Re: The transformer screen/shield conundrum

2003-07-01 Thread John Woodgate

I read in !emc-pstc that Rich Nute  wrote (in
<200307011612.jaa01...@epgc264.sdd.hp.com>) about 'The transformer
screen/shield conundrum' on Tue, 1 Jul 2003:

>So, you can't really consider North American 240 V
>mains circuits in this discussion.  We don't.
>
>*

I think that's debatable, but probably doesn't need any further debate
at this point.
>
>I do agree that electricity consumption per head in 
>North America is probably greater than in Europe.
>
>Having lived in Spain, I believe that North American 
>appliances are bigger and therefore consume more 
>electricity.  


It depends indirectly on where you lived in Spain. Some rural supplies
are rated at only 6 kVA per household. Naturally, they don't have too
many 3 kW appliances in those households.


[snip]
>
>Neither of these topics has anything to do with the
>current available into a fault before the circuit
>breaker operates.

They are about matters which you raised in your responses, and
indirectly refer to the crucial matter of supply impedance.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Re: The transformer screen/shield conundrum

2003-07-01 Thread Rich Nute




Hi John:


>   >If the breakers are 230 V/16 A and 120 V/15 A, then
>   >the power distributed at 230 V is roughly twice that
>   >at 120 V.
>   
>   But your '120 V' is also '240 V' for some equipment. Besides, I think I
>   was being 'generous'; electrical energy consumption per head in USA is
>   probably greater than in Europe.

In North America, the 240 V is supplied to high-power-
consumption equipment such as water heaters, electric
ovens, electric cook-tops, electric clothes dryers,
electric furnaces, and air conditioners.

The 240-V circuits are rated 20, 30, and 50 amps.

In North America, typical equipment is not rated for
use on 240 V, but 120 V.  While 240 V is supplied to
each home, use of 240 V for applications other than 
those I mentioned, would require a special electrical 
installation.  This is extremely rare.

So, you can't really consider North American 240 V
mains circuits in this discussion.  We don't.

*

I do agree that electricity consumption per head in 
North America is probably greater than in Europe.

Having lived in Spain, I believe that North American 
appliances are bigger and therefore consume more 
electricity.  Also, NA electrical appliances tend to 
be less efficient than Euro appliances.  NA clothes 
and dish washers use much more water than Euro 
versions.

*

Neither of these topics has anything to do with the
current available into a fault before the circuit
breaker operates.


Best regards,
Rich







This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Re: The transformer screen/shield conundrum

2003-07-01 Thread John Woodgate

I read in !emc-pstc that Rich Nute  wrote (in
<200306302129.oaa24...@epgc264.sdd.hp.com>) about 'The transformer
screen/shield conundrum' on Mon, 30 Jun 2003:


>I disagree that the same power is distributed at
>230 V and 120 V.

We have a certain amount of misunderstanding.
>
>If the breakers are 230 V/16 A and 120 V/15 A, then
>the power distributed at 230 V is roughly twice that
>at 120 V.

But your '120 V' is also '240 V' for some equipment. Besides, I think I
was being 'generous'; electrical energy consumption per head in USA is
probably greater than in Europe.
>
>My subject was *not* supply voltage tolerance, but 
>system *design* goal for percent voltage drop at max
>rated load (the circuit-breaker rating).  

OK, that's clear now.
>
>I really believe that EEs in Europe design supply 
>systems to 3% voltage drop at rated current, 16 A,
>just as they do in North America.  The reason I so 
>believe is that the wire sizes for 15 A (NA) or 16 A 
>(Euro) circuits are nearly the same.  The same size 
>wire at (nearly) the same current would give (nearly) 
>the same percent voltage drop.

Yes, well, it's actually 3.3% for the worst case, see the amendment to
IEC/EN 61000-3-3. But 3% normally.
>
>(If the system source impedance is 0.47 ohms, then, at
>230 V, the system voltage drop would be slightly more
>than 6% at maximum rated load.)

Yes, but that 0.47 ohms is the source impedance at the point of common
coupling (PCC), which you weren't addressing, AIUI. Your 3% is the drop
>from the PCC to the wall socket?
>
>We really weren't talking about voltage, but about 
>the maximum current into a fault in cord-connected
>equipment.  The voltage tolerance can be ignored for
>this purpose.

Yes, but the voltage tolerance provides information on the impedance,
which is itself not specified, and the impedance is what determines the
prospective fault current.
>
>>   That still gives 490 A, which would be embarrassingly big, but it apples
>>   at the 'point of common connection', not at the wall socket and still
>>   less at the equipment. 
>
>My comments were for the current available at the
>wall socket.  In North America, building wiring is 
>designed for maximum 3% voltage drop at maximum 
>rated current.

