Re: [PSES] Arc Flash Requirements NFPA 79

2014-12-17 Thread Brian Oconnell
Unless specifically stated in the safety standard used to assess the end-use 
equipment, dunno. Might want to look at NFPA70E article 130.

Due to the calculations that must be performed in order properly label 
equipment, gonna guess that the 'generic' warnings/cautions and symbols could 
be applied at factory, with specific data at installation.

Brian

From: Nyffenegger, Dave [mailto:dave.nyffeneg...@bhemail.com] 
Sent: Wednesday, December 17, 2014 11:34 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] Arc Flash Requirements NFPA 79

So I’m looking at the new NFPA 79 2015 (which you can view on-line for free 
now) and they have added 16.2.3 Electrical equipment for industrial machines 
such as control panels and disconnects shall be marked according to ANSI Z535.4 
to warn of shock and arc flash hazards.  I don’t have a copy of the ANSI 
standard.    NFPA 79 doesn’t say anything further regarding applying the label 
in the field or in the factory.    Do we assume this implies field labeling as 
it’s been or does this mean we are now to apply the arc flash labels in the 
factory?  I’m guessing the ANSI standard only covers the label and says nothing 
about when the label is applied.

-Dave

From: Scott Aldous [mailto:0220f70c299a-dmarc-requ...@ieee.org] 
Sent: Tuesday, November 25, 2014 11:43 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] Arc Flash Requirements NFPA 79

FYI - Regarding the SCCR, it's really not about the interrupt rating of 
overcurrent protection devices. It relates to the ability of the equipment to 
withstand the fault currents that overcurrent devices would let through in a 
short circuit event. Looking through the supplement in UL 508A is instructive. 
If you try to evaluate through the "weakest link" method rather than testing, 
values are assigned to components commonly found in switchgear, including bus 
bars. If you have overcurrent protection that is current lmiting, it helps 
reduce the required withstand rating of components downstream, but this is 
dependent on the extent of current limiting rather than interrupt rating.

On Tue, Nov 25, 2014 at 8:33 AM, Ted Eckert  wrote:
Hello Brian,

The role the enclosure plays in arc flash protection may be less than you would 
expect. The concern about arc flash isn't for normal operation of the 
equipment. Arc flash and arc blasts are considered an issue for the servicing 
of equipment. The concern is that service personnel may accidentally create a 
short circuit between two phases or a phase and ground. This could occur due to 
improperly de-energizing circuits or when a metal tool or part is accidentally 
placed such that it creates a short circuit.

NFPA 70E requires that the arc flash boundary be calculated, although it is 
assumed to be 4 feet (1.2 meters) for typical small equipment rated 250 V or 
less connected to a branch circuit breaker. The boundary will be greater 
depending on the rating of the circuits overcurrent protector. NFPA 70E 
requires that untrained and unprotected personnel must remain outside of that 
boundary during the service of equipment. Personnel inside of that boundary 
must be properly trained and they must be wearing the correct PPE based on the 
arc flash hazard risk. Since this is an issue during the servicing of equipment 
when doors are open and covers are off, the enclosure provides no protection. 
The arc flash rules just require marking indicating the hazard so that service 
personnel can take the proper precautions.

Field wired equipment that never needs to be serviced live should be marked 
with instructions to disconnect all power before servicing. If this can be done 
properly, arc flash marking may not be required. The marking may not be 
required if the equipment is installed with an external disconnect. Arc flash 
marking is generally not required for plug connected equipment.

Pick your favorite search engine and search for "arc flash labels" and you will 
find examples of the marking typically required.

Ted Eckert
Compliance Engineer
Microsoft Corporation
ted.eck...@microsoft.com

The opinions expressed are my own and do not necessarily reflect those of my 
employer.

-Original Message-
From: Kunde, Brian [mailto:brian_ku...@lecotc.com]
Sent: Tuesday, November 25, 2014 6:08 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] Arc Flash Requirements NFPA 79

Thanks for the input.

Because our products are Laboratory Equipment and not Industrial Machines, I 
assume NFPA 79 would not apply. So the SCCR on the nameplate would not be 
required. It would be difficult to provide anyway. Since we are only required 
to provide supplementary over current protection the SCCR value is really 
unknown. Our Circuit Breaker manufacturer rates their parts with a 5kA SCCR but 
to my understanding they don't even have to survive the test. So the Branch 
Circuit Breaker is relied upon to provide the protection and the necessary

Re: [PSES] Arc Flash Requirements NFPA 79

2014-12-17 Thread Mike Sherman ----- Original Message -----
Dave -- 

ANSI Z535.4 is the standard for warning labels for equipment. Clarion, and 
likely other vendors, have samples on their web page. 

Mike 

- Original Message -

From: "Dave Nyffenegger"  
To: "EMC-PSTC"  
Sent: Wednesday, December 17, 2014 1:34:29 PM 
Subject: Re: [PSES] Arc Flash Requirements NFPA 79 



So I’m looking at the new NFPA 79 2015 (which you can view on-line for free 
now) and they have added 16.2.3 Electrical equipment for industrial machines 
such as control panels and disconnects shall be marked according to ANSI Z535.4 
to warn of shock and arc flash hazards. I don’t have a copy of the ANSI 
standard. NFPA 79 doesn’t say anything further regarding applying the label in 
the field or in the factory. Do we assume this implies field labeling as it’s 
been or does this mean we are now to apply the arc flash labels in the factory? 
I’m guessing the ANSI standard only covers the label and says nothing about 
when the label is applied. 



