RE: EFT/Burst Immunity Question

2006-05-17 Thread emc-p...@ieee.org

Hi Wendy: 

You still have a common ground in the test setup - it's the large metal plate
under the system.  See IEC 61000-4-4:1995, Figure 6.  In this diagram they
call it a 'Reference plane'. 

As far as what combinations of lines to test: 
- If the product standard specifies IEC 61000-4-4:1995, you are required to do
L & N separately. 
- If the product standard specifies IEC 61000-4-4:2004, you are required to
test them simultaneously.  See Tom Sato's reply on the issue further done in
this email. 

You are free to test additional combinations of L & N (I know, there aren't
many choices in this case).  If the system fails one of these nonstandard
tests, you (or the customer) can decide whether to treat this as a failure
that requires a solution. 

Pat Lawler
EMC Engineer
Condor DC Power Supplies, Inc.

"wendy"  wrote on 05/16/2006 05:52:04 PM:
> What about 2 Lines supply (L and N only) - since there is no common ground
> do we still test common mode testing - that is L+N?
> Wendy Nya

> -Original Message-
> From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of
> cb...@ntcnet.com
> Sent: Wednesday, May 17, 2006 1:12 AM
> To: pat_law...@condordc.com
> Cc: emc-p...@ieee.org
> Subject: Re: EFT/Burst Immunity Question

> Pat,

> At my previous employer, we had an EFT test system.  I used to test all
> combnations; but I only "counted" the failures that happened during common
> mode testing (at the time it was L1, then L2, then PE...)  Now it's just
> L1,L2,PE simultaneously.

> I can remember a few instances where the product would pass the required
> tests but fail the other coupling methods.

> Chris Maxwell

> 
> > For companies/test labs that perform all possible combinations of EFT
> > coupling: have you had cases where the extra tests did cause the system to
> > fail?  Whether a system fails in the field after extensive testing is a
> > different story, since the field waveform & conditions may be different
> > from the IEC61000-4-4 test.
> >
> > Pat Lawler
> > EMC Engineer
> > Condor DC Power Supplies
> >
> > emc-p...@ieee.org wrote on 05/16/2006 07:06:06 AM:
> >> I believe Brian is correct here.  If you follow the most recent spec
> >> (IEC 61000-4-4:2004) then you only have to perform tests on all lines at
> >> once common mode.  BUT it would behoove each company to test the overall
> >> hardiness of their design on all the possible couplings (differential
> >> and common mode) to uncover any potential design issues.
> >> Regards,
> >> Rodger
> >
> >> -Original Message-
> >> From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of
> >> brian_ku...@leco.com
> >> Sent: Tuesday, May 16, 2006 9:49 AM
> >> To: emc-p...@ieee.org
> >> Subject: Re:RE: EFT/Burst Immunity Question
> >
> >> To perform the test on all combinations doesn't take that much longer.
> >> As a
> >> corporate lab we have continued to test all combinations for the purpose
> >> of
> >> possibly finding a weakness in the design. If our product, by chance,
> >> passed the
> >> common mode test but failed when testing an individual line, we want to
> >> know
> >> about it. It is very likely that such a problem will show up in the
> >> field. Noise
> >> on the Power line is probably our biggest issue in the field. We test
> >> everything
> >> we can in as many modes as we can and we still, on occasion, will have a
> >> customer site where we struggle with some strange noise problem. My
> >> possition on
> >> this is, if you have the equipment, the means, and the time, test it!
> >> Brian
> >>
> >> Reply Separator
> >> Subject:RE: EFT/Burst Immunity Question
> >> Author: vef00...@nifty.ne.jp
> >> Date:   5/16/2006 9:26 AM
> >
> >> On Tue, 16 May 2006 10:27:30 +0300,
> >>  wrote:
> >
> >> > If you follow the latest IEC 61000-4-4 it is only common mode test,
> >> > that is L1,L2,PE.
> >
> >> It is quite clear in IEC 61000-4-4:2004, as the clause 7.3.1.1
> >> of the standard now says:
> >> The test voltage shall be applied ***simultaneously*** between
> >> a ground reference plane and all of the power supply terminals ...
> >> and the corresponding figures also indicate that the disturbance
> >> are to be injected to all lines at once.
> >> However, IEC 61000-4-4:1995 clause 7.3.1 simply says:
> >> The test voltage shall be ap

RE: EFT/Burst Immunity Question

2006-05-16 Thread emc-p...@ieee.org
What about 2 Lines supply (L and N only) - since there is no common ground
do we still test common mode testing - that is L+N?

Wendy Nya


From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of
cb...@ntcnet.com
Sent: Wednesday, May 17, 2006 1:12 AM
To: pat_law...@condordc.com
Cc: emc-p...@ieee.org
Subject: Re: EFT/Burst Immunity Question

Pat,

At my previous employer, we had an EFT test system.  I used to test all
combnations; but I only "counted" the failures that happened during common
mode testing (at the time it was L1, then L2, then PE...)  Now it's just
L1,L2,PE simultaneously.

I can remember a few instances where the product would pass the required
tests but fail the other coupling methods.

