Re: Survey: Experiences with EMI Consultants

1996-07-17 Thread Stephen Phillips
 Max, 

 It sounds as though you don't have any expertise in-house, so I 
would recommend getting a consultant into the design phase - as 
early as possible.  Alot will depend upon the product though. The 
higher the frequency - the tougher the problems, pcb routing is 
critical.  Do you have to meet Class A or Class B?  Is the enclosure 
metal, is it already designed,   I would suggest that the 
consultant work directly with the design engineers during schematic 
review, a mechanical review, and largely during pcb layout.  The 
more you do then, the less you have do worry about later, you 
may find that you don't even need the consultant through the 
testing and certification phase.  But if you wait UNTIL then, 
you may wind up losing alot of sleep.  

 You don't say where you're located, so I can't recommend anyone 
specific, but in my experience - yes - there are excellent consultants 
available - worldwide (but also, buyer beware).  

 I hope this helps some.  

 Best regards, 

 Stephen C. Phillips 
 Telecom Engineer 
 === 
 Direct: 508-244-8116   Fax: 508-244-8039 

   |   |Cisco Systems, Inc. 
  ||| |||   Core Business Unit 
 |   |  250 Apollo Drive  
   |   |Chelmsford, MA 01824 
 |  U.S.A. 
 E-mail: step...@cisco.com 
 === 
 All opinions expressed are my own, not necessarily those of Cisco Systems. 

- Begin Included Message -

>From owner-emc-p...@mail.ieee.org Fri Jul 12 16:52:15 1996
To: emc-p...@ieee.org
Subject: Survey: Experiences with EMI Consultants
From: Max 

I am wondering if anyone has had experience with hiring EMI/EMC
consultants to solve their problems and what sort of results they have
obtained.

I would be very interested in any details that anyone might be able to
provide.  For example, did you use a consultant after the system was
prototyped or early on, during the design process.  Was the consultant
most useful at providing board-level, design suggestions or was he
most helpful at providing after-the-fact type fixes that pertain to
cabinet design and I/O cable filtering and grounding techniques, etc. 
Also, did the consultant, deal directly with design engineers or
interface with just one person within your company, etc.?

Does anyone have the names of any good consultants?

Max Kelson
mkel...@es.com

- End Included Message -


RE: creepage and clearance in IEC1010-1

1996-07-17 Thread T . Haworth






 Clause D1, Annex D, IEC1010-1
 
 This clause does imply that you can reduce C&C  (ignore the entire 
 annex) provided certain conditions are met;
 
 -Circuit is not mains
 -All single fault tests in 4.4 do not result in hazard
 -No hazard accessible after fault
 
 Without this clause being present the whole of annex D would be 
 mandatory whenever invoked by the standard.  I can't see any other 
 way to interpret it.
 
 It may not help you very much though.  If you reduce your C&Cs to 
 the point where they only meet the requirements of Basic 
 Insulation then clause 4.4.2.11 may demand that this Insulation  
 be short-circuited.  (Failure of basic insulation is a Single 
 Fault).
 
 Individual cases differ but obviously be very careful if you are 
 relying on fault testing to get you through. I would rather keep 
 my C&Cs within Annex D if function permits it.
  
 Regards,
 
 
 Trevor Haworth.
 Product Approvals Manager
 Design to Distribution Ltd
 t.hawo...@kid0109.wins.icl.co.uk
 
 
 


Re: Voltage for 3 pahse systems

1996-07-17 Thread Chris Dupres
Hi Moshe.

You wrote:

>  Would anyone know what are the voltages/frequencies used in the 
>  various countries/environments around the world for high power 
>  industrial 3 phase equipment?
>  
As others have suggested, a very good document id the British 
Standards book/wallchart "World Electricity Supplies". supplied by 
their export support group 'THE' (Technical Help for Exporters).

Apart from the voltages and frequencies, this book gives invaluable 
information on the TYPE of supply. e.g. :
Star. centre Neutral, centre Earth. (5 wire)
Star, centre Neutral/Earth (4 wire)
Delta, one point earthed, centre tapped one leg earth,
Open Delta, centre tapped one side, end earthed.

...and just about every possible combination of three phases, neutral 
and earth mathmatically possible!  Most are used somewhere on this 
mortal coil of ours.


Chris Dupres
EMC Specialist. VG Microtech.
cdup...@vacgen.fisons.co.uk
tel +44 (0) 1825 761077
fax +44 (0) 1825 768343
'Opinions expressed are personal, not necessarily Corporate'


Analog phone for ISDN BRI in Australia

1996-07-17 Thread austest
Phones, (either analogue or digial) that interface via the ISDN 
(BRI or PRI) have the ability to make calls to PSTN telephones. 
Rightly or wrongly, Austel require all ISDN products with telephones
(digital or POTS via ISDN) to comply with Austel TS004 for voice 
frequency performance, along with safety to TS001, EMI & TS013 
or TS014 of course.

We can test to TS013 BRI part B (layer 1), which calls up TS004. 

