I watched this interesting thread and noticed that none of you recalled the
susceptibility of the system.

We had severe problems with susceptibility of computers with Ethernet coax
connection. As a matter of fact did not find any computer meeting the
requirements for industrial environment of the 61000-4-4 (burst). They all
failed at levels of a couple of hundred volts. Using capacitor coupled BNCs
helps a bit.

We simply bonded the shield to ground. I have to notice, that all computers
attached to the network were in the same floor of the same building.


Best regards

George

**
* Dr. Georg M. Dancau   * HAUNI MASCHINENBAU AG  *
* g.m.dan...@ieee.org   * Manager Product Development*
* TEL: +49 40 7250 2102 * K.A.Koerber Chaussee 8..32 *
* FAX: +49 40 7250 3801 * 21033 Hamburg, Germany *
**
* home: Tel: +49 4122 99453 * Hauptstr. 60a  *
*   Fax: +49 4122 99454 * 25492 Heist, Germany   *
*  Cellular: +49 175 5805280**
**

From: Ken Javor ken.ja...@emccompliance.com
To: Stone, Richard A (Richard) rsto...@lucent.com; 'Knighten, Jim L'
jk100...@teradata-ncr.com; emc-p...@majordomo.ieee.org
Sent: Wednesday, March 05, 2003 11:10 PM
Subject: Re: Ethernet coax connection



 Thanks to all who answered in MINUTES assisting an EMI troubleshoot on
 something that is of great national value.

 This forum is a tremendous resource!




 on 3/5/03 4:46 PM, Stone, Richard A (Richard) at rsto...@lucent.com wrote:

  we've had good success with the
  built capacitance of 9000pf as well,
  depending on test being discussed and
  frequency, certain cap. values from the shielded
  ring of the UNgrounded ring to earth works well
  for low freq.. 30 mhz.
  Richard,
  -Original Message-
  From: Knighten, Jim L [mailto:jk100...@teradata-ncr.com]
  Sent: Wednesday, March 05, 2003 4:12 PM
  To: Ken Javor; emc-p...@majordomo.ieee.org
  Subject: RE: Ethernet coax connection
 
 
 
  Ken,
 
  It is a potential shock hazard if the coax run is long and runs from
  building to building (for instance) where the ground potentials may be
  different in the different buildings.  One can develop a large potential
on
  the shield of the cable, so that if you put yourself between the cable
  shield and ground you may get a strong shock.  That is the reason for
  isolating the shield from more than one direct connection to ground.  It
is
  a real issue.  The result for EMI is, as you have noted, the creation of
an
  egregious EMI offender.  I have used the chassis mounted BNC connectors
with
  built-in capacitors successfully.
 
  Jim
 
 
  Jim Knighten, Ph.D.
  Teradata, a Division of NCR  http://www.ncr.com
  17095 Via Del Campo
  San Diego, CA 92127
  USA
  Tel: 858-485-2537
  Fax: 858-485-3788
  jim.knigh...@ncr.com
 
  -Original Message-
  From:  Ken Javor [mailto:ken.ja...@emccompliance.com]
  Sent: Wednesday, March 05, 2003 12:58 PM
  To: Knighten, Jim L; emc-p...@majordomo.ieee.org
  Subject: Re: Ethernet coax connection
 
  Assume complete ignorance on my part.  What is the safety concern?
 
 
  on 3/5/03 3:50 PM, Knighten, Jim L at jk100...@teradata-ncr.com wrote:
 
  Ken,
 
  Safety considerations are the reason for the spec requirement.  You are
  allowed to ground the shield at one point.
 
  Try using a BNC coax connector with a built-in capacitor to ground.
That
  gives you an AC connection to ground and is often quite effective.
These
  are off-the-shelf parts.
 
  Jim
 
 
  Jim Knighten, Ph.D.
  Teradata, a Division of NCR  http://www.ncr.com
  17095 Via Del Campo
  San Diego, CA 92127
  USA
  Tel: 858-485-2537
  Fax: 858-485-3788
  jim.knigh...@ncr.com
 
  -Original Message-
  From:  Ken Javor [mailto:ken.ja...@emccompliance.com]
  Sent: Wednesday, March 05, 2003 12:38 PM
  To: emc-p...@majordomo.ieee.org
  Subject: Ethernet coax connection
 
 
  Question for list members:
 
  Background:  I am troubleshooting a complex integration of military
  hardware
  and COTS.  One COTS piece of equipment has an RG-58 coaxial connection,
  but
  the coax connector is an isolated feedthrough bnc.  From a radiated
  emissions point-of-view, that is hurting us.  One of the engineers here
  said
  that is part of the spec - Ethernet shields are not supposed to be
chassis
  grounded.
 
  Question:  Can someone please explain the reason for that, and how this
is
  usually handled to minimize radiated emissions?
 
  Thank you.
 
  Ken Javor
  EMC Compliance
  Huntsville, Alabama
  256/650-5261
 
 
 
  ---
  This message is from the IEEE EMC Society Product Safety
  Technical Committee emc-pstc discussion list.
 
  Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/
 
  To cancel your

RE: Ethernet coax connection

2003-03-10 Thread Knighten, Jim L

George,

The physics of this is quite understandable.  If you have a piece of
electronic gear that emits radiation, it will also receive radiation with
similar efficiency.  If you provide the AC short to chassis ground that the
BNC capacitor provides, then not only is internal radiation shunted to
chassis and prevented from getting outside the chassis, but external
radiation is also shunted to chassis which makes it more difficult for it to
penetrate into the sensitive internal regions of the electronic system.  

Bonding all the shields to ground is an eminently practical solution, but
you produce a custom system, as another poster noted, rather than a
10Base2 system.

Jim 


Jim Knighten, Ph.D.
Teradata, a Division of NCR http://www.ncr.com
17095 Via Del Campo
San Diego, CA 92127
USA
Tel: 858-485-2537
Fax: 858-485-3788
jim.knigh...@ncr.com

 -Original Message-
From:   Georg M. Dancau [mailto:g.m.dan...@dancau.de] 
Sent:   Sunday, March 09, 2003 1:16 PM
To: Ken Javor; emc-p...@majordomo.ieee.org
Subject:Re: Ethernet coax connection


Hi Group,

I watched this interesting thread and noticed that none of you recalled the
susceptibility of the system.

We had severe problems with susceptibility of computers with Ethernet coax
connection. As a matter of fact did not find any computer meeting the
requirements for industrial environment of the 61000-4-4 (burst). They all
failed at levels of a couple of hundred volts. Using capacitor coupled BNCs
helps a bit.

We simply bonded the shield to ground. I have to notice, that all computers
attached to the network were in the same floor of the same building.


Best regards

George

**
* Dr. Georg M. Dancau   * HAUNI MASCHINENBAU AG  *
* g.m.dan...@ieee.org   * Manager Product Development*
* TEL: +49 40 7250 2102 * K.A.Koerber Chaussee 8..32 *
* FAX: +49 40 7250 3801 * 21033 Hamburg, Germany *
**
* home: Tel: +49 4122 99453 * Hauptstr. 60a  *
*   Fax: +49 4122 99454 * 25492 Heist, Germany   *
*  Cellular: +49 175 5805280**
**

From: Ken Javor ken.ja...@emccompliance.com
To: Stone, Richard A (Richard) rsto...@lucent.com; 'Knighten, Jim L'
jk100...@teradata-ncr.com; emc-p...@majordomo.ieee.org
Sent: Wednesday, March 05, 2003 11:10 PM
Subject: Re: Ethernet coax connection



 Thanks to all who answered in MINUTES assisting an EMI troubleshoot on
 something that is of great national value.