Yes, OK, that works in Europe as well.
>
>In NA, at the point of common connection between the 
>building and the electicity supplier, the electricity 
>supplier maintains a nearly constant voltage.  He 
>does so not only by his system design, but also by 
>dynamically adjusting the voltage of the source.

Two points there:

1. Yes, in Europe the voltage may be 'nearly constant', but it is only
the 'declared voltage' for some customers. Those nearer the substation
transformer get more, and those further away get less, but within legal
limits. Typically, one transformer feeds 200 to 500 residential
customers.

2. It is possible to adjust the LV voltage but only by adjusting the MV
supply to the transformers. On-load tap-changing at LV is extremely
rare. In the Americas, this adjustment is not so easy, because of the
very large number of transformers, some of which are likely at a given
time to be lightly loaded, and some heavily loaded. Most of the source
impedance of the LV network is in the transformer, so those that are
heavily loaded will deliver fewer volts, and if the MV were increased to
compensate, the lightly-loaded transformers would deliver too many
volts. Of course, seasonal load variations tend to affect each
transformer equally, so MV adjustment does work in this case.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Re: The transformer screen/shield conundrum

2003-06-30 Thread Rich Nute




Hi John:


>   >For 3% voltage drop at maximum rated load, the 
>   >source resistance is about 0.2 ohm.  So the 
>   >maximum rms current would be system nominal 
>   >voltage divided by 0.2 ohm, or 600 amps for 120
>   >V and 1150 amps for 230 V.  
>   
>   For 230V, there are two modifications. One is that roughly the same
>   *power* is distributed as at 120 V, so the system impedance would be
>   doubled. But, in addition, the supply voltage tolerances are greater
>   than 3%: in Europe the tolerance is about double, so, overall, the
>   system impedance could be four times that 0.2 ohm. But in fact, 90% of
>   supplies are below 0.47 ohms (see IEC 60725, under amendment).

I disagree that the same power is distributed at
230 V and 120 V.

If the breakers are 230 V/16 A and 120 V/15 A, then
the power distributed at 230 V is roughly twice that
at 120 V.

My subject was *not* supply voltage tolerance, but 
system *design* goal for percent voltage drop at max
rated load (the circuit-breaker rating).  

I really believe that EEs in Europe design supply 
systems to 3% voltage drop at rated current, 16 A,
just as they do in North America.  The reason I so 
believe is that the wire sizes for 15 A (NA) or 16 A 
(Euro) circuits are nearly the same.  The same size 
wire at (nearly) the same current would give (nearly) 
the same percent voltage drop.

(If the system source impedance is 0.47 ohms, then, at
230 V, the system voltage drop would be slightly more
than 6% at maximum rated load.)

We really weren't talking about voltage, but about 
the maximum current into a fault in cord-connected
equipment.  The voltage tolerance can be ignored for
this purpose.

>   That still gives 490 A, which would be embarrassingly big, but it apples
>   at the 'point of common connection', not at the wall socket and still
>   less at the equipment. 

My comments were for the current available at the
wall socket.  In North America, building wiring is 
designed for maximum 3% voltage drop at maximum 
rated current.

In NA, at the point of common connection between the 
building and the electicity supplier, the electricity 
supplier maintains a nearly constant voltage.  He 
does so not only by his system design, but also by 
dynamically adjusting the voltage of the source.


Best regards,
Rich






This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Re: The transformer screen/shield conundrum

2003-06-30 Thread John Woodgate

I read in !emc-pstc that Rich Nute  wrote (in
<200306301811.laa23...@epgc264.sdd.hp.com>) about 'The transformer
screen/shield conundrum' on Mon, 30 Jun 2003:

>For 3% voltage drop at maximum rated load, the 
>source resistance is about 0.2 ohm.  So the 
>maximum rms current would be system nominal 
>voltage divided by 0.2 ohm, or 600 amps for 120
>V and 1150 amps for 230 V.  

For 230V, there are two modifications. One is that roughly the same
*power* is distributed as at 120 V, so the system impedance would be
doubled. But, in addition, the supply voltage tolerances are greater
than 3%: in Europe the tolerance is about double, so, overall, the
system impedance could be four times that 0.2 ohm. But in fact, 90% of
supplies are below 0.47 ohms (see IEC 60725, under amendment).

That still gives 490 A, which would be embarrassingly big, but it apples
at the 'point of common connection', not at the wall socket and still
less at the equipment. 
>
>At these currents, the overcurrent device will
>operate in about 0.01 second maximum, which is 
>less than 1 cycle at either 50 Hz or 60 Hz.  So,
>the current will never rise to the calculated
>currents.