-Dave 



From: Scott Aldous [mailto:0220f70c299a-dmarc-requ...@ieee.org] 
Sent: Tuesday, November 25, 2014 11:43 AM 
To: EMC-PSTC@LISTSERV.IEEE.ORG 
Subject: Re: [PSES] Arc Flash Requirements NFPA 79 




FYI - Regarding the SCCR, it's really not about the interrupt rating of 
overcurrent protection devices. It relates to the ability of the equipment to 
withstand the fault currents that overcurrent devices would let through in a 
short circuit event. Looking through the supplement in UL 508A is instructive. 
If you try to evaluate through the "weakest link" method rather than testing, 
values are assigned to components commonly found in switchgear, including bus 
bars. If you have overcurrent protection that is current lmiting, it helps 
reduce the required withstand rating of components downstream, but this is 
dependent on the extent of current limiting rather than interrupt rating. 





On Tue, Nov 25, 2014 at 8:33 AM, Ted Eckert < ted.eck...@microsoft.com > wrote: 

Hello Brian, 

The role the enclosure plays in arc flash protection may be less than you would 
expect. The concern about arc flash isn't for normal operation of the 
equipment. Arc flash and arc blasts are considered an issue for the servicing 
of equipment. The concern is that service personnel may accidentally create a 
short circuit between two phases or a phase and ground. This could occur due to 
improperly de-energizing circuits or when a metal tool or part is accidentally 
placed such that it creates a short circuit. 

NFPA 70E requires that the arc flash boundary be calculated, although it is 
assumed to be 4 feet (1.2 meters) for typical small equipment rated 250 V or 
less connected to a branch circuit breaker. The boundary will be greater 
depending on the rating of the circuits overcurrent protector. NFPA 70E 
requires that untrained and unprotected personnel must remain outside of that 
boundary during the service of equipment. Personnel inside of that boundary 
must be properly trained and they must be wearing the correct PPE based on the 
arc flash hazard risk. Since this is an issue during the servicing of equipment 
when doors are open and covers are off, the enclosure provides no protection. 
The arc flash rules just require marking indicating the hazard so that service 
personnel can take the proper precautions. 

Field wired equipment that never needs to be serviced live should be marked 
with instructions to disconnect all power before servicing. If this can be done 
properly, arc flash marking may not be required. The marking may not be 
required if the equipment is installed with an external disconnect. Arc flash 
marking is generally not required for plug connected equipment. 

Pick your favorite search engine and search for "arc flash labels" and you will 
find examples of the marking typically required. 

Ted Eckert 
Compliance Engineer 
Microsoft Corporation 
ted.eck...@microsoft.com 

The opinions expressed are my own and do not necessarily reflect those of my 
employer. 

-Original Message- 
From: Kunde, Brian [mailto: brian_ku...@lecotc.com ] 


Sent: Tuesday, November 25, 2014 6:08 AM 
To: EMC-PSTC@LISTSERV.IEEE.ORG 
Subject: Re: [PSES] Arc Flash Requirements NFPA 79 

Thanks for the input. 

Because our products are Laboratory Equipment and not Industrial Machines, I 
assume NFPA 79 would not apply. So the SCCR on the nameplate would not be 
required. It would be difficult to provide anyway. Since we are only required 
to provide supplementary over current protection the SCCR value is really 
unknown. Our Circuit Breaker manufacturer rates their parts with a 5kA SCCR but 
to my understanding they don't even have to survive the test. So the Branch 
Circuit Breaker is relied upon to provide the protection and the necessary SCCR 
value would be based on the Customer's power system. 

The SCCR value is interesting to me. For those of you who has to design your 
product

Re: [PSES] Arc Flash Requirements NFPA 79

2014-12-17 Thread Nyffenegger, Dave
So I’m looking at the new NFPA 79 2015 (which you can view on-line for free 
now) and they have added 16.2.3 Electrical equipment for industrial machines 
such as control panels and disconnects shall be marked according to ANSI Z535.4 
to warn of shock and arc flash hazards.  I don’t have a copy of the ANSI 
standard.NFPA 79 doesn’t say anything further regarding applying the label 
in the field or in the factory.Do we assume this implies field labeling as 
it’s been or does this mean we are now to apply the arc flash labels in the 
factory?  I’m guessing the ANSI standard only covers the label and says nothing 
about when the label is applied.

-Dave

From: Scott Aldous [mailto:0220f70c299a-dmarc-requ...@ieee.org]
Sent: Tuesday, November 25, 2014 11:43 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] Arc Flash Requirements NFPA 79

FYI - Regarding the SCCR, it's really not about the interrupt rating of 
overcurrent protection devices. It relates to the ability of the equipment to 
withstand the fault currents that overcurrent devices would let through in a 
short circuit event. Looking through the supplement in UL 508A is instructive. 
If you try to evaluate through the "weakest link" method rather than testing, 
values are assigned to components commonly found in switchgear, including bus 
bars. If you have overcurrent protection that is current lmiting, it helps 
reduce the required withstand rating of components downstream, but this is 
dependent on the extent of current limiting rather than interrupt rating.