 This forum is a tremendous resource!




 on 3/5/03 4:46 PM, Stone, Richard A (Richard) at rsto...@lucent.com wrote:

  we've had good success with the
  built capacitance of 9000pf as well,
  depending on test being discussed and
  frequency, certain cap. values from the shielded
  ring of the UNgrounded ring to earth works well
  for low freq.. 30 mhz.
  Richard,
  -Original Message-
  From: Knighten, Jim L [mailto:jk100...@teradata-ncr.com]
  Sent: Wednesday, March 05, 2003 4:12 PM
  To: Ken Javor; emc-p...@majordomo.ieee.org
  Subject: RE: Ethernet coax connection
 
 
 
  Ken,
 
  It is a potential shock hazard if the coax run is long and runs from
  building to building (for instance) where the ground potentials may be
  different in the different buildings.  One can develop a large potential
on
  the shield of the cable, so that if you put yourself between the cable
  shield and ground you may get a strong shock.  That is the reason for
  isolating the shield from more than one direct connection to ground.  It
is
  a real issue.  The result for EMI is, as you have noted, the creation of
an
  egregious EMI offender.  I have used the chassis mounted BNC connectors
with
  built-in capacitors successfully.
 
  Jim
 
 
  Jim Knighten, Ph.D.
  Teradata, a Division of NCR  http://www.ncr.com
  17095 Via Del Campo
  San Diego, CA 92127
  USA
  Tel: 858-485-2537
  Fax: 858-485-3788
  jim.knigh...@ncr.com
 
  -Original Message-
  From:  Ken Javor [mailto:ken.ja...@emccompliance.com]
  Sent: Wednesday, March 05, 2003 12:58 PM
  To: Knighten, Jim L; emc-p...@majordomo.ieee.org
  Subject: Re: Ethernet coax connection
 
  Assume complete ignorance on my part.  What is the safety concern?
 
 
  on 3/5/03 3:50 PM, Knighten, Jim L at jk100...@teradata-ncr.com wrote:
 
  Ken,
 
  Safety considerations are the reason for the spec requirement.  You are
  allowed to ground the shield at one point.
 
  Try using a BNC coax connector with a built-in capacitor to ground.
That
  gives you an AC connection to ground and is often quite effective.
These
  are off-the-shelf parts.
 
  Jim
 
 
  Jim Knighten, Ph.D.
  Teradata, a Division of NCR  http://www.ncr.com
  17095 Via Del Campo
  San Diego, CA 92127
  USA
  Tel: 858-485-2537
  Fax: 858-485-3788
  jim.knigh...@ncr.com

RE: Ethernet coax connection

2003-03-06 Thread neve...@attbi.com

The one-point connection od the 10 Base- coax shield is specified by IEEE 
standard 802.3. In my (2000) revision, it is e.g. in paragraph 8.7.2.2., page 
158.

to prevent the building up of voltages that may result in undue hazard to 
connected equipment or to persons.


However, when twisted-pair (differential) interface is used in 10/100/ and
1000 
Mbps Ethernet, the cabling may be unshielded twisted pair (UTP) or shielded 
twisted pair (STP). There isn't such a requirement to connect the shield at 
only one side in that case. E.g. section 41.4.2.2 of the same standard 
describes it, and it says that if the shielded cable is used, then 

the shield may be grounded at both ends according to local regulations
and 
ISO/IEC 11801, 1995, and as long as the ground potential difference between 
both ends of the network segments is less than 1 Vrms.


Neven
 
 Rich,
 
 I think you must be correct.  I do have anecdotal evidence of persons being
 knocked on their butts by grabbing hold of an Ethernet coax in a large
 facility and trying to connect it to a computer.
 
 My experience is in EMC and the 10Base2 Ethernet (coax) is a persistent
 offender.  (Actually, the twisted pair stuff has its own set of EMC
 problems.)
 
 Regards,
 
 Jim
 
 
 Jim Knighten, Ph.D.
 Teradata, a Division of NCR   http://www.ncr.com
 17095 Via Del Campo
 San Diego, CA 92127
 USA
 Tel: 858-485-2537
 Fax: 858-485-3788
 jim.knigh...@ncr.com
 
  -Original Message-
 From: Rich Nute [mailto:ri...@sdd.hp.com] 
 Sent: Wednesday, March 05, 2003 4:31 PM
 To:   Knighten, Jim L
 Cc:   ken.ja...@emccompliance.com; emc-p...@majordomo.ieee.org
 Subject:  Re: Ethernet coax connection
 
 
 
 
 Hi Jim:
 
It is a potential shock hazard if the coax run is long and runs from
building to building (for instance) where the ground potentials may be
different in the different buildings.  One can develop a large potential
 on
the shield of the cable, so that if you put yourself between the cable
shield and ground you may get a strong shock.  That is the reason for
isolating the shield from more than one direct connection to ground.  It
 is
a real issue.  
 
 I don't believe the issue is that of electric shock.  I don't believe the
 current and resistance of the neutral are high enough to develop 30 volts
 (the shock hazard limit).
 Instead, I believe the problem is that, with two connections, the shield is
 in parallel with the neutral.  That means that some of the neutral current
 will pass through the shield, and will likely open a PWB trace somewhere.
 In the process, the PWB trace heating may start a fire.
 I believe the circuit is:
 (You may not be able to read this schematic if your mail reader is not set
 for plain ASCII text.)
 
 
 L  Bldg A
  +-++
  | ||
  | ||
  | |   | |
 (~) 120 V  |   | | load
  | |   | |
  | ||
  |N||
  +-++-+-+
  |utility  |   || Bldg A  |
  |ground   |   || ground  |
  |rod  |   || rod |PE   BNC shield
-   |   |  -   ++
 ---|   |   ---   |
  - |   |-|
|   | |
|   | |
|   | |
|   | L   Bldg B  |
++|
|||
|||
|   | |   |
|   | | load  |
|   | |   |
|||
| N  ||
++-+-+|
 | Bldg B  |  |
 | ground  |  |
 | rod |PE|
   -   ++
 ---  BNC shield
 -
 
 
 You can see from the schematic that the shield is in parallel with both the
 neutral and the earth-ground.  Being in parallel, it will carry some of the
 neutral current, depending on the respective resistances.
 Because of both the neutral and the earth-ground, the voltage should never
 approach 30 volts (1/4 of the mains voltage).  But, there can be a very high
 current in the shield of the BNC cable

RE: Ethernet coax connection

2003-03-06 Thread Grasso, Charles

I seem to recall that -years ago-
IBM had an interface DC voltage spec.
IBM required that BEFORE attaching a
building-to-building interface cable to
an EUT, that a DC voltage measurement be
made between the shield of the cable
and the EUT chassis. If the voltage exceeded
1.5V (I think) the installer was instructed
NOT to attach the cable. 