Martin Garwood
aust...@mpx.com.au


Courtesy of RCIC
http://uc.com/compliance_engineering/




Re: Analog phone for ISDN BRI in Australia

1996-07-17 Thread DAVID_C_MITCHELL
Item Subject: Analog phone for ISDN BRI in Australia
Received: from relay.hp.com by hpausa1.aus.hp.com with ESMTP
(1.37.109.16/15.5+ECS 3.4 Openmail) id AA025600275; Tue, 16 Jul 1996 
22:31:18 +1000
Received: from ruebert.ieee.org by relay.hp.com with ESMTP
(1.37.109.16/15.5+ECS 3.3) id AA259060271; Tue, 16 Jul 1996 05:31:11 
-0700
Received: (from daemon@localhost) by ruebert.ieee.org (8.7.5/8.7.3) id GAA19286 
for emc-pstc-list; Tue, 16 Jul 1996 06:07:42 -0400 (EDT)
From: pman...@shiva.com
Message-Id: <199607161001.gaa09...@apollo.gti.net>
List-Post: emc-pstc@listserv.ieee.org
Date: 16 Jul 96 05:59:23
To: t...@sdd.hp.com
Cc: emc-p...@ieee.org
Subject: Analog phone for ISDN BRI in Australia
X-Mailer: Allaire Cold Fusion 1.5
Sender: owner-emc-p...@majordomo.ieee.org
Precedence: bulk
Reply-To: pman...@shiva.com
X-Resent-To: Multiple Recipients 
X-Listname: emc-pstc
X-List-Description: Product Safety Tech. Committee, EMC Society
X-Info: Help requests to  emc-pstc-requ...@majordomo.ieee.org
X-Info: [Un]Subscribe requests to  majord...@majordomo.ieee.org
X-Moderator-Address: emc-pstc-appro...@majordomo.ieee.org

...

Item Subject: Analog phone for ISDN BRI in Australia
 Greetings Pierre-Marie,
 
 I had such a product approved a couple of years ago with another 
 company.  What is tested depends heavily on the test lab being used 
 but in most cases its valid. They are concerned with such things as 
 gain, distortion, tone generation (eg. busy tone and dial tone) and 
 DTMF recognition. They may also test the PSTN line voltage and ring 
 wave for voltage and safety.
 
 Austel are concerned with protecting the network, the users and 
 maintaining a level of performance.
 
 If you have a specific issue you wish to discuss, I suggest you talk 
 to Dr Vembanor Marney on +61 3 9828 7328. He the senior test report 
 reviewer for Austel.
 
 
 I hope this helps
 
 
 Regards 
 
 David
 
 --
 David Mitchell
 Regulatory Specialist 
 Hewlett-Packard Australian Telecom Operation
 347 Burwood Highway, Burwood East, Victoria, Australia 3151. 
 Internet: david_c_mitch...@aus.hp.com
 HPdesk: DAVID C. MITCHELL / HP-Australia, om2
 Phone: +61 3 9210 5610, Telnet 2105610, Fax: +61 3 92105570
 --




__ Reply Separator 
_
Subject: Analog phone for ISDN BRI in Australia
Author:  Non-HP-owner-emc-pstc (owner-emc-p...@majordomo.ieee.org) at 
HP-Australia,shargw1
List-Post: emc-pstc@listserv.ieee.org
Date:16/7/96 5:59 AM


On our ISDN BRI product there is an analog input phone to be used on the 
ISDN.We have been requested to test this feature based on TS003,related to 
PSTN.However there is NO external connection to PSTN rather to ISDN network. 
This analog input should be covered by the TS013 (ISDN BRI). 
Has somebody experienced the same problem ? 
thanks for your answer
Pierre-Marie ANDRE pan...@shiva.com
Shiva International 
 
Pierre-Marie Andre
pman...@shiva.com
 
 
Courtesy of RCIC
http://uc.com/compliance_engineering/
 
 


Re: crrepage and clearance in IEC1010-1

1996-07-17 Thread D. Teninty
John,

Look at Clause 3.8 of ANSI/ISA S82.01-1994 (US harmonized version of IEC 1010-1)
for a definition of "mains".  Clause D.1 means that if your circuit (input or 
measuring) 
DOES NOT connect to the mains, then you may test according to the single fault 
conditions of Clause 4.4.  For example; if your instrument takes a measurement 
of the 
voltage at a wall socket of 120 V then you must meet the CREEPAGE AND 
CLEARANCE requirements .

Dan Teninty P.E.
Senior Product Safety Engineer 
teni...@tc.fluke.com
FLUKE  Corporation
Everett, Washington
(206) 356-6035
(206) 356-6490 fax




I=92ve never been able to fully determine the intent and meaning of
clause D.1 of IEC1010-1, which states:



Suppose I have a double insulation system which relies on both
supplementary insulation and basic values of creepage and
clearance (C&C) to keep the operator safe from hazardous live
(non-mains) conductors.  Couldn=92t I invoke D.1 to permit me to
make my C&Cs as small as I want, thereby effectively reducing my
entire insulation system to that of basic levels? =20

Am I completely missing the meaning of  D.1, and if so, can
anybody explain the intent and ramifications of this clause?  =20

Regards,
John Quinlan
quinl...@voicenet.com
=20





Re: Voltage for 3 pahse syst

1996-07-17 Thread Tony Fredriksson

Hi,

The World Electric Guide website URL is

 http://www.cris.com/~kropla/electric.htm

Enjoy.

tony_fredriks...@netpower.com

 --
From: Kazimier Gawrzyjal
To: Moshe Valdman
Cc: emc-pstc
Subject: Re: Voltage for 3 pahse syst
List-Post: emc-pstc@listserv.ieee.org
Date: Tuesday, July 16, 1996 12:54PM

  RE>Voltage for 3 pahse systems  7/16/96
   Kaz-ESN 765-4805

Moshe,

I  believe there exists a document, put out by the U.S. Department of =
Commerce (National Technical Information Service), titled " Electric =
Current Abroad 1991 Edition".  By the title, this document is likely out =
of date but still highly useful.. It outlines power systems throughout =
the world as well as the type of attachment plugs used in principal =
cities throughout the world.

There may also be a website available.

Regards,
Kaz Gawrzyjal
Safety Engineer
Nortel
0307...@nt.com

 --
List-Post: emc-pstc@listserv.ieee.org
Date: 7/16/96 10:35 AM
To: Kazimier Gawrzyjal
From: Moshe Valdman
   - E X T E R N A L L Y  O R I G I N A T E D  M E S S A G E -

 Hello everyone,

 Sorry, I asked this several days ago and got no response, so maybe =
the
 email just didn't come through.

 Would anyone know what are the voltages/frequencies used in the
 various countries/environments around the world for high power
 industrial 3 phase equipment?

 thanks
 moshe valdman


 -- RFC822 Header Follows --
Received: by nmisq2.miss.nt.com with SMTP;16 Jul 1996 10:33:31 -0400
Received: from ruebert.ieee.org by corpgate.rich.nt.com with SMTP (PP);
  Tue, 16 Jul 1996 14:31:26 +
Received: (from daemon@localhost) by ruebert.ieee.org (8.7.5/8.7.3) id =
JAA23446
  for emc-pstc-list; Tue, 16 Jul 1996 09:44:15 -0400 (EDT)
List-Post: emc-pstc@listserv.ieee.org
Date: Tue, 16 Jul 96 16:34:16 EST
From: Moshe Valdman 
Message-Id: <9606168375.aa837560...@mail.stil.scitex.com>
To: emc-p...@ieee.org
Subject: Voltage for 3 pahse systems
Sender: owner-emc-p...@majordomo.ieee.org
Precedence: bulk
Reply-To: Moshe Valdman 
X-Resent-To: Multiple Recipients 
X-Listname: emc-pstc
X-List-Description: Product Safety Tech. Committee, EMC Society
X-Info: Help requests to emc-pstc-requ...@majordomo.ieee.org
X-Info: [Un]Subscribe requests to majord...@majordomo.ieee.org
X-Moderator-Address: emc-pstc-appro...@majordomo.ieee.org




RE: EN60950 Transition Periods for ITE

1996-07-17 Thread George Sparacino/UB Networks
Hello All,

My question involves license upgrades for EN60950.  I have an ITE product that 
was tested and approved to 60950 1988.
TUV notified me in April, 1996 that, as of Jan 1st 1996,  my product license 
was no longer valid and that I would have to update to EN60950 A2 1993 
(minimum).  The gating factor here turns out to be the third party power supply 
which meets EN60950 A2, 1991.  There would be an additional cost (payable to 
TUV of course) involved to upgrade the  power supply license not to mention any 
redesign.   I'd rather not go through this if it's not necessary.

I have a chart which explains the transition periods for EN60950.  This chart 
comes from TUV.  The way I am reading it, it tells me that for products 
certified before March 1 1995,  EN60950  A2 1991 is good until 3/1/2000.

Is my interpretation correct?? or is EN 60950 A2 1993 the minimum 
acceptable version for existing ITE products?

As always, all related view points are appreciated.

Thanks,
George Sparacino
508-691-4635


Re: TTE Directive as it applies to VSATs

1996-07-17 Thread Victor L. Boersma
You should have come to the seminar we gave last week in Toronto and San Jose as
it was stimulated by the proposed new CTE (Connected Telecommunications
Equipment)
Directive.  The proposal is still being worked and if there is a draft text, it
is not out yet.

However, one of the facets of the new proposal is to do away with all "a-priori"
testing and
rely on "a-posteriori" surveillance, for all telecom terminal equipment.  It is
going to be a couple
of years before you see it.  By that time, if you get a-posteriori" surveilled,
you'd better
have your act together because any equipment that fails to meet the essential
requirements
of the new Directive (NOT ETSI Standards) will be found "defective" and subject
to the full
force of the Product Liability Directive with fines up to 70 M ecus.

Ciao,


Vic