Chris Maxwell


> For companies/test labs that perform all possible combinations of EFT
> coupling: have you had cases where the extra tests did cause the system to
> fail?  Whether a system fails in the field after extensive testing is a
> different story, since the field waveform & conditions may be different
> from the IEC61000-4-4 test.
>
> Pat Lawler
> EMC Engineer
> Condor DC Power Supplies
>
> emc-p...@ieee.org wrote on 05/16/2006 07:06:06 AM:
>> I believe Brian is correct here.  If you follow the most recent spec
>> (IEC 61000-4-4:2004) then you only have to perform tests on all lines at
>> once common mode.  BUT it would behoove each company to test the overall
>> hardiness of their design on all the possible couplings (differential
>> and common mode) to uncover any potential design issues.
>> Regards,
>> Rodger
>
>> -Original Message-
>> From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of
>> brian_ku...@leco.com
>> Sent: Tuesday, May 16, 2006 9:49 AM
>> To: emc-p...@ieee.org
>> Subject: Re:RE: EFT/Burst Immunity Question
>
>> To perform the test on all combinations doesn't take that much longer.
>> As a
>> corporate lab we have continued to test all combinations for the purpose
>> of
>> possibly finding a weakness in the design. If our product, by chance,
>> passed the
>> common mode test but failed when testing an individual line, we want to
>> know
>> about it. It is very likely that such a problem will show up in the
>> field. Noise
>> on the Power line is probably our biggest issue in the field. We test
>> everything
>> we can in as many modes as we can and we still, on occasion, will have a
>> customer site where we struggle with some strange noise problem. My
>> possition on
>> this is, if you have the equipment, the means, and the time, test it!
>> Brian
>>
>> Reply Separator
>> Subject:RE: EFT/Burst Immunity Question
>> Author: vef00...@nifty.ne.jp
>> Date:   5/16/2006 9:26 AM
>
>> On Tue, 16 May 2006 10:27:30 +0300,
>>  wrote:
>
>> > If you follow the latest IEC 61000-4-4 it is only common mode test,
> that
>> > is L1,L2,PE.
>
>> It is quite clear in IEC 61000-4-4:2004, as the clause 7.3.1.1
>> of the standard now says:
>> The test voltage shall be applied ***simultaneously*** between
>> a ground reference plane and all of the power supply terminals ...
>> and the corresponding figures also indicate that the disturbance
>> are to be injected to all lines at once.
>> However, IEC 61000-4-4:1995 clause 7.3.1 simply says:
>> The test voltage shall be applied between a ground reference
>> plane and each of the power supply terminals ...
>> and the corresponding figures suggest that the disturbance are
>> to be injected to each of the lines one by one.
>
>> Regards,
>> Tom
>> Tomonori Sato  
>> URL: http://homepage3.nifty.com/tsato/
>
> -
> 
> This message is from the IEEE Product Safety Engineering Society
> emc-pstc discussion list.Website:  http://www.ieee-pses.org/
>
> To post a message to the list, send your e-mail to emc-p...@ieee.org
>
> Instructions:  http://listserv.ieee.org/request/user-guide.html
>
> List rules: http://www.ieee-pses.org/listrules.html
>
> For help, send mail to the list administrators:
>
>  Scott Douglas   emcp...@ptcnh.net
>  Mike Cantwell   mcantw...@ieee.org
>
> For policy questions, send mail to:
>
>  Jim Bacher: j.bac...@ieee.org
>  David Heald:emc-p...@daveheald.com
>
> All emc-pstc postings are archived and searchable on the web at:
>
> http://www.ieeecommunities.org/emc-pstc
>

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.We

Re: EFT/Burst Immunity Question

2006-05-16 Thread emc-p...@ieee.org
Pat,

At my previous employer, we had an EFT test system.  I used to test all
combnations; but I only "counted" the failures that happened during common
mode testing (at the time it was L1, then L2, then PE...)  Now it's just
L1,L2,PE simultaneously.

I can remember a few instances where the product would pass the required
tests but fail the other coupling methods.

Chris Maxwell


> For companies/test labs that perform all possible combinations of EFT
> coupling: have you had cases where the extra tests did cause the system to
> fail?  Whether a system fails in the field after extensive testing is a
> different story, since the field waveform & conditions may be different
> from the IEC61000-4-4 test.
>
> Pat Lawler
> EMC Engineer
> Condor DC Power Supplies
>
> emc-p...@ieee.org wrote on 05/16/2006 07:06:06 AM:
>> I believe Brian is correct here.  If you follow the most recent spec
>> (IEC 61000-4-4:2004) then you only have to perform tests on all lines at
>> once common mode.  BUT it would behoove each company to test the overall
>> hardiness of their design on all the possible couplings (differential
>> and common mode) to uncover any potential design issues.
>> Regards,
>> Rodger
>
>> -Original Message-
>> From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of
>> brian_ku...@leco.com
>> Sent: Tuesday, May 16, 2006 9:49 AM
>> To: emc-p...@ieee.org
>> Subject: Re:RE: EFT/Burst Immunity Question
>
>> To perform the test on all combinations doesn't take that much longer.
>> As a
>> corporate lab we have continued to test all combinations for the purpose
>> of
>> possibly finding a weakness in the design. If our product, by chance,
>> passed the
>> common mode test but failed when testing an individual line, we want to
>> know
>> about it. It is very likely that such a problem will show up in the
>> field. Noise
>> on the Power line is probably our biggest issue in the field. We test
>> everything
>> we can in as many modes as we can and we still, on occasion, will have a
>> customer site where we struggle with some strange noise problem. My
>> possition on
>> this is, if you have the equipment, the means, and the time, test it!
>> Brian
>>
>> Reply Separator
>> Subject:RE: EFT/Burst Immunity Question
>> Author: vef00...@nifty.ne.jp
>> Date:   5/16/2006 9:26 AM
>
>> On Tue, 16 May 2006 10:27:30 +0300,
>>  wrote:
>
>> > If you follow the latest IEC 61000-4-4 it is only common mode test,
> that
>> > is L1,L2,PE.
>
>> It is quite clear in IEC 61000-4-4:2004, as the clause 7.3.1.1
>> of the standard now says:
>> The test voltage shall be applied ***simultaneously*** between
>> a ground reference plane and all of the power supply terminals ...
>> and the corresponding figures also indicate that the disturbance
>> are to be injected to all lines at once.
>> However, IEC 61000-4-4:1995 clause 7.3.1 simply says:
>> The test voltage shall be applied between a ground reference
>> plane and each of the power supply terminals ...
>> and the corresponding figures suggest that the disturbance are
>> to be injected to each of the lines one by one.
>
>> Regards,
>> Tom
>> Tomonori Sato  
>> URL: http://homepage3.nifty.com/tsato/
>
> -
> 
> This message is from the IEEE Product Safety Engineering Society
> emc-pstc discussion list.Website:  http://www.ieee-pses.org/
>
> To post a message to the list, send your e-mail to emc-p...@ieee.org
>
> Instructions:  http://listserv.ieee.org/request/user-guide.html
>
> List rules: http://www.ieee-pses.org/listrules.html
>
> For help, send mail to the list administrators:
>
>  Scott Douglas   emcp...@ptcnh.net
>  Mike Cantwell   mcantw...@ieee.org
>
> For policy questions, send mail to:
>
>  Jim Bacher: j.bac...@ieee.org
>  David Heald:emc-p...@daveheald.com
>
> All emc-pstc postings are archived and searchable on the web at:
>
> http://www.ieeecommunities.org/emc-pstc
>

