Re: [PSES] NEC vs CEC for Transformer Protection

2015-04-01 Thread Kunde, Brian
To all, thank you for some great input.

Many of you explained the science behind protecting a transformer from 
overheating but unfortunately the CSA inspector don't care, nor has the 
authority to make a decision or ruling; he can only apply what the CEC says in 
this case, which really limits our options.

We even contacted the transformer manufacture and their CSA Engineer and they 
are both baffled by the requirements in the CEC for small dry-type transformers.

It really seems like sections 26-254 and 26-256 are backward in regard to 
dry-type transformers. How many other than dry-type transformers do you see 
rated under 2 amps.

It also appears as if thermal protection is not a viable protection method for 
dry-type transformers. Really? My thermally protected 24VAC furnace and 
door-bell transformers would seem to violate the CEC.

It would seem our only option is to add overcurrent protection to the secondary 
side of the transformer so we can size the Primary OPD so not to nuisance trip 
due to inrush currents.

I was really hoping we were missing something.

Thanks again.
The Other Brian


-Original Message-
From: Brian Oconnell [mailto:oconne...@tamuracorp.com]
Sent: Monday, March 30, 2015 1:56 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] NEC vs CEC for Transformer Protection

5085-3/CSA No66.3 scoped only where class 2 or 3 stuff is required, and 
generally not considered for industrial environment where the secondary circuit 
not exposed. Other than Class 2 would be scoped by UL1012 and CSA107.1.

For industrial control transformers, the scoped standard would probably be 
UL508 or UL508A, where the tables in clause 42 of 508A would apply for 
overcurrent protection of both transformer sides. In U.S. (not certain about 
Mexico), anything over 2kVA is considered a power transformer, where branch 
circuit protection is required; for Canada all power transformers are provided 
current interrupt via the branch circuit protection, and supplementary 
protection device must be certified per CSA No235-4.

For distribution transformers over 10kVA, UL1561 and CSA No47 are scoped, where 
branch protection not necessarily considered, and probably not relevant to this 
discussion.

Brian


From: Brian Gregory [mailto:brian_greg...@netzero.net]
Sent: Monday, March 30, 2015 10:03 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] NEC vs CEC for Transformer Protection

I'd restate Dave's case below to say:  PE's are really only required for Public 
Sector work.  Industrial/commercial products are certified (where necessary) by 
NRTL testing, and - as Brian has noted - by application of CEC/NEC.

Brian Kunde's situation appears to be that NEC and CEC have conflicting 
interpretations of what allows for a safe installation.

1.  dry type is any transformer not encased in oil or other cooling 
dielectric media.  It can be encapsulated.  See UL 5085 or CSA C22.2 No.66.1 to 
be sure.
2.  Ideally, the vendor has guidelines backed up by test data, or if it's CSA 
listed, their file provides guidance;  but that may not be judged suitable to 
your application.  When confronted with a picky inspector (right or wrong), you 
get into a difficult place.  I agree with you that a 2 or 2.25 A slo-blow fuse 
is best, esp. when the vendor says 1.8 is too small and you have to go looking 
look for special long-delay types (which will vary, thereby pose reliability 
problems).  However, an inspector is difficult to outflank, for reasons which 
are generally all good.

So, if #2 (mfr. test data) doesn't resolve the situation, I see two 
alternatives:

2a:  have test data showing that ~2A sustained** current does not lead to 
temperatures that lead to an insulation breakdown, and present that to the 
inspector.
2b:  have an NRTL do a field label of the equipment to allow the inspector to 
hang his safety hat on the NRTL report.


**  The time that this current needs to be sustained would be in either UL 
5085-3 or C22.2 #66.1 under temperature or abnormal testing (sorry, don't have 
them handy) in real world terms, this is 10~15 min. but in some cases is 
stretched out until the XF gets to a stable temperature.

Good luck!

Brian Gregory
720-450-4933


-- Original Message --
From: Nyffenegger, Dave dave.nyffeneg...@bhemail.com
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] NEC vs CEC for Transformer Protection
Date: Sun, 29 Mar 2015 16:03:28 +

Engineers doing any sort of direct public work in the U.S. must be licensed 
or working under a (licensed) PE (in which case they are not an engineer in the 
eyes of the law) regardless of the discipline.  This applies to private 
consulting firms doing public work or within government agencies.  The same 
industrial exception exists in the US and this does carry through to products 
for sale.

-Dave
From: Kunde, Brian [mailto:brian_ku...@lecotc.com]
Sent: Friday, March 27, 2015 1:27 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: [PSES] NEC vs CEC

Re: [PSES] NEC vs CEC for Transformer Protection

2015-04-01 Thread John Woodgate
In message 
64D32EE8B9CBDD44963ACB076A5F6ABB026D7789@Mailbox-Tech.lecotech.local, 
dated Wed, 1 Apr 2015, Kunde, Brian brian_ku...@lecotc.com writes:


It would seem our only option is to add overcurrent protection to the 
secondary side of the transformer so we can size the Primary OPD so not 
to nuisance trip due to inrush currents.


Since that appears to be specifically permitted, it is probably the 
optimum solution.

--
OOO - Own Opinions Only. With best wishes. See www.jmwa.demon.co.uk
When I turn my back on the sun, it's to look for a rainbow
John Woodgate, J M Woodgate and Associates, Rayleigh, Essex UK

-

This message is from the IEEE Product Safety Engineering Society emc-pstc discussion 
list. To post a message to the list, send your e-mail to emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas sdoug...@ieee.org
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com


Re: [PSES] NEC vs CEC for Transformer Protection

2015-03-30 Thread Bob LaFrance
Greetings,

Interesting thread.  I normally design SMPS, but went through this exercise a 
few months back with a 15kVA transformer.

RK5 class fuses  seem to me to be able to handle large inrush that a 
transformer will source.  Thermal circuit breakers are slow to respond and may 
provide the delay necessary to get it up and running.  Ametherm corporation 
produces inrush limiters to mitigate transformer inrush.  They have a design 
guide on their web site. 