But the overcurrent device must be rated to break the prospective
current. HBC fuses rated at 1500 A are OK, but many EBC fuses are rated
at 150 A, and it is doubtful that they can be used with 230 V mains
supplies.
>
>So, the maximum current is set by the overcurrent
>device characteristics, not by the resistance of
>the supply system.
>
>If we assume a time of 1 cycle (0.02 s), then 
>a typical overcurrent device will trip at a 
>maximum of 20 times the rated current.  So the 
>maximum current for a 15-amp overcurrent device 
>for a duration of 1 cycle will be about 300 amps.
>
>If we add in the resistance of a 2-meter power 
>cord (0.05 ohm per wire) and the maximum 
>resistance of the equipment (0.10 ohm), then the
>maximum fault current is less than 300 amps.
>Indeed, it drops to about 150-200 amps.

Yes, I agree, but still uncomfortably in excess of 150 A. I think we
need supplies of fuses rated at 300 A, not 150 A or 1500 A.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Re: The transformer screen/shield conundrum

2003-06-30 Thread Rich Nute



Hi Richard and John:


>   >[R_Hughes >] I know it as prospective short-circuit current, but maybe I
go
>   >boldly whereas you boldly go?
>   
>   Do we know what the current values are in various countries, for
>   equipment connected to wall-sockets? Assuming that the mains lead has
>   the resistance that can be deduced from the maximum permissible
>   resistance of its PEC.

The short-circuit current value is limited by 
the sum of the resistance of the phase conductor 
and the resistance of the neutral/PE conductor
(assuming all three conductors are the same
size).

The resistance is a function of the physical
distance (length of wire) from the distribution
transformer and the contact resistances of the
various connections and overcurrent devices in
the current path.  

Since the distance from the distribution 
transformer to the load can vary from relatively 
small to quite long, the deduction of the 
maximum permissable resistance of the PE and
other conductors seems indeterminable.

However, according to my USA EE colleagues, the
design of distribution systems is based on no
more than 3% voltage drop (wrt nominal voltage)
at maximum rated load, regardless of distance 
>from the distribution transformer to the load.

If we can assume this to be true throughout the
world, then we can deduce both the mains lead
resistance and the PE conductor resistance.  

See my paper, "Equipotentiality and Grounding, 
Derivation of Grounding Resistance for Equipment,"

http://www.ewh.ieee.org/soc/emcs/pstc/tech-spk.htm

Click on "equipotentiality and grounding."

Page 20 gives the source resistance for mains
systems as a function of system voltage drop and
maximum rated current.

For 3% voltage drop at maximum rated load, the 
source resistance is about 0.2 ohm.  So the 
maximum rms current would be system nominal 
voltage divided by 0.2 ohm, or 600 amps for 120
V and 1150 amps for 230 V.  

At these currents, the overcurrent device will
operate in about 0.01 second maximum, which is 
less than 1 cycle at either 50 Hz or 60 Hz.  So,
the current will never rise to the calculated
currents.

So, the maximum current is set by the overcurrent
device characteristics, not by the resistance of
the supply system.

If we assume a time of 1 cycle (0.02 s), then 
a typical overcurrent device will trip at a 
maximum of 20 times the rated current.  So the 
maximum current for a 15-amp overcurrent device 
for a duration of 1 cycle will be about 300 amps.

If we add in the resistance of a 2-meter power 
cord (0.05 ohm per wire) and the maximum 
resistance of the equipment (0.10 ohm), then the
maximum fault current is less than 300 amps.
Indeed, it drops to about 150-200 amps.


Best regards,
Rich






This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Re: The transformer screen/shield conundrum

2003-06-29 Thread John Woodgate

I read in !emc-pstc that richhug...@aol.com wrote (in <6C87B93E.0C9D7087
.0ba45...@aol.com>) about 'The transformer screen/shield conundrum' on
Sat, 28 Jun 2003:

>[R_Hughes >] I know it as prospective short-circuit current, but maybe I go
>boldly whereas you boldly go?

Do we know what the current values are in various countries, for
equipment connected to wall-sockets? Assuming that the mains lead has
the resistance that can be deduced from the maximum permissible
resistance of its PEC.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



re: The transformer screen/shield conundrum

2003-06-29 Thread richhug...@aol.com

Rich,

RN>  I'm surprised that, today, a SMPS would used screen/
shield construction.  

[R_Hughes >] Not all power supplies are switch mode, even today.  I bet that
the HiFi addicts who say that they can hear the difference between a valve
amp and a transistor amp would absolutely hate the idea of anything other
than a pig-iron transformer (not intended to be a technical description,
John).

RN> I presