A statement in the product's site prep guide to say  Installation by a
locally licensed electrician is required. Electrical installation must
conform to local jurisdiction electrical code.  would be helpful.

By including this statement the local licensed electrician must used the
proper cordset and plug cap as mandated by local code regardless of the
country location.

Regards,   Paul J. Smith
  Teradyne, Boston

the above opinion is my own and not that of my employer.




John Woodgate j...@jmwa.demon.co.uk@majordomo.ieee.org on 01/15/2002
11:05:36 PM

Please respond to John Woodgate j...@jmwa.demon.co.uk

Sent by:  owner-emc-p...@majordomo.ieee.org


To:   emc-p...@majordomo.ieee.org
cc:

Subject:  Re: Mains cords



I read in !emc-pstc that rob.humph...@reuters.com wrote (in T58779cc7bc
c407b706...@reuters.com) about 'Mains cords', on Tue, 15 Jan 2002:
Can anyone tell me if equipment supplied as compliant to IEC60950 and has
an IEC
mains inlet plug
 has to be supplied with its mains cord if it is not supplied to an end
user?

To which country/ies is it to be supplied?
--
Regards, John Woodgate, OOO - Own Opinions Only.
http://www.jmwa.demon.co.uk
After swimming across the Hellespont, I felt like a Hero.

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old
messages are imported into the new server.




---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


RE: Mains cords

2002-01-15 Thread Loop, Robert

Hi Rob,

The quick answer to your question is no.  If you do not supply the
cordset, you must supply a description of the cordset that is suitable
for your equipment.  The description can be in the form of a flyer or a
part of your installation guide and in the language of the country in
which it is sold.

The description should include information on the following:

*   The maximum length (4.5 m/15 feet)
*   The nominal size of the conductors expressed in mm squared
*   The cordage should bear the HAR mark of the approval mark of
the country in which it is sold
*   A description of the attachment plug
*   If the cordset is used as the disconnect device, there should be
a statement about plugging it into an unobstructed wall outlet

Sincerely,
Robert Loop
Engineering Supervisor
Wyle Laboratories 
Product Safety
ph - (256) 837-4411 x313
fax- (256) 721-0144
e-mail: rl...@hnt.wylelabs.com


 --
 From: rob.humph...@reuters.com[SMTP:rob.humph...@reuters.com]
 Reply To: rob.humph...@reuters.com
 Sent: Tuesday, January 15, 2002 11:28 AM
 To:   emc-p...@ieee.org
 Subject:  Mains cords
 
 
 Can anyone tell me if equipment supplied as compliant to IEC60950 and
 has an IEC mains inlet plug
  has to be supplied with its mains cord if it is not supplied to an
 end user?
 
 Thanks for any help
 
 Rob
 
 
 
 
 
 
 -- --
 Visit our Internet site at http://www.reuters.com
 
 Any views expressed in this message are those of  the  individual
 sender,  except  where  the sender specifically states them to be
 the views of Reuters Ltd.
 
 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.
 
 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/
 
 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc
 
 For help, send mail to the list administrators:
  Michael Garretson:pstc_ad...@garretson.org
  Dave Healddavehe...@mediaone.net
 
 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
  Jim Bacher: j.bac...@ieee.org
 
 All emc-pstc postings are archived and searchable on the web at:
 No longer online until our new server is brought online and the
 old messages are imported into the new server.
 

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


RE: Mains Cords in the UK and the fuse rating

2001-12-03 Thread Ehler, Kyle
I agree provided there is no earthing conductor.
I thought the 2 meter cord length happens to meet earth fault requirements
as many cords are 3 conductor and the 60950 standard specifies the ground 
conductor resistance to be less than 0.1 ohms as verified by test.
kyle

-Original Message-
From: Rich Nute [mailto:ri...@sdd.hp.com]
Sent: Friday, November 30, 2001 6:39 PM
To: j...@jmwa.demon.co.uk
Cc: emc-p...@majordomo.ieee.org
Subject: Re: Mains Cords in the UK and the fuse rating


snip

So, the 2-meter length restriction (0.092 ohms) 
appears not to be in consideration of the short-
circuit current.  It appears that a 0.75 sq mm
cord could be 20 meters in length (0.92 ohms) and 
still operate the overcurrent device.