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to emc-p...@ieee.org

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

 Scott Douglas   emcp...@ptcnh.net
 Mike Cantwell   mcantw...@ieee.org

For policy questions, send mail to:

 Jim Bacher: j.bac...@ieee.org
 David Heald:emc-p...@daveheald.com

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc



Re: EFT/Burst Immunity Question

2006-05-16 Thread emc-p...@ieee.org

For companies/test labs that perform all possible combinations of EFT
coupling: have you had cases where the extra tests did cause the system to
fail?  Whether a system fails in the field after extensive testing is a
different story, since the field waveform & conditions may be different from
the IEC61000-4-4 test. 

Pat Lawler
EMC Engineer
Condor DC Power Supplies 

emc-p...@ieee.org wrote on 05/16/2006 07:06:06 AM:
> I believe Brian is correct here.  If you follow the most recent spec
> (IEC 61000-4-4:2004) then you only have to perform tests on all lines at
> once common mode.  BUT it would behoove each company to test the overall
> hardiness of their design on all the possible couplings (differential
> and common mode) to uncover any potential design issues. 
> Regards,
> Rodger

> -Original Message-
> From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of
> brian_ku...@leco.com
> Sent: Tuesday, May 16, 2006 9:49 AM
> To: emc-p...@ieee.org
> Subject: Re:RE: EFT/Burst Immunity Question

> To perform the test on all combinations doesn't take that much longer.
> As a
> corporate lab we have continued to test all combinations for the purpose
> of
> possibly finding a weakness in the design. If our product, by chance,
> passed the
> common mode test but failed when testing an individual line, we want to
> know
> about it. It is very likely that such a problem will show up in the
> field. Noise
> on the Power line is probably our biggest issue in the field. We test
> everything
> we can in as many modes as we can and we still, on occasion, will have a
> customer site where we struggle with some strange noise problem. My
> possition on
> this is, if you have the equipment, the means, and the time, test it!
> Brian
> 
> Reply Separator
> Subject:RE: EFT/Burst Immunity Question
> Author: vef00...@nifty.ne.jp
> Date:   5/16/2006 9:26 AM

> On Tue, 16 May 2006 10:27:30 +0300,
>  wrote:

> > If you follow the latest IEC 61000-4-4 it is only common mode test, that
> > is L1,L2,PE. 

> It is quite clear in IEC 61000-4-4:2004, as the clause 7.3.1.1
> of the standard now says:
> The test voltage shall be applied ***simultaneously*** between
> a ground reference plane and all of the power supply terminals ...
> and the corresponding figures also indicate that the disturbance
> are to be injected to all lines at once.
> However, IEC 61000-4-4:1995 clause 7.3.1 simply says:
> The test voltage shall be applied between a ground reference
> plane and each of the power supply terminals ...
> and the corresponding figures suggest that the disturbance are
> to be injected to each of the lines one by one.

> Regards,
> Tom
> Tomonori Sato  
> URL: http://homepage3.nifty.com/tsato/ -
 This message
is from the IEEE Product Safety Engineering Society emc-pstc discussion list.
Website: http://www.ieee-pses.org/ 

To post a message to the list, send your e-mail to emc-p...@ieee.org 


Instructions: http://listserv.ieee.org/request/user-guide.html 


List rules: http://www.ieee-pses.org/listrules.html 


For help, send mail to the list administrators: 


Scott Douglas emcp...@ptcnh.net Mike Cantwell mcantw...@ieee.org 


For policy questions, send mail to: 


Jim Bacher: j.bac...@ieee.org David Heald: emc-p...@daveheald.com 


All emc-pstc postings are archived and searchable on the web at: 


http://www.ieeecommunities.org/emc-pstc




RE: RE: EFT/Burst Immunity Question

2006-05-16 Thread emc-p...@ieee.org
I believe Brian is correct here.  If you follow the most recent spec
(IEC 61000-4-4:2004) then you only have to perform tests on all lines at
once common mode.  BUT it would behoove each company to test the overall
hardiness of their design on all the possible couplings (differential
and common mode) to uncover any potential design issues.

Regards,
Rodger


From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of
brian_ku...@leco.com
Sent: Tuesday, May 16, 2006 9:49 AM
To: emc-p...@ieee.org
Subject: Re:RE: EFT/Burst Immunity Question

To perform the test on all combinations doesn't take that much longer.
As a
corporate lab we have continued to test all combinations for the purpose
of
possibly finding a weakness in the design. If our product, by chance,
passed the
common mode test but failed when testing an individual line, we want to
know
about it. It is very likely that such a problem will show up in the
field. Noise
on the Power line is probably our biggest issue in the field. We test
everything
we can in as many modes as we can and we still, on occasion, will have a
customer site where we struggle with some strange noise problem. My
possition on
this is, if you have the equipment, the means, and the time, test it!
Brian


Reply Separator
Subject:    RE: EFT/Burst Immunity Question
Author: vef00...@nifty.ne.jp
List-Post: emc-pstc@listserv.ieee.org
Date:   5/16/2006 9:26 AM

On Tue, 16 May 2006 10:27:30 +0300,
 wrote:

> If you follow the latest IEC 61000-4-4 it is only common mode test,
that
> is L1,L2,PE.

It is quite clear in IEC 61000-4-4:2004, as the clause 7.3.1.1
of the standard now says:

The test voltage shall be applied ***simultaneously*** between
a ground reference plane and all of the power supply terminals ...

and the corresponding figures also indicate that the disturbance
are to be injected to all lines at once.