If this problem has gone away - maybe to better
building codes - the hurrah!. This was not 
always the case.


Best Regards
Charles Grasso
Senior Compliance Engineer
Echostar Communications Corp.
Tel:  303-706-5467
Fax: 303-799-6222
Cell: 303-204-2974
Email: charles.gra...@echostar.com;  
Email Alternate: chasgra...@ieee.org
 



From: Knighten, Jim L [mailto:jk100...@teradata-ncr.com] 
Sent: Thursday, March 06, 2003 10:17 AM
To: john...@itesafety.com
Cc: emc-p...@majordomo.ieee.org
Subject: RE: Ethernet coax connection



I knew that I was headed for trouble when I responded to Ken Javor original
question about EMI frustrations with 10Base2 Ethernet.  I figured the safety
guys would pummel me a little - and I accept the comments.  However, I
couldn't resist since I have experienced the same EMI frustrations.

Nevertheless, good EMI engineers are sometimes faced with an existing design
that uses 10Base2 (legacy, if you will) and has the severe EMI problem that
an experienced EMI engineer could anticipate.  Ignoring it is unacceptable
from a regulatory point of view (in the case of commercial products), or
from other spec and/or contract reasons in the government world.  Many, if
not most of the practical solutions appear to violate either the letter or
the spirit of the Ethernet 10Base2 spec.  This puts the EMI engineer in the
same seemingly untenable spot that Ken Javor appeared to be in yesterday.
I've been there and I empathize.  

Jim


Jim Knighten, Ph.D.
Teradata, a Division of NCR http://www.ncr.com
17095 Via Del Campo
San Diego, CA 92127
USA
Tel: 858-485-2537
Fax: 858-485-3788
jim.knigh...@ncr.com

 -Original Message-
From:   Robert Johnson [mailto:john...@itesafety.com] 
Sent:   Wednesday, March 05, 2003 9:53 PM
To: Knighten, Jim L
Cc: emc-p...@majordomo.ieee.org
Subject:RE: Ethernet coax connection

  File: Robert Johnson.vcf  If you have shock level differences between
the grounds in two different buildings, either an entire building isn't
connected to an earth electrode, or someone is paying a whopping electric
bill to heat up mother earth. I suspect the shock situation you were talking
about was a power cross condition, either to the cable or within equipment.
I hope it was diagnosed and fixed.

The voltage differences between two buildings are generally very low, on the
order of a couple volts, but due to fractional ohm impedances are capable of
very high currents. Building maintenance procedures should routinely be
checking for ground currents since they indicate faults in the power system.

Note that in accordance with IEC 62102, 10base2 is an SELV circuit and
should not be used for exposed plant (between building) wiring. Ethernet
distance specs and application recommendations also go against exposed plant
wiring. Ethernet 10base5 is considered a TNV-1 circuit and suitable for
exposed plant use, is insulated and requires single point grounding. Optical
fiber is a better recent development and the best answer for exposed plant
lines these days.

Note that IEC 62102 provides an extensive list of interconnect circuit types
and what category they fit into with regard to shock level (SELV, TNV,
hazardous, etc). It's an important reference for any engineer designing
interconnect circuits in determining isolation needs.


Bob Johnson
ITE Safety
 


From: owner-emc-p...@majordomo.ieee.org
[mailto:owner-emc-p...@majordomo.ieee.org] On Behalf Of Knighten, Jim L
Sent: Wednesday, March 05, 2003 7:51 PM
To: Rich Nute
Cc: ken.ja...@emccompliance.com; emc-p...@majordomo.ieee.org
Subject: RE: Ethernet coax connection


Rich,

I think you must be correct.  I do have anecdotal evidence of persons being
knocked on their butts by grabbing hold of an Ethernet coax in a large
facility and trying to connect it to a computer.

My experience is in EMC and the 10Base2 Ethernet (coax) is a persistent
offender.  (Actually, the twisted pair stuff has its own set of EMC
problems.)

Regards,

Jim


Jim Knighten, Ph.D.
Teradata, a Division of NCR http://www.ncr.com
17095 Via Del Campo
San Diego, CA 92127
USA
Tel: 858-485-2537
Fax: 858-485-3788
jim.knigh...@ncr.com

 -Original Message-
From:   Rich Nute [mailto:ri...@sdd.hp.com] 
Sent:   Wednesday, March 05, 2003 4:31 PM
To: Knighten, Jim L
Cc: ken.ja...@emccompliance.com; emc-p...@majordomo.ieee.org
Subject:Re: Ethernet coax connection




Hi Jim:

   It is a potential shock hazard if the coax run is long and runs from
   building to building (for instance) where the ground potentials may be
   different in the different buildings.  One can develop a large

RE: Ethernet coax connection

2003-03-06 Thread david_ster...@ademco.com

ANSI/IEEE 802.3 specifies 10Base2 earthing at some point along the cable,
but not at any node.  10Base2 nodes typically are an isolated (DC/DC + level
shifter) 9-volt part of the PBWA with a high resistance connection to
chassis.  

[RF radiation is higher and RF immunity is lower than 10BaseT.  The 'shield'
is a conductor so it radiates if not earthed.]  

To reduce emissions ground the cable at a single point (typical office
installations had punch blocks in the wiring closet); additional points may
introduce ground loops.  Other replies suggest an AC ground...you need to
eliminate odd-order harmonics (typically 5th to 13th).  Also check COTS
10Base2 component specifications:  some were only Class A.

It is difficult dealing with legacy technology.  Choices of COTS 10Base2 are
limited, EMC modifications change it to 'custom.'

David


From: Ken Javor [mailto:ken.ja...@emccompliance.com]
Sent: Wednesday, March 05, 2003 3:38 PM
To: emc-p...@majordomo.ieee.org
Subject: Ethernet coax connection



Question for list members:

Background:  I am troubleshooting a complex integration of military hardware
and COTS.  One COTS piece of equipment has an RG-58 coaxial connection, but
the coax connector is an isolated feedthrough bnc.  From a radiated
emissions point-of-view, that is hurting us.  One of the engineers here said
that is part of the spec - Ethernet shields are not supposed to be chassis
grounded.

Question:  Can someone please explain the reason for that, and how this is
usually handled to minimize radiated emissions?

Thank you.

Ken Javor
EMC Compliance
Huntsville, Alabama
256/650-5261




This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Re: Ethernet coax connection

2003-03-06 Thread Ken Javor

Thanks to all who answered in MINUTES assisting an EMI troubleshoot on
something that is of great national value.