Best regards,
Rich


Re: Mains Cords in the UK and the fuse rating

2001-12-01 Thread John Woodgate

I read in !emc-pstc that Rich Nute ri...@sdd.hp.com wrote (in
200112010039.qaa15...@epgc196.sdd.hp.com) about 'Mains Cords in the UK
and the fuse rating', on Fri, 30 Nov 2001:
So, the 2-meter length restriction (0.092 ohms) 
appears not to be in consideration of the short-
circuit current.  It appears that a 0.75 sq mm
cord could be 20 meters in length (0.92 ohms) and 
still operate the overcurrent device.

The disconnection time in Europe has to be much less than 1 minute.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
After swimming across the Hellespont, I felt like a Hero. 

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


Re: Mains Cords in the UK and the fuse rating

2001-12-01 Thread Rich Nute




Hi John:


   More significantly, its resistance affects the maximum short-circuit
   current that can flow.

This is a valid consideration with regard to safety.

Given a 6-amp maximum, 0.75 sq mm size, and 2 meters
length.

In North America, 2X rated current is the 1-minute 
operating time of a fuse or circuit-breaker.  The
maximum resistance of the power cord (assuming a
short at the load end of the cord) would be:


  120 V
   R  =  ---  =  4 ohms.
   30 A

From the wire tables, 0.75 sq mm wire is about 0.023 
ohm/meter.

For 4 ohms resistance we would need 4/0.023 or 173
meters of wire, or a 2-wire cord of about 85 meters.

In continental Europe, using the same assumptions 
about current and operating time, the maximum 
resistance of the cord would be:


  230 V
   R  =  ---  =  7.1 ohms.
   32 A

The wire length would be 7.1/0.023 or 312 meters,
and the cord length would be 156 meters.

So, the 2-meter length restriction (0.092 ohms) 
appears not to be in consideration of the short-
circuit current.  It appears that a 0.75 sq mm
cord could be 20 meters in length (0.92 ohms) and 
still operate the overcurrent device.


Best regards,
Rich




---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


Re: Mains Cords in the UK and the fuse rating

2001-11-30 Thread John Woodgate

I read in !emc-pstc that Rich Nute ri...@sdd.hp.com wrote (in
200111301943.laa15...@epgc196.sdd.hp.com) about 'Mains Cords in the UK
and the fuse rating', on Fri, 30 Nov 2001:
The length of the cord will affect the voltage at 
the load end of the cord. 

More significantly, its resistance affects the maximum short-circuit
current that can flow.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
After swimming across the Hellespont, I felt like a Hero. 

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


Re: Mains Cords in the UK and the fuse rating

2001-11-30 Thread Rich Nute






   For an IT product there is a restriction in the use of mains cords with a
   cross
   sectional area of 0.75mm2 for units up to 6 amps when the cord is greater
   than
   2m in length (EN60950: 2000 section 3.2.5)

I am curious as to the hazard that is prevented by
this length requirement.

Fundamentally, the power cord comprises a very long
resistor.  The higher the current, the more power is
dissipated in the resistor.  The power is uniformly
distributed throughout the length of the power cord.
The power dissipated in the resistor is converted to
thermal energy (heat).  So, the higher the current,
the higher the temperature of the wire.

The cord insulation has a maximum temperature rating.
Since the temperature of the wire is a function of
the current, the cord current must be limited to a
value that does not cause excessive insulation 
temperature.

In terms of length, since the power is uniformly
distributed, I see no reason to limit the length --
at least insofar as controlling the insulation
temperature.

The length of the cord will affect the voltage at 
the load end of the cord.  The higher the current,
the lower the voltage.  I suppose a supply voltage
being applied to the equipment that is below its 
rated voltage could cause overheating or some low-
voltage induced fault in the equipment.  This would 
imply a non-linear load of some sort, or a motor 
load.

If this is the reason for the length restriction,
I would much prefer the length restriction to be
related to a specific load rather than to all loads.
(Large-diameter cords are difficult to manage.)


Best regards,
Rich



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


RE: Mains Cords in the UK and the fuse rating

2001-11-30 Thread Crabb, John

Almost certainly the answer will be found in BS1363 Part 1, 
Specification for rewirable and non-rewirable 13A fused plugs.
(I assume you are referring to UK plugs, as I don't know of
any other plug with a fuse).

My copy of BS1363 is rather old, but there is a table which shows
a 3A (5A) fuse used with 0.5 sq mm cord, and 13A fuses used with 
0.75, 1.0, 1.25 and 1.5 sq mm cord.

A note states the figure in brackets indicates the fuse rating 
where a non-rewirable plug/cord assembly is used with certain 
types of equipment where the use of a 5A fuse-link is necessary
because of the high instantaneous input current.

So the answer to your question is yes, BS1363 specifies a 13A fuse
for 0.75 sq mm cords. 

Regards,
John Crabb, Development Excellence (Product Safety) , 
NCR  Financial Solutions Group Ltd.,  Kingsway West, Dundee, Scotland. DD2
3XX
E-Mail :john.cr...@scotland.ncr.com
Tel: +44 (0)1382-592289  (direct ). Fax +44 (0)1382-622243.   VoicePlus
6-341-2289.

-Original Message-
From: Chris Allen [mailto:chris_al...@eur.3com.com]
Sent: 29 November 2001 14:14
To: emc-p...@majordomo.ieee.org
Subject: Mains Cords in the UK and the fuse rating

For an IT product there is a restriction in the use of mains cords with a
cross
sectional area of 0.75mm2 for units up to 6 amps when the cord is greater
than
2m in length (EN60950: 2000 section 3.2.5)

Can anyone tell me is there is a requirement (in any standard) specifying a
maximum fuse rating that should be fitted to the plug of such a cord and
what it
is?

Thanks in advance.

Kind regards,
Chris.

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


RE: Mains Cords in the UK and the fuse rating

2001-11-30 Thread WELLMAN,RON (A-PaloAlto,ex1)

I recommend that you get copies of BS 1362 and all parts of BS 1363 from
BSI. You may also want to get a copy of EN 60799. 

Regards,
+=+
|Ronald R. Wellman|Voice : 408-345-8229   |
|Agilent Technologies |FAX   : 408-553-2412   |
|5301 Stevens Creek Blvd.,|E-Mail: ron_well...@agilent.com|
|Mailstop 54L-BB  |WWW   : http://www.agilent.com |
|Santa Clara, California 95052 USA|   |
+=+
| Common sense is the collection of prejudices acquired by age   |
|  eighteen. - Albert Einstein   |
+=+



-Original Message-
From: Chris Allen [mailto:chris_al...@eur.3com.com]
Sent: Thursday, November 29, 2001 6:14 AM
To: emc-p...@majordomo.ieee.org
Subject: Mains Cords in the UK and the fuse rating






For an IT product there is a restriction in the use of mains cords with a
cross
sectional area of 0.75mm2 for units up to 6 amps when the cord is greater
than
2m in length (EN60950: 2000 section 3.2.5)

Can anyone tell me is there is a requirement (in any standard) specifying a
maximum fuse rating that should be fitted to the plug of such a cord and
what it
is?

Thanks in advance.

Kind regards,
Chris.



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old
messages are imported into the new server.

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


Re: Mains Cords in the UK and the fuse rating

2001-11-29 Thread John Woodgate

I read in !emc-pstc that Chris Allen chris_al...@eur.3com.com wrote
(in 80256b13.004f5079...@notesmta.eur.3com.com) about 'Mains Cords in
the UK and the fuse rating', on Thu, 29 Nov 2001:
For an IT product there is a restriction in the use of mains cords with a cross
sectional area of 0.75mm2 for units up to 6 amps when the cord is greater than
2m in length (EN60950: 2000 section 3.2.5)

This, AIUI, is based on requirements in USA and Continental Europe for
the (6 A?) fuse in the consumer unit to operate correctly. A L-E fault
current of at least 9 A must flow.

Can anyone tell me is there is a requirement (in any standard) specifying a
maximum fuse rating that should be fitted to the plug of such a cord and what 
it
is?
BS1363. It was Table 2 in the 1984 edition, but may have moved. In that
edition, a 13 A fuse was allowed, but you should check with the latest
edition.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
After swimming across the Hellespont, I felt like a Hero. 

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.