RE: Ground Fault Circuit Interrupter tripping

2007-08-20 Thread emc-p...@ieee.org
Hi Brian:


First, you should measure the current in the ground
wire with an oscilloscope and a current probe or 
measure the voltage across a low-value resistance 
such as 10 ohms in series with the ground wire.

Second, you should measure the current in the ground
wire with a RMS ammeter.  

These should confirm that the difference current is
tripping the GFCI.

If the high frequency is what is causing the GFCI to
trip, you might want to consider re-designing the
EMC filter to lower the high-frequency currents in
the ground wire.  An ideal EMC filter should return 
the currents generated in the power supply to the
power supply, not via the mains circuits.  

The worst-case fix is to use a 1:1 isolation transformer
between the mains and your equipment.  

Make the measurements so that you know what is causing
the GFCI to trip.


Best regards,
Rich



 -Original Message-
 From: Kunde, Brian [mailto:brian_ku...@lecotc.com] 
 Sent: Monday, August 20, 2007 6:50 AM
 To: ri...@ieee.org; emc-p...@ieee.org
 Subject: RE: Ground Fault Circuit Interrupter tripping
 
 
 Thanks for the great information. Let me see if I'm 
 comprehending it correctly.
 
 - A product can pass the leakage current test and not pose a 
 hazard to the user but still trip a GFCI. 
 
 In such cases, is there an alternative to the GFCI? If the 
 NEC requires a GFCI in a location but a device used in that 
 location falsely trips the GFCI, can you wire the instrument 
 without the GFCI and still meet the NEC requirements? (are 
 their exclusions?). Is there something you can do, such as 
 provide an addition safety earth ground connection, instead 
 of the GFCI?
 
 If I'm correctly understanding the reason our product is 
 tripping the GFCI, there is nothing we can do about it. So, 
 our only choice is to find an exclusion or an alternate to 
 the GFCI that would satify everyone.  Any suggestions would 
 be appreciated.
 
 The Other Brian
 
 
 -Original Message-
 From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf 
 Of rn...@san.rr.com
 Sent: Friday, August 17, 2007 2:17 PM
 To: emc-p...@ieee.org
 Subject: RE: Ground Fault Circuit Interrupter tripping
 
 Hello John:
 
 
  I've never measured the 'frequency response' (trip current vs.
  frequency) of a GFCI (they don't occur in UK, we have RCCBs) but I
  suspect that the trip current is higher than the design value at 
  higher frequencies.
 
 As far as I know, there is no frequency compensation in the 
 GFCI.  The frequency response is determined by the core 
 characteristics and the IC amplifier characteristics.
 
 Virtually all US/Canada GFCIs use the National Semiconductor 
 LM1851 IC.  The data sheet includes some good information on 
 GFCI circuits and circuit performance.  There are no 
 frequency response specs that I could find.  Here is the URL 
 for the LM1851 and data sheet:
 
 http://www.national.com/mpf/LM/LM1851.html
 
 Here is another web site for GFCI information:
 
 http://www.codecheck.com/gfci_principal.htm
 
 The original question pointed out that the leakage current 
 was in spec, but the load nevertheless tripped the GFCI. The 
 only conclusion is that the leakage current meter and the 
 GFCI do not have the same measuring circuits -- which they 
 don't.  We do know that the leakage current measuring network 
 accounts for the response of the body to frequency, while the 
 GFCI has no such metering circuit network.
 
 
 Best regards,
 Rich
 
 
 Richard Nute
 Product Safety Consultant
 San Diego
 

 

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to emc-p...@ieee.org

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

 Scott Douglas   emcp...@ptcnh.net
 Mike Cantwell   mcantw...@ieee.org

For policy questions, send mail to:

 Jim Bacher: j.bac...@ieee.org
 David Heald:emc-p...@daveheald.com

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc

__
This email has been scanned by the MessageLabs Email Security System.
For more information please visit http://www.messagelabs.com/email 
__



RE: Ground Fault Circuit Interrupter tripping

2007-08-20 Thread emc-p...@ieee.org
Thanks for the great information. Let me see if I'm comprehending it
correctly.

- A product can pass the leakage current test and not pose a hazard to
the user but still trip a GFCI. 

In such cases, is there an alternative to the GFCI? If the NEC requires
a GFCI in a location but a device used in that location falsely trips
the GFCI, can you wire the instrument without the GFCI and still meet
the NEC requirements? (are their exclusions?). Is there something you
can do, such as provide an addition safety earth ground connection,
instead of the GFCI?

If I'm correctly understanding the reason our product is tripping the
GFCI, there is nothing we can do about it. So, our only choice is to
find an exclusion or an alternate to the GFCI that would satify
everyone.  Any suggestions would be appreciated.

The Other Brian



From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of
rn...@san.rr.com
Sent: Friday, August 17, 2007 2:17 PM
To: emc-p...@ieee.org
Subject: RE: Ground Fault Circuit Interrupter tripping

Hello John:


 I've never measured the 'frequency response' (trip current vs.
 frequency) of a GFCI (they don't occur in UK, we have RCCBs) but I 
 suspect that the trip current is higher than the design value at 
 higher frequencies.

As far as I know, there is no frequency compensation in the GFCI.  The
frequency response is determined by the core characteristics and the IC
amplifier characteristics.

Virtually all US/Canada GFCIs use the National Semiconductor
LM1851 IC.  The data sheet includes some good information on GFCI
circuits and circuit performance.  There are no frequency response specs
that I could find.  Here is the URL for the
LM1851 and data sheet:

http://www.national.com/mpf/LM/LM1851.html

Here is another web site for GFCI information:

http://www.codecheck.com/gfci_principal.htm

The original question pointed out that the leakage current was in spec,
but the load nevertheless tripped the GFCI.
The only conclusion is that the leakage current meter and the GFCI do
not have the same measuring circuits -- which they don't.  We do know
that the leakage current measuring network accounts for the response of
the body to frequency, while the GFCI has no such metering circuit
network.


Best regards,
Rich


Richard Nute
Product Safety Consultant
San Diego

   

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to emc-p...@ieee.org

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

 Scott Douglas   emcp...@ptcnh.net
 Mike Cantwell   mcantw...@ieee.org

For policy questions, send mail to:

 Jim Bacher: j.bac...@ieee.org
 David Heald:emc-p...@daveheald.com

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc

LECO Corporation Notice:  This communication may contain confidential
information intended for the named recipient(s) only. If you received this by
mistake, please destroy it and notify us of the error.  Thank  you.

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to emc-p...@ieee.org

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

 Scott Douglas   emcp...@ptcnh.net
 Mike Cantwell   mcantw...@ieee.org

For policy questions, send mail to:

 Jim Bacher: j.bac...@ieee.org
 David Heald:emc-p...@daveheald.com

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc

__
This email has been scanned by the MessageLabs Email Security System.
For more information please visit http://www.messagelabs.com/email 
__



A book for China RoHS

2007-08-20 Thread emc-p...@ieee.org
To Those Who are Interested in:

 

The China Quality Management Association for Electronics Industry (CQAE)
published a book in regard to the China RoHS.   The news is available at 
http://www.cqae.com/zxdt-xw.asp?column_id=978
http://www.cqae.com/zxdt-xw.asp?column_id=978.

 

This book contains three parts: domestic and foreign policies and regulations,
technical papers, and list of green electronic product manufacturers.   It
includes the Administrative Measure and related standards, regulations in
English and Japanese.  It is about 500 pages.

 

If you are interested in this book, please contact:

 

Contact Phone No.: +86-10-6820-7850

Fax No.:  +86-10-6827-3279

Contact Person:Mr. LiDong QIN ( 秦立东)

Address:Room 215, Building 13, No. 27, Wan Shou Road,
Beijing 100846, China  ( 北京市海淀区万寿路 27 号 13 号楼215,
邮编:100846)

E-mail:  mailto:c...@cqae.com c...@cqae.com

Web Site:www.cqae.com 
__
This email has been scanned by the MessageLabs Email Security System.
For more information please visit http://www.messagelabs.com/email 
__




Re: What is killer joules?

2007-08-20 Thread emc-p...@ieee.org
On the other hand my ICD supplies 35 joules at full power. Not sure of the
voltage.

Bob Heller
3M EMC Laboratory, 76-1-01
St. Paul, MN 55107-1208
Tel:  651- 778-6336
Fax:  651-778-6252



   
 John Woodgate 
 jmw@jmwa.demon.c 
 o.uk  To 
 Sent by:  emc-p...@ieee.org   
 emc-p...@ieee.org  cc 
   
   Subject 
 08/18/2007 01:18  Re: What is killer joules?  
 PM
   
   
   
   
   




In message web-153134...@california.com, dated Sat, 18 Aug 2007,
Robert A. Macy m...@california.com writes:

Thanks to all who answered this question.

The culmination of information:

350mJ is safe

20J is lethal

I find your conclusions questionable and I would advise great caution.
It was pointed out to you that 350 mJ stored in a supercapacitor at 2 V
is most unlikely to be lethal if applied to a person's skin, but a far
smaller charge could produce a lethal current if applied below the skin.
--
OOO - Own Opinions Only. Try www.jmwa.demon.co.uk and www.isce.org.uk
There are benefits from being irrational - just ask the square root of 2.
John Woodgate, J M Woodgate and Associates, Rayleigh, Essex UK

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to emc-p...@ieee.org

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

 Scott Douglas   emcp...@ptcnh.net
 Mike Cantwell   mcantw...@ieee.org

For policy questions, send mail to:

 Jim Bacher: j.bac...@ieee.org
 David Heald:emc-p...@daveheald.com

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to emc-p...@ieee.org

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

 Scott Douglas   emcp...@ptcnh.net
 Mike Cantwell   mcantw...@ieee.org

For policy questions, send mail to:

 Jim Bacher: j.bac...@ieee.org
 David Heald:emc-p...@daveheald.com

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc

__
This email has been scanned by the MessageLabs Email Security System.
For more information please visit http://www.messagelabs.com/email 
__