This forum is a tremendous resource!




on 3/5/03 4:46 PM, Stone, Richard A (Richard) at rsto...@lucent.com wrote:

 we've had good success with the
 built capacitance of 9000pf as well,
 depending on test being discussed and
 frequency, certain cap. values from the shielded
 ring of the UNgrounded ring to earth works well
 for low freq.. 30 mhz.
 Richard,
 -Original Message-
 From: Knighten, Jim L [mailto:jk100...@teradata-ncr.com]
 Sent: Wednesday, March 05, 2003 4:12 PM
 To: Ken Javor; emc-p...@majordomo.ieee.org
 Subject: RE: Ethernet coax connection
 
 
 
 Ken,
 
 It is a potential shock hazard if the coax run is long and runs from
 building to building (for instance) where the ground potentials may be
 different in the different buildings.  One can develop a large potential on
 the shield of the cable, so that if you put yourself between the cable
 shield and ground you may get a strong shock.  That is the reason for
 isolating the shield from more than one direct connection to ground.  It is
 a real issue.  The result for EMI is, as you have noted, the creation of an
 egregious EMI offender.  I have used the chassis mounted BNC connectors with
 built-in capacitors successfully.
 
 Jim
 
 
 Jim Knighten, Ph.D.
 Teradata, a Division of NCR  http://www.ncr.com
 17095 Via Del Campo
 San Diego, CA 92127
 USA
 Tel: 858-485-2537
 Fax: 858-485-3788
 jim.knigh...@ncr.com
 
 -Original Message-
 From:  Ken Javor [mailto:ken.ja...@emccompliance.com]
 Sent: Wednesday, March 05, 2003 12:58 PM
 To: Knighten, Jim L; emc-p...@majordomo.ieee.org
 Subject: Re: Ethernet coax connection
 
 Assume complete ignorance on my part.  What is the safety concern?
 
 
 on 3/5/03 3:50 PM, Knighten, Jim L at jk100...@teradata-ncr.com wrote:
 
 Ken,
 
 Safety considerations are the reason for the spec requirement.  You are
 allowed to ground the shield at one point.
 
 Try using a BNC coax connector with a built-in capacitor to ground.  That
 gives you an AC connection to ground and is often quite effective.  These
 are off-the-shelf parts.
 
 Jim
 
 
 Jim Knighten, Ph.D.
 Teradata, a Division of NCR  http://www.ncr.com
 17095 Via Del Campo
 San Diego, CA 92127
 USA
 Tel: 858-485-2537
 Fax: 858-485-3788
 jim.knigh...@ncr.com
 
 -Original Message-
 From:  Ken Javor [mailto:ken.ja...@emccompliance.com]
 Sent: Wednesday, March 05, 2003 12:38 PM
 To: emc-p...@majordomo.ieee.org
 Subject: Ethernet coax connection
 
 
 Question for list members:
 
 Background:  I am troubleshooting a complex integration of military
 hardware
 and COTS.  One COTS piece of equipment has an RG-58 coaxial connection,
 but
 the coax connector is an isolated feedthrough bnc.  From a radiated
 emissions point-of-view, that is hurting us.  One of the engineers here
 said
 that is part of the spec - Ethernet shields are not supposed to be chassis
 grounded.
 
 Question:  Can someone please explain the reason for that, and how this is
 usually handled to minimize radiated emissions?
 
 Thank you.
 
 Ken Javor
 EMC Compliance
 Huntsville, Alabama
 256/650-5261
 
 
 
 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.
 
 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/
 
 To cancel your subscription, send mail to:
 majord...@ieee.org
 with the single line:
 unsubscribe emc-pstc
 
 For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com
 
 For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org
 
 Archive is being moved, we will announce when it is back on-line.
 All emc-pstc postings are archived and searchable on the web at:
 http://www.ieeecommunities.org/emc-pstc
 

-- 

Ken Javor
EMC Compliance
Huntsville, Alabama
256/650-5261




This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: Ethernet coax connection

2003-03-06 Thread Knighten, Jim L

I knew that I was headed for trouble when I responded to Ken Javor original
question about EMI frustrations with 10Base2 Ethernet.  I figured the safety
guys would pummel me a little - and I accept the comments.  However, I
couldn't resist since I have experienced the same EMI frustrations.

Nevertheless, good EMI engineers are sometimes faced with an existing design
that uses 10Base2 (legacy, if you will) and has the severe EMI problem that
an experienced EMI engineer could anticipate.  Ignoring it is unacceptable
from a regulatory point of view (in the case of commercial products), or
from other spec and/or contract reasons in the government world.  Many, if
not most of the practical solutions appear to violate either the letter or
the spirit of the Ethernet 10Base2 spec.  This puts the EMI engineer in the
same seemingly untenable spot that Ken Javor appeared to be in yesterday.
I've been there and I empathize.  

Jim


Jim Knighten, Ph.D.
Teradata, a Division of NCR http://www.ncr.com
17095 Via Del Campo
San Diego, CA 92127
USA
Tel: 858-485-2537
Fax: 858-485-3788
jim.knigh...@ncr.com

 -Original Message-
From:   Robert Johnson [mailto:john...@itesafety.com] 
Sent:   Wednesday, March 05, 2003 9:53 PM
To: Knighten, Jim L
Cc: emc-p...@majordomo.ieee.org
Subject:RE: Ethernet coax connection

  File: Robert Johnson.vcf  If you have shock level differences between
the grounds in two different
buildings, either an entire building isn't connected to an earth electrode,
or someone is paying a whopping electric bill to heat up mother earth. I
suspect the shock situation you were talking about was a power cross
condition, either to the cable or within equipment. I hope it was diagnosed
and fixed.

The voltage differences between two buildings are generally very low, on the
order of a couple volts, but due to fractional ohm impedances are capable of
very high currents. Building maintenance procedures should routinely be
checking for ground currents since they indicate faults in the power system.

Note that in accordance with IEC 62102, 10base2 is an SELV circuit and
should not be used for exposed plant (between building) wiring. Ethernet
distance specs and application recommendations also go against exposed plant
wiring. Ethernet 10base5 is considered a TNV-1 circuit and suitable for
exposed plant use, is insulated and requires single point grounding. Optical
fiber is a better recent development and the best answer for exposed plant
lines these days.

Note that IEC 62102 provides an extensive list of interconnect circuit types
and what category they fit into with regard to shock level (SELV, TNV,
hazardous, etc). It's an important reference for any engineer designing
interconnect circuits in determining isolation needs.


Bob Johnson
ITE Safety
 


From: owner-emc-p...@majordomo.ieee.org
[mailto:owner-emc-p...@majordomo.ieee.org] On Behalf Of Knighten, Jim L
Sent: Wednesday, March 05, 2003 7:51 PM
To: Rich Nute
Cc: ken.ja...@emccompliance.com; emc-p...@majordomo.ieee.org
Subject: RE: Ethernet coax connection


Rich,

I think you must be correct.  I do have anecdotal evidence of persons being
knocked on their butts by grabbing hold of an Ethernet coax in a large
facility and trying to connect it to a computer.

My experience is in EMC and the 10Base2 Ethernet (coax) is a persistent
offender.  (Actually, the twisted pair stuff has its own set of EMC
problems.)