However, IEC 61000-4-4:1995 clause 7.3.1 simply says:

The test voltage shall be applied between a ground reference
plane and each of the power supply terminals ...

and the corresponding figures suggest that the disturbance are
to be injected to each of the lines one by one.

Regards,
Tom


Tomonori Sato  
URL: http://homepage3.nifty.com/tsato/

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to emc-p...@ieee.org

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

Scott Douglas   emcp...@ptcnh.net
Mike Cantwell   mcantw...@ieee.org

For policy questions, send mail to:

Jim Bacher: j.bac...@ieee.org
David Heald:emc-p...@daveheald.com

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to emc-p...@ieee.org

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

 Scott Douglas   emcp...@ptcnh.net
 Mike Cantwell   mcantw...@ieee.org

For policy questions, send mail to:

 Jim Bacher: j.bac...@ieee.org
 David Heald:emc-p...@daveheald.com

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to emc-p...@ieee.org

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

 Scott Douglas   emcp...@ptcnh.net
 Mike Cantwell   mcantw...@ieee.org

For policy questions, send mail to:

 Jim Bacher: j.bac...@ieee.org
 David Heald:emc-p...@daveheald.com

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc



Re:RE: EFT/Burst Immunity Question

2006-05-16 Thread emc-p...@ieee.org
To perform the test on all combinations doesn't take that much longer. As a
corporate lab we have continued to test all combinations for the purpose of
possibly finding a weakness in the design. If our product, by chance, passed
the
common mode test but failed when testing an individual line, we want to know
about it. It is very likely that such a problem will show up in the field.
Noise
on the Power line is probably our biggest issue in the field. We test
everything
we can in as many modes as we can and we still, on occasion, will have a
customer site where we struggle with some strange noise problem. My possition
on
this is, if you have the equipment, the means, and the time, test it!
Brian


Reply Separator
Subject:    RE: EFT/Burst Immunity Question
Author: vef00...@nifty.ne.jp
List-Post: emc-pstc@listserv.ieee.org
Date:   5/16/2006 9:26 AM

On Tue, 16 May 2006 10:27:30 +0300,
 wrote:

> If you follow the latest IEC 61000-4-4 it is only common mode test, that
> is L1,L2,PE.

It is quite clear in IEC 61000-4-4:2004, as the clause 7.3.1.1
of the standard now says:

The test voltage shall be applied ***simultaneously*** between
a ground reference plane and all of the power supply terminals ...

and the corresponding figures also indicate that the disturbance
are to be injected to all lines at once.

However, IEC 61000-4-4:1995 clause 7.3.1 simply says:

The test voltage shall be applied between a ground reference
plane and each of the power supply terminals ...

and the corresponding figures suggest that the disturbance are
to be injected to each of the lines one by one.

Regards,
Tom


Tomonori Sato  
URL: http://homepage3.nifty.com/tsato/

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to emc-p...@ieee.org

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

Scott Douglas   emcp...@ptcnh.net
Mike Cantwell   mcantw...@ieee.org

For policy questions, send mail to:

Jim Bacher: j.bac...@ieee.org
David Heald:emc-p...@daveheald.com

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to emc-p...@ieee.org

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

 Scott Douglas   emcp...@ptcnh.net
 Mike Cantwell   mcantw...@ieee.org

For policy questions, send mail to:

 Jim Bacher: j.bac...@ieee.org
 David Heald:emc-p...@daveheald.com

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc



RE: EFT/Burst Immunity Question

2006-05-16 Thread emc-p...@ieee.org
On Tue, 16 May 2006 10:27:30 +0300,
   wrote:

> If you follow the latest IEC 61000-4-4 it is only common mode test, that
> is L1,L2,PE.

It is quite clear in IEC 61000-4-4:2004, as the clause 7.3.1.1
of the standard now says:

  The test voltage shall be applied ***simultaneously*** between
  a ground reference plane and all of the power supply terminals ...

and the corresponding figures also indicate that the disturbance
are to be injected to all lines at once.

However, IEC 61000-4-4:1995 clause 7.3.1 simply says:

  The test voltage shall be applied between a ground reference
  plane and each of the power supply terminals ...

and the corresponding figures suggest that the disturbance are
to be injected to each of the lines one by one.

Regards,
Tom


Tomonori Sato  
URL: http://homepage3.nifty.com/tsato/

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to emc-p...@ieee.org

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

 Scott Douglas   emcp...@ptcnh.net
 Mike Cantwell   mcantw...@ieee.org

For policy questions, send mail to:

 Jim Bacher: j.bac...@ieee.org
 David Heald:emc-p...@daveheald.com

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc



RE: EFT/Burst Immunity Question

2006-05-16 Thread emc-p...@ieee.org
If you follow the latest IEC 61000-4-4 it is only common mode test, that is
L1,L2,PE.
 
Regards,
Ari Honkala


  _  

From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of ext
owner-emc-p...@listserv.ieee.org
Sent: 16. toukokuuta 2006 4:02
To: emc-p...@ieee.org
Subject: EFT/Burst Immunity Question


Hello group,
 
I have a question for EFT testing on power lines.  I have a case of two
different labs doing it different ways.  I could not find anything in the
standard to determine which one is right.  Please include a reference to a
part of the standard to back up your answer.
 