Inrush current is a function of source voltage as well as transformer 
characteristics as previously mentioned in thread.  Input side impedance can 
also play a part in the play.

Regards,
Bob
N9NEO




-Original Message-
From: John Woodgate [mailto:j...@jmwa.demon.co.uk] 
Sent: Sunday, March 29, 2015 11:59 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] NEC vs CEC for Transformer Protection

In message b3cae477-8211-419c-8dc7-b3df60f37...@ieee.org, dated Sun,
29 Mar 2015, Mr. Doug Nix C.E.T. d...@ieee.org writes:

I can’t disagree with any of your statements, only say that this is 
what is commonly done in practice. Many machine builders have people 
doing design work who have only minimal qualifications - 2 yr 
technician diplomas, or people that have “learned by doing”. It depends 
on the company involved. This is also frequently true of US machine 
builders. These shops are often very small and have no engineers on 
staff.

I think that's the same in most countries. There are many official training 
schemes, but there are industry sectors that are not 'sexy' 
enough to attract the necessary government support to establish a scheme.

You may not be aware of this, but in the US, there is no requirement 
that people doing engineering work be licensed, with a few specific 
exceptions in the civil engineering realm.

There isn't in Britain, either. There is a series of qualification levels but 
no licensing, in the electrical/electronic industry anyway.
--
OOO - Own Opinions Only. With best wishes. See www.jmwa.demon.co.uk When I turn 
my back on the sun, it's to look for a rainbow John Woodgate, J M Woodgate and 
Associates, Rayleigh, Essex UK

-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas sdoug...@ieee.org
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com

-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas sdoug...@ieee.org
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com


Re: [PSES] NEC vs CEC for Transformer Protection

2015-03-30 Thread John Woodgate
In message 
2313bb439627e348a579b7b3f41d9c143d364...@newcastle.creare.com, dated 
Mon, 30 Mar 2015, Bob LaFrance b...@creare.com writes:


Inrush current is a function of source voltage as well as transformer 
characteristics as previously mentioned in thread.


Naturally.


Input side impedance can also play a part in the play.


Yes, when you get to 15 kVA (or a little less) at 230 V, the supply 
impedance is a significant factor.

--
OOO - Own Opinions Only. With best wishes. See www.jmwa.demon.co.uk
When I turn my back on the sun, it's to look for a rainbow
John Woodgate, J M Woodgate and Associates, Rayleigh, Essex UK

-

This message is from the IEEE Product Safety Engineering Society emc-pstc discussion 
list. To post a message to the list, send your e-mail to emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas sdoug...@ieee.org
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com


Re: [PSES] NEC vs CEC for Transformer Protection

2015-03-30 Thread Brian Gregory
 I'd restate Dave's case below to say:  PE's are really only required for 
Public Sector work.  Industrial/commercial products are certified (where 
necessary) by NRTL testing, and - as Brian has noted - by application of 
CEC/NEC. Brian Kunde's situation appears to be that NEC and CEC have 
conflicting interpretations of what allows for a safe installation. 1.  dry 
type is any transformer not encased in oil or other cooling dielectric media.  
It can be encapsulated.  See UL 5085 or CSA C22.2 No.66.1 to be sure.2.  
Ideally, the vendor has guidelines backed up by test data, or if it's CSA 
listed, their file provides guidance;  but that may not be judged suitable to 
your application.  When confronted with a picky inspector (right or wrong), you 
get into a difficult place.  I agree with you that a 2 or 2.25 A slo-blow fuse 
is best, esp. when the vendor says 1.8 is too small and you have to go looking 
look for special long-delay types (which will vary, thereby pose reliability 
problems).  However, an inspector is difficult to outflank, for reasons which 
are generally all good. So, if #2 (mfr. test data) doesn't resolve the 
situation, I see two alternatives:  2a:  have test data showing that ~2A 
sustained** current does not lead to temperatures that lead to an insulation 
breakdown, and present that to the inspector.2b:  have an NRTL do a field label 
of the equipment to allow the inspector to hang his safety hat on the NRTL 
report.  **  The time that this current needs to be sustained would be in 
either UL 5085-3 or C22.2 #66.1 under temperature or abnormal testing (sorry, 
don't have them handy) in real world terms, this is 10~15 min. but in some 
cases is stretched out until the XF gets to a stable temperature. Good luck! 
Brian Gregory
720-450-4933

-- Original Message --
From: Nyffenegger, Dave dave.nyffeneg...@bhemail.com
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] NEC vs CEC for Transformer Protection
Date: Sun, 29 Mar 2015 16:03:28 +

Engineers doing any sort of direct public work in the U.S. must be licensed 
or working under a (licensed) PE (in which case they are not an engineer in the 
eyes of the law) regardless of the discipline.  This applies to private 
consulting firms doing public work or within government agencies.  The same 
industrial exception exists in the US and this does carry through to products 
for sale.

-Dave


From: Kunde, Brian [mailto:brian_ku...@lecotc.com]
Sent: Friday, March 27, 2015 1:27 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: [PSES] NEC vs CEC for Transformer Protection
 
Please help.
 
We have a product, laboratory equipment, that has a 330 watt 1:1 230Vac 
isolation transformer.  330w / 230V = 1.34 amps.
 
To protect this transformer we applied the US-NEC table 450.3(B) to where the 
primary protector can be up to 300% of the of 1.34 amps. The transformer 
manufacturer recommended a 2.25A time lag circuit breaker to handle the inrush 
current from this transformer. Life is good.
 
Then, we had this product inspected in Canada to which they apply the Canadian 
Electric Code section 26-256, ldquo;Overcurrent protection for dry=type 
transformer circuits rated 750V or lessrdquo;, which states the primary 
overcurrent protection device cannot exceed 125% of the transformer current 
rating. Thatrsquo;s 134 amps * 1.25 (125%) = 1.78 amps. Rounded up, the 
inspector said we had to use a fuse or breaker no larger than 1.8 amps.
 
We notified the transformer manufacturer who said (and we confirmed) that 1.8 
amp protection device will nuisance trip due to Inrush Currents.
 