Regards,

Jim


Jim Knighten, Ph.D.
Teradata, a Division of NCR http://www.ncr.com
17095 Via Del Campo
San Diego, CA 92127
USA
Tel: 858-485-2537
Fax: 858-485-3788
jim.knigh...@ncr.com

 -Original Message-
From:   Rich Nute [mailto:ri...@sdd.hp.com] 
Sent:   Wednesday, March 05, 2003 4:31 PM
To: Knighten, Jim L
Cc: ken.ja...@emccompliance.com; emc-p...@majordomo.ieee.org
Subject:Re: Ethernet coax connection




Hi Jim:

   It is a potential shock hazard if the coax run is long and runs from
   building to building (for instance) where the ground potentials may be
   different in the different buildings.  One can develop a large potential
on
   the shield of the cable, so that if you put yourself between the cable
   shield and ground you may get a strong shock.  That is the reason for
   isolating the shield from more than one direct connection to ground.  It
is
   a real issue.  

I don't believe the issue is that of electric shock.  I don't believe the
current and resistance of the neutral are high enough to develop 30 volts
(the shock hazard limit).
Instead, I believe the problem is that, with two connections, the shield is
in parallel with the neutral.  That means that some of the neutral current
will pass through the shield, and will likely open a PWB trace somewhere.
In the process, the PWB trace heating may start a fire.
I believe the circuit is:
(You may not be able to read this schematic if your mail reader is not set
for plain ASCII text.)


L

Re: Ethernet coax connection

2003-03-06 Thread John Woodgate

I read in !emc-pstc that Knighten, Jim L jk100...@teradata-ncr.com
wrote (in 61A60D883863D411A36600D0B785B50C0D8C6EC0@susdayte51.daytonoh.
ncr.com) about 'Ethernet coax connection' on Wed, 5 Mar 2003:
One can develop a large potential on
the shield of the cable, so that if you put yourself between the cable
shield and ground you may get a strong shock. 

If there is enough voltage to give a 'strong shock', there is far more
than enough to pass shield current sufficient to burn the cable up.
Ground potential differences are typically sources with milliohm
internal impedances.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: Ethernet coax connection

2003-03-06 Thread Robert Johnson
This is a multi-part message in MIME format.
If you have shock level differences between the grounds in two different
buildings, either an entire building isn't connected to an earth electrode,
or someone is paying a whopping electric bill to heat up mother earth. I
suspect the shock situation you were talking about was a power cross
condition, either to the cable or within equipment. I hope it was diagnosed
and fixed.

The voltage differences between two buildings are generally very low, on the
order of a couple volts, but due to fractional ohm impedances are capable of
very high currents. Building maintenance procedures should routinely be
checking for ground currents since they indicate faults in the power system.

Note that in accordance with IEC 62102, 10base2 is an SELV circuit and
should not be used for exposed plant (between building) wiring. Ethernet
distance specs and application recommendations also go against exposed plant
wiring. Ethernet 10base5 is considered a TNV-1 circuit and suitable for
exposed plant use, is insulated and requires single point grounding. Optical
fiber is a better recent development and the best answer for exposed plant
lines these days.

Note that IEC 62102 provides an extensive list of interconnect circuit types
and what category they fit into with regard to shock level (SELV, TNV,
hazardous, etc). It's an important reference for any engineer designing
interconnect circuits in determining isolation needs.


Bob Johnson
ITE Safety
 


From: owner-emc-p...@majordomo.ieee.org
[mailto:owner-emc-p...@majordomo.ieee.org] On Behalf Of Knighten, Jim L
Sent: Wednesday, March 05, 2003 7:51 PM
To: Rich Nute
Cc: ken.ja...@emccompliance.com; emc-p...@majordomo.ieee.org
Subject: RE: Ethernet coax connection


Rich,

I think you must be correct.  I do have anecdotal evidence of persons being
knocked on their butts by grabbing hold of an Ethernet coax in a large
facility and trying to connect it to a computer.

My experience is in EMC and the 10Base2 Ethernet (coax) is a persistent
offender.  (Actually, the twisted pair stuff has its own set of EMC
problems.)

Regards,

Jim


Jim Knighten, Ph.D.
Teradata, a Division of NCR http://www.ncr.com
17095 Via Del Campo
San Diego, CA 92127
USA
Tel: 858-485-2537
Fax: 858-485-3788
jim.knigh...@ncr.com

 -Original Message-
From:   Rich Nute [mailto:ri...@sdd.hp.com] 
Sent:   Wednesday, March 05, 2003 4:31 PM
To: Knighten, Jim L
Cc: ken.ja...@emccompliance.com; emc-p...@majordomo.ieee.org
Subject:Re: Ethernet coax connection




Hi Jim:

   It is a potential shock hazard if the coax run is long and runs from
   building to building (for instance) where the ground potentials may be
   different in the different buildings.  One can develop a large potential
on
   the shield of the cable, so that if you put yourself between the cable
   shield and ground you may get a strong shock.  That is the reason for
   isolating the shield from more than one direct connection to ground.  It
is
   a real issue.  

I don't believe the issue is that of electric shock.  I don't believe the
current and resistance of the neutral are high enough to develop 30 volts
(the shock hazard limit).
Instead, I believe the problem is that, with two connections, the shield is
in parallel with the neutral.  That means that some of the neutral current
will pass through the shield, and will likely open a PWB trace somewhere.
In the process, the PWB trace heating may start a fire.
I believe the circuit is:
(You may not be able to read this schematic if your mail reader is not set
for plain ASCII text.)


L  Bldg A
 +-++
 | ||
 | ||
 | |   | |
(~) 120 V  |   | | load
 | |   | |
 | ||
 |N||
 +-++-+-+
 |utility  |   || Bldg A  |
 |ground   |   || ground  |
 |rod  |   || rod |PE   BNC shield
   -   |   |  -   ++
---|   |   ---   |
 - |   |-|
   |   | |
   |   | |
   |   | |
   |   | L   Bldg B  |
   ++|
   |||
   |||
   |   | |   |
   |   | | load

RE: Ethernet coax connection

2003-03-05 Thread Knighten, Jim L

Rich,

I think you must be correct.  I do have anecdotal evidence of persons being
knocked on their butts by grabbing hold of an Ethernet coax in a large
facility and trying to connect it to a computer.

My experience is in EMC and the 10Base2 Ethernet (coax) is a persistent
offender.  (Actually, the twisted pair stuff has its own set of EMC
problems.)

Regards,

Jim


Jim Knighten, Ph.D.
Teradata, a Division of NCR http://www.ncr.com
17095 Via Del Campo
San Diego, CA 92127
USA
Tel: 858-485-2537
Fax: 858-485-3788
jim.knigh...@ncr.com

 -Original Message-
From:   Rich Nute [mailto:ri...@sdd.hp.com] 
Sent:   Wednesday, March 05, 2003 4:31 PM
To: Knighten, Jim L
Cc: ken.ja...@emccompliance.com; emc-p...@majordomo.ieee.org
Subject:Re: Ethernet coax connection




Hi Jim:

   It is a potential shock hazard if the coax run is long and runs from
   building to building (for instance) where the ground potentials may be
   different in the different buildings.  One can develop a large potential
on
   the shield of the cable, so that if you put yourself between the cable
   shield and ground you may get a strong shock.  That is the reason for
   isolating the shield from more than one direct connection to ground.  It
is
   a real issue.  

I don't believe the issue is that of electric shock.  I don't believe the
current and resistance of the neutral are high enough to develop 30 volts
(the shock hazard limit).
Instead, I believe the problem is that, with two connections, the shield is
in parallel with the neutral.  That means that some of the neutral current
will pass through the shield, and will likely open a PWB trace somewhere.
In the process, the PWB trace heating may start a fire.
I believe the circuit is:
(You may not be able to read this schematic if your mail reader is not set
for plain ASCII text.)


L  Bldg A
 +-++
 | ||
 | ||
 | |   | |
(~) 120 V  |   | | load
 | |   | |
 | ||
 |N||
 +-++-+-+
 |utility  |   || Bldg A  |
 |ground   |   || ground  |
 |rod  |   || rod |PE   BNC shield
   -   |   |  -   ++
---|   |   ---   |
 - |   |-|
   |   | |
   |   | |
   |   | |
   |   | L   Bldg B  |
   ++|
   |||
   |||
   |   | |   |
   |   | | load  |
   |   | |   |
   |||
   | N  ||
   ++-+-+|
| Bldg B  |  |
| ground  |  |
| rod |PE|
  -   ++
---  BNC shield
-


You can see from the schematic that the shield is in parallel with both the
neutral and the earth-ground.  Being in parallel, it will carry some of the
neutral current, depending on the respective resistances.
Because of both the neutral and the earth-ground, the voltage should never
approach 30 volts (1/4 of the mains voltage).  But, there can be a very high
current in the shield of the BNC cable.

Best regards,
Rich





This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: Ethernet coax connection

2003-03-05 Thread Knighten, Jim L

Ken,

It depends if compliance with the Ethernet standard is important to you.  If
you connect to anyone else's network where someone else may be dealing with
a coax that is grounded on your end, then it is probably important.  If not,
then it may not matter.  This is a product safety issue.  I have used
10BaseT (10 Megabit twisted pair Ethernet) in which we shield on both ends
within our system.  Whatever goes out to the world is not grounded on either
end.

I am assuming from your messages that this may be a military system, so the
product safety rules may be different than for commercial equipment.

Jim


Jim Knighten, Ph.D.
Teradata, a Division of NCR http://www.ncr.com
17095 Via Del Campo
San Diego, CA 92127
USA
Tel: 858-485-2537
Fax: 858-485-3788
jim.knigh...@ncr.com

 -Original Message-
From:   Ken Javor [mailto:ken.ja...@emccompliance.com] 
Sent:   Wednesday, March 05, 2003 1:09 PM
To: Robert Macy; emc-p...@ieee.org
Subject:Re: Ethernet coax connection


If all the ac equipment is powered by the same local source, and all the ac
powered equipment is case-grounded within the same rack, is it correct to
assume that the safety issue is moot?  That is, can I then use a grounded
bnc connector at both ends?

on 3/5/03 4:02 PM, Robert Macy at m...@california.com wrote:

 It is my understanding there is a spec relating to both the voltage
handling
 capability and the impedance between ethernet coax and earth ground.
 
 At low frequency (must be more than a certain level) it is quite high in
 order to prevent potentially damaging ground loops from forming.  At high
 frequency (must be less than a certain level) to effectively reference the
 shield to chassis potential and make certain that the coax doesn't
radiate.
 
 There are manufacturers that sell coax panel connectors with the proper
 built in capacitor.  I recall $10 each price tag.
 
 I further recall that we used to use 0.001uF 2kV caps.  WELL DRESSED AND
 MOUNTED EXTREMELY PROPERLY.
 
 Vaguely remember that the impedance was to be more than 1Meg at 60Hz and
 less than 50 at 3MHz, but you should check the ethernet spec.
 
 You can tell a lot about the cap's mounting (and quality) by looking at
the
 spectrum of the radiated emissions.  For example, internal clock and the
cap
 is referenced to a noisy spot.  Or, spectrum related to the ethernet
traffic
 and a loop exists around the coax terminations and bypass cap.
 
 - Robert -
 
 Robert A. Macy, PEm...@california.com
 408 286 3985  fx 408 297 9121
 AJM International Electronics Consultants
 101 E San Fernando, Suite 402
 San Jose, CA  95112
 
 
 - Original Message -
 From: Ken Javor ken.ja...@emccompliance.com
 To: emc-p...@majordomo.ieee.org
 Sent: Wednesday, March 05, 2003 12:37 PM
 Subject: Ethernet coax connection
 
 
 
 Question for list members:
 
 Background:  I am troubleshooting a complex integration of military
 hardware
 and COTS.  One COTS piece of equipment has an RG-58 coaxial connection,
 but
 the coax connector is an isolated feedthrough bnc.  From a radiated
 emissions point-of-view, that is hurting us.  One of the engineers here
 said
 that is part of the spec - Ethernet shields are not supposed to be
chassis
 grounded.
 
 Question:  Can someone please explain the reason for that, and how this
is
 usually handled to minimize radiated emissions?
 
 Thank you.
 
 Ken Javor
 EMC Compliance
 Huntsville, Alabama
 256/650-5261
 
 
 

-- 

Ken Javor
EMC Compliance
Huntsville, Alabama
256/650-5261




This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http

RE: Ethernet coax connection

2003-03-05 Thread Stone, Richard A (Richard)

we've had good success with the 
built capacitance of 9000pf as well,
depending on test being discussed and
frequency, certain cap. values from the shielded
ring of the UNgrounded ring to earth works well
for low freq.. 30 mhz.
Richard,

From: Knighten, Jim L [mailto:jk100...@teradata-ncr.com]
Sent: Wednesday, March 05, 2003 4:12 PM
To: Ken Javor; emc-p...@majordomo.ieee.org
Subject: RE: Ethernet coax connection



Ken,

It is a potential shock hazard if the coax run is long and runs from
building to building (for instance) where the ground potentials may be
different in the different buildings.  One can develop a large potential on
the shield of the cable, so that if you put yourself between the cable
shield and ground you may get a strong shock.  That is the reason for
isolating the shield from more than one direct connection to ground.  It is
a real issue.  The result for EMI is, as you have noted, the creation of an
egregious EMI offender.  I have used the chassis mounted BNC connectors with
built-in capacitors successfully.

Jim


Jim Knighten, Ph.D.
Teradata, a Division of NCR http://www.ncr.com
17095 Via Del Campo
San Diego, CA 92127
USA
Tel: 858-485-2537
Fax: 858-485-3788
jim.knigh...@ncr.com

 -Original Message-
From:   Ken Javor [mailto:ken.ja...@emccompliance.com] 
Sent:   Wednesday, March 05, 2003 12:58 PM
To: Knighten, Jim L; emc-p...@majordomo.ieee.org
Subject:Re: Ethernet coax connection

Assume complete ignorance on my part.  What is the safety concern?


on 3/5/03 3:50 PM, Knighten, Jim L at jk100...@teradata-ncr.com wrote:

 Ken,
 
 Safety considerations are the reason for the spec requirement.  You are
 allowed to ground the shield at one point.
 
 Try using a BNC coax connector with a built-in capacitor to ground.  That
 gives you an AC connection to ground and is often quite effective.  These
 are off-the-shelf parts.
 
 Jim
 
 
 Jim Knighten, Ph.D.
 Teradata, a Division of NCR  http://www.ncr.com
 17095 Via Del Campo
 San Diego, CA 92127
 USA
 Tel: 858-485-2537
 Fax: 858-485-3788
 jim.knigh...@ncr.com
 
 -Original Message-
 From:  Ken Javor [mailto:ken.ja...@emccompliance.com]
 Sent: Wednesday, March 05, 2003 12:38 PM
 To: emc-p...@majordomo.ieee.org
 Subject: Ethernet coax connection
 
 
 Question for list members:
 
 Background:  I am troubleshooting a complex integration of military
hardware
 and COTS.  One COTS piece of equipment has an RG-58 coaxial connection,
but
 the coax connector is an isolated feedthrough bnc.  From a radiated
 emissions point-of-view, that is hurting us.  One of the engineers here
said
 that is part of the spec - Ethernet shields are not supposed to be chassis
 grounded.
 
 Question:  Can someone please explain the reason for that, and how this is
 usually handled to minimize radiated emissions?
 
 Thank you.
 
 Ken Javor
 EMC Compliance
 Huntsville, Alabama
 256/650-5261
 
 
 
 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.
 
 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/
 
 To cancel your subscription, send mail to:
 majord...@ieee.org
 with the single line:
 unsubscribe emc-pstc
 
 For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com
 
 For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org
 
 Archive is being moved, we will announce when it is back on-line.
 All emc-pstc postings are archived and searchable on the web at:
 http://www.ieeecommunities.org/emc-pstc
 

-- 

Ken Javor
EMC Compliance
Huntsville, Alabama
256/650-5261



This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute

RE: Ethernet coax connection

2003-03-05 Thread Knighten, Jim L

Ken,

It is a potential shock hazard if the coax run is long and runs from
building to building (for instance) where the ground potentials may be
different in the different buildings.  One can develop a large potential on
the shield of the cable, so that if you put yourself between the cable
shield and ground you may get a strong shock.  That is the reason for
isolating the shield from more than one direct connection to ground.  It is
a real issue.  The result for EMI is, as you have noted, the creation of an
egregious EMI offender.  I have used the chassis mounted BNC connectors with
built-in capacitors successfully.

Jim


Jim Knighten, Ph.D.
Teradata, a Division of NCR http://www.ncr.com
17095 Via Del Campo
San Diego, CA 92127
USA
Tel: 858-485-2537
Fax: 858-485-3788
jim.knigh...@ncr.com

 -Original Message-
From:   Ken Javor [mailto:ken.ja...@emccompliance.com] 
Sent:   Wednesday, March 05, 2003 12:58 PM
To: Knighten, Jim L; emc-p...@majordomo.ieee.org
Subject:Re: Ethernet coax connection

Assume complete ignorance on my part.  What is the safety concern?


on 3/5/03 3:50 PM, Knighten, Jim L at jk100...@teradata-ncr.com wrote:

 Ken,
 
 Safety considerations are the reason for the spec requirement.  You are
 allowed to ground the shield at one point.
 
 Try using a BNC coax connector with a built-in capacitor to ground.  That
 gives you an AC connection to ground and is often quite effective.  These
 are off-the-shelf parts.
 
 Jim
 
 
 Jim Knighten, Ph.D.
 Teradata, a Division of NCR  http://www.ncr.com
 17095 Via Del Campo
 San Diego, CA 92127
 USA
 Tel: 858-485-2537
 Fax: 858-485-3788
 jim.knigh...@ncr.com
 
 -Original Message-
 From:  Ken Javor [mailto:ken.ja...@emccompliance.com]
 Sent: Wednesday, March 05, 2003 12:38 PM
 To: emc-p...@majordomo.ieee.org
 Subject: Ethernet coax connection
 
 
 Question for list members:
 
 Background:  I am troubleshooting a complex integration of military
hardware
 and COTS.  One COTS piece of equipment has an RG-58 coaxial connection,
but
 the coax connector is an isolated feedthrough bnc.  From a radiated
 emissions point-of-view, that is hurting us.  One of the engineers here
said
 that is part of the spec - Ethernet shields are not supposed to be chassis
 grounded.
 
 Question:  Can someone please explain the reason for that, and how this is
 usually handled to minimize radiated emissions?
 
 Thank you.
 
 Ken Javor
 EMC Compliance
 Huntsville, Alabama
 256/650-5261
 
 
 
 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.
 
 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/
 
 To cancel your subscription, send mail to:
 majord...@ieee.org
 with the single line:
 unsubscribe emc-pstc
 
 For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com
 
 For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org
 
 Archive is being moved, we will announce when it is back on-line.
 All emc-pstc postings are archived and searchable on the web at:
 http://www.ieeecommunities.org/emc-pstc
 

-- 

Ken Javor
EMC Compliance
Huntsville, Alabama
256/650-5261



This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Re: Ethernet coax connection

2003-03-05 Thread Ken Javor

Jim,

Thank you!  That took care of my concern.

Ken



on 3/5/03 4:11 PM, Knighten, Jim L at jk100...@teradata-ncr.com wrote:

 Ken,
 
 It is a potential shock hazard if the coax run is long and runs from
 building to building (for instance) where the ground potentials may be
 different in the different buildings.  One can develop a large potential on
 the shield of the cable, so that if you put yourself between the cable
 shield and ground you may get a strong shock.  That is the reason for
 isolating the shield from more than one direct connection to ground.  It is
 a real issue.  The result for EMI is, as you have noted, the creation of an
 egregious EMI offender.  I have used the chassis mounted BNC connectors with
 built-in capacitors successfully.
 
 Jim
 
 
 Jim Knighten, Ph.D.
 Teradata, a Division of NCR  http://www.ncr.com
 17095 Via Del Campo
 San Diego, CA 92127
 USA
 Tel: 858-485-2537
 Fax: 858-485-3788
 jim.knigh...@ncr.com
 
 -Original Message-
 From:  Ken Javor [mailto:ken.ja...@emccompliance.com]
 Sent: Wednesday, March 05, 2003 12:58 PM
 To: Knighten, Jim L; emc-p...@majordomo.ieee.org
 Subject: Re: Ethernet coax connection
 
 Assume complete ignorance on my part.  What is the safety concern?
 
 
 on 3/5/03 3:50 PM, Knighten, Jim L at jk100...@teradata-ncr.com wrote:
 
 Ken,
 
 Safety considerations are the reason for the spec requirement.  You are
 allowed to ground the shield at one point.
 
 Try using a BNC coax connector with a built-in capacitor to ground.  That
 gives you an AC connection to ground and is often quite effective.  These
 are off-the-shelf parts.
 
 Jim
 
 
 Jim Knighten, Ph.D.
 Teradata, a Division of NCR  http://www.ncr.com
 17095 Via Del Campo
 San Diego, CA 92127
 USA
 Tel: 858-485-2537
 Fax: 858-485-3788
 jim.knigh...@ncr.com
 
 -Original Message-
 From:  Ken Javor [mailto:ken.ja...@emccompliance.com]
 Sent: Wednesday, March 05, 2003 12:38 PM
 To: emc-p...@majordomo.ieee.org
 Subject: Ethernet coax connection
 
 
 Question for list members:
 
 Background:  I am troubleshooting a complex integration of military
 hardware
 and COTS.  One COTS piece of equipment has an RG-58 coaxial connection,
 but
 the coax connector is an isolated feedthrough bnc.  From a radiated
 emissions point-of-view, that is hurting us.  One of the engineers here
 said
 that is part of the spec - Ethernet shields are not supposed to be chassis
 grounded.
 