1.  EFT on all coupling combinations, this is the way I have always known
people to do it.
L1
L2
L1, L2
L1, PE
L2, PE
L1,L2,PE
PE
 
2.  EFT on the following coupling combinations:
L1
L2
PE
 
Regards,
Tim Pierce
-  This
message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. Website: http://www.ieee-pses.org/ 

To post a message to the list, send your e-mail to emc-p...@ieee.org 


Instructions: http://listserv.ieee.org/request/user-guide.html 


List rules: http://www.ieee-pses.org/listrules.html 


For help, send mail to the list administrators: 


Scott Douglas emcp...@ptcnh.net Mike Cantwell mcantw...@ieee.org 


For policy questions, send mail to: 


Jim Bacher: j.bac...@ieee.org David Heald: emc-p...@daveheald.com 


All emc-pstc postings are archived and searchable on the web at: 


http://www.ieeecommunities.org/emc-pstc 

-  This
message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. Website: http://www.ieee-pses.org/ 

To post a message to the list, send your e-mail to emc-p...@ieee.org 


Instructions: http://listserv.ieee.org/request/user-guide.html 


List rules: http://www.ieee-pses.org/listrules.html 


For help, send mail to the list administrators: 


Scott Douglas emcp...@ptcnh.net Mike Cantwell mcantw...@ieee.org 


For policy questions, send mail to: 


Jim Bacher: j.bac...@ieee.org David Heald: emc-p...@daveheald.com 


All emc-pstc postings are archived and searchable on the web at: 


http://www.ieeecommunities.org/emc-pstc 




Re: EFT/Burst Immunity Question

2006-05-16 Thread emc-p...@ieee.org
In message <37e.2d758a2.319a7...@aol.com>, dated Mon, 15 May 2006, 
emcp...@aol.com writes
>Please include a reference to a part of the standard to back up your 
>answer.

WHICH standard are you using? Number and date or edition number, if 
possible.
-- 
OOO - Own Opinions Only. Try www.jmwa.demon.co.uk and www.isce.org.uk
2006 is YMMVI- Your mileage may vary immensely.

John Woodgate, J M Woodgate and Associates, Rayleigh, Essex UK

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to emc-p...@ieee.org

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

 Scott Douglas   emcp...@ptcnh.net
 Mike Cantwell   mcantw...@ieee.org

For policy questions, send mail to:

 Jim Bacher: j.bac...@ieee.org
 David Heald:emc-p...@daveheald.com

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc



EFT/Burst Immunity Question

2006-05-15 Thread emc-p...@ieee.org
Hello group,
 
I have a question for EFT testing on power lines.  I have a case of two
different labs doing it different ways.  I could not find anything in the
standard to determine which one is right.  Please include a reference to a
part of the standard to back up your answer.
 
1.  EFT on all coupling combinations, this is the way I have always known
people to do it.
L1
L2
L1, L2
L1, PE
L2, PE
L1,L2,PE
PE
 
2.  EFT on the following coupling combinations:
L1
L2
PE
 
Regards,
Tim Pierce
-  This
message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. Website: http://www.ieee-pses.org/ 

To post a message to the list, send your e-mail to emc-p...@ieee.org 


Instructions: http://listserv.ieee.org/request/user-guide.html 


List rules: http://www.ieee-pses.org/listrules.html 


For help, send mail to the list administrators: 


Scott Douglas emcp...@ptcnh.net Mike Cantwell mcantw...@ieee.org 


For policy questions, send mail to: 


Jim Bacher: j.bac...@ieee.org David Heald: emc-p...@daveheald.com 


All emc-pstc postings are archived and searchable on the web at: 


http://www.ieeecommunities.org/emc-pstc 




RE: EFT/Burst

2000-06-12 Thread Mike Hopkins

You are correct for purposes of COMPLIANCE to EN55024 and application of
a CE Mark, you test each line with respect to a reference ground (PE), but
as I'm sure you're aware, a customer can ask for whatever they think is
relevant. 

Mike Hopkins
mhopk...@keytek.com


-Original Message-
From: Roncone Paolo [mailto:paolo.ronc...@compuprint.it]
Sent: Wednesday, June 07, 2000 11:46 AM
To: 'emc-p...@ieee.org'
Subject: EFT/Burst



Group,

we are currently discussing with one OEM the interpretation of EFT/Burst
test requirements per EN55024 and EN61000-4-4 to a printer. 
Specifically we are discussing the requirements of application of bursts to
AC power lines. Our understanding is that they must be applied between each
(single) power supply conductor and reference ground (or protective earth),
as specified in EN61000-4-4 section 7.3.1. Also fig.4 and fig.11 in the same
document seem to confirm this.
Our OEM customer says that all combinations of phase, neutral and protective
earth should be tested. They actually tested both singular AC lines and also
more than one AC line. The printer passed the test in the first mode and
failed in the second mode.

Any comments / interpretations would be highly appreciated.

Paolo Roncone
Compuprint s.p.a.
Italy

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



Re: EFT/Burst

2000-06-08 Thread Georg M. Dancau

Hi Paolo

now we get the truth. It a phenomenon We observe very often:
In your case following happens:
You apply the pulses on common mode to the whole system (printer),
especially to the housing (if any) or to metal parts.
Currents flow back to the EFT generator through the interface lines, in your
case through the network cable.
Thus the worse case should be:
-apply the EFT pulses to ALL THREE lines
-connect the other end of the (shielded) network cable to the
  ground reference plane.
 Thus you will have the highest currents through this line.

Since the coupling capacity in the EFT generator is about 33nF, you will
possibly
observe more severe disturbances then when coupling the pulses into the
network cable using the capacitive coupling clamp (about 200pF).

You did not tell us what kind of network you use.
A: Thin wire (coax, 50Ohm)

If you use thin wire ethernet the shield of the RG58 cable is not connected
to the chassis. If the BNC connector is not capacitively decoupled (e.g.
10nF, very short leads, between cable shield and chassis) it is not worth
testing. I did not see any computer or peripheral of this kind that meets
the requirements.

B: UTP (unshielded twisted pair)
Your EUT might have a chance, depending on the layout of the network PCB

C: STP (shielded twisted pair)
The only solution that really works. Check the RJ45 connector (should have
connections for the shield and should be contacted to the housing of the
EUT).

Good luck

George

**
* Dr. Georg M. Dancau   * HAUNI MASCHINENBAU AG  *
* g.m.dan...@ieee.org   * Manager Technology Research*
* TEL: +49 40 7250 2102 * K.A.Koerber Chaussee 8..32 *
* FAX: +49 40 7250 3801 * 21033 Hamburg, Germany *
**
* home: Tel: +49 4122 99451 * Hauptstr. 60a  *
*   Fax: +49 4122 99454 * 25492 Heist, Germany   *
**
- Original Message -
From: "Paolo Roncone" 
To: 
Sent: Thursday, June 08, 2000 2:08 PM
Subject: Re: EFT/Burst


>
> Thank you for your replies to my first inquiry.
> In particular, George's observation that sec. 7.3.1 applies only to
post-installation tests made me realize that I missed the right point in the
standard, that is sec.7.2.2. I just don't understand why the guys who wrote
the document were not specific in the more important (and used) case of
tests performed in labs (those are mostly the ones used to verify
compliance). So they leave the door open to any possible combination of
phase/neutral/ground when applying the bursts to the AC line.
> One important point that I didn't mention in my previous note was that the
failure is not specifically  related to the printer, but to a LAN/Ethernet
box that is attached. Our OEM got 2 different printers to fail under the
same conditions (bursts with positive polarity @ 1kV applied to Line and
Protective Earth (PE) simultaneously) with the very same box attached. The
printer stops printing and go to a Ready state. You are able to make the
printer Not Ready and back to Ready, but it does not continue to print. the
PC driving the printer says the data timed out sending to the device.
> The same printers don't fail when tested without this LAN box.
> Our feeling is they want to pull us into working on the problem because
the vendor of the LAN box is not so willing or able to help.
>
> Of course any additional hints can be very helpful.
>
>
> Paolo Roncone
>
>
>
> ---
> This message is from the IEEE EMC Society Product Safety
> Technical Committee emc-pstc discussion list.
>
> To cancel your subscription, send mail to:
>  majord...@ieee.org
> with the single line:
>  unsubscribe emc-pstc
>
> For help, send mail to the list administrators:
>  Jim Bacher:  jim_bac...@mail.monarch.com
>  Michael Garretson:pstc_ad...@garretson.org
>
> For policy questions, send mail to:
>  Richard Nute:   ri...@ieee.org
>
>


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



RE: EFT/Burst

2000-06-08 Thread UMBDENSTOCK

Georg,

You were right on the money when you identified the requirement for post
installations.  Similar to the case in many standards, the area of interest
is silent -- nothing is said about the application in 7.2.2.  When I find
this lack of information, I begin my search for guidance in the next best
place.  In this case, it was the instruction given in 7.3.1.  Ultimately, a
CB answers the question.  Our tests include "true common mode" as well as
individual lines.

We have found some problems in burn-in where the power source was dirty
similar to the effects caused by the EFT tests.  We were able to observe the
same type of failures in the lab when common mode EFT signals were applied.
So this test does represent some real world possibilities.

Don Umbdenstock


> --
> From: Georg M. Dancau[SMTP:dan...@compuserve.com]
> Reply To: Georg M. Dancau
> Sent: Thursday, June 08, 2000 3:28 AM
> To:   INTERNET:umbdenst...@sensormatic.com
> Cc:   paolo.ronc...@compuprint.it; emc-p...@ieee.org
> Subject:  RE: EFT/Burst
> 
> 
> Paolo,
> 
> I agree with Don on the interpretation of "each" as opposite to "all"
> lines.
> I also confirm, that we find most faults when testing in common mode:
>-L  AND N against "reference ground"
>-L, N AND PE against "reference ground"
>-(sometimes) PE against "reference ground"
> 
> However, section 7.3.1 applies for tests made "at the installation place"
> (sorry, this is the translation for "PĆ¼rfungen am Aufstellungsort"). For
> test performed
> in a lab, you should apply section 7.2.2. There is no specification
> conerning "each" and
> "all".
> 
> We always perform test including L+N, L+N+PE, PE only.
> 
> Hope this helps.
> 
> Best regards
> 
> George
> 
> 
> Nachricht geschrieben von INTERNET:umbdenst...@sensormatic.com
> > 
> 
> Paolo,
> 
> EN55024 does not directly address the issue, rather it refers you to EN
> 61000-4-4.  Clause 7.3.1 states " . . . applied between a reference ground
> plane and each  of the power supply terminals . . .".  The key is "each"
> instead of "all".  From a purely regulatory perspective, it appears you
> have
> a valid point the way I read the standard.  Other standards do indicate
> "true common mode" as a requirement.  By the way, the "reference ground"
> may
> be at a different potential than "protective earth".  That's why a number
> of
> test sets have a test mode to test EFT between PE and ground reference.
> Check out the bonding and set up requirements carefully.  
> 
> However, a weakness in the design has been detected in "true common mode"
> test mode.  Are you confident that your customer will not be bothered by
> the
> design weakness, whatever those manifestations are?  Of course that is a
> quality issue, not a regulatory issue.
> 
> Good luck,
> 
> Don Umbdenstock
> 
> 
> 
> > --
> > From: Roncone Paolo[SMTP:paolo.ronc...@compuprint.it]
> > Reply To: Roncone Paolo
> > Sent: Wednesday, June 07, 2000 11:45 AM
> > To:   'emc-p...@ieee.org'
> > Subject:  EFT/Burst
> > 
> > 
> > Group,
> > 
> > we are currently discussing with one OEM the interpretation of EFT/Burst
> > test requirements per EN55024 and EN61000-4-4 to a printer. 
> > Specifically we are discussing the requirements of application of bursts
> > to
> > AC power lines. Our understanding is that they must be applied between
> > each
> > (single) power supply conductor and reference ground (or protective
> > earth),
> > as specified in EN61000-4-4 section 7.3.1. Also fig.4 and fig.11 in the
> > same
> > document seem to confirm this.
> > Our OEM customer says that all combinations of phase, neutral and
> > protective
> > earth should be tested. They actually tested both singular AC lines and
> > also
> > more than one AC line. The printer passed the test in the first mode and
> > failed in the second mode.
> > 
> > Any comments / interpretations would be highly appreciated.
> > 
> > Paolo Roncone
> > Compuprint s.p.a.
> > Italy
> <
> 
> 
> ---
> This message is from the IEEE EMC Society Product Safety
> Technical Committee emc-pstc discussion list.
> 
> To cancel your subscription, send mail to:
>  majord...@ieee.org
> with the single line:
>  unsubscribe emc-pstc
> 
> For help, send mail to the list administrators:
>  Jim Bacher: 

Re: EFT/Burst

2000-06-08 Thread Paolo Roncone

Thank you for your replies to my first inquiry.
In particular, George's observation that sec. 7.3.1 applies only to 
post-installation tests made me realize that I missed the right point in the 
standard, that is sec.7.2.2. I just don't understand why the guys who wrote the 
document were not specific in the more important (and used) case of tests 
performed in labs (those are mostly the ones used to verify compliance). So 
they leave the door open to any possible combination of phase/neutral/ground 
when applying the bursts to the AC line.
One important point that I didn't mention in my previous note was that the 
failure is not specifically  related to the printer, but to a LAN/Ethernet box 
that is attached. Our OEM got 2 different printers to fail under the same 
conditions (bursts with positive polarity @ 1kV applied to Line and Protective 
Earth (PE) simultaneously) with the very same box attached. The printer stops 
printing and go to a Ready state. You are able to make the printer Not Ready 
and back to Ready, but it does not continue to print. the PC driving the 
printer says the data timed out sending to the device.
The same printers don't fail when tested without this LAN box.
Our feeling is they want to pull us into working on the problem because the 
vendor of the LAN box is not so willing or able to help.

Of course any additional hints can be very helpful.
 

Paolo Roncone



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



RE: EFT/Burst

2000-06-08 Thread Georg M. Dancau

Paolo,

I agree with Don on the interpretation of "each" as opposite to "all"
lines.
I also confirm, that we find most faults when testing in common mode:
   -L  AND N against "reference ground"
   -L, N AND PE against "reference ground"
   -(sometimes) PE against "reference ground"

However, section 7.3.1 applies for tests made "at the installation place"
(sorry, this is the translation for "PĆ¼rfungen am Aufstellungsort"). For
test performed
in a lab, you should apply section 7.2.2. There is no specification
conerning "each" and
"all".

We always perform test including L+N, L+N+PE, PE only.

Hope this helps.

Best regards

George


Nachricht geschrieben von INTERNET:umbdenst...@sensormatic.com
> 

Paolo,

EN55024 does not directly address the issue, rather it refers you to EN
61000-4-4.  Clause 7.3.1 states " . . . applied between a reference ground
plane and each  of the power supply terminals . . .".  The key is "each"
instead of "all".  From a purely regulatory perspective, it appears you
have
a valid point the way I read the standard.  Other standards do indicate
"true common mode" as a requirement.  By the way, the "reference ground"
may
be at a different potential than "protective earth".  That's why a number
of
test sets have a test mode to test EFT between PE and ground reference.
Check out the bonding and set up requirements carefully.  

However, a weakness in the design has been detected in "true common mode"
test mode.  Are you confident that your customer will not be bothered by
the
design weakness, whatever those manifestations are?  Of course that is a
quality issue, not a regulatory issue.

Good luck,

Don Umbdenstock



> --
> From:     Roncone Paolo[SMTP:paolo.ronc...@compuprint.it]
> Reply To: Roncone Paolo
> Sent:     Wednesday, June 07, 2000 11:45 AM
> To:   'emc-p...@ieee.org'
> Subject:  EFT/Burst
> 
> 
> Group,
> 
> we are currently discussing with one OEM the interpretation of EFT/Burst
> test requirements per EN55024 and EN61000-4-4 to a printer. 
> Specifically we are discussing the requirements of application of bursts
> to
> AC power lines. Our understanding is that they must be applied between
> each
> (single) power supply conductor and reference ground (or protective
> earth),
> as specified in EN61000-4-4 section 7.3.1. Also fig.4 and fig.11 in the
> same
> document seem to confirm this.
> Our OEM customer says that all combinations of phase, neutral and
> protective
> earth should be tested. They actually tested both singular AC lines and
> also
> more than one AC line. The printer passed the test in the first mode and
> failed in the second mode.
> 
> Any comments / interpretations would be highly appreciated.
> 
> Paolo Roncone
> Compuprint s.p.a.
> Italy
<


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



RE: EFT/Burst

2000-06-08 Thread Gert Gremmen
HELLO PAOLO AND DON +GROUP

I agree with Don about this topic, but want to add
that a printer that fails on true common mode (2 or all 3 wires to REF)
and passes in a single wire configuration is on the edge of
failing. I suggest, whatever the outcome of the discussion with your
customer, to evaluate what happens in a larger batch then one.
Possibly over 50% fails in single wire too, or better the full
batch passes in true common mode. In short, this type of pass/failure
dilemma asks for statistical evaluation, to make sure your decision
is based on proper grounds.
In addition, what happens if in the near furure an ECO changes the brand
of f.a. mains filter, or even worse, the filter manufacturer changes details
without announcing them. Other components may have equal impact

Regards,

Gert Gremmen, (Ing)

ce-test, qualified testing

===
Web presence  http://www.cetest.nl
CE-shop http://www.cetest.nl/ce_shop.htm
/-/ Compliance testing is our core business /-/
===


>>-Original Message-
>>From: owner-emc-p...@ieee.org [mailto:owner-emc-p...@ieee.org]On Behalf
>>Of umbdenst...@sensormatic.com
>>Sent: Wednesday, June 07, 2000 8:44 PM
>>To: emc-p...@ieee.org; paolo.ronc...@compuprint.it
>>Subject: RE: EFT/Burst
>>
>>
>>
>>Paolo,
>>
>>EN55024 does not directly address the issue, rather it refers you to EN
>>61000-4-4.  Clause 7.3.1 states " . . . applied between a reference ground
>>plane and each  of the power supply terminals . . .".  The key is "each"
>>instead of "all".  From a purely regulatory perspective, it
>>appears you have
>>a valid point the way I read the standard.  Other standards do indicate
>>"true common mode" as a requirement.  By the way, the "reference
>>ground" may
>>be at a different potential than "protective earth".  That's why
>>a number of
>>test sets have a test mode to test EFT between PE and ground reference.
>>Check out the bonding and set up requirements carefully.
>>
>>However, a weakness in the design has been detected in "true common mode"
>>test mode.  Are you confident that your customer will not be
>>bothered by the
>>design weakness, whatever those manifestations are?  Of course that is a
>>quality issue, not a regulatory issue.
>>
>>Good luck,
>>
>>Don Umbdenstock
>>
>>
>>
>>> ------
>>> From:   Roncone Paolo[SMTP:paolo.ronc...@compuprint.it]
>>> Reply To:   Roncone Paolo
>>> Sent:   Wednesday, June 07, 2000 11:45 AM
>>> To: 'emc-p...@ieee.org'
>>> Subject:EFT/Burst
>>>
>>>
>>> Group,
>>>
>>> we are currently discussing with one OEM the interpretation of EFT/Burst
>>> test requirements per EN55024 and EN61000-4-4 to a printer.
>>> Specifically we are discussing the requirements of application of bursts
>>> to
>>> AC power lines. Our understanding is that they must be applied between
>>> each
>>> (single) power supply conductor and reference ground (or protective
>>> earth),
>>> as specified in EN61000-4-4 section 7.3.1. Also fig.4 and fig.11 in the
>>> same
>>> document seem to confirm this.
>>> Our OEM customer says that all combinations of phase, neutral and
>>> protective
>>> earth should be tested. They actually tested both singular AC lines and
>>> also
>>> more than one AC line. The printer passed the test in the first mode and
>>> failed in the second mode.
>>>
>>> Any comments / interpretations would be highly appreciated.
>>>
>>> Paolo Roncone
>>> Compuprint s.p.a.
>>> Italy
>>>
>>> ---
>>> This message is from the IEEE EMC Society Product Safety
>>> Technical Committee emc-pstc discussion list.
>>>
>>> To cancel your subscription, send mail to:
>>>  majord...@ieee.org
>>> with the single line:
>>>  unsubscribe emc-pstc
>>>
>>> For help, send mail to the list administrators:
>>>  Jim Bacher:  jim_bac...@mail.monarch.com
>>>  Michael Garretson:pstc_ad...@garretson.org
>>>
>>> For policy questions, send mail to:
>>>  Richard Nute:   ri...@ieee.org
>>>
>>>
>>
>>---
>>This message is from the IEEE EMC Society Product Safety
>>Technical Committee emc-pstc discussion list.
>>
>>To cancel your subscription, send mail to:
>> majord...@ieee.org
>>with the single line:
>> unsubscribe emc-pstc
>>
>>For help, send mail to the list administrators:
>> Jim Bacher:  jim_bac...@mail.monarch.com
>> Michael Garretson:pstc_ad...@garretson.org
>>
>>For policy questions, send mail to:
>> Richard Nute:   ri...@ieee.org
>>
>>
<>

RE: EFT/Burst

2000-06-07 Thread UMBDENSTOCK

Paolo,

EN55024 does not directly address the issue, rather it refers you to EN
61000-4-4.  Clause 7.3.1 states " . . . applied between a reference ground
plane and each  of the power supply terminals . . .".  The key is "each"
instead of "all".  From a purely regulatory perspective, it appears you have
a valid point the way I read the standard.  Other standards do indicate
"true common mode" as a requirement.  By the way, the "reference ground" may
be at a different potential than "protective earth".  That's why a number of
test sets have a test mode to test EFT between PE and ground reference.
Check out the bonding and set up requirements carefully.  

However, a weakness in the design has been detected in "true common mode"
test mode.  Are you confident that your customer will not be bothered by the
design weakness, whatever those manifestations are?  Of course that is a
quality issue, not a regulatory issue.

Good luck,

Don Umbdenstock



> --
> From: Roncone Paolo[SMTP:paolo.ronc...@compuprint.it]
> Reply To: Roncone Paolo
> Sent:     Wednesday, June 07, 2000 11:45 AM
> To:   'emc-p...@ieee.org'
> Subject:  EFT/Burst
> 
> 
> Group,
> 
> we are currently discussing with one OEM the interpretation of EFT/Burst
> test requirements per EN55024 and EN61000-4-4 to a printer. 
> Specifically we are discussing the requirements of application of bursts
> to
> AC power lines. Our understanding is that they must be applied between
> each
> (single) power supply conductor and reference ground (or protective
> earth),
> as specified in EN61000-4-4 section 7.3.1. Also fig.4 and fig.11 in the
> same
> document seem to confirm this.
> Our OEM customer says that all combinations of phase, neutral and
> protective
> earth should be tested. They actually tested both singular AC lines and
> also
> more than one AC line. The printer passed the test in the first mode and
> failed in the second mode.
> 
> Any comments / interpretations would be highly appreciated.
> 
> Paolo Roncone
> Compuprint s.p.a.
> Italy
> 
> ---
> This message is from the IEEE EMC Society Product Safety
> Technical Committee emc-pstc discussion list.
> 
> To cancel your subscription, send mail to:
>  majord...@ieee.org
> with the single line:
>  unsubscribe emc-pstc
> 
> For help, send mail to the list administrators:
>  Jim Bacher:  jim_bac...@mail.monarch.com
>  Michael Garretson:pstc_ad...@garretson.org
> 
> For policy questions, send mail to:
>  Richard Nute:   ri...@ieee.org
> 
> 

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



EFT/Burst

2000-06-07 Thread Roncone Paolo

Group,

we are currently discussing with one OEM the interpretation of EFT/Burst
test requirements per EN55024 and EN61000-4-4 to a printer. 
Specifically we are discussing the requirements of application of bursts to
AC power lines. Our understanding is that they must be applied between each
(single) power supply conductor and reference ground (or protective earth),
as specified in EN61000-4-4 section 7.3.1. Also fig.4 and fig.11 in the same
document seem to confirm this.
Our OEM customer says that all combinations of phase, neutral and protective
earth should be tested. They actually tested both singular AC lines and also
more than one AC line. The printer passed the test in the first mode and
failed in the second mode.

Any comments / interpretations would be highly appreciated.

Paolo Roncone
Compuprint s.p.a.
Italy

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org