The transformer CSA inspector and a representative from Littelfuse both are 
telling us that the inspector applied the wrong section of the Electric Code 
and that section 26-254, ldquo;Overcurrent protection for power and 
distribution transformer circuits rated 750 V or less, other than dry-type 
transformersrdquo; should be applied.  This section of the CEC does alien 
better with the US-NEC.
 
However, what is a ldquo;dry-type transformerrdquo;??  From my understanding, 
our transformer is not an oil or dielectric cooled transformer and it should be 
considered a ldquo;Dry-Typerdquo; transformer which would make the inspector 
correct in applying section 26-256.
 
Am I missing something here?  It makes sense that the NEC and CEC should track 
closely in this regard but it appears as Canadarsquo;s requirement for 
dry-type transformers trump these low current transformers that would be 
impossible to properly protect according to their code.
 


This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product

Re: [PSES] NEC vs CEC for Transformer Protection

2015-03-30 Thread Brian Oconnell
5085-3/CSA No66.3 scoped only where class 2 or 3 stuff is required, and 
generally not considered for industrial environment where the secondary circuit 
not exposed. Other than Class 2 would be scoped by UL1012 and CSA107.1.

For industrial control transformers, the scoped standard would probably be 
UL508 or UL508A, where the tables in clause 42 of 508A would apply for 
overcurrent protection of both transformer sides. In U.S. (not certain about 
Mexico), anything over 2kVA is considered a power transformer, where branch 
circuit protection is required; for Canada all power transformers are provided 
current interrupt via the branch circuit protection, and supplementary 
protection device must be certified per CSA No235-4. 

For distribution transformers over 10kVA, UL1561 and CSA No47 are scoped, where 
branch protection not necessarily considered, and probably not relevant to this 
discussion.

Brian


From: Brian Gregory [mailto:brian_greg...@netzero.net] 
Sent: Monday, March 30, 2015 10:03 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] NEC vs CEC for Transformer Protection
 
I'd restate Dave's case below to say:  PE's are really only required for Public 
Sector work.  Industrial/commercial products are certified (where necessary) by 
NRTL testing, and - as Brian has noted - by application of CEC/NEC.
 
Brian Kunde's situation appears to be that NEC and CEC have conflicting 
interpretations of what allows for a safe installation.
 
1.  dry type is any transformer not encased in oil or other cooling 
dielectric media.  It can be encapsulated.  See UL 5085 or CSA C22.2 No.66.1 to 
be sure.
2.  Ideally, the vendor has guidelines backed up by test data, or if it's CSA 
listed, their file provides guidance;  but that may not be judged suitable to 
your application.  When confronted with a picky inspector (right or wrong), you 
get into a difficult place.  I agree with you that a 2 or 2.25 A slo-blow fuse 
is best, esp. when the vendor says 1.8 is too small and you have to go looking 
look for special long-delay types (which will vary, thereby pose reliability 
problems).  However, an inspector is difficult to outflank, for reasons which 
are generally all good.
 
So, if #2 (mfr. test data) doesn't resolve the situation, I see two 
alternatives: 
 
2a:  have test data showing that ~2A sustained** current does not lead to 
temperatures that lead to an insulation breakdown, and present that to the 
inspector.
2b:  have an NRTL do a field label of the equipment to allow the inspector to 
hang his safety hat on the NRTL report.
 
 
**  The time that this current needs to be sustained would be in either UL 
5085-3 or C22.2 #66.1 under temperature or abnormal testing (sorry, don't have 
them handy) in real world terms, this is 10~15 min. but in some cases is 
stretched out until the XF gets to a stable temperature.
 
Good luck!
 
Brian Gregory
720-450-4933


-- Original Message --
From: Nyffenegger, Dave dave.nyffeneg...@bhemail.com
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] NEC vs CEC for Transformer Protection
Date: Sun, 29 Mar 2015 16:03:28 +

Engineers doing any sort of direct public work in the U.S. must be licensed 
or working under a (licensed) PE (in which case they are not an engineer in the 
eyes of the law) regardless of the discipline.  This applies to private 
consulting firms doing public work or within government agencies.  The same 
industrial exception exists in the US and this does carry through to products 
for sale.

-Dave
From: Kunde, Brian [mailto:brian_ku...@lecotc.com]
Sent: Friday, March 27, 2015 1:27 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: [PSES] NEC vs CEC for Transformer Protection
 
Please help.
 
We have a product, laboratory equipment, that has a 330 watt 1:1 230Vac 
isolation transformer.  330w / 230V = 1.34 amps.
 
To protect this transformer we applied the US-NEC table 450.3(B) to where the 
primary protector can be up to 300% of the of 1.34 amps. The transformer 
manufacturer recommended a 2.25A time lag circuit breaker to handle the inrush 
current from this transformer. Life is good.
 
Then, we had this product inspected in Canada to which they apply the Canadian 
Electric Code section 26-256, Overcurrent protection for dry=type transformer 
circuits rated 750V or less, which states the primary overcurrent protection 
device cannot exceed 125% of the transformer current rating. That's 134 amps * 
1.25 (125%) = 1.78 amps. Rounded up, the inspector said we had to use a fuse or 
breaker no larger than 1.8 amps.
 
We notified the transformer manufacturer who said (and we confirmed) that 1.8 
amp protection device will nuisance trip due to Inrush Currents.
 
The transformer CSA inspector and a representative from Littelfuse both are 
telling us that the inspector applied the wrong section of the Electric Code 
and that section 26-254, Overcurrent protection for power and distribution 
transformer circuits rated 750 V or less, other than dry

Re: [PSES] NEC vs CEC for Transformer Protection

2015-03-29 Thread Mr. Doug Nix C.E.T.
John,

I can’t disagree with any of your statements, only say that this is what is 
commonly done in practice. Many machine builders have people doing design work 
who have only minimal qualifications - 2 yr technician diplomas, or people that 
have “learned by doing”. It depends on the company involved. This is also 
frequently true of US machine builders. These shops are often very small and 
have no engineers on staff.

You may not be aware of this, but in the US, there is no requirement that 
people doing engineering work be licensed, with a few specific exceptions in 
the civil engineering realm.

In Canada, it depends on the Province or Territory. In Ontario, where I 
practice, the Engineer’s Act contains a clause commonly called the “industrial 
exception” that is supposed to provide an out to employers who have 
non-licenced technical people doing work that is considered to be “engineering” 
under the act. The activities are supposed to be limited to work on the 
employer’s manufacturing equipment, not product for sale, but in practice no 
distinction is made. Unfortunately, the other side of this is that the 
definition of Professional Engineering is so broad that you might be challenged 
for making your own lunch under the act. It’s a mess, IMO.

Anyway, many of the machine electrical designers that I’ve dealt with over the 
years have never seen a time-current curve, and wouldn’t know how to use one, 
even if you showed it to them. Ohm’s law? well maybe… 

Doug

 On 29-Mar-15, at 08:58, John Woodgate j...@jmwa.demon.co.uk wrote:
 
 In message 9dd08e56-75ed-4ae5-a80a-26a08324b...@ieee.org, dated Sun, 29 Mar 
 2015, Mr. Doug Nix C.E.T. d...@ieee.org writes:
 
 Typically, designers in Canada use two general rules for guidance in 
 protecting transformers, with little actual calculation of inrush currents 
 considered:
 
 1) If no secondary OCD is provided, then the primary OCD will be selected at 
 125% of rated full load current, if inrush proves a problem, then a device 
 with slower opening characteristics will be selected.
 
 It might need to be too slow to be available.
 
 2) If the secondary is protected at 125% of rated, then the primary OCD may 
 be selected at 300% or less of of rated.
 
 That's a sensible solution. Presumably, the Canadian reg. is encouraging that 
 solution.
 
 These guiding rules generally allow for inrush and provide some degree of 
 protection for the transformer. They also meet the CEC requirements. For 
 most industrial controls applications, you will not find designers going any 
 deeper than this. I have yet to see a machine builder spend any time on 
 temperature rise tests or on detailed inrush calculations.
 
 OK, but supply voltage/winding resistance is hardly difficult.
 
 This does not detract from the need to do the testing and come up with a 
 more correctly selected value, but rather speaks to the lack of adequate 
 time allowed for design, and the fact that very few degreed electrical 
 engineers are employed as equipment designers in Canada, so the level of 
 engineering expertise involved in the design is lower than what one might 
 expect.
 
 One hopes that they know Ohm's Law, but realise that one may be disappointed.
 
 -- 
 OOO - Own Opinions Only. With best wishes. See www.jmwa.demon.co.uk
 When I turn my back on the sun, it's to look for a rainbow
 John Woodgate, J M Woodgate and Associates, Rayleigh, Essex UK
 
 -
 
 This message is from the IEEE Product Safety Engineering Society emc-pstc 
 discussion list. To post a message to the list, send your e-mail to 
 emc-p...@ieee.org
 
 All emc-pstc postings are archived and searchable on the web at:
 http://www.ieee-pses.org/emc-pstc.html
 
 Attachments are not permitted but the IEEE PSES Online Communities site at 
 http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
 formats), large files, etc.
 
 Website:  http://www.ieee-pses.org/
 Instructions:  http://www.ieee-pses.org/list.html (including how to 
 unsubscribe)
 List rules: http://www.ieee-pses.org/listrules.html
 
 For help, send mail to the list administrators:
 Scott Douglas sdoug...@ieee.org
 Mike Cantwell mcantw...@ieee.org
 
 For policy questions, send mail to:
 Jim Bacher:  j.bac...@ieee.org
 David Heald: dhe...@gmail.com

-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)

Re: [PSES] NEC vs CEC for Transformer Protection

2015-03-29 Thread Nyffenegger, Dave
Engineers doing any sort of direct public work in the U.S. must be licensed 
or working under a (licensed) PE (in which case they are not an engineer in the 
eyes of the law) regardless of the discipline.  This applies to private 
consulting firms doing public work or within government agencies.  The same 
industrial exception exists in the US and this does carry through to products 
for sale.

-Dave

-Original Message-
From: Mr. Doug Nix C.E.T. [mailto:d...@ieee.org] 
Sent: Sunday, March 29, 2015 11:40 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] NEC vs CEC for Transformer Protection

John,

I can’t disagree with any of your statements, only say that this is what is 
commonly done in practice. Many machine builders have people doing design work 
who have only minimal qualifications - 2 yr technician diplomas, or people that 
have “learned by doing”. It depends on the company involved. This is also 
frequently true of US machine builders. These shops are often very small and 
have no engineers on staff.

You may not be aware of this, but in the US, there is no requirement that 
people doing engineering work be licensed, with a few specific exceptions in 
the civil engineering realm.

In Canada, it depends on the Province or Territory. In Ontario, where I 
practice, the Engineer’s Act contains a clause commonly called the “industrial 
exception” that is supposed to provide an out to employers who have 
non-licenced technical people doing work that is considered to be “engineering” 
under the act. The activities are supposed to be limited to work on the 
employer’s manufacturing equipment, not product for sale, but in practice no 
distinction is made. Unfortunately, the other side of this is that the 
definition of Professional Engineering is so broad that you might be challenged 
for making your own lunch under the act. It’s a mess, IMO.

Anyway, many of the machine electrical designers that I’ve dealt with over the 
years have never seen a time-current curve, and wouldn’t know how to use one, 
even if you showed it to them. Ohm’s law? well maybe… 

Doug

 On 29-Mar-15, at 08:58, John Woodgate j...@jmwa.demon.co.uk wrote:
 
 In message 9dd08e56-75ed-4ae5-a80a-26a08324b...@ieee.org, dated Sun, 29 Mar 
 2015, Mr. Doug Nix C.E.T. d...@ieee.org writes:
 
 Typically, designers in Canada use two general rules for guidance in 
 protecting transformers, with little actual calculation of inrush currents 
 considered:
 
 1) If no secondary OCD is provided, then the primary OCD will be selected at 
 125% of rated full load current, if inrush proves a problem, then a device 
 with slower opening characteristics will be selected.
 
 It might need to be too slow to be available.
 
 2) If the secondary is protected at 125% of rated, then the primary OCD may 
 be selected at 300% or less of of rated.
 
 That's a sensible solution. Presumably, the Canadian reg. is encouraging that 
 solution.
 
 These guiding rules generally allow for inrush and provide some degree of 
 protection for the transformer. They also meet the CEC requirements. For 
 most industrial controls applications, you will not find designers going any 
 deeper than this. I have yet to see a machine builder spend any time on 
 temperature rise tests or on detailed inrush calculations.
 
 OK, but supply voltage/winding resistance is hardly difficult.
 
 This does not detract from the need to do the testing and come up with a 
 more correctly selected value, but rather speaks to the lack of adequate 
 time allowed for design, and the fact that very few degreed electrical 
 engineers are employed as equipment designers in Canada, so the level of 
 engineering expertise involved in the design is lower than what one might 
 expect.
 
 One hopes that they know Ohm's Law, but realise that one may be disappointed.
 
 --
 OOO - Own Opinions Only. With best wishes. See www.jmwa.demon.co.uk 
 When I turn my back on the sun, it's to look for a rainbow John 
 Woodgate, J M Woodgate and Associates, Rayleigh, Essex UK
 
 -
 
 This message is from the IEEE Product Safety Engineering Society 
 emc-pstc discussion list. To post a message to the list, send your 
 e-mail to emc-p...@ieee.org
 
 All emc-pstc postings are archived and searchable on the web at:
 http://www.ieee-pses.org/emc-pstc.html
 
 Attachments are not permitted but the IEEE PSES Online Communities site at 
 http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
 formats), large files, etc.
 
 Website:  http://www.ieee-pses.org/
 Instructions:  http://www.ieee-pses.org/list.html (including how to 
 unsubscribe) List rules: http://www.ieee-pses.org/listrules.html
 
 For help, send mail to the list administrators:
 Scott Douglas sdoug...@ieee.org
 Mike Cantwell mcantw...@ieee.org
 
 For policy questions, send mail to:
 Jim Bacher:  j.bac...@ieee.org
 David Heald: dhe...@gmail.com

Re: [PSES] NEC vs CEC for Transformer Protection

2015-03-29 Thread John Woodgate
In message b3cae477-8211-419c-8dc7-b3df60f37...@ieee.org, dated Sun, 
29 Mar 2015, Mr. Doug Nix C.E.T. d...@ieee.org writes:


I can’t disagree with any of your statements, only say that this is 
what is commonly done in practice. Many machine builders have people 
doing design work who have only minimal qualifications - 2 yr 
technician diplomas, or people that have “learned by doing”. It 
depends on the company involved. This is also frequently true of US 
machine builders. These shops are often very small and have no 
engineers on staff.


I think that's the same in most countries. There are many official 
training schemes, but there are industry sectors that are not 'sexy' 
enough to attract the necessary government support to establish a 
scheme.


You may not be aware of this, but in the US, there is no requirement 
that people doing engineering work be licensed, with a few specific 
exceptions in the civil engineering realm.


There isn't in Britain, either. There is a series of qualification 
levels but no licensing, in the electrical/electronic industry anyway.

--
OOO - Own Opinions Only. With best wishes. See www.jmwa.demon.co.uk
When I turn my back on the sun, it's to look for a rainbow
John Woodgate, J M Woodgate and Associates, Rayleigh, Essex UK

-

This message is from the IEEE Product Safety Engineering Society emc-pstc discussion 
list. To post a message to the list, send your e-mail to emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas sdoug...@ieee.org
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com


Re: [PSES] NEC vs CEC for Transformer Protection

2015-03-29 Thread Mr. Doug Nix C.E.T.
Typically, designers in Canada use two general rules for guidance in protecting 
transformers, with little actual calculation of inrush currents considered: 

1) If no secondary OCD is provided, then the primary OCD will be selected at 
125% of rated full load current, if inrush proves a problem, then a device with 
slower opening characteristics will be selected.
2) If the secondary is protected at 125% of rated, then the primary OCD may be 
selected at 300% or less of of rated.

These guiding rules generally allow for inrush and provide some degree of 
protection for the transformer. They also meet the CEC requirements. For most 
industrial controls applications, you will not find designers going any deeper 
than this. I have yet to see a machine builder spend any time on temperature 
rise tests or on detailed inrush calculations. This does not detract from the 
need to do the testing and come up with a more correctly selected value, but 
rather speaks to the lack of adequate time allowed for design, and the fact 
that very few degreed electrical engineers are employed as equipment designers 
in Canada, so the level of engineering expertise involved in the design is 
lower than what one might expect. Outside of the industrial equipment realm, 
larger companies building consumer products and looking for maximum cost 
reductions in components would be far more likely to spend the time and money 
on the testing and analysis described by Rich, John, Brian and the o!
 thers that have contributed to this interesting thread.

Doug Nix
d...@ieee.org
+1 519 729 5704

 On 29-Mar-15, at 03:20, John Woodgate j...@jmwa.demon.co.uk wrote:
 
 In message 
 blupr02mb1162ba09cc137bdb35ca50ac1...@blupr02mb116.namprd02.prod.outlook
 .com, dated Sun, 29 Mar 2015, Brian Oconnell oconne...@tamuracorp.com 
 writes:
 
 nrush peak for 50/60Hz transformers mostly from  magnetizing current - core 
 saturation and residual flux, and of course input V. As the saturation curve 
 does not extend past the pi/2 inrush peak, any further inrush past a few 
 mSec is typically from filling up the coulomb buckets on the secondary side. 
 This is a tau-based thing, so both DCR and Z would be used to determine the 
 current-interrupt component's expected I2T.
 
 I did many tests on inrush to determine the requirements in IEC/EN 61000-3-3. 
 The worst case is when the supply was switched off with the core flux at 
 maximum, which then decays to the remanent point (H_r, B_r), because the core 
 is a closed magnetic circuit.
 