 Question:  Can someone please explain the reason for that, and how this is
 usually handled to minimize radiated emissions?
 
 Thank you.
 
 Ken Javor
 EMC Compliance
 Huntsville, Alabama
 256/650-5261
 
 
 
 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.
 
 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/
 
 To cancel your subscription, send mail to:
 majord...@ieee.org
 with the single line:
 unsubscribe emc-pstc
 
 For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com
 
 For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org
 
 Archive is being moved, we will announce when it is back on-line.
 All emc-pstc postings are archived and searchable on the web at:
 http://www.ieeecommunities.org/emc-pstc
 

-- 

Ken Javor
EMC Compliance
Huntsville, Alabama
256/650-5261




This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Re: Ethernet coax connection

2003-03-05 Thread Ken Javor

If all the ac equipment is powered by the same local source, and all the ac
powered equipment is case-grounded within the same rack, is it correct to
assume that the safety issue is moot?  That is, can I then use a grounded
bnc connector at both ends?

on 3/5/03 4:02 PM, Robert Macy at m...@california.com wrote:

 It is my understanding there is a spec relating to both the voltage handling
 capability and the impedance between ethernet coax and earth ground.
 
 At low frequency (must be more than a certain level) it is quite high in
 order to prevent potentially damaging ground loops from forming.  At high
 frequency (must be less than a certain level) to effectively reference the
 shield to chassis potential and make certain that the coax doesn't radiate.
 
 There are manufacturers that sell coax panel connectors with the proper
 built in capacitor.  I recall $10 each price tag.
 
 I further recall that we used to use 0.001uF 2kV caps.  WELL DRESSED AND
 MOUNTED EXTREMELY PROPERLY.
 
 Vaguely remember that the impedance was to be more than 1Meg at 60Hz and
 less than 50 at 3MHz, but you should check the ethernet spec.
 
 You can tell a lot about the cap's mounting (and quality) by looking at the
 spectrum of the radiated emissions.  For example, internal clock and the cap
 is referenced to a noisy spot.  Or, spectrum related to the ethernet traffic
 and a loop exists around the coax terminations and bypass cap.
 
 - Robert -
 
 Robert A. Macy, PEm...@california.com
 408 286 3985  fx 408 297 9121
 AJM International Electronics Consultants
 101 E San Fernando, Suite 402
 San Jose, CA  95112
 
 
 - Original Message -
 From: Ken Javor ken.ja...@emccompliance.com
 To: emc-p...@majordomo.ieee.org
 Sent: Wednesday, March 05, 2003 12:37 PM
 Subject: Ethernet coax connection
 
 
 
 Question for list members:
 
 Background:  I am troubleshooting a complex integration of military
 hardware
 and COTS.  One COTS piece of equipment has an RG-58 coaxial connection,
 but
 the coax connector is an isolated feedthrough bnc.  From a radiated
 emissions point-of-view, that is hurting us.  One of the engineers here
 said
 that is part of the spec - Ethernet shields are not supposed to be chassis
 grounded.
 
 Question:  Can someone please explain the reason for that, and how this is
 usually handled to minimize radiated emissions?
 
 Thank you.
 
 Ken Javor
 EMC Compliance
 Huntsville, Alabama
 256/650-5261
 
 
 

-- 

Ken Javor
EMC Compliance
Huntsville, Alabama
256/650-5261




This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Re: Ethernet coax connection

2003-03-05 Thread Ken Javor

Assume complete ignorance on my part.  What is the safety concern?


on 3/5/03 3:50 PM, Knighten, Jim L at jk100...@teradata-ncr.com wrote:

 Ken,
 
 Safety considerations are the reason for the spec requirement.  You are
 allowed to ground the shield at one point.
 
 Try using a BNC coax connector with a built-in capacitor to ground.  That
 gives you an AC connection to ground and is often quite effective.  These
 are off-the-shelf parts.
 
 Jim
 
 
 Jim Knighten, Ph.D.
 Teradata, a Division of NCR  http://www.ncr.com
 17095 Via Del Campo
 San Diego, CA 92127
 USA
 Tel: 858-485-2537
 Fax: 858-485-3788
 jim.knigh...@ncr.com
 
 -Original Message-
 From:  Ken Javor [mailto:ken.ja...@emccompliance.com]
 Sent: Wednesday, March 05, 2003 12:38 PM
 To: emc-p...@majordomo.ieee.org
 Subject: Ethernet coax connection
 
 
 Question for list members:
 
 Background:  I am troubleshooting a complex integration of military hardware
 and COTS.  One COTS piece of equipment has an RG-58 coaxial connection, but
 the coax connector is an isolated feedthrough bnc.  From a radiated
 emissions point-of-view, that is hurting us.  One of the engineers here said
 that is part of the spec - Ethernet shields are not supposed to be chassis
 grounded.
 
 Question:  Can someone please explain the reason for that, and how this is
 usually handled to minimize radiated emissions?
 
 Thank you.
 
 Ken Javor
 EMC Compliance
 Huntsville, Alabama
 256/650-5261
 
 
 
 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.
 
 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/
 
 To cancel your subscription, send mail to:
 majord...@ieee.org
 with the single line:
 unsubscribe emc-pstc
 
 For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com
 
 For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org
 
 Archive is being moved, we will announce when it is back on-line.
 All emc-pstc postings are archived and searchable on the web at:
 http://www.ieeecommunities.org/emc-pstc
 

-- 

Ken Javor
EMC Compliance
Huntsville, Alabama
256/650-5261




This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: Ethernet coax connection

2003-03-05 Thread Knighten, Jim L

Ken,

Safety considerations are the reason for the spec requirement.  You are
allowed to ground the shield at one point.

Try using a BNC coax connector with a built-in capacitor to ground.  That
gives you an AC connection to ground and is often quite effective.  These
are off-the-shelf parts.

Jim


Jim Knighten, Ph.D.
Teradata, a Division of NCR http://www.ncr.com
17095 Via Del Campo
San Diego, CA 92127
USA
Tel: 858-485-2537
Fax: 858-485-3788
jim.knigh...@ncr.com

 -Original Message-
From:   Ken Javor [mailto:ken.ja...@emccompliance.com] 
Sent:   Wednesday, March 05, 2003 12:38 PM
To: emc-p...@majordomo.ieee.org
Subject:Ethernet coax connection


Question for list members:

Background:  I am troubleshooting a complex integration of military hardware
and COTS.  One COTS piece of equipment has an RG-58 coaxial connection, but
the coax connector is an isolated feedthrough bnc.  From a radiated
emissions point-of-view, that is hurting us.  One of the engineers here said
that is part of the spec - Ethernet shields are not supposed to be chassis
grounded.

Question:  Can someone please explain the reason for that, and how this is
usually handled to minimize radiated emissions?

Thank you.

Ken Javor
EMC Compliance
Huntsville, Alabama
256/650-5261




This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc