EN60950-1 Table 5B error?

2006-06-13 Thread emc-p...@ieee.org
Referring to the 2nd last column (between independent secondary
circuits, working voltage U 42.4Vpk), why would Functional insulation
require a 500V test but Basic/Supplemental/Reinforced have no test?  Is
this table wrong?

For components (optocoupler, SMT transformer) crossing a Functional
isolation boundary between an SELV circuit and another SELV circuit (an
ethernet circuit in this case), do I need to specify electric strength
requirements?  

Thanks,

Jim Eichner, P.Eng. 
Compliance Engineering Manager
Xantrex Technology Inc. 
e-mail: jim.eich...@xantrex.com 
web: www.xantrex.com 
Any opinions expressed are those of my invisible friend.
Confidentiality Notice: This email message, including any attachments,
is for the sole use of the intended recipient(s) and may contain
confidential and privileged information. Any unauthorized review, use,
disclosure or distribution is prohibited. If you are not the intended
recipient, please contact the sender by reply e-mail and destroy all
copies of the original message.

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to emc-p...@ieee.org

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

 Scott Douglas   emcp...@ptcnh.net
 Mike Cantwell   mcantw...@ieee.org

For policy questions, send mail to:

 Jim Bacher: j.bac...@ieee.org
 David Heald:emc-p...@daveheald.com

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc



Digilog design and tesla coils

2006-06-13 Thread emc-p...@ieee.org
Hi All,

I have posted the first real Doug Unplugged informal podcast on 
digilog design and a story about my Tesla coil. Looks like I will be 
posting new shows on Wednesday and on the weekend to start. Maybe 
daily at some point.

The URL for this show is:

4 1/2 minute mp3 file:

http://emcesd-podcast.com/unplugged/2006/June/2006-0613up.mp3

same file with .dcs ending in case you can't download an mp3 file:

http://emcesd-podcast.com/unplugged/2006/June/2006-0613up.dcs

I would like some feedback as to whether my more formal podcasts or 
these new informal ones are preferred.

The Unplugged home is:

http://emcesd-podcast.com/unplugged

My podcast page home is:

http://emcesd-podcast.com

Also send me some technical questions you think I might be able to 
help with and I will try to answer them in a podcast. You can remain 
anonymous if you like as the source of the question.

Doug

-- 

 ___  _   Doug Smith
  \  / )  P.O. Box 1457
   =  Los Gatos, CA 95031-1457
_ / \ / \ _   TEL/FAX: 408-356-4186/358-3799
  /  /\  \ ] /  /\  \ Mobile:  408-858-4528
|  q-( )  |  o  |Email:   d...@dsmith.org
  \ _ /]\ _ / Website: http://www.dsmith.org


-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to emc-p...@ieee.org

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

 Scott Douglas   emcp...@ptcnh.net
 Mike Cantwell   mcantw...@ieee.org

For policy questions, send mail to:

 Jim Bacher: j.bac...@ieee.org
 David Heald:emc-p...@daveheald.com

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc



Re: EN 60204-1: 1997 vs. 1998 vs. 2006

2006-06-13 Thread emc-p...@ieee.org
In message p0623090bc0b4a85899ce@[10.247.58.220], dated Tue, 13 Jun 
2006, Nick Williams nick.willi...@conformance.co.uk writes

The last list of machinery standards to be published in the OJ was 
dated 31 December 2005 and I wouldn't be surprised if there was a 12 
month gap before the next one. Likewise, the last LVD list was 16 
Novermber 2005 and I'd expect a 12 month gap for the next.

People are complaining about this, because the standards process is 
continuous, and an 11 month delay in updating the OJ is causing 
problems, especially when a standard is amended to correct errors.

Who mentioned EN 55022 then? I wouldn't do such a thing. (;-)
-- 
OOO - Own Opinions Only. Try www.jmwa.demon.co.uk and www.isce.org.uk
2006 is YMMVI- Your mileage may vary immensely.

John Woodgate, J M Woodgate and Associates, Rayleigh, Essex UK

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to emc-p...@ieee.org

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

 Scott Douglas   emcp...@ptcnh.net
 Mike Cantwell   mcantw...@ieee.org

For policy questions, send mail to:

 Jim Bacher: j.bac...@ieee.org
 David Heald:emc-p...@daveheald.com

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc



Re: EN 60204-1: 1997 vs. 1998 vs. 2006

2006-06-13 Thread emc-p...@ieee.org
In message 
ofbcc5ed40.67f57bbb-on8825718c.005ed5ef-8825718c.005f0...@teal.com, 
dated Tue, 13 Jun 2006, pat.law...@slpower.com writes
I need to order the current issue of EN 60204-1 (Safety of machinery –
 Electrical equipment of machines).   When I went to the EUR-Lex 
website at
http://ec.europa.eu/enterprise/newapproach/standardization/harmstds/refl
ist/machines.html
it lists EN 60204-1:1997 as the current edition, with no amendments. 
 So far, so good.

But when I look at websites that sell standards, I see listings for 
1997, 1998, and 2006.
- Should I simply buy the 1997 edition, or are there 
changes/corrections that forced the 1998 version to be published?

The '1998' version is the national implementation of the formal 
'publication' by CENELEC of the EN dated 1997, which was probably 
published in November or December 1997, so the national standards carry 
the 1998 date.

- Is the 2006 version on the verge of announcement in the OJ?  If so, 
it sounds like that should be used to evaluate my product.

 From the public part of the CENELEC web site, you can get:

Standard reference EN 60204-1:200X
Reference document IEC 60204-1:2005 (Modified)
Technical body CLC/TC 44X
IEC technical body IEC/TC 44

Dor 2006-06-01
Dav -
Doa 2006-12-01
Dop 2007-06-01
Dow 2009-06-01

The doa (date of adoption)  is not till December, so it would be a bit 
premature to use it as soon as it's published.
-- 
OOO - Own Opinions Only. Try www.jmwa.demon.co.uk and www.isce.org.uk
2006 is YMMVI- Your mileage may vary immensely.

John Woodgate, J M Woodgate and Associates, Rayleigh, Essex UK

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to emc-p...@ieee.org

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

 Scott Douglas   emcp...@ptcnh.net
 Mike Cantwell   mcantw...@ieee.org

For policy questions, send mail to:

 Jim Bacher: j.bac...@ieee.org
 David Heald:emc-p...@daveheald.com

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc



Re: RF Power Amplifiers

2006-06-13 Thread emc-p...@ieee.org
In message c0b458a0.3ddd1%ken.ja...@emccompliance.com, dated Tue, 13 
Jun 2006, Ken Javor ken.ja...@emccompliance.com writes
A quick calculation will show that if an immunity requirement of 10 V/m 
is imposed at 105 MHz on a 420 MHz tuned receiver with a sensitivity of 
100 dBm, the harmonic content at 420 MHz needs to be on the order of 
100 dB down from the carrier.  That is quite unrealistic even for a VHF 
source for which 420 MHz is out-of-band, let alone a broadband 
amplifier and antenna combination that covers (typically) 80 - 1000 MHz.

Of course. You need to use very arcane methods to do that sort of test. 
A narrow band-pass filter at 105 MHz plus notch filters at harmonic 
frequencies. Complex and difficult. Even more exotic techniques are 
known.
-- 
OOO - Own Opinions Only. Try www.jmwa.demon.co.uk and www.isce.org.uk
2006 is YMMVI- Your mileage may vary immensely.

John Woodgate, J M Woodgate and Associates, Rayleigh, Essex UK

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to emc-p...@ieee.org

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

 Scott Douglas   emcp...@ptcnh.net
 Mike Cantwell   mcantw...@ieee.org

For policy questions, send mail to:

 Jim Bacher: j.bac...@ieee.org
 David Heald:emc-p...@daveheald.com

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc



Re: RF Power Amplifiers

2006-06-13 Thread emc-p...@ieee.org
That is definitely the way to deal with the issue.  The receiver IF filter
will definitely reject energy 500 kHz off the tuned frequency in a traditional
superheterodyne receiver.  I could still see the front end being desensitized,
 but it will take more harmonic energy to do that.



From: Bob Richards b...@toprudder.com
List-Post: emc-pstc@listserv.ieee.org
Date: Tue, 13 Jun 2006 10:25:50 -0700 (PDT)
To: emc-p...@ieee.org
Subject: Re: RF Power Amplifiers




I'm not familiar with the specific test requirements for receivers, but the
1000-4-3 spec allows step sizes of 1% of the fundamental. If not required to
do otherwise, I would arrange the test frequencies so the subharmonic
frequencies are avoided, IOW, instead of testing at 105 MHz, test at 104.5 and
105.5 MHz. I would think the selectivity of most receivers would reject these
signals.
 

 
Bob Richards, NCT.

Ken Javor ken.ja...@emccompliance.com wrote:
 


A quick calculation will show that if an immunity requirement of 10 V/m is
imposed at 105 MHz on a 420 MHz tuned receiver with a sensitivity of -100 dBm,
the harmonic content at 420 MHz needs to be on the order of 100 dB down from
the carrier.  That is quite unrealistic even for a VHF source for which 420
MHz is out-of-band, let alone a broadband amplifier and antenna combination
that covers (typically) 80 - 1000 MHz.
 



-  This
message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list.Website:  http://www.ieee-pses.org/ 

To post a message to the list, send your e-mail to emc-p...@ieee.org 

Instructions:  http://listserv.ieee.org/request/user-guide.html 

List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators: 

Scott Douglas   emcp...@ptcnh.net Mike Cantwell  
mcantw...@ieee.org 

For policy questions, send mail to: 

Jim Bacher: j.bac...@ieee.org David Heald:   
emc-p...@daveheald.com 

All emc-pstc postings are archived and searchable on the web at: 

http://www.ieeecommunities.org/emc-pstc 



-  This
message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. Website: http://www.ieee-pses.org/ 

To post a message to the list, send your e-mail to emc-p...@ieee.org 


Instructions: http://listserv.ieee.org/request/user-guide.html 


List rules: http://www.ieee-pses.org/listrules.html 


For help, send mail to the list administrators: 


Scott Douglas emcp...@ptcnh.net Mike Cantwell mcantw...@ieee.org 


For policy questions, send mail to: 


Jim Bacher: j.bac...@ieee.org David Heald: emc-p...@daveheald.com 


All emc-pstc postings are archived and searchable on the web at: 


http://www.ieeecommunities.org/emc-pstc 




Re: EN 60204-1: 1997 vs. 1998 vs. 2006

2006-06-13 Thread emc-p...@ieee.org
Unless the information on the CENELEC web site is out of date, there 
isn't an EN 60204-1:2006 yet. There  _is_ an IEC 60204-1:2005 but the 
CENELEC site indicates that there will be modifications (differences) 
between the IEC and EN versions.

The 1997/1998 confusion probably arises because the original CENELEC 
version of the EN was dated 1997 but BSI did not get round to 
publishing it until 1998, so BS EN 60204-1:1998 is the same as EN 
60204-1:1997.

The last list of machinery standards to be published in the OJ was 
dated 31 December 2005 and I wouldn't be surprised if there was a 12 
month gap before the next one. Likewise, the last LVD list was 16 
Novermber 2005 and I'd expect a 12 month gap for the next.

If the new version of EN 60204-1 is imminent then it will be 
published before this and will presumably appear in the next OJ list, 
but if you have a product which needs evaluation right now, I would 
not hesitate to use the 1997 version.

Nick.




At 10:17 am -0700 13/6/06, pat.law...@slpower.com wrote:
Hi all:

I need to order the current issue of EN 60204-1 (Safety of 
machinery - Electrical equipment of machines).   When I went to the 
EUR-Lex website at
http://ec.europa.eu/enterprise/newappr
ach/standardization/harmstds/reflist/machines.html
it lists EN 60204-1:1997 as the current edition, with no amendments. 
 So far, so good.

But when I look at websites that sell standards, I see listings for 
1997, 1998, and 2006.
- Should I simply buy the 1997 edition, or are there 
changes/corrections that forced the 1998 version to be published?
- Is the 2006 version on the verge of announcement in the OJ?  If 
so, it sounds like that should be used to evaluate my product.

Thanks,
Pat Lawler
Engineer
SL Power Electronics Corp.

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to emc-p...@ieee.org

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

 Scott Douglas   emcp...@ptcnh.net
 Mike Cantwell   mcantw...@ieee.org

For policy questions, send mail to:

 Jim Bacher: j.bac...@ieee.org
 David Heald:emc-p...@daveheald.com

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc



Re: RF Power Amplifiers

2006-06-13 Thread emc-p...@ieee.org
I'm not familiar with the specific test requirements for receivers, but the
1000-4-3 spec allows step sizes of 1% of the fundamental. If not required to
do otherwise, I would arrange the test frequencies so the subharmonic
frequencies are avoided, IOW, instead of testing at 105 MHz, test at 104.5 and
105.5 MHz. I would think the selectivity of most receivers would reject these
signals.
 
Bob Richards, NCT.

Ken Javor ken.ja...@emccompliance.com wrote:

A quick calculation will show that if an immunity requirement of 10 V/m is
imposed at 105 MHz on a 420 MHz tuned receiver with a sensitivity of -100 dBm,
the harmonic content at 420 MHz needs to be on the order of 100 dB down from
the carrier.  That is quite unrealistic even for a VHF source for which 420
MHz is out-of-band, let alone a broadband amplifier and antenna combination
that covers (typically) 80 - 1000 MHz.


 

-  This
message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. Website: http://www.ieee-pses.org/ 

To post a message to the list, send your e-mail to emc-p...@ieee.org 


Instructions: http://listserv.ieee.org/request/user-guide.html 


List rules: http://www.ieee-pses.org/listrules.html 


For help, send mail to the list administrators: 


Scott Douglas emcp...@ptcnh.net Mike Cantwell mcantw...@ieee.org 


For policy questions, send mail to: 


Jim Bacher: j.bac...@ieee.org David Heald: emc-p...@daveheald.com 


All emc-pstc postings are archived and searchable on the web at: 


http://www.ieeecommunities.org/emc-pstc




EN 60204-1: 1997 vs. 1998 vs. 2006

2006-06-13 Thread emc-p...@ieee.org

Hi all: 

I need to order the current issue of EN 60204-1 (Safety of machinery – 
Electrical equipment of machines).   When I went to the EUR-Lex website at 
http://ec.europa.eu/enterprise/newapproach/standardization/harmstds/reflist/machines.html
 
it lists EN 60204-1:1997 as the current edition, with no amendments.  So far, 
so good. 

But when I look at websites that sell standards, I see listings for 1997, 1998, 
and 2006. 
- Should I simply buy the 1997 edition, or are there changes/corrections that 
forced the 1998 version to be published? 
- Is the 2006 version on the verge of announcement in the OJ?  If so, it sounds 
like that should be used to evaluate my product. 

Thanks, 
Pat Lawler 
Engineer 
SL Power Electronics Corp. 



Re: RF Power Amplifiers

2006-06-13 Thread emc-p...@ieee.org
A quick calculation will show that if an immunity requirement of 10 V/m is
imposed at 105 MHz on a 420 MHz tuned receiver with a sensitivity of -100 dBm,
the harmonic content at 420 MHz needs to be on the order of 100 dB down from
the carrier.  That is quite unrealistic even for a VHF source for which 420
MHz is out-of-band, let alone a broadband amplifier and antenna combination
that covers (typically) 80 - 1000 MHz.



From: Bill Owsley wdows...@yahoo.com
List-Post: emc-pstc@listserv.ieee.org
Date: Tue, 13 Jun 2006 09:23:18 -0700 (PDT)
To: Grace Lin graceli...@gmail.com, Bob Richards b...@toprudder.com
Cc: emc-p...@ieee.org
Subject: Re: RF Power Amplifiers




The harmonic content mentioned adds quite a bit to the measured field strength.
 
As the harmonics are filtered out (a lower level), the field strength drops,
so the drive and/or output power is boosted to get the field strength back up,
 and the harmonic content rises faster than the fundamental, so more filter is
added and more power added, and soon there is one BIG power amp required to
get the field strength at the fundamental without the harmonics.  ps.  If the
device being tested has a receiver, the harmonic energy can provide some
distracting results at unexpected times. ie. The 420 MHz rcvr fails (cannot
receive) at 105 MHz. Immunity test freq. pps. The receiver under test was good
for -100 dB signals so the harmonics had to rather low to not swamp out the
intended signal.
 


Grace Lin graceli...@gmail.com wrote:
 


 
Dear All,
 

 
Thank you very much for many members who has replied online and offline.  I
value your expert comments.  So far, I have learned that antenna's VSWR, cable
loss (at high frequency), and 80% AM modulation are the factors to count on. 
The new requirements from the third edition of IEC61000-4-3 are important
factors too. 

Many members suggest to choose an amplifier triple times' power as calculated
(i.e. 500W for 80-1000MHz), which I agree with.  However, two sales
representatives from two amplifier manufacturers suggest a 150W for
80-1000MHz.  I get lost. 
 

 
Kindest regards,
 
Grace
 

 

 
On 6/10/06, Bob Richards b...@toprudder.com wrote:   


 
 
Mac,
 

 
Yeah, good point, I forgot to mention that.
 

 
The the old 15dB requirement may not be enough. At a lab where I used to work,
we tested down to 26 MHz regularly. The difference in antenna factors between
26 and 52 MHz were terrible. When calibrating at 26 MHz at only 1/3 the rated
power of the amp, the signal level at 52 MHz dominated. This was with a very
common 500w amplifier, at 10v/m level. We ended up using an Amplifier Research
2500w amp for the 10v/m test. Way overkill, but it points out the fact that
you can't just calculate the power required to generate a desired field
strength and use that figure to size your amp. You may need to double or even
triple that figure just to meet the harmonics requirement. 
 
 

 
Bob Richards, NCT.
 
 


Elliott Mac-FME001 fme...@motorola.com wrote:
 


 
Grace, 
 

 
I agree that trying a demonstrator before you buy is the best approach. 
 

 
One thing that you want to take into consideration besides the compression
points that Bob mentioned is the harmonic / distortion requirements mentioned
in section 6 of 61000-4-3. 
 

 
The 2006 version of IEC 61000-4-3 is a bit different than the current version
of EN 61000-4-3. 
 

 
IEC 61000-4-3:2006 [expected to be published as EN this year] requires that
harmonics in the uniform field area field be at least 6 dB below the
fundamental. There is a lot of good info in Annex D about how to accomplish /
measure this. 
 

 
The current EN 61000-4-3 requires that the amplifier not produce harmonics 
15 dB below carrier. 
 

 
Whichever amp you choose, make sure that you take these considerations into
account as well. 
 

 
Good luck!
 

 
Mac Elliott



 
-  This
message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. Website: http://www.ieee-pses.org/   
To post a message to the list, send your e-mail to emc-p...@ieee.org   
Instructions: http://listserv.ieee.org/request/user-guide.html   
List rules: http://www.ieee-pses.org/listrules.html   
For help, send mail to the list administrators:   
Scott Douglas emcp...@ptcnh.net Mike Cantwell mcantw...@ieee.org   
For policy questions, send mail to:   
Jim Bacher: j.bac...@ieee.org David Heald: emc-p...@daveheald.com   
All emc-pstc postings are archived and searchable on the web at:   
http://www.ieeecommunities.org/emc-pstc 
 
 
 
 
 
 
 
 
 
 
 
 
 
 
 
 



-  This
message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. Website: http://www.ieee-pses.org/   
To post a message to the list, send your e-mail to emc-p...@ieee.org   
Instructions: http://listserv.ieee.org/request/user-guide.html   
List rules: 

Re: RF Power Amplifiers

2006-06-13 Thread emc-p...@ieee.org
The harmonic content mentioned adds quite a bit to the measured field strength.
As the harmonics are filtered out (a lower level), the field strength drops,
so the drive and/or output power is boosted to get the field strength back up,
 and the harmonic content rises faster than the fundamental, so more filter is
added and more power added, and soon there is one BIG power amp required to
get the field strength at the fundamental without the harmonics.  ps.  If the
device being tested has a receiver, the harmonic energy can provide some
distracting results at unexpected times. ie. The 420 MHz rcvr fails (cannot
receive) at 105 MHz. Immunity test freq. pps. The receiver under test was good
for -100 dB signals so the harmonics had to rather low to not swamp out the
intended signal.


Grace Lin graceli...@gmail.com wrote:

Dear All,
 
Thank you very much for many members who has replied online and offline.  I
value your expert comments.  So far, I have learned that antenna's VSWR, cable
loss (at high frequency), and 80% AM modulation are the factors to count on. 
The new requirements from the third edition of IEC61000-4-3 are important
factors too. 

Many members suggest to choose an amplifier triple times' power as calculated
(i.e. 500W for 80-1000MHz), which I agree with.  However, two sales
representatives from two amplifier manufacturers suggest a 150W for
80-1000MHz.  I get lost. 
 
Kindest regards,
Grace
 
 
On 6/10/06, Bob Richards b...@toprudder.com wrote: 

Mac,
 
Yeah, good point, I forgot to mention that.
 
The the old 15dB requirement may not be enough. At a lab where I used to work,
we tested down to 26 MHz regularly. The difference in antenna factors between
26 and 52 MHz were terrible. When calibrating at 26 MHz at only 1/3 the rated
power of the amp, the signal level at 52 MHz dominated. This was with a very
common 500w amplifier, at 10v/m level. We ended up using an Amplifier Research
2500w amp for the 10v/m test. Way overkill, but it points out the fact that
you can't just calculate the power required to generate a desired field
strength and use that figure to size your amp. You may need to double or even
triple that figure just to meet the harmonics requirement. 

 
Bob Richards, NCT.



Elliott Mac-FME001 fme...@motorola.com wrote:

Grace, 
 
I agree that trying a demonstrator before you buy is the best approach. 
 
One thing that you want to take into consideration besides the compression
points that Bob mentioned is the harmonic / distortion requirements mentioned
in section 6 of 61000-4-3. 
 
The 2006 version of IEC 61000-4-3 is a bit different than the current version
of EN 61000-4-3. 
 
IEC 61000-4-3:2006 [expected to be published as EN this year] requires that
harmonics in the uniform field area field be at least 6 dB below the
fundamental. There is a lot of good info in Annex D about how to accomplish /
measure this. 
 
The current EN 61000-4-3 requires that the amplifier not produce harmonics 
15 dB below carrier. 
 
Whichever amp you choose, make sure that you take these considerations into
account as well. 
 
Good luck!
 
Mac Elliott


-  This
message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. Website: http://www.ieee-pses.org/ 
To post a message to the list, send your e-mail to emc-p...@ieee.org 
Instructions: http://listserv.ieee.org/request/user-guide.html 
List rules: http://www.ieee-pses.org/listrules.html 
For help, send mail to the list administrators: 
Scott Douglas emcp...@ptcnh.net Mike Cantwell mcantw...@ieee.org 
For policy questions, send mail to: 
Jim Bacher: j.bac...@ieee.org David Heald: emc-p...@daveheald.com 
All emc-pstc postings are archived and searchable on the web at: 
http://www.ieeecommunities.org/emc-pstc 

-  This
message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. Website: http://www.ieee-pses.org/ 
To post a message to the list, send your e-mail to emc-p...@ieee.org 
Instructions: http://listserv.ieee.org/request/user-guide.html 
List rules: http://www.ieee-pses.org/listrules.html 
For help, send mail to the list administrators: 
Scott Douglas emcp...@ptcnh.net Mike Cantwell mcantw...@ieee.org 
For policy questions, send mail to: 
Jim Bacher: j.bac...@ieee.org David Heald: emc-p...@daveheald.com 
All emc-pstc postings are archived and searchable on the web at: 
http://www.ieeecommunities.org/emc-pstc 


__
Do You Yahoo!?
Tired of spam? Yahoo! Mail has the best spam protection around 
http://mail.yahoo.com - ---
 This message is from the IEEE
Product Safety Engineering Society emc-pstc discussion list. Website:
http://www.ieee-pses.org/ 


To post a message to the list, send your e-mail to emc-p...@ieee.org 


Instructions: 

FW: IEEE EMC Soc. UKRI Chapter Event Notice - The National Space Centre Leicester , 21st June 2006. - Update - .

2006-06-13 Thread emc-p...@ieee.org
Everyone

 

Here is an updated programme for the next meeting of the IEEE UK and Republic
of Ireland EMC Chapter.  The event is free to all, but please note the
requirement to register in advance.

 

The paper by Angela Nothofer will be particularly interesting for those who
have been following the test method developments for fully anechoic rooms.

 

Best wishes

 

Brian

 

Brian Jones

EMC Consultant

IEEE UKRI EMC Chapter Vice-Chairman

 

 

  _  

From: ukri...@ieee.org [mailto:ukri...@ieee.org] On Behalf Of Roy Ediss
Sent: 09 June 2006 16:10
To: ukri...@listserv.ieee.org
Cc: webmaster-u...@ieee.org; j.newbe...@ieee.org; c.ja...@soton.ac.uk
Subject: IEEE EMC Soc. UKRI Chapter Event Notice - The National Space Centre
Leicester , 21st June 2006. - Update - .

 


Event Notice.   

IEEE Electromagnetic Compatibility Soc. UKRI Chapter. 

You are invited to attend the forthcoming Special Event at: 
The National Space Centre, 
Exploration Drive, Leicester,  LE4 5NS http://www.spacecentre.co.uk
on Wednesday 21st  June 2006.  
Attendees will be able to explore the site in the afternoon. 

Presentation session 10:00 – 14:00, on: 
Space\Aerospace EMC and Some Topical Measurement Subjects. 

Location:  Endeavour Suite.

Agenda.

09:30 - 10:00Arrival
10:00 - 10:05Welcome. 
10:05 - 10:40EMC testing for space environments. Ken Newman,
EMC manager, Intertek
10:40 - 11:15The need for good measurement from EMC testing.
 Christopher Jones.  BAE Systems.Warton. 
11:15 - 11:30Break. Coffee/Tea and refreshments. 
11:30 - 12:15The use of fully anechoic rooms above 1GHz. 
Angela Nothofer, George Green Institute for Electromagnetics Research.
12:15 - 13:00Lunch break. 
13:00 - 13:30An explanation of the Reference Site Method (RSM)
for evaluating the performance of OATS  SARs.  John Wombwell, EMC Hire.   
13:30 - 14:00Is that result real?  The hidden dangers of
compression.  David Mawdsley. Laplace. 
14:00End of presentations.   Time to explore the Space
Centre.


Information available on speakers and talks: 

Ken Newman, EMC manager, Intertek. EMC testing for space environments. 
EMC testing for space environments involves several stages of test and
qualification. First is each individual scientific instrument or sub-assembly
on the space vehicle. Second is the space vehicle (payload) compatibility with
the launch vehicle. Last but not least, is the EMC phenomena and
interoperability of the spacecraft in the space environment. This presentation
by Intertek will provide a brief introduction to each of these aspects of
qualification, which will include the tests that are likely to be required at
each phase. 

David Mawdsley. Laplace.'Is that result real? The hidden dangers of
compression.
All pre-ampifiers and analysers, be they spectrum analysers or receivers, have
a hidden weakness. They can (and will) distort results, producing false
spectra if not set up correctly. The talk will cover examples of this effect,
explain the causes, show how to check for its presence and explain how it can
be avoided. 

The need for good measurement from EMC testing.  Dr. Christopher Jones. 
The emphasis in EMC testing is too often on testing and not sufficiently on
measurement.  This would be understandable for pass/fail, go/no-go testing,
but for qualification testing where the measured data is used as part of the
equation in a safe use clearance, the quality of the measurement and
presentation of data is all important.  In this talk Chris Jones will describe
the kind of process that has to be applied to the latest electromagnetic
hazards clearances, driven by the growing reliance on complex, inter-dependant
electrical and electronic systems for safety, specifically in the aircraft
industry for safe continued flight and landing.  Examples will be drawn from
the clearances for lightning, ESD and EMP threats. 


The event is an open meeting.  All welcome.
There is no charge for meeting attendance or entrance to the Space Centre. 
If you plan to attend this event you need to register by informing: Roy Ediss
Email;roy.ed...@philips.com
For registration you will need to provide: 
Full name, 
Company, (if applicable), 
Contact phone number. 

Book early to avoid disappointment. 

Boosters Restaurant is available on the site for attendees to buy lunch if
they wish. 

For an interactive map of the site see: 
http://www.spacecentre.co.uk/exhibition/interactivemap.htm 

View the location details and map available at: 
http://www.spacecentre.co.uk/visitingus/index.htm 
Or use http://www.multimap.com  and enter: LE4 5NS 

Parking is readily available on-site.   
NOTE: The carpark is normally pay-and-display but meeting delegates can get a
free parking pass from the entrance desk.

Travel by rail to Leicester station,  for timetable information 

Re: DOCOPOCOSS for EN 60065 : 1998

2006-06-13 Thread emc-p...@ieee.org
Scott

To presume compliance by applying the harmonised standard, the
manufacturer need to place the product on the market before the
DOCOPOCOSS.

Have a look at section 2.3 of Guide to the implementation of directives
based on the New Approach and the Global Approach (the blue
book)http://ec.europa.eu/enterprise/ne
approach/legislation/guide/document/1999_1282_en.pdf

regards
Charlie

 A question about the Date of Cessation of Presumption of Conformity of
 the Superseded Standard.

 If a product is tested to (and the CB Report indicates) EN 60065 : 1998,
 when is the last time that product can be sold to a customer? More
 specifically, if a product is near it's end of life by that date, can we
 build ahead and ship to the warehouse before that date? We will not be
 able to sell all to customers by that date, but they would be built and
 in storage. So is it still legal to sell these pre-built products to
 customers after the date?

 I know the date is March 1, 2007. We have some products close to end of
 life, say EOL by June 2007.  Can we build that extra few months of sales
 and put them in storage in February and then still sell them after
 March? We're not talking RoHS here, only and specifically safety and the
 CE Mark.

 As always, I look forward to your expert replies, and I thank you in
 advance.

 Scott Douglas
 sdoug...@ptcnh.net

 -
 
 This message is from the IEEE Product Safety Engineering Society
 emc-pstc discussion list.Website:  http://www.ieee-pses.org/

 To post a message to the list, send your e-mail to emc-p...@ieee.org

 Instructions:  http://listserv.ieee.org/request/user-guide.html

 List rules: http://www.ieee-pses.org/listrules.html

 For help, send mail to the list administrators:

  Scott Douglas   emcp...@ptcnh.net
  Mike Cantwell   mcantw...@ieee.org

 For policy questions, send mail to:

  Jim Bacher: j.bac...@ieee.org
  David Heald:emc-p...@daveheald.com

 All emc-pstc postings are archived and searchable on the web at:

 http://www.ieeecommunities.org/emc-pstc


-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to emc-p...@ieee.org

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

 Scott Douglas   emcp...@ptcnh.net
 Mike Cantwell   mcantw...@ieee.org

For policy questions, send mail to:

 Jim Bacher: j.bac...@ieee.org
 David Heald:emc-p...@daveheald.com

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc



Re: DOCOPOCOSS for EN 60065 : 1998

2006-06-13 Thread emc-p...@ieee.org
In message 448e2655.3000...@ptcnh.net, dated Mon, 12 Jun 2006, Scott 
Douglas sdoug...@ptcnh.net writes
If a product is tested to (and the CB Report indicates) EN 60065 : 
1998, when is the last time that product can be sold to a customer? 
More specifically, if a product is near it's end of life by that date, 
can we build ahead and ship to the warehouse before that date? We will 
not be able to sell all to customers by that date, but they would be 
built and in storage. So is it still legal to sell these pre-built 
products to customers after the date?

Not if you have retained ownership after the docopocoss.

I know the date is March 1, 2007. We have some products close to end of 
life, say EOL by June 2007.  Can we build that extra few months of 
sales and put them in storage in February and then still sell them 
after March? We're not talking RoHS here, only and specifically safety 
and the CE Mark.

No, you must 'place [them] on the market' before the cut-off date, by 
putting them into the distribution chain.  Depending on how you market 
the products, your distributors may agree to take them into stock, but 
ownership must be transferred from your company to them.

You may feel that this is not sensible, but if it were not so, abuse of 
the docopocoss would be easy. There seem to be no other way of doing it.
-- 
OOO - Own Opinions Only. Try www.jmwa.demon.co.uk and www.isce.org.uk
2006 is YMMVI- Your mileage may vary immensely.

John Woodgate, J M Woodgate and Associates, Rayleigh, Essex UK

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to emc-p...@ieee.org

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

 Scott Douglas   emcp...@ptcnh.net
 Mike Cantwell   mcantw...@ieee.org

For policy questions, send mail to:

 Jim Bacher: j.bac...@ieee.org
 David Heald:emc-p...@daveheald.com

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc



Re: WEEE Labeling of Components vs. Systems

2006-06-13 Thread emc-p...@ieee.org
In message 
offebd41a2.f2c14b39-on6525718c.0017aaf4-6525718c.00184...@scmmicro.co.in
 , dated Tue, 13 Jun 2006, kbalasubraman...@scmmicro.co.in writes

For an expert like John if things are appearing as complete mess, 
what will be the fate of others. I am not able to sleep peacefully 
while thinking 1st July 2006. What kind of penalties can be expected, 
any idea?

You should not be too apprehensive. If you can show that you did the 
best you could under the circumstances, any penalty is likely to be 
mild, of the nature of an official 'you must improve' instruction to the 
company concerned. Individuals are rarely pursued, unless they have 
clearly been dishonest.