 If the supply is then switched on at a voltage zero, with the voltage rising 
 in the direction to (try to) increase the core flux, the core saturates hard, 
 since Br with modern materials is nearly equal to B_sat, and the voltage is 
 thus 'trying' to reach nearly 2B_sat. The permeability drops to 1,  so the 
 inductance drops to a very low value, and the only other significant 
 impedance in the circuit is the winding resistance.
 
 In most cases, the very high inrush current lasts for half a cycle (we are 
 considering RMS values, not peak, so our values are nominally averaged over a 
 whole cycle), but the currents in the following half-cycles don't decay to 
 the steady-state value for several more cycles, and the current in the second 
 half-cycle may be large enough to need taking into account in looking at the 
 necessary I^2t value of the protective device.
 -- 
 OOO - Own Opinions Only. With best wishes. See www.jmwa.demon.co.uk
 When I turn my back on the sun, it's to look for a rainbow
 John Woodgate, J M Woodgate and Associates, Rayleigh, Essex UK
 
 -
 
 This message is from the IEEE Product Safety Engineering Society emc-pstc 
 discussion list. To post a message to the list, send your e-mail to 
 emc-p...@ieee.org
 
 All emc-pstc postings are archived and searchable on the web at:
 http://www.ieee-pses.org/emc-pstc.html
 
 Attachments are not permitted but the IEEE PSES Online Communities site at 
 http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
 formats), large files, etc.
 
 Website:  http://www.ieee-pses.org/
 Instructions:  http://www.ieee-pses.org/list.html (including how to 
 unsubscribe)
 List rules: http://www.ieee-pses.org/listrules.html
 
 For help, send mail to the list administrators:
 Scott Douglas sdoug...@ieee.org
 Mike Cantwell mcantw...@ieee.org
 
 For policy questions, send mail to:
 Jim Bacher:  j.bac...@ieee.org
 David Heald: dhe...@gmail.com

-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be 

Re: [PSES] NEC vs CEC for Transformer Protection

2015-03-29 Thread John Woodgate
In message 9dd08e56-75ed-4ae5-a80a-26a08324b...@ieee.org, dated Sun, 
29 Mar 2015, Mr. Doug Nix C.E.T. d...@ieee.org writes:


Typically, designers in Canada use two general rules for guidance in 
protecting transformers, with little actual calculation of inrush 
currents considered:


1) If no secondary OCD is provided, then the primary OCD will be 
selected at 125% of rated full load current, if inrush proves a 
problem, then a device with slower opening characteristics will be 
selected.


It might need to be too slow to be available.

2) If the secondary is protected at 125% of rated, then the primary OCD 
may be selected at 300% or less of of rated.


That's a sensible solution. Presumably, the Canadian reg. is encouraging 
that solution.


These guiding rules generally allow for inrush and provide some degree 
of protection for the transformer. They also meet the CEC requirements. 
For most industrial controls applications, you will not find designers 
going any deeper than this. I have yet to see a machine builder spend 
any time on temperature rise tests or on detailed inrush calculations.


OK, but supply voltage/winding resistance is hardly difficult.

This does not detract from the need to do the testing and come up with 
a more correctly selected value, but rather speaks to the lack of 
adequate time allowed for design, and the fact that very few degreed 
electrical engineers are employed as equipment designers in Canada, so 
the level of engineering expertise involved in the design is lower than 
what one might expect.


One hopes that they know Ohm's Law, but realise that one may be 
disappointed.


--
OOO - Own Opinions Only. With best wishes. See www.jmwa.demon.co.uk
When I turn my back on the sun, it's to look for a rainbow
John Woodgate, J M Woodgate and Associates, Rayleigh, Essex UK

-

This message is from the IEEE Product Safety Engineering Society emc-pstc discussion 
list. To post a message to the list, send your e-mail to emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas sdoug...@ieee.org
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com


Re: [PSES] NEC vs CEC for Transformer Protection

2015-03-29 Thread John Woodgate
In message 
blupr02mb1162ba09cc137bdb35ca50ac1...@blupr02mb116.namprd02.prod.outlook
.com, dated Sun, 29 Mar 2015, Brian Oconnell oconne...@tamuracorp.com 
writes:


nrush peak for 50/60Hz transformers mostly from  magnetizing current - 
core saturation and residual flux, and of course input V. As the 
saturation curve does not extend past the pi/2 inrush peak, any further 
inrush past a few mSec is typically from filling up the coulomb buckets 
on the secondary side. This is a tau-based thing, so both DCR and Z 
would be used to determine the current-interrupt component's expected I2T.


I did many tests on inrush to determine the requirements in IEC/EN 
61000-3-3. The worst case is when the supply was switched off with the 
core flux at maximum, which then decays to the remanent point (H_r, 
B_r), because the core is a closed magnetic circuit.


If the supply is then switched on at a voltage zero, with the voltage 
rising in the direction to (try to) increase the core flux, the core 
saturates hard, since Br with modern materials is nearly equal to B_sat, 
and the voltage is thus 'trying' to reach nearly 2B_sat. The 
permeability drops to 1,  so the inductance drops to a very low value, 
and the only other significant impedance in the circuit is the winding 
resistance.


In most cases, the very high inrush current lasts for half a cycle (we 
are considering RMS values, not peak, so our values are nominally 
averaged over a whole cycle), but the currents in the following 
half-cycles don't decay to the steady-state value for several more 
cycles, and the current in the second half-cycle may be large enough to 
need taking into account in looking at the necessary I^2t value of the 
protective device.

--
OOO - Own Opinions Only. With best wishes. See www.jmwa.demon.co.uk
When I turn my back on the sun, it's to look for a rainbow
John Woodgate, J M Woodgate and Associates, Rayleigh, Essex UK

-

This message is from the IEEE Product Safety Engineering Society emc-pstc discussion 
list. To post a message to the list, send your e-mail to emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas sdoug...@ieee.org
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com


Re: [PSES] NEC vs CEC for Transformer Protection

2015-03-28 Thread Brian Oconnell
Inrush peak for 50/60Hz transformers mostly from  magnetizing current - core 
saturation and residual flux, and of course input V. As the saturation curve 
does not extend past the pi/2 inrush peak, any further inrush past a few mSec 
is typically from filling up the coulomb buckets on the secondary side. This is 
a tau-based thing, so both DCR and Z would be used to determine the 
current-interrupt component's expected I2T. Inrush for the 'small' transformer 
is being discussed can have peak inrush well over 20x rated continuous. For the 
smaller industrial control stuff under 5kVA, series thermistor in lieu of fuse 
is common where wire and breaker are correctly sized.

The AHJ's focus should be on SCCR, which is inversely proportional to the DCR 
of the secondary windings, and coordination between the distribution breaker 
and the fuse. Perhaps you can distract the assessment person with a Bugs Bunny 
or Daffy Duck cartoon on your pad/laptop.

Brian

-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas sdoug...@ieee.org
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com


[PSES] NEC vs CEC for Transformer Protection

2015-03-28 Thread Richard Nute


Hi Brian:


I can't help you with the CEC.

Both the NEC and CEC are quite wrong to specify
overcurrent protection as a function of rated
input current.  

Overcurrent protection is protection for fault
condition current, which is not a function of
rated input current.  The fuse value is always
greater than the input current rating, but how
much greater?

Overcurrent of a mains-frequency transformer is
caused by three major faults:
1)  Shorted turns of the primary winding;
2)  Shorted turns of the secondary winding;
3)  Overload of the secondary winding.

Each of these faults results in heating of the
transformer insulation.  

Shorted turns are usually mechanically-caused or
thermally-caused. 

Thermally-caused insulation failure can be
controlled by a fuse in the primary.  Load the
secondary and measure the insulation temperature.
When the temperature reaches the transformer
insulation temperature rating, note the input
current.   Select a fuse value that is about the
same as the overload input current.  This will
protect the transformer.  

I've attached a paper that first appeared in the
Product Safety Newsletter, Volume 3, Number 3,
May-June 1990 entitled Selecting the fuse value.
The PSN is available to IEEE members at 

 
https://ewh.ieee.org/soc/pses/Downloads/newsletter
s/90v03n3.pdf


Good luck,
Rich



From: Kunde, Brian [mailto:brian_ku...@lecotc.com]

Sent: Friday, March 27, 2015 1:27 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
mailto:EMC-PSTC@LISTSERV.IEEE.ORG 
Subject: [PSES] NEC vs CEC for Transformer
Protection

Please help.
 
We have a product, laboratory equipment, that has
a 330 watt 1:1 230Vac isolation transformer.  330w
/ 230V = 1.34 amps.
 
To protect this transformer we applied the US-NEC
table 450.3(B) to where the primary protector can
be up to 300% of the of 1.34 amps. The transformer
manufacturer recommended a 2.25A time lag circuit
breaker to handle the inrush current from this
transformer. Life is good.
 
Then, we had this product inspected in Canada to
which they apply the Canadian Electric Code
section 26-256, Overcurrent protection for
dry=type transformer circuits rated 750V or less,
which states the primary overcurrent protection
device cannot exceed 125% of the transformer
current rating. That's 134 amps * 1.25 (125%) =
1.78 amps. Rounded up, the inspector said we had
to use a fuse or breaker no larger than 1.8 amps.
 
We notified the transformer manufacturer who said
(and we confirmed) that 1.8 amp protection device
will nuisance trip due to Inrush Currents. 
 
The transformer CSA inspector and a representative
from Littelfuse both are telling us that the
inspector applied the wrong section of the
Electric Code and that section 26-254,
Overcurrent protection for power and distribution
transformer circuits rated 750 V or less, other
than dry-type transformers should be applied.
This section of the CEC does alien better with the
US-NEC. 
 
However, what is a dry-type transformer??  From
my understanding, our transformer is not an oil or
dielectric cooled transformer and it should be
considered a Dry-Type transformer which would
make the inspector correct in applying section
26-256.
 
Am I missing something here?  It makes sense that
the NEC and CEC should track closely in this
regard but it appears as Canada's requirement for
dry-type transformers trump these low current
transformers that would be impossible to properly
protect according to their code.
 
Thanks to all for any information or advice.
 
The Other Brian
 
 


-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas sdoug...@ieee.org
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com


Re: [PSES] NEC vs CEC for Transformer Protection

2015-03-28 Thread Gary Tornquist
Hi Rich,
You mention the failure modes of a mains frequency transformer.  I'd expect the 
same applies to switch mode high frequency transformer, or is there something 
else to consider?

A good article! - I just skimmed it :).
Cheers,
Gary Tornquist
Microsoft

From: Richard Nute [mailto:ri...@ieee.org]
Sent: Saturday, March 28, 2015 9:58 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: [PSES] NEC vs CEC for Transformer Protection


Hi Brian:


I can't help you with the CEC.

Both the NEC and CEC are quite wrong to specify overcurrent protection as a 
function of rated input current.

Overcurrent protection is protection for fault condition current, which is not 
a function of rated input current.  The fuse value is always greater than the 
input current rating, but how much greater?

Overcurrent of a mains-frequency transformer is caused by three major faults:

1)  Shorted turns of the primary winding;

2)  Shorted turns of the secondary winding;

3)  Overload of the secondary winding.

Each of these faults results in heating of the transformer insulation.

Shorted turns are usually mechanically-caused or thermally-caused.

Thermally-caused insulation failure can be controlled by a fuse in the primary. 
 Load the secondary and measure the insulation temperature.  When the 
temperature reaches the transformer insulation temperature rating, note the 
input current.   Select a fuse value that is about the same as the overload 
input current.  This will protect the transformer.

I've attached a paper that first appeared in the Product Safety Newsletter, 
Volume 3, Number 3, May-June 1990 entitled Selecting the fuse value.  The PSN 
is available to IEEE members at

https://ewh.ieee.org/soc/pses/Downloads/newsletters/90v03n3.pdf


Good luck,

Rich


From: Kunde, Brian [mailto:brian_ku...@lecotc.com]
Sent: Friday, March 27, 2015 1:27 PM
To: EMC-PSTC@LISTSERV.IEEE.ORGmailto:EMC-PSTC@LISTSERV.IEEE.ORG
Subject: [PSES] NEC vs CEC for Transformer Protection

Please help.



We have a product, laboratory equipment, that has a 330 watt 1:1 230Vac 
isolation transformer.  330w / 230V = 1.34 amps.



To protect this transformer we applied the US-NEC table 450.3(B) to where the 
primary protector can be up to 300% of the of 1.34 amps. The transformer 
manufacturer recommended a 2.25A time lag circuit breaker to handle the inrush 
current from this transformer. Life is good.



Then, we had this product inspected in Canada to which they apply the Canadian 
Electric Code section 26-256, Overcurrent protection for dry=type transformer 
circuits rated 750V or less, which states the primary overcurrent protection 
device cannot exceed 125% of the transformer current rating. That's 134 amps * 
1.25 (125%) = 1.78 amps. Rounded up, the inspector said we had to use a fuse or 
breaker no larger than 1.8 amps.



We notified the transformer manufacturer who said (and we confirmed) that 1.8 
amp protection device will nuisance trip due to Inrush Currents.



The transformer CSA inspector and a representative from Littelfuse both are 
telling us that the inspector applied the wrong section of the Electric Code 
and that section 26-254, Overcurrent protection for power and distribution 
transformer circuits rated 750 V or less, other than dry-type transformers 
should be applied.  This section of the CEC does alien better with the US-NEC.



However, what is a dry-type transformer??  From my understanding, our 
transformer is not an oil or dielectric cooled transformer and it should be 
considered a Dry-Type transformer which would make the inspector correct in 
applying section 26-256.



Am I missing something here?  It makes sense that the NEC and CEC should track 
closely in this regard but it appears as Canada's requirement for dry-type 
transformers trump these low current transformers that would be impossible to 
properly protect according to their code.



Thanks to all for any information or advice.



The Other Brian




-


This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
emc-p...@ieee.orgmailto:emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)http://www.ieee-pses.org/list.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas sdoug...@ieee.orgmailto:sdoug...@ieee.org
Mike Cantwell mcantw...@ieee.orgmailto:mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher j.bac...@ieee.orgmailto:j.bac...@ieee.org
David Heald

Re: [PSES] NEC vs CEC for Transformer Protection

2015-03-28 Thread John Woodgate
In message 000201d06978$5f687e60$1e397b20$@ieee.org, dated Sat, 28 Mar 
2015, Richard Nute ri...@ieee.org writes:


Thermally-caused insulation failure can be controlled by a fuse in the 
primary.  Load the secondary and measure the insulation temperature. 


I think you have to reduce the load resistance below the normal value to 
obtain an increased temperature rise.


When the temperature reaches the transformer insulation temperature 
rating, note the input current.   Select a fuse value that is about the 
same as the overload input current.  This will protect the transformer. 


But it might fail due to inrush current. The maximum inrush current is 
determined by the supply voltage and the primary winding resistance. 
Normally, you need to look at the I-squared-t curves for fuses or 
breakers and choose the device which will not fail if that current lasts 
for at least a half-cycle of the supply frequency. In some cases, high 
inrush current can last longer than a half-cycle so you may need to 
choose a yet higher rated fuse or breaker, or one with a longer 
pre-arcing time.


The Canadian code seems not to take inrush current into account. 125% 
might be a ball-park figure for the result of Richard's test. Note that 
in the quest for greater efficiency, winding resistances are likely to 
be kept to the minimum possible values, leading to high maximum inrush 
currents.

--
OOO - Own Opinions Only. With best wishes. See www.jmwa.demon.co.uk
When I turn my back on the sun, it's to look for a rainbow
John Woodgate, J M Woodgate and Associates, Rayleigh, Essex UK

-

This message is from the IEEE Product Safety Engineering Society emc-pstc discussion 
list. To post a message to the list, send your e-mail to emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas sdoug...@ieee.org
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com


[PSES] NEC vs CEC for Transformer Protection

2015-03-27 Thread Kunde, Brian
Please help.

We have a product, laboratory equipment, that has a 330 watt 1:1 230Vac 
isolation transformer.  330w / 230V = 1.34 amps.

To protect this transformer we applied the US-NEC table 450.3(B) to where the 
primary protector can be up to 300% of the of 1.34 amps. The transformer 
manufacturer recommended a 2.25A time lag circuit breaker to handle the inrush 
current from this transformer. Life is good.

Then, we had this product inspected in Canada to which they apply the Canadian 
Electric Code section 26-256, Overcurrent protection for dry=type transformer 
circuits rated 750V or less, which states the primary overcurrent protection 
device cannot exceed 125% of the transformer current rating. That's 134 amps * 
1.25 (125%) = 1.78 amps. Rounded up, the inspector said we had to use a fuse or 
breaker no larger than 1.8 amps.

We notified the transformer manufacturer who said (and we confirmed) that 1.8 
amp protection device will nuisance trip due to Inrush Currents.

The transformer CSA inspector and a representative from Littelfuse both are 
telling us that the inspector applied the wrong section of the Electric Code 
and that section 26-254, Overcurrent protection for power and distribution 
transformer circuits rated 750 V or less, other than dry-type transformers 
should be applied.  This section of the CEC does alien better with the US-NEC.

However, what is a dry-type transformer??  From my understanding, our 
transformer is not an oil or dielectric cooled transformer and it should be 
considered a Dry-Type transformer which would make the inspector correct in 
applying section 26-256.

Am I missing something here?  It makes sense that the NEC and CEC should track 
closely in this regard but it appears as Canada's requirement for dry-type 
transformers trump these low current transformers that would be impossible to 
properly protect according to their code.

Thanks to all for any information or advice.

The Other Brian



LECO Corporation Notice: This communication may contain confidential 
information intended for the named recipient(s) only. If you received this by 
mistake, please destroy it and notify us of the error. Thank you.

-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas sdoug...@ieee.org
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com