Re: wire size

2003-01-22 Thread Ronald R. Wellman

Here is what I have:

Total Cross Sectional Area (mm)^2(Brown  Sharpe) AWG of single conductor
107.1459
84.9487000
67.433300
53.48210
42.40611
33.62362
26.66743
21.14744
16.76395
13.29936
10.54967
8.36748
6.63269
5.260410
4.172811
3.310312
2.624513
2.081614
1.651315
1.309016
1.038717
0.823518
0.652719
0.517620
0.410421
0.325622
0.258123
0.204724
0.162425
0.128826
0.102027
0.081028
0.064229
0.051030
0.040431
0.032032
0.025433
0.020134
0.016035
0.012736
0.010037
0.008038
0.006339
0.005040



At 04:02 PM 1/22/2003 -0500, jgoedd...@tycoint.com wrote:

Safety people,

I would like to know what the standard wire sizes are in Europe, comparable
to 12AWG, 14AWG, 16AWG, 18AWG solid.

Would anyone across the pond be willing to assist on this. Or, anyone else
that has the info.

Thank you

  James  Goedderz
  Product Safety Engineer
  Tyco Safety Products - Sensormatic
 

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
  majord...@ieee.org
with the single line:
  unsubscribe emc-pstc

For help, send mail to the list administrators:
  Ron Pickard:  emc-p...@hypercom.com
  Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
  Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
 http://ieeepstc.mindcruiser.com/
 Click on browse and then emc-pstc mailing list




This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list



ESD

2003-01-22 Thread drcuthbert

This probably comes under the heading of due diligence. 

   Dave Cuthbert



Kris,

In my reading of the standard, and the next modification will include
that clearly, you need to test discharges to the shell of the USB
connector, as there will not be a connector in there all the time.

There is another strong argument: The user might plug a charged (e.g.
hand-held) device into the USB port.

Of course, the main criteria is survival, as you cannot test
connectivity if there is no USB device.

But if you have multiple USB connectors, another USB device might loose
connection when discharging to a different USB connector.

David Pommerenke



This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list



Surge requirements for DC power supplies

2003-01-22 Thread Gandler, Mark

Hello Group,
does anybody aware of any standard or requirement for DC power port surges
for indoor ( central office ) applications?
I know EN 55024 (IEC 61000-4-5) specify surge tests for DC ports that may
connect to outside lines.
It could be in Europe (-48V or -60V) or North America; ETSI, EN , BellCore:
anything goes.
Thanks in advance,
Mark Gandler
Ciena



This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list



RE: wire size

2003-01-22 Thread Sylvia Toma
This is a multi-part message in MIME format.


The following is an useful link for wire size conversion:

http://www.eraser.com/main.cgi?m=wirecalc

Attached is a pdf file from the same website for wire size conversion
(i.e. AWG to mm).

Sylvia


From: jgoedd...@tycoint.com [mailto:jgoedd...@tycoint.com]
Sent: Wednesday, January 22, 2003 1:02 PM
To: emc-p...@majordomo.ieee.org
Subject: wire size



Safety people,

I would like to know what the standard wire sizes are in Europe,
comparable
to 12AWG, 14AWG, 16AWG, 18AWG solid.

Would anyone across the pond be willing to assist on this. Or, anyone
else
that has the info.

Thank you

 James  Goedderz
 Product Safety Engineer
 Tyco Safety Products - Sensormatic
 


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list

Title: RE: wire size








The following is an useful link for wire size conversion:


http://www.eraser.com/main.cgi?m=wirecalc


Attached is a pdf file from the same website for wire size conversion

(i.e. AWG to mm).


Sylvia


-Original Message-

From: jgoedd...@tycoint.com [mailto:jgoedd...@tycoint.com]

Sent: Wednesday, January 22, 2003 1:02 PM

To: emc-p...@majordomo.ieee.org

Subject: wire size




Safety people,


I would like to know what the standard wire sizes are in Europe,

comparable

to 12AWG, 14AWG, 16AWG, 18AWG solid.


Would anyone across the pond be willing to assist on this. Or, anyone

else

that has the info.


Thank you


 James Goedderz

 Product Safety Engineer

 Tyco Safety Products - Sensormatic

 


---

This message is from the IEEE EMC Society Product Safety

Technical Committee emc-pstc discussion list.


Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/


To cancel your subscription, send mail to:

 majord...@ieee.org

with the single line:

 unsubscribe emc-pstc


For help, send mail to the list administrators:

 Ron Pickard: emc-p...@hypercom.com

 Dave Heald: davehe...@attbi.com


For policy questions, send mail to:

 Richard Nute: ri...@ieee.org

 Jim Bacher: j.bac...@ieee.org


All emc-pstc postings are archived and searchable on the web at:

 http://ieeepstc.mindcruiser.com/

 Click on browse and then emc-pstc mailing list






wire_conversion_chart.pdf
Description: Binary data


Re: wire size

2003-01-22 Thread Andre Boons

James,

12AWG= 4.0 mm2
14AWG= 2.5 mm2
16AWG= 1.5 mm2
18AWG= 0.75mm2

Regards,
Andre



From: jgoedd...@tycoint.com
Reply-To: jgoedd...@tycoint.com
To: emc-p...@majordomo.ieee.org
Subject: wire size
Date: Wed, 22 Jan 2003 16:02:08 -0500


Safety people,

I would like to know what the standard wire sizes are in Europe, comparable
to 12AWG, 14AWG, 16AWG, 18AWG solid.

Would anyone across the pond be willing to assist on this. Or, anyone else
that has the info.

Thank you

  James  Goedderz
  Product Safety Engineer
  Tyco Safety Products - Sensormatic
 

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
  majord...@ieee.org
with the single line:
  unsubscribe emc-pstc

For help, send mail to the list administrators:
  Ron Pickard:  emc-p...@hypercom.com
  Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
  Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
 http://ieeepstc.mindcruiser.com/
 Click on browse and then emc-pstc mailing list


_
Hotmail: je gratis e-mail ! http://www.msn.be/hotmail



This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list



RE: ESD Contact discharge fitted connector

2003-01-22 Thread Pommerenke, David

Kris,

In my reading of the standard, and the next modificaiton will include
that clearly, you need to test discharges to the shell of the USB
connector, as there will not be a connector in there all the time.

There is another strong arguemnt: The user might plug a charged (e.g.
hand-held) device into the USB port.

Of course, the main criteria is survival, as you cannot test
connectivity if there is no USB device.

But if you have multiple USB connectors, another USB device might loose
connection when discharging to a different USB connector.

David Pommerenke





From: Carpentier Kristiaan [mailto:carpenti...@thmulti.com] 
Sent: Wednesday, January 22, 2003 10:48 AM
To: emc-p...@majordomo.ieee.org
Subject: ESD Contact discharge fitted connector


Hello group,

A Class II product has 3 interfaces.
2 interfaces have plastic connectors, with no metal shell.
3rd interface is USB plastic connector but with metal shell.

The housing of the product is plastic (non conductive)
The USB connector is fitted with a USB plug molded in plastic.

Test set-up for immunity testing (ESD) is done with all interface plugs
connected to verify performance of all interfaces.
Consequently, no conductive parts are accessible and contact discharge
must
not be applied.
But the product can also used without USB connection; the USB connector
shell becomes then accessible.

Question:
Is ESD Contact test required on USB connector without plug taken into
account that USB performance cannot be monitored at that time (and the
other
interfaces must be verified in another way)?

More generic: can we exclude ESD contact testing by fitting all
connectors
with plugs on a product ?

FYI:
IEC61000-4-5+A1+A2 states that Contact ESD is not required (par 8.3.1 c)
for
those points and surfaces of equipment which are no longer accessibel
after
FIXED installation or after following the instructions for use.

Regards,
Kris



This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list



RE: Three Phase Power in Japan?

2003-01-22 Thread Evangeline Cometa

John:
I briefly scanned the quoted database. Approval mark for China is now CCC
(China Compulsory Certification) which replaces CCEE and CCIB as of May 1,
2002 but fully implemented May 1, 2003. References could be made available
off-line if you wish.

There is also PSE mark in a circle for Japan for non-specified items and
S-JQA mark(voluntary). T-Mark under DENTORI has been replaced by the PSE
marks under DENAN Law.

Also, if I may add, although some countries may not have approval marks, a
certificate of conformity must be obtained as customs clearance document for
any imported shipment (such as Kuwait and Saudi Arabia).

Thanks,
Evangeline Cometa
CSA International

 -Original Message-
 From: John Barnes [mailto:jrbar...@iglou.com]
 Sent: Wednesday, January 22, 2003 2:10 PM
 To: rbus...@es.com; emc-p...@ieee.org
 Subject: Re: Three Phase Power in Japan?
 
(snip)
 *  INTERNATIONAL PRIMARY POWER, PLUGS, LANGUAGES, APPROVAL MARKS, AND 
APPROVAL AGENCIES, at
http://www.dbicorporation.com/internat/internat.htm
(full database covering 300 countries, 360KB, 50+ pages 
 printed out).
 
(snip)
 If you spot any errors or major omissions in it, please let me know so
 that I can fix them.
 
 Thanks!
   John Barnes KS4GL, PE, NCE, ESDC Eng, SM IEEE
   dBi Corporation
   http://www.dbicorporation.com/
 
 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.
 
 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/
 
 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc
 
 For help, send mail to the list administrators:
  Ron Pickard:  emc-p...@hypercom.com
  Dave Heald:   davehe...@attbi.com
 
 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
  Jim Bacher: j.bac...@ieee.org
 
 All emc-pstc postings are archived and searchable on the web at:
 http://ieeepstc.mindcruiser.com/
 Click on browse and then emc-pstc mailing list
 





--IMPORTANT NOTICE-- 
This message is intended only for the use of the person or organization to
which it is addressed, and may contain information that is privileged,
confidential and exempt from disclosure under applicable law. If the reader
of this message is not the intended recipient, or responsible for delivering
the message to the intended recipient, you are hereby notified that any
dissemination, distribution or copying of this communication is strictly
prohibited. If you have received this communication in error, please notify
the sender immediately by email or telephone and delete the original message
immediately.  Thank you.


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list



RE: Acoustic noise calculations for multiple shelves

2003-01-22 Thread drcuthbert

Quite right for uncorrelated noise. 

To add to this discussing we can think about the response of the human ear
to sound
level. A 3 dB increase in SPL does not sound twice as loud. If I 
remember correctly it takes a 6-8 dB increase to sound twice as loud. So
is the
goal to meet a standard or for operator comfort? 

  Dave Cuthbert
  Micron Tech


From: Ken Javor [mailto:ken.ja...@emccompliance.com]
Sent: Wednesday, January 22, 2003 10:56 AM
To: Luttrell, Lyle; 'Gandler, Mark'; emc-p...@majordomo.ieee.org
Subject: Re: Acoustic noise calculations for multiple shelves



I would further amplify on this comment.  It is not just a 10 log vs. 20 log
calculation.  Sound power is the quantity of interest, so by definition it
is a 10 log relationship .  But someone said add 3 dB for each added
component.  That is incorrect.  You only add 3 dB for the second component.
The issue is that the sound pressure level (exclusive of localized
interference effects) adds as the square root of the sum of the squares.
And that is what you get when you use 10 log(number of units).


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list



wire size

2003-01-22 Thread jgoedd...@tycoint.com

Safety people,

I would like to know what the standard wire sizes are in Europe, comparable
to 12AWG, 14AWG, 16AWG, 18AWG solid.

Would anyone across the pond be willing to assist on this. Or, anyone else
that has the info.

Thank you

 James  Goedderz
 Product Safety Engineer
 Tyco Safety Products - Sensormatic
 


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list



RE: Acoustic noise calculations for multiple shelves (Correction)

2003-01-22 Thread Chris Maxwell

Ahhh!  Guilty!  Thanks Ken.

From my posting below, the part about 3dB for each shelf is WRONG!!.   
Hopefully, I didn't corrupt any innocent minds.  It would be more correct to
say 3dB for each factor of two, 1 to 2, 2 to 4...  I'm glad that I wasn't
designing any airplanes today!  

SNIP
For sound, the worst case would be to add 3dB  for each shelf.  However, in
the real world, the noise probably won't all add together (there will be
power/phase/frequency differences).  
SNIP

Chris Maxwell | Design Engineer - Optical Division
email chris.maxw...@nettest.com | dir +1 315 266 5128 | fax +1 315 797 8024

NetTest | 6 Rhoads Drive, Utica, NY 13502 | USA
web www.nettest.com | tel +1 315 797 4449 | 




 -Original Message-
 From: Ken Javor [SMTP:ken.ja...@emccompliance.com]
 Sent: Wednesday, January 22, 2003 12:56 PM
 To:   Luttrell, Lyle; 'Gandler, Mark'; emc-p...@majordomo.ieee.org
 Subject:  Re: Acoustic noise calculations for multiple shelves
 
 
 I would further amplify on this comment.  It is not just a 10 log vs. 20 log
 calculation.  Sound power is the quantity of interest, so by definition it
 is a 10 log relationship .  But someone said add 3 dB for each added
 component.  That is incorrect.  You only add 3 dB for the second component.
 The issue is that the sound pressure level (exclusive of localized
 interference effects) adds as the square root of the sum of the squares.
 And that is what you get when you use 10 log(number of units).
 
 
 


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list



Re: Three Phase Power in Japan?

2003-01-22 Thread John Barnes

Rick,
The bookletWorld Electricity Supplies, 5th Edition   published by
BSi in April 1989 says:
*  Japan (East):
   -  50+/-0.2Hz
   -  Household voltages 200/100(K), 100(L)
   -  Commercial voltages 200/100(H)(K)
   -  Industrial voltages 6.6kV, 200/100(H), 200(G)(J)
   -  Voltage tolerance +/-10%
*  Japan (West):
   -  60+/-0.1Hz
   -  Household voltages 210/105(K), 200/100(K), 100(L)
   -  Commercial voltages 210/105(H)(K), 200/100(K), 100(L)
   -  Industrial voltages 22kV, 6.6kV, 210/105(H), 200/100(H)
   -  Voltage tolerance +/-10%

(G) is three-phase delta; four-wire; earthed mid point of phase
(H) is three-phase open delta; four-wire; earthed mid point of phase
(J) is three-phase open delta; three-wire; earthed junction of phases
(K) is single-phase; three-wire; earthed mid point (same as we use in 
the United States)
(L) is single-phase; two-wire; earthed end of phase

This booklet is one of the very few sources that discusses the topology
of various countries' electrical power distribution systems.  It costs
65 English pounds, and you can order it from BSi at
http://www.bsi-global.com/Technical+Information/Publications/
_Publications/tig38.xalter

This is one of the 60 sources that Oscar Overton and I used to compile
our web pages:
*  INTERNATIONAL POWER, PLUGS, AND LANGUAGES, at
   http://www.dbicorporation.com/internat/intpower.htm
   (summary covering 240 countries, 60KB, 9 pages printed out)
*  INTERNATIONAL PRIMARY POWER, PLUGS, LANGUAGES, APPROVAL MARKS, AND 
   APPROVAL AGENCIES, at
   http://www.dbicorporation.com/internat/internat.htm
   (full database covering 300 countries, 360KB, 50+ pages printed out).

I am incorporatingINTERNATIONAL POWER, PLUGS, AND LANGUAGES
into the book that I am writing for Kluwer,Robust Electronic Design
Reference   , to be published late this year.

If you spot any errors or major omissions in it, please let me know so
that I can fix them.

Thanks!
John Barnes KS4GL, PE, NCE, ESDC Eng, SM IEEE
dBi Corporation
http://www.dbicorporation.com/


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list



Re: Acoustic noise calculations for multiple shelves

2003-01-22 Thread Ken Javor

I would further amplify on this comment.  It is not just a 10 log vs. 20 log
calculation.  Sound power is the quantity of interest, so by definition it
is a 10 log relationship .  But someone said add 3 dB for each added
component.  That is incorrect.  You only add 3 dB for the second component.
The issue is that the sound pressure level (exclusive of localized
interference effects) adds as the square root of the sum of the squares.
And that is what you get when you use 10 log(number of units).


From: Luttrell, Lyle lluttr...@peakstor.com
To: 'Gandler, Mark' mgand...@ciena.com, emc-p...@majordomo.ieee.org
Subject: RE: Acoustic noise calculations for multiple shelves
Date: Wed, Jan 22, 2003, 9:23 AM



 Mark,
 You need to know what type of level you are working with.
 Sound power level (re 1pW) of multiple sources is straightforward: 10*log(n)
 = 13 dB for n=20. This is essentially independent of measurement
 environment.
 Sound pressure level (re 20uPa) depends on the sound power level plus the
 environment (measurement distance and room conditions). If you have a sound
 pressure level of a unit measured in free space conditions at a distance,
 the level due to multiple identical sources in the same environment will
 typically be no more than 10*log(n) because the distance to the acoustic
 centers of all sources will not be identical.

 Lyle F. Luttrell, PE
 PeAk Storage Solutions, Div of MaxOptix
 303-664-8286 fax 303-664-8299
 lluttr...@peakstor.com

 -Original Message-
 From: Gandler, Mark [mailto:mgand...@ciena.com]
 Sent: Tuesday, January 21, 2003 4:31 PM
 To: emc-p...@majordomo.ieee.org
 Subject: Acoustic noise calculations for multiple shelves


 Hello Group!
 Imagine you are going to install 20 small chassis (shelves) in one rack in
 Central Office.
 If you know your acoustic noise level from one chassis, is it any way to
 calculate total noise?
 Sorry, if it is not the smartest question.
 Please reply!!! Need an answer!!!
 Thanks,
 Mark Gandler
 Ciena

 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.

 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc

 For help, send mail to the list administrators:
  Ron Pickard:  emc-p...@hypercom.com
  Dave Heald:   davehe...@attbi.com

 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
  Jim Bacher: j.bac...@ieee.org

 All emc-pstc postings are archived and searchable on the web at:
 http://ieeepstc.mindcruiser.com/
 Click on browse and then emc-pstc mailing list

 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.

 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc

 For help, send mail to the list administrators:
  Ron Pickard:  emc-p...@hypercom.com
  Dave Heald:   davehe...@attbi.com

 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
  Jim Bacher: j.bac...@ieee.org

 All emc-pstc postings are archived and searchable on the web at:
 http://ieeepstc.mindcruiser.com/
 Click on browse and then emc-pstc mailing list
 


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list



RE: Acoustic noise calculations for multiple shelves

2003-01-22 Thread Gandler, Mark

Lyle and Everybody How answered my question!!!
Thank you very much for the fast and clear responses!
It is great to have this forum.
Mark Gandler
Ciena


From: Luttrell, Lyle [mailto:lluttr...@peakstor.com]
Sent: Wednesday, January 22, 2003 7:24 AM
To: Gandler, Mark; emc-p...@majordomo.ieee.org
Subject: RE: Acoustic noise calculations for multiple shelves



Mark,
You need to know what type of level you are working with.
Sound power level (re 1pW) of multiple sources is straightforward: 10*log(n)
= 13 dB for n=20. This is essentially independent of measurement
environment.
Sound pressure level (re 20uPa) depends on the sound power level plus the
environment (measurement distance and room conditions). If you have a sound
pressure level of a unit measured in free space conditions at a distance,
the level due to multiple identical sources in the same environment will
typically be no more than 10*log(n) because the distance to the acoustic
centers of all sources will not be identical. 

Lyle F. Luttrell, PE
PeAk Storage Solutions, Div of MaxOptix
303-664-8286 fax 303-664-8299
lluttr...@peakstor.com


From: Gandler, Mark [mailto:mgand...@ciena.com] 
Sent: Tuesday, January 21, 2003 4:31 PM
To: emc-p...@majordomo.ieee.org
Subject: Acoustic noise calculations for multiple shelves


Hello Group!
Imagine you are going to install 20 small chassis (shelves) in one rack in
Central Office.
If you know your acoustic noise level from one chassis, is it any way to
calculate total noise?
Sorry, if it is not the smartest question.
Please reply!!! Need an answer!!!
Thanks,
Mark Gandler
Ciena


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list



way OT: (was RE: jurisdiction, overlap, and delegation in USA rules.)

2003-01-22 Thread Peter L. Tarver

This discussion is getting astray from the content
requirements of the list.  If, after this posting, anyone
wishes to continue this discussion, I invite you to take it
off the list.  I'd be pleased to participate.

Still not quite correct, John, but I can see how an outsider
might consider it semantical.  The arrangement is bottom-up,
rather than delegated from the top down.  In fighting occurs
when the higher level of government oversteps its bounds.
It's kind of like, you're not the boss of me, that we
bloody colonists told Mother.

As to delegation, the US Constitution spells out the
authority of the federal government and everything else is
left to the state and local governments.  Each state has a
similar constitution that more or less does the same thing
with county and municipal governments.  For instance, the
Tenth Amendment to the US Constitution makes it clear that
whatever authority is not explicitly given to the federal
government is reserved to the states (I suppose this could
be interpreted as delegation, but delegation implies you
will do this, whereas the Constitution says, we're not
going to do that, but you can if you want to.).

Where this gets muddled is when the Hamiltonians get a wild
hair that there oughtta be a law about this and that, and
in the process infringe on states rights or individual
rights of the citizenry.  Sometimes by unfunded mandate,
sometimes by directly trying to increase the centralization
of government, sometimes by blatant usurpation.  Usurpation
most often occurs by the Executive Branch departments'
issuing edicts from their lesser, included bodies that,
where through the necessary and proper clause of the
Constitution, Congress has given their regulations the
power of law.


Regards,

Peter L. Tarver, PE
Product Safety Manager
Sanmina-SCI Homologation Services
San Jose, CA
peter.tar...@sanmina-sci.com

 From: John Woodgate
 Sent: Tuesday, January 21, 2003 1:04 PM

 OK, this is a semantic issue. IMHO, 'delegation'
 is the appropriate word
 if there is a written law that prescribes how
 authority is allocated.
 If, OTOH, it is a situation like English 'common
 law', which is not
 necessarily written as a statute but stems from
 tradition and case law,
 then 'supersession' may be the better word. I
 *think* that the autonomy
 of the US states is of that nature, the federal
 Constitution simply
 affirming what was already established.
 --
 Regards, John Woodgate



This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list



ESD Contact discharge fitted connector

2003-01-22 Thread Carpentier Kristiaan

Hello group,

A Class II product has 3 interfaces.
2 interfaces have plastic connectors, with no metal shell.
3rd interface is USB plastic connector but with metal shell.

The housing of the product is plastic (non conductive)
The USB connector is fitted with a USB plug molded in plastic.

Test set-up for immunity testing (ESD) is done with all interface plugs
connected to verify performance of all interfaces.
Consequently, no conductive parts are accessible and contact discharge must
not be applied.
But the product can also used without USB connection; the USB connector
shell becomes then accessible.

Question:
Is ESD Contact test required on USB connector without plug taken into
account that USB performance cannot be monitored at that time (and the other
interfaces must be verified in another way)?

More generic: can we exclude ESD contact testing by fitting all connectors
with plugs on a product ?

FYI:
IEC61000-4-5+A1+A2 states that Contact ESD is not required (par 8.3.1 c) for
those points and surfaces of equipment which are no longer accessibel after
FIXED installation or after following the instructions for use.

Regards,
Kris



This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list



RE: Acoustic noise calculations for multiple shelves

2003-01-22 Thread Luttrell, Lyle

Mark,
You need to know what type of level you are working with.
Sound power level (re 1pW) of multiple sources is straightforward: 10*log(n)
= 13 dB for n=20. This is essentially independent of measurement
environment.
Sound pressure level (re 20uPa) depends on the sound power level plus the
environment (measurement distance and room conditions). If you have a sound
pressure level of a unit measured in free space conditions at a distance,
the level due to multiple identical sources in the same environment will
typically be no more than 10*log(n) because the distance to the acoustic
centers of all sources will not be identical. 

Lyle F. Luttrell, PE
PeAk Storage Solutions, Div of MaxOptix
303-664-8286 fax 303-664-8299
lluttr...@peakstor.com


From: Gandler, Mark [mailto:mgand...@ciena.com] 
Sent: Tuesday, January 21, 2003 4:31 PM
To: emc-p...@majordomo.ieee.org
Subject: Acoustic noise calculations for multiple shelves


Hello Group!
Imagine you are going to install 20 small chassis (shelves) in one rack in
Central Office.
If you know your acoustic noise level from one chassis, is it any way to
calculate total noise?
Sorry, if it is not the smartest question.
Please reply!!! Need an answer!!!
Thanks,
Mark Gandler
Ciena


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list



Language Requirements for User Interfaces--CE Mark

2003-01-22 Thread don_macart...@selinc.com

Dear Group:

From the harmonized list of standards published in the official journal of
European communities, I do not see any CE Mark standards/requirements which
cover the
Languages of User Interfaces for products sold into Europe.

Do any such requirements exist?

Thanks in advance for any guidance you may be able to provide.
Don




This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list



RE: Acoustic noise calculations for multiple shelves

2003-01-22 Thread Chris Maxwell

I saw a posting which said add 6dB for a factor of 2.  That is incorrect; when
you are dealing with sound.  My apologies to this poster; no disrespect
intended.  

When dealing with sound and power, add 3dB for a factor of two.

A factor of two only works out to 6dB if you are dealing with voltage, field
strength (and possibly some other measurements).   

There was a long thread which went into the gory mathematical details about a
year ago.  I'll spare everyone the details; but I'd be glad to explain to
anyone who contacts me offline.

For sound, the worst case would be to add 3dB for each shelf.  However, in the
real world, the noise probably won't all add together (there will be
power/phase/frequency differences).  

  I saw Paul Hare's response which said to add 13dB for 20 chassis.  That
sounds about right to me ;-) 

Chris Maxwell | Design Engineer - Optical Division
email chris.maxw...@nettest.com | dir +1 315 266 5128 | fax +1 315 797 8024

NetTest | 6 Rhoads Drive, Utica, NY 13502 | USA
web www.nettest.com | tel +1 315 797 4449 | 







This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list



Re: Japanese Laser Requirements

2003-01-22 Thread T.Sato

On Mon, 20 Jan 2003 09:26:16 -0600,
  rick_hokan...@datacard.com wrote:

 Does anyone have any experience with selling Class IV Lasers in Japan?
 Does Japan follow the same International standards as Europe/ US for Laser
 safety?

We have JIS C 6802, which is a modified version of IEC 60825-1.

Portable laser products are covered by Consumer Product Safety Law,
and procedure including third-party certification would be required
for products covered by the Law.

Regards,
Tom


Tomonori Sato  vef00...@nifty.ne.jp
URL: http://member.nifty.ne.jp/tsato/



This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list



Re: Acoustic noise calculations for multiple shelves

2003-01-22 Thread John Woodgate

I read in !emc-pstc that Neil Helsby nei...@solid-state-logic.com
wrote (in 20030122.8281...@mis.configured.host) about 'Acoustic noise
calculations for multiple shelves' on Wed, 22 Jan 2003:
The simple answer is that the result will be logarithmic – double the 
noise and you add 6 dB. 

The noises are uncorrelated (largely), so you add 3 dB, not 6.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list



Re: Acoustic noise calculations for multiple shelves

2003-01-22 Thread Neil Helsby

The simple answer is that the result will be logarithmic – double the 
noise and you add 6 dB. In practice it probably isn't and neither will 
the on-site result when compared to your office measurements unless all 
conditions are identical.

We measure the audio noise (mainly from fans) from our products in a 
studio environment. Noise is directional and over the length of a product
noise from one end has little effect on the noise measurement from the 
other end. Studio finish absorbs much of the noise but it is not 
acoustically dead. Now take the product into a metal lined room and, due 
to reflections, the measurement levels increase.

Not much help I'm afraid but hope it gives food for thought.

Neil Helsby


**
This email and any files transmitted with it are confidential and
intended solely for the use of the individual or entity to whom they
are addressed. If you have received this email in error please notify
the system manager.

This footnote also confirms that this email message has been swept by
MIMEsweeper for the presence of computer viruses.

www.mimesweeper.com
**



This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list



EU - Theme: Single Market, Regulation, New and Global Approach

2003-01-22 Thread John Allen

Hi Folks

Just found a page on the Commission site which lists all the various
Commission guides to the Directives (LVD, EMC etc), i.e:

http://europa.eu.int/comm/enterprise/library/lib-regulation/libr-regulation.
html

Worth a look!

Regards

John Allen
Technical Consultant
Electromagnetics, Safety and Reliability Group
ERA Technology Ltd
Cleeve Rd
Leatherhead
Surrey KT22 7SA
Tel:+44 (0) 1372-367025 (Direct)
+44 (0) 1372-367000 (Switchboard)
Fax:+44 (0) 1372-367102 (Fax)




*
Copyright ERA Technology Ltd. 2002. (www.era.co.uk). All rights reserved. 
The information supplied in this Commercial Communication should be treated
in confidence.
No liability whatsoever is accepted for any loss or damage 
suffered as a result of accessing this message or any attachments.

_
This e-mail has been scanned for viruses by the WorldCom Internet Managed
Scanning Service - powered by MessageLabs. For further information visit
http://www.worldcom.com


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list



RE: Acoustic noise calculations for multiple shelves

2003-01-22 Thread JP Hare

Hi Mark,

If you understand the fact that adding two sources of the same level gives
you a 3dB increase, you can do some quick addition.

Let's say one of your small chassis has a noise level of 75dB.  If you add a
second one you would get a total noise level of 78dB.  (Of course this does
not consider cancellation due to superposition, but at least this is a worst
case scenario.)  If you add another pair of chassis (i.e. total of four),
you get to 81 dB.  And so on and so on...

When the noise levels are different, then it becomes a little more
difficult.  Without going into great detail here, you should add 13dB to the
level of a single chassis to get the noise level for 20 chassis...

Hope this helps...
Paul Hare




From: owner-emc-p...@majordomo.ieee.org
[mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of Gandler, Mark
Sent: Tuesday, January 21, 2003 6:31 PM
To: emc-p...@majordomo.ieee.org
Subject: Acoustic noise calculations for multiple shelves



Hello Group!
Imagine you are going to install 20 small chassis (shelves) in one rack in
Central Office.
If you know your acoustic noise level from one chassis, is it any way to
calculate total noise?
Sorry, if it is not the smartest question.
Please reply!!! Need an answer!!!
Thanks,
Mark Gandler
Ciena


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list



This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list



RMCEMC Bonus February meeting

2003-01-22 Thread Charles Grasso

To all interested parties:

The RMCEMC is having a bonus February meeting:

Presenter:  Colin Brench, HP Principal Member of technical Staff (Bio)

Date :Feb 5th 2003

Location :   Front Range Community College, Westminster Colorado. Room
Timberline (S117)

Times :5:30 -6:30 Social Hour at the Community College Cafeteria.
6:45 : Assemble at the room
7:00- 9:00 Presentations

What we will see: 1) Antenna Behavior and Use - (What Really goes on during
a test?!
2) Understanding EMI Shield Behavior in Real Product 
Environments

Please go to our website: http://www.ieee.org/rmcemc for full details

Thank you
Charles Grasso
Vice-Chair



This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list