On Tue, Nov 25, 2014 at 8:33 AM, Ted Eckert 
mailto:ted.eck...@microsoft.com>> wrote:
Hello Brian,

The role the enclosure plays in arc flash protection may be less than you would 
expect. The concern about arc flash isn't for normal operation of the 
equipment. Arc flash and arc blasts are considered an issue for the servicing 
of equipment. The concern is that service personnel may accidentally create a 
short circuit between two phases or a phase and ground. This could occur due to 
improperly de-energizing circuits or when a metal tool or part is accidentally 
placed such that it creates a short circuit.

NFPA 70E requires that the arc flash boundary be calculated, although it is 
assumed to be 4 feet (1.2 meters) for typical small equipment rated 250 V or 
less connected to a branch circuit breaker. The boundary will be greater 
depending on the rating of the circuits overcurrent protector. NFPA 70E 
requires that untrained and unprotected personnel must remain outside of that 
boundary during the service of equipment. Personnel inside of that boundary 
must be properly trained and they must be wearing the correct PPE based on the 
arc flash hazard risk. Since this is an issue during the servicing of equipment 
when doors are open and covers are off, the enclosure provides no protection. 
The arc flash rules just require marking indicating the hazard so that service 
personnel can take the proper precautions.

Field wired equipment that never needs to be serviced live should be marked 
with instructions to disconnect all power before servicing. If this can be done 
properly, arc flash marking may not be required. The marking may not be 
required if the equipment is installed with an external disconnect. Arc flash 
marking is generally not required for plug connected equipment.

Pick your favorite search engine and search for "arc flash labels" and you will 
find examples of the marking typically required.

Ted Eckert
Compliance Engineer
Microsoft Corporation
ted.eck...@microsoft.com<mailto:ted.eck...@microsoft.com>

The opinions expressed are my own and do not necessarily reflect those of my 
employer.

-Original Message-
From: Kunde, Brian 
[mailto:brian_ku...@lecotc.com<mailto:brian_ku...@lecotc.com>]
Sent: Tuesday, November 25, 2014 6:08 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG<mailto:EMC-PSTC@LISTSERV.IEEE.ORG>
Subject: Re: [PSES] Arc Flash Requirements NFPA 79

Thanks for the input.

Because our products are Laboratory Equipment and not Industrial Machines, I 
assume NFPA 79 would not apply. So the SCCR on the nameplate would not be 
required. It would be difficult to provide anyway. Since we are only required 
to provide supplementary over current protection the SCCR value is really 
unknown. Our Circuit Breaker manufacturer rates their parts with a 5kA SCCR but 
to my understanding they don't even have to survive the test. So the Branch 
Circuit Breaker is relied upon to provide the protection and the necessary SCCR 
value would be based on the Customer's power system.

The SCCR value is interesting to me. For those of you who has to design your 
products to meet a specific SCCR value, what do you design for? Are there 
typical values you shoot for? How high of value must you design for? So if you 
design for say 10kA and your customer wants 50kA what do you do?

Thanks for the information regarding Arc

Re: [PSES] Arc Flash Requirements NFPA 79

2014-11-25 Thread Scott Aldous
FYI - Regarding the SCCR, it's really not about the interrupt rating of
overcurrent protection devices. It relates to the ability of the equipment
to withstand the fault currents that overcurrent devices would let through
in a short circuit event. Looking through the supplement in UL 508A is
instructive. If you try to evaluate through the "weakest link" method
rather than testing, values are assigned to components commonly found in
switchgear, including bus bars. If you have overcurrent protection that is
current lmiting, it helps reduce the required withstand rating of
components downstream, but this is dependent on the extent of current
limiting rather than interrupt rating.

On Tue, Nov 25, 2014 at 8:33 AM, Ted Eckert 
wrote:

> Hello Brian,
>
> The role the enclosure plays in arc flash protection may be less than you
> would expect. The concern about arc flash isn't for normal operation of the
> equipment. Arc flash and arc blasts are considered an issue for the
> servicing of equipment. The concern is that service personnel may
> accidentally create a short circuit between two phases or a phase and
> ground. This could occur due to improperly de-energizing circuits or when a
> metal tool or part is accidentally placed such that it creates a short
> circuit.
>
> NFPA 70E requires that the arc flash boundary be calculated, although it
> is assumed to be 4 feet (1.2 meters) for typical small equipment rated 250
> V or less connected to a branch circuit breaker. The boundary will be
> greater depending on the rating of the circuits overcurrent protector. NFPA
> 70E requires that untrained and unprotected personnel must remain outside
> of that boundary during the service of equipment. Personnel inside of that
> boundary must be properly trained and they must be wearing the correct PPE
> based on the arc flash hazard risk. Since this is an issue during the
> servicing of equipment when doors are open and covers are off, the
> enclosure provides no protection. The arc flash rules just require marking
> indicating the hazard so that service personnel can take the proper
> precautions.
>
> Field wired equipment that never needs to be serviced live should be
> marked with instructions to disconnect all power before servicing. If this
> can be done properly, arc flash marking may not be required. The marking
> may not be required if the equipment is installed with an external
> disconnect. Arc flash marking is generally not required for plug connected
> equipment.
>
> Pick your favorite search engine and search for "arc flash labels" and you
> will find examples of the marking typically required.
>
> Ted Eckert
> Compliance Engineer
> Microsoft Corporation
> ted.eck...@microsoft.com
>
> The opinions expressed are my own and do not necessarily reflect those of
> my employer.
>
> -Original Message-----
> From: Kunde, Brian [mailto:brian_ku...@lecotc.com]
> Sent: Tuesday, November 25, 2014 6:08 AM
> To: EMC-PSTC@LISTSERV.IEEE.ORG
> Subject: Re: [PSES] Arc Flash Requirements NFPA 79
>
> Thanks for the input.
>
> Because our products are Laboratory Equipment and not Industrial Machines,
> I assume NFPA 79 would not apply. So the SCCR on the nameplate would not be
> required. It would be difficult to provide anyway. Since we are only
> required to provide supplementary over current protection the SCCR value is
> really unknown. Our Circuit Breaker manufacturer rates their parts with a
> 5kA SCCR but to my understanding they don't even have to survive the test.
> So the Branch Circuit Breaker is relied upon to provide the protection and
> the necessary SCCR value would be based on the Customer's power system.
>
> The SCCR value is interesting to me. For those of you who has to design
> your products to meet a specific SCCR value, what do you design for? Are
> there typical values you shoot for? How high of value must you design for?
> So if you design for say 10kA and your customer wants 50kA what do you do?
>
> Thanks for the information regarding Arc Flash. I'm assuming that if our
> chassis (fire enclosure) meets the constructional requirements of IEC/EN/UL
> 61010-1 that it should contain an Arc Flash; especially with a 230VAC
> powered instrument where the energy to produce an Arc Flash is somewhat
> limited. I have also been asked by customers if our chassis meet the NEMA
> requirements. I assume the question is in regards to Arc Flash.
>
> Thanks again for the info. It was most helpful.
>
> The Other Brian
>
>
> -Original Message-
> From: Mr. Doug Nix C.E.T. [mailto:d...@ieee.org]
> Sent: Monday, November 24, 2014 4:32 PM
> To: EMC-PSTC@LISTSERV.IEEE.ORG
> Subject: Re: [PSES] Arc Flash Requirements NFPA 79
>
&

Re: [PSES] Arc Flash Requirements NFPA 79

2014-11-25 Thread Ted Eckert
Hello Brian,

The role the enclosure plays in arc flash protection may be less than you would 
expect. The concern about arc flash isn't for normal operation of the 
equipment. Arc flash and arc blasts are considered an issue for the servicing 
of equipment. The concern is that service personnel may accidentally create a 
short circuit between two phases or a phase and ground. This could occur due to 
improperly de-energizing circuits or when a metal tool or part is accidentally 
placed such that it creates a short circuit. 

NFPA 70E requires that the arc flash boundary be calculated, although it is 
assumed to be 4 feet (1.2 meters) for typical small equipment rated 250 V or 
less connected to a branch circuit breaker. The boundary will be greater 
depending on the rating of the circuits overcurrent protector. NFPA 70E 
requires that untrained and unprotected personnel must remain outside of that 
boundary during the service of equipment. Personnel inside of that boundary 
must be properly trained and they must be wearing the correct PPE based on the 
arc flash hazard risk. Since this is an issue during the servicing of equipment 
when doors are open and covers are off, the enclosure provides no protection. 
The arc flash rules just require marking indicating the hazard so that service 
personnel can take the proper precautions.

Field wired equipment that never needs to be serviced live should be marked 
with instructions to disconnect all power before servicing. If this can be done 
properly, arc flash marking may not be required. The marking may not be 
required if the equipment is installed with an external disconnect. Arc flash 
marking is generally not required for plug connected equipment.

Pick your favorite search engine and search for "arc flash labels" and you will 
find examples of the marking typically required. 

Ted Eckert
Compliance Engineer
Microsoft Corporation
ted.eck...@microsoft.com

The opinions expressed are my own and do not necessarily reflect those of my 
employer.

-Original Message-
From: Kunde, Brian [mailto:brian_ku...@lecotc.com] 
Sent: Tuesday, November 25, 2014 6:08 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] Arc Flash Requirements NFPA 79

Thanks for the input.

Because our products are Laboratory Equipment and not Industrial Machines, I 
assume NFPA 79 would not apply. So the SCCR on the nameplate would not be 
required. It would be difficult to provide anyway. Since we are only required 
to provide supplementary over current protection the SCCR value is really 
unknown. Our Circuit Breaker manufacturer rates their parts with a 5kA SCCR but 
to my understanding they don't even have to survive the test. So the Branch 
Circuit Breaker is relied upon to provide the protection and the necessary SCCR 
value would be based on the Customer's power system.

The SCCR value is interesting to me. For those of you who has to design your 
products to meet a specific SCCR value, what do you design for? Are there 
typical values you shoot for? How high of value must you design for? So if you 
design for say 10kA and your customer wants 50kA what do you do?

Thanks for the information regarding Arc Flash. I'm assuming that if our 
chassis (fire enclosure) meets the constructional requirements of IEC/EN/UL 
61010-1 that it should contain an Arc Flash; especially with a 230VAC powered 
instrument where the energy to produce an Arc Flash is somewhat limited. I have 
also been asked by customers if our chassis meet the NEMA requirements. I 
assume the question is in regards to Arc Flash.

Thanks again for the info. It was most helpful.

The Other Brian


-Original Message-
From: Mr. Doug Nix C.E.T. [mailto:d...@ieee.org]
Sent: Monday, November 24, 2014 4:32 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] Arc Flash Requirements NFPA 79

Dave, Brian,

Electrical field inspectors commonly require that labels of the type I 
referenced be installed by the manufacturer. The detailed labels with the arc 
flash degree and the details on the PPE requirements can only be installed post 
installation and post arc-flash hazard analysis. This is a workplace 
requirement, and not a manufacturer requirement.

Dave is correct about the Short-Circuit Withstand Rating (SCCR). This has been 
part of the nameplate requirements for many years.

Doug

On 24-Nov-14, at 16:10, Nyffenegger, Dave  wrote:

> Over the years recently there has been more emphasis on arc flash due to 
> injuries.  You can search on it.  The issue is the potential for arc flash 
> when the control panels are open and powered by the electrician which can 
> cause clothing to catch fire.  It's not so much an issue of containing an arc 
> flash within the enclosure, a fire enclosure should do this regardless.
>
> I asked our NRTL test engineer about arc flash warning label requirements a 
> few months ago and he pointed out that wording in NFPA 70 s

Re: [PSES] Arc Flash Requirements NFPA 79

2014-11-25 Thread John Woodgate
In message 
<64D32EE8B9CBDD44963ACB076A5F6ABB026C5D9A@Mailbox-Tech.lecotech.local>, 
dated Tue, 25 Nov 2014, "Kunde, Brian"  writes:


with a 230VAC powered instrument where the energy to produce an Arc 
Flash is somewhat limited.


There is quite a lot of energy available. It depends on the power supply 
current rating, but a ball-park industrial 230 V supply branch impedance 
at 50 Hz is 0.2 ohms[*]. So the short-circuit current is 1150 A and the 
power is 264500 W.


[*] For a 10% voltage drop at full load, 0.2 ohms means a circuit rating 
of a modest 115 A.

--
OOO - Own Opinions Only. With best wishes. See www.jmwa.demon.co.uk
When I turn my back on the sun, it's to look for a rainbow
John Woodgate, J M Woodgate and Associates, Rayleigh, Essex UK

-

This message is from the IEEE Product Safety Engineering Society emc-pstc discussion 
list. To post a message to the list, send your e-mail to 

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas 
Mike Cantwell 

For policy questions, send mail to:
Jim Bacher:  
David Heald: 


Re: [PSES] Arc Flash Requirements NFPA 79

2014-11-25 Thread Kunde, Brian
Thanks for the input.

Because our products are Laboratory Equipment and not Industrial Machines, I 
assume NFPA 79 would not apply. So the SCCR on the nameplate would not be 
required. It would be difficult to provide anyway. Since we are only required 
to provide supplementary over current protection the SCCR value is really 
unknown. Our Circuit Breaker manufacturer rates their parts with a 5kA SCCR but 
to my understanding they don't even have to survive the test. So the Branch 
Circuit Breaker is relied upon to provide the protection and the necessary SCCR 
value would be based on the Customer's power system.

The SCCR value is interesting to me. For those of you who has to design your 
products to meet a specific SCCR value, what do you design for? Are there 
typical values you shoot for? How high of value must you design for? So if you 
design for say 10kA and your customer wants 50kA what do you do?

Thanks for the information regarding Arc Flash. I'm assuming that if our 
chassis (fire enclosure) meets the constructional requirements of IEC/EN/UL 
61010-1 that it should contain an Arc Flash; especially with a 230VAC powered 
instrument where the energy to produce an Arc Flash is somewhat limited. I have 
also been asked by customers if our chassis meet the NEMA requirements. I 
assume the question is in regards to Arc Flash.

Thanks again for the info. It was most helpful.

The Other Brian


-Original Message-
From: Mr. Doug Nix C.E.T. [mailto:d...@ieee.org]
Sent: Monday, November 24, 2014 4:32 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] Arc Flash Requirements NFPA 79

Dave, Brian,

Electrical field inspectors commonly require that labels of the type I 
referenced be installed by the manufacturer. The detailed labels with the arc 
flash degree and the details on the PPE requirements can only be installed post 
installation and post arc-flash hazard analysis. This is a workplace 
requirement, and not a manufacturer requirement.

Dave is correct about the Short-Circuit Withstand Rating (SCCR). This has been 
part of the nameplate requirements for many years.

Doug

On 24-Nov-14, at 16:10, Nyffenegger, Dave  wrote:

> Over the years recently there has been more emphasis on arc flash due to 
> injuries.  You can search on it.  The issue is the potential for arc flash 
> when the control panels are open and powered by the electrician which can 
> cause clothing to catch fire.  It's not so much an issue of containing an arc 
> flash within the enclosure, a fire enclosure should do this regardless.
>
> I asked our NRTL test engineer about arc flash warning label requirements a 
> few months ago and he pointed out that wording in NFPA 70 states that arc 
> flash warning labels are to be applied on site during machine installation.  
> There is not a requirement for the manufacturer to apply the warning.  I 
> don't have my copy of NFPA 70 in front of me but I recall I confirmed the 
> wording.   I recall I also confirmed the same on the OSHA web site.  These 
> labels can be purchased off the shelf.
>
> NFPA-79: Sec. 16.4 requires the SCCR of electrical control panels to be put 
> on the product nameplate.  UL 508A:  Supplement SB has instructions for 
> determining SCCR.  If your product doesn't contain an electrical control 
> panel and no internal branch circuits you may not need the rating.
>
> I've only had an NRTL certify to NFPA 79 for field labeling/marking.
>
> -Dave
>
> -Original Message-
> From: Kunde, Brian [mailto:brian_ku...@lecotc.com]
> Sent: Monday, November 24, 2014 3:29 PM
> To: EMC-PSTC@LISTSERV.IEEE.ORG
> Subject: [PSES] Arc Flash Requirements NFPA 79
>
> Our company produces Laboratory Equipment. We design to the IEC/EN/UL 61010-1 
> series of standards and the NFPA 70 NEC.
>
> Some of our instruments can be quite large; slightly bigger than an upright 
> piano. They typically are powered by 230VAC, 20A to 50A branch circuits. It 
> is typical that our instruments are installed near or in a heavy industrial 
> environment even though they are not considered Industrial Machines. They are 
> sometimes mistaken as Industrial Machines.
>
> Recently, we have had customers ask the following questions about our 
> instruments:
>
> *   Proof that the electrical system complies to NFPA 79.
> *   Are the electrical enclosures marked for arc flash hazard per NFPA 79?
> *   What is the Short Circuit Current Rating (SCCR) of our instruments?
>
>
> Typically we simply reply that our instruments are not Industrial Machines 
> and that is that. However, if there is information we can provide that would 
> be helpful, we would like to do so.
>
> I can see where our customer may wish to power our instrument from a circuit 
> that is capable of producing very high short 

Re: [PSES] Arc Flash Requirements NFPA 79

2014-11-24 Thread Mr. Doug Nix C.E.T.
Dave, Brian,

Electrical field inspectors commonly require that labels of the type I 
referenced be installed by the manufacturer. The detailed labels with the arc 
flash degree and the details on the PPE requirements can only be installed post 
installation and post arc-flash hazard analysis. This is a workplace 
requirement, and not a manufacturer requirement.

Dave is correct about the Short-Circuit Withstand Rating (SCCR). This has been 
part of the nameplate requirements for many years.

Doug

On 24-Nov-14, at 16:10, Nyffenegger, Dave  wrote:

> Over the years recently there has been more emphasis on arc flash due to 
> injuries.  You can search on it.  The issue is the potential for arc flash 
> when the control panels are open and powered by the electrician which can 
> cause clothing to catch fire.  It's not so much an issue of containing an arc 
> flash within the enclosure, a fire enclosure should do this regardless.
> 
> I asked our NRTL test engineer about arc flash warning label requirements a 
> few months ago and he pointed out that wording in NFPA 70 states that arc 
> flash warning labels are to be applied on site during machine installation.  
> There is not a requirement for the manufacturer to apply the warning.  I 
> don't have my copy of NFPA 70 in front of me but I recall I confirmed the 
> wording.   I recall I also confirmed the same on the OSHA web site.  These 
> labels can be purchased off the shelf.
> 
> NFPA-79: Sec. 16.4 requires the SCCR of electrical control panels to be put 
> on the product nameplate.  UL 508A:  Supplement SB has instructions for 
> determining SCCR.  If your product doesn't contain an electrical control 
> panel and no internal branch circuits you may not need the rating.
> 
> I've only had an NRTL certify to NFPA 79 for field labeling/marking.   
> 
> -Dave
> 
> -Original Message-
> From: Kunde, Brian [mailto:brian_ku...@lecotc.com] 
> Sent: Monday, November 24, 2014 3:29 PM
> To: EMC-PSTC@LISTSERV.IEEE.ORG
> Subject: [PSES] Arc Flash Requirements NFPA 79
> 
> Our company produces Laboratory Equipment. We design to the IEC/EN/UL 61010-1 
> series of standards and the NFPA 70 NEC.
> 
> Some of our instruments can be quite large; slightly bigger than an upright 
> piano. They typically are powered by 230VAC, 20A to 50A branch circuits. It 
> is typical that our instruments are installed near or in a heavy industrial 
> environment even though they are not considered Industrial Machines. They are 
> sometimes mistaken as Industrial Machines.
> 
> Recently, we have had customers ask the following questions about our 
> instruments:
> 
> *   Proof that the electrical system complies to NFPA 79.
> *   Are the electrical enclosures marked for arc flash hazard per NFPA 79?
> *   What is the Short Circuit Current Rating (SCCR) of our instruments?
> 
> 
> Typically we simply reply that our instruments are not Industrial Machines 
> and that is that. However, if there is information we can provide that would 
> be helpful, we would like to do so.
> 
> I can see where our customer may wish to power our instrument from a circuit 
> that is capable of producing very high short circuit current (SCC). If this 
> exceeds the 5kA rating of our internal Supplementary Protection Device, then 
> our customer would have to supply a Brach Circuit Breaker that can handle the 
> SCC.
> 
> High SCC can also cause a concern for Arc Flash. I do not know the 
> requirements of NFPA 79 and how it affects Arc Flash. For instance,  since 
> our chassis meets the mechanical requirements called out in IEC 61010-1, is 
> it likely that our chasses will contain the arc flash hazards?
> 
> Is there any part of NFPA 79 that could apply to our instruments; to the 
> mechanical or electrical system?
> 
> Has something changed recently which would explain why we are now receiving 
> these type of questions?
> 
> Thanks for any input or advice.
> 
> The Other Brian
> 
> 
> 
> 
> 
> 
> LECO Corporation Notice: This communication may contain confidential 
> information intended for the named recipient(s) only. If you received this by 
> mistake, please destroy it and notify us of the error. Thank you.
> 
> -
> 
> This message is from the IEEE Product Safety Engineering Society emc-pstc 
> discussion list. To post a message to the list, send your e-mail to 
> 
> 
> All emc-pstc postings are archived and searchable on the web at:
> http://www.ieee-pses.org/emc-pstc.html
> 
> Attachments are not permitted but the IEEE PSES Online Communities site at 
> http://product-compliance.oc.ie

Re: [PSES] Arc Flash Requirements NFPA 79

2014-11-24 Thread Nyffenegger, Dave
Over the years recently there has been more emphasis on arc flash due to 
injuries.  You can search on it.  The issue is the potential for arc flash when 
the control panels are open and powered by the electrician which can cause 
clothing to catch fire.  It's not so much an issue of containing an arc flash 
within the enclosure, a fire enclosure should do this regardless.

I asked our NRTL test engineer about arc flash warning label requirements a few 
months ago and he pointed out that wording in NFPA 70 states that arc flash 
warning labels are to be applied on site during machine installation.  There is 
not a requirement for the manufacturer to apply the warning.  I don't have my 
copy of NFPA 70 in front of me but I recall I confirmed the wording.   I recall 
I also confirmed the same on the OSHA web site.  These labels can be purchased 
off the shelf.

NFPA-79: Sec. 16.4 requires the SCCR of electrical control panels to be put on 
the product nameplate.  UL 508A:  Supplement SB has instructions for 
determining SCCR.  If your product doesn't contain an electrical control panel 
and no internal branch circuits you may not need the rating.

I've only had an NRTL certify to NFPA 79 for field labeling/marking.   

-Dave

-Original Message-
From: Kunde, Brian [mailto:brian_ku...@lecotc.com] 
Sent: Monday, November 24, 2014 3:29 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: [PSES] Arc Flash Requirements NFPA 79

Our company produces Laboratory Equipment. We design to the IEC/EN/UL 61010-1 
series of standards and the NFPA 70 NEC.

Some of our instruments can be quite large; slightly bigger than an upright 
piano. They typically are powered by 230VAC, 20A to 50A branch circuits. It is 
typical that our instruments are installed near or in a heavy industrial 
environment even though they are not considered Industrial Machines. They are 
sometimes mistaken as Industrial Machines.

Recently, we have had customers ask the following questions about our 
instruments:

*   Proof that the electrical system complies to NFPA 79.
*   Are the electrical enclosures marked for arc flash hazard per NFPA 79?
*   What is the Short Circuit Current Rating (SCCR) of our instruments?


Typically we simply reply that our instruments are not Industrial Machines and 
that is that. However, if there is information we can provide that would be 
helpful, we would like to do so.

I can see where our customer may wish to power our instrument from a circuit 
that is capable of producing very high short circuit current (SCC). If this 
exceeds the 5kA rating of our internal Supplementary Protection Device, then 
our customer would have to supply a Brach Circuit Breaker that can handle the 
SCC.

High SCC can also cause a concern for Arc Flash. I do not know the requirements 
of NFPA 79 and how it affects Arc Flash. For instance,  since our chassis meets 
the mechanical requirements called out in IEC 61010-1, is it likely that our 
chasses will contain the arc flash hazards?

Is there any part of NFPA 79 that could apply to our instruments; to the 
mechanical or electrical system?

Has something changed recently which would explain why we are now receiving 
these type of questions?

Thanks for any input or advice.

The Other Brian






LECO Corporation Notice: This communication may contain confidential 
information intended for the named recipient(s) only. If you received this by 
mistake, please destroy it and notify us of the error. Thank you.

-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 


All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to 
unsubscribe) List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas 
Mike Cantwell 

For policy questions, send mail to:
Jim Bacher:  
David Heald: 

-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 


All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List ru

Re: [PSES] Arc Flash Requirements NFPA 79

2014-11-24 Thread Douglas Nix
Brian,

Based on the information you’ve provided, I think you are on the right track 
using 61010-1. There are portions of NFPA 79 that might be helpful to you, like 
those covering operator device and light colours, and standard panel wire 
colour coding that is used in industrial machines. There are also useful piece 
with relation to the design and integration of interlocks and emergency stop 
systems that you might also find helpful. Having said that, if you are using 
ISO 13850 (E-stop), ISO 14119 (Guards) and ISO 14120 (interlocks), and one of 
ISO 13849-1/-2 or IEC 62061 (Functional Safety), you are probably farther 
ahead, even in a North American market IMO.

NFPA 79 is not a certification standard, but a design standard, and therefore 
you will not find labs that will certify to this standard.

NFPA 79 does not include arc flash requirements; Arc flash is covered by NFPA 
70E and IEEE 1584. As far as 70E is concerned, a label indicating that an arc 
flash hazard assessment should be down by the user of the equipment is all that 
is required. Here’s a typical example. The user is required to conduct the 
assessment and determine the required shock hazard and arc flash hazard 
boundaries, and then the appropriate PPE. This cannot be done by the 
manufacturer.

--
Doug Nix
d...@mac.com
+1 (519) 729-5704

"Electricity is actually made up of extremely tiny particles called electrons, 
that you cannot see with the naked eye unless you have been drinking." - Dave 
Barry

On 24-Nov-14, at 15:28, Kunde, Brian  wrote:

> Our company produces Laboratory Equipment. We design to the IEC/EN/UL 61010-1 
> series of standards and the NFPA 70 NEC.
> 
> Some of our instruments can be quite large; slightly bigger than an upright 
> piano. They typically are powered by 230VAC, 20A to 50A branch circuits. It 
> is typical that our instruments are installed near or in a heavy industrial 
> environment even though they are not considered Industrial Machines. They are 
> sometimes mistaken as Industrial Machines.
> 
> Recently, we have had customers ask the following questions about our 
> instruments:
> 
> *   Proof that the electrical system complies to NFPA 79.
> *   Are the electrical enclosures marked for arc flash hazard per NFPA 79?
> *   What is the Short Circuit Current Rating (SCCR) of our instruments?
> 
> 
> Typically we simply reply that our instruments are not Industrial Machines 
> and that is that. However, if there is information we can provide that would 
> be helpful, we would like to do so.
> 
> I can see where our customer may wish to power our instrument from a circuit 
> that is capable of producing very high short circuit current (SCC). If this 
> exceeds the 5kA rating of our internal Supplementary Protection Device, then 
> our customer would have to supply a Brach Circuit Breaker that can handle the 
> SCC.
> 
> High SCC can also cause a concern for Arc Flash. I do not know the 
> requirements of NFPA 79 and how it affects Arc Flash. For instance,  since 
> our chassis meets the mechanical requirements called out in IEC 61010-1, is 
> it likely that our chasses will contain the arc flash hazards?
> 
> Is there any part of NFPA 79 that could apply to our instruments; to the 
> mechanical or electrical system?
> 
> Has something changed recently which would explain why we are now receiving 
> these type of questions?
> 
> Thanks for any input or advice.
> 
> The Other Brian
> 
> 
> 
> 
> 
> 
> LECO Corporation Notice: This communication may contain confidential 
> information intended for the named recipient(s) only. If you received this by 
> mistake, please destroy it and notify us of the error. Thank you.
> 
> -
> 
> This message is from the IEEE Product Safety Engineering Society emc-pstc 
> discussion list. To post a message to the list, send your e-mail to 
> 
> 
> All emc-pstc postings are archived and searchable on the web at:
> http://www.ieee-pses.org/emc-pstc.html
> 
> Attachments are not permitted but the IEEE PSES Online Communities site at 
> http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
> formats), large files, etc.
> 
> Website:  http://www.ieee-pses.org/
> Instructions:  http://www.ieee-pses.org/list.html (including how to 
> unsubscribe)
> List rules: http://www.ieee-pses.org/listrules.html
> 
> For help, send mail to the list administrators:
> Scott Douglas 
> Mike Cantwell 
> 
> For policy questions, send mail to:
> Jim Bacher:  
> David Heald: 


-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 


All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
htt

[PSES] Arc Flash Requirements NFPA 79

2014-11-24 Thread Kunde, Brian
Our company produces Laboratory Equipment. We design to the IEC/EN/UL 61010-1 
series of standards and the NFPA 70 NEC.

Some of our instruments can be quite large; slightly bigger than an upright 
piano. They typically are powered by 230VAC, 20A to 50A branch circuits. It is 
typical that our instruments are installed near or in a heavy industrial 
environment even though they are not considered Industrial Machines. They are 
sometimes mistaken as Industrial Machines.

Recently, we have had customers ask the following questions about our 
instruments:

*   Proof that the electrical system complies to NFPA 79.
*   Are the electrical enclosures marked for arc flash hazard per NFPA 79?
*   What is the Short Circuit Current Rating (SCCR) of our instruments?


Typically we simply reply that our instruments are not Industrial Machines and 
that is that. However, if there is information we can provide that would be 
helpful, we would like to do so.

I can see where our customer may wish to power our instrument from a circuit 
that is capable of producing very high short circuit current (SCC). If this 
exceeds the 5kA rating of our internal Supplementary Protection Device, then 
our customer would have to supply a Brach Circuit Breaker that can handle the 
SCC.

High SCC can also cause a concern for Arc Flash. I do not know the requirements 
of NFPA 79 and how it affects Arc Flash. For instance,  since our chassis meets 
the mechanical requirements called out in IEC 61010-1, is it likely that our 
chasses will contain the arc flash hazards?

Is there any part of NFPA 79 that could apply to our instruments; to the 
mechanical or electrical system?

Has something changed recently which would explain why we are now receiving 
these type of questions?

Thanks for any input or advice.

The Other Brian






LECO Corporation Notice: This communication may contain confidential 
information intended for the named recipient(s) only. If you received this by 
mistake, please destroy it and notify us of the error. Thank you.

-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 


All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas 
Mike Cantwell 

For policy questions, send mail to:
Jim Bacher:  
David Heald: