUG] Battery backup at large sites I’m a little unclear, are you looking for an AC UPS, or to run everything off DC? You mention inverter so I’m thinking you want an AC system? Also, is this going in a controlled environment like a NOC, or will it be in an outdoor temperature environment? And what is your budget? Sounds like you are finding $1,000 too expensive? If you are looking for an AC UPS that you attach your own battery bank to, that is spec’d for outdoor temps, and that has all the features built in, look at Alpha FXM series. Crossover Distribution can get you quotes. FXM650 would meet your power requirements, but I’d look at FXM1100 as long as you’re OK with a 48V battery string. From: Af [mailto:af-boun...@afmug.com] On Behalf Of Gino Villarini Sent: Tuesday, December 27, 2016 4:42 AM To:af@afmug.com Subject: Re: [AFMUG] Battery backup at large sites Eltek or Emerson Rectifier system On 12/27/16, 2:36 AM, "Af on behalf of Josh Corson" <af-boun...@afmug.com Gino Villarini President Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968 on behalf of j...@bluebitnetworks.com> wrote: >What is everyone using as a battery backup at sites that cannot use a >standard off the shelve UPS? >The site in mention is probably using 500 watts max. The battery side >of things is a no brainer - calculate run time, determine your bank, >buy batteries. >However, what are you using for: > >1. Inverter / charger >2. Network monitoring capability when AC goes out with SNMP. > >The hardest challenge I've found is sourcing something for network >monitoring that isn't an all in one charger/inverter like the ICT >models at 1k. > >Always wondered if you could rig a APC network card to work in a battery >bank... > >If anyone could share the layout of their system I'd appreciate it! > >Josh > >Sent from my iPhone
Re: [AFMUG] Battery backup at large sites
Old sites we replace/use an APC 750 XL with big batteries from Batteries Plus. We get some good deals on them. New sites or anything we can replace and do DC (24vdc) we'll use Meanwell AD-155B (IIRC) and DR40. From this point forward we'll probably be deploying Netonix switches. If you need sync on the Ethernet ports you'll have to go with Packetflux. Josh Luthman Office: 937-552-2340 Direct: 937-552-2343 1100 Wayne St Suite 1337 Troy, OH 45373 On Tue, Dec 27, 2016 at 9:21 AM, Ken Hohhof <af...@kwisp.com> wrote: > I’m a little unclear, are you looking for an AC UPS, or to run everything > off DC? You mention inverter so I’m thinking you want an AC system? > > > > Also, is this going in a controlled environment like a NOC, or will it be > in an outdoor temperature environment? > > > > And what is your budget? Sounds like you are finding $1,000 too expensive? > > > > If you are looking for an AC UPS that you attach your own battery bank to, > that is spec’d for outdoor temps, and that has all the features built in, > look at Alpha FXM series. Crossover Distribution can get you quotes. > FXM650 would meet your power requirements, but I’d look at FXM1100 as long > as you’re OK with a 48V battery string. > > > > > > *From:* Af [mailto:af-boun...@afmug.com] *On Behalf Of *Gino Villarini > *Sent:* Tuesday, December 27, 2016 4:42 AM > *To:* af@afmug.com > *Subject:* Re: [AFMUG] Battery backup at large sites > > > > Eltek or Emerson Rectifier system > > On 12/27/16, 2:36 AM, "Af on behalf of Josh Corson" <af-boun...@afmug.com > > > > *Gino Villarini* > > President > > Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968 > > on behalf of j...@bluebitnetworks.com> wrote: > > >What is everyone using as a battery backup at sites that cannot use a > >standard off the shelve UPS? > >The site in mention is probably using 500 watts max. The battery side > >of things is a no brainer - calculate run time, determine your bank, > >buy batteries. > >However, what are you using for: > > > >1. Inverter / charger > >2. Network monitoring capability when AC goes out with SNMP. > > > >The hardest challenge I've found is sourcing something for network > >monitoring that isn't an all in one charger/inverter like the ICT > >models at 1k. > > > >Always wondered if you could rig a APC network card to work in a battery > >bank... > > > >If anyone could share the layout of their system I'd appreciate it! > > > >Josh > > > >Sent from my iPhone >
Re: [AFMUG] Battery backup at large sites
I'm a little unclear, are you looking for an AC UPS, or to run everything off DC? You mention inverter so I'm thinking you want an AC system? Also, is this going in a controlled environment like a NOC, or will it be in an outdoor temperature environment? And what is your budget? Sounds like you are finding $1,000 too expensive? If you are looking for an AC UPS that you attach your own battery bank to, that is spec'd for outdoor temps, and that has all the features built in, look at Alpha FXM series. Crossover Distribution can get you quotes. FXM650 would meet your power requirements, but I'd look at FXM1100 as long as you're OK with a 48V battery string. From: Af [mailto:af-boun...@afmug.com] On Behalf Of Gino Villarini Sent: Tuesday, December 27, 2016 4:42 AM To: af@afmug.com Subject: Re: [AFMUG] Battery backup at large sites Eltek or Emerson Rectifier system On 12/27/16, 2:36 AM, "Af on behalf of Josh Corson" <af-boun...@afmug.com Gino Villarini President Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968 on behalf of j...@bluebitnetworks.com <mailto:j...@bluebitnetworks.com> > wrote: >What is everyone using as a battery backup at sites that cannot use a >standard off the shelve UPS? >The site in mention is probably using 500 watts max. The battery side >of things is a no brainer - calculate run time, determine your bank, >buy batteries. >However, what are you using for: > >1. Inverter / charger >2. Network monitoring capability when AC goes out with SNMP. > >The hardest challenge I've found is sourcing something for network >monitoring that isn't an all in one charger/inverter like the ICT >models at 1k. > >Always wondered if you could rig a APC network card to work in a battery >bank... > >If anyone could share the layout of their system I'd appreciate it! > >Josh > >Sent from my iPhone
Re: [AFMUG] Battery backup at large sites
Eltek or Emerson Rectifier system On 12/27/16, 2:36 AM, "Af on behalf of Josh Corson"wrote: >What is everyone using as a battery backup at sites that cannot use a >standard off the shelve UPS? >The site in mention is probably using 500 watts max. The battery side >of things is a no brainer - calculate run time, determine your bank, >buy batteries. >However, what are you using for: > >1. Inverter / charger >2. Network monitoring capability when AC goes out with SNMP. > >The hardest challenge I've found is sourcing something for network >monitoring that isn't an all in one charger/inverter like the ICT >models at 1k. > >Always wondered if you could rig a APC network card to work in a battery >bank... > >If anyone could share the layout of their system I'd appreciate it! > >Josh > >Sent from my iPhone
Re: [AFMUG] Battery backup at large sites
The tool you're looking for in relation to the monitoring is a packetflux sitemonitor base unit. Others can point you toward the chargers. On Dec 26, 2016 11:36 PM, "Josh Corson"wrote: > What is everyone using as a battery backup at sites that cannot use a > standard off the shelve UPS? > The site in mention is probably using 500 watts max. The battery side > of things is a no brainer - calculate run time, determine your bank, > buy batteries. > However, what are you using for: > > 1. Inverter / charger > 2. Network monitoring capability when AC goes out with SNMP. > > The hardest challenge I've found is sourcing something for network > monitoring that isn't an all in one charger/inverter like the ICT > models at 1k. > > Always wondered if you could rig a APC network card to work in a battery > bank... > > If anyone could share the layout of their system I'd appreciate it! > > Josh > > Sent from my iPhone >
Re: [AFMUG] Battery backup at large sites
apc xl series has additional packs, you supposedly can calculate other vendor battery packs to the appropriate number of external packs in the gui I tried tearing the guts of a 750xl out and cobbling a din mount apc, but at the end of the day it was just a grain elevator waiting to explode On Tue, Dec 27, 2016 at 12:36 AM, Josh Corsonwrote: > What is everyone using as a battery backup at sites that cannot use a > standard off the shelve UPS? > The site in mention is probably using 500 watts max. The battery side > of things is a no brainer - calculate run time, determine your bank, > buy batteries. > However, what are you using for: > > 1. Inverter / charger > 2. Network monitoring capability when AC goes out with SNMP. > > The hardest challenge I've found is sourcing something for network > monitoring that isn't an all in one charger/inverter like the ICT > models at 1k. > > Always wondered if you could rig a APC network card to work in a battery > bank... > > If anyone could share the layout of their system I'd appreciate it! > > Josh > > Sent from my iPhone > -- If you only see yourself as part of the team but you don't see your team as part of yourself you have already failed as part of the team.