The best safeguard is to write down at length what you did in order to 
try to comply, and what you wanted to do but couldn't, due to matters 
beyond your control.

 I have been told that while EMC directive was introduced at the 
beginning lot of vigilance activities went on but subsequently it got 
reduced, is this correct?

Not as far as I know; there was a quiet period before serious 
enforcement activity started.

Consider how many millions of products there are out there, and what 
would happen  if action were taken against a company that HAS actually 
done its best to cope with the confusing legislation and the 
non-availability of suitable parts. A good defence lawyer would ensure 
that all those problems were brought out in court and splashed all over 
the media.  The authorities would look like asses or villains, and I 
suspect they know that.

The real victim might be a small manufacturer who hasn't even tried to 
comply, perhaps through not knowing what needs to be done, and who can't 
afford to hire a good lawyer.
-- 
OOO - Own Opinions Only. Try www.jmwa.demon.co.uk and www.isce.org.uk
2006 is YMMVI- Your mileage may vary immensely.

John Woodgate, J M Woodgate and Associates, Rayleigh, Essex UK

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to emc-p...@ieee.org

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

 Scott Douglas   emcp...@ptcnh.net
 Mike Cantwell   mcantw...@ieee.org

For policy questions, send mail to:

 Jim Bacher: j.bac...@ieee.org
 David Heald:emc-p...@daveheald.com

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc



DOCOPOCOSS for EN 60065 : 1998

2006-06-13 Thread emc-p...@ieee.org
A question about the Date of Cessation of Presumption of Conformity of 
the Superseded Standard.

If a product is tested to (and the CB Report indicates) EN 60065 : 1998, 
when is the last time that product can be sold to a customer? More 
specifically, if a product is near it's end of life by that date, can we 
build ahead and ship to the warehouse before that date? We will not be 
able to sell all to customers by that date, but they would be built and 
in storage. So is it still legal to sell these pre-built products to 
customers after the date?

I know the date is March 1, 2007. We have some products close to end of 
life, say EOL by June 2007.  Can we build that extra few months of sales 
and put them in storage in February and then still sell them after 
March? We're not talking RoHS here, only and specifically safety and the 
CE Mark.

As always, I look forward to your expert replies, and I thank you in 
advance.

Scott Douglas
sdoug...@ptcnh.net

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to emc-p...@ieee.org

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

 Scott Douglas   emcp...@ptcnh.net
 Mike Cantwell   mcantw...@ieee.org

For policy questions, send mail to:

 Jim Bacher: j.bac...@ieee.org
 David Heald:emc-p...@daveheald.com

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc



Re: WEEE Labeling of Components vs. Systems

2006-06-13 Thread emc-p...@ieee.org
Dear John  other experts,
  For an expert like John if things are appearing as complete mess,
what will be the fate of others. I am not able to sleep peacefully while
thinking 1st July 2006. What kind of penalties can be expected, any idea?
I have been told that while EMC directive was introduced at the beginning
lot of vigilance activities went on but subsequently it got reduced, is
this correct?


Sincerely

K.Balasubramanian
Project Leader - Hardware.


   
 John Woodgate 
 jmw@jmwa.demon.c 
 o.uk  To 
 Sent by:  emc-p...@ieee.org   
 emc-p...@ieee.org  cc 
   
   Subject 
 06/12/2006 09:01  Re: WEEE Labeling of Components vs. 
 PMSystems 
   
   
   
   
   
   




In message 20060612151511.73191.qm...@web55512.mail.re4.yahoo.com,
dated Mon, 12 Jun 2006, Andy Garcia arg...@yahoo.com writes
It has always been my understanding that WEEE labeling is required on
devices, instruments, apparatus, what have you, but not on any of the
sub-assemblies or specific components.

I am now told that entities in Europe are requiring that items such as
detachable power cords also need to be WEEE labeled.  The justification
is that since these parts can become detached from the presumably
labeled instrument, it must also be labeled separately.  I cannot see
where this is directly addressed in the directive.

Has anyone also come accross this issue?  Are you labeling systems, as
well as specific sub-components of those systems?

It's a complete mess. Just do what you are asked to do and soldier
on.. (with a lead-free soldier, of course)
--
OOO - Own Opinions Only. Try www.jmwa.demon.co.uk and www.isce.org.uk
2006 is YMMVI- Your mileage may vary immensely.

John Woodgate, J M Woodgate and Associates, Rayleigh, Essex UK

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to emc-p...@ieee.org

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

 Scott Douglas   emcp...@ptcnh.net
 Mike Cantwell   mcantw...@ieee.org

For policy questions, send mail to:

 Jim Bacher: j.bac...@ieee.org
 David Heald:emc-p...@daveheald.com

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to emc-p...@ieee.org

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

 Scott Douglas   emcp...@ptcnh.net
 Mike Cantwell   mcantw...@ieee.org

For policy questions, send mail to:

 Jim Bacher: j.bac...@ieee.org
 David Heald:emc-p...@daveheald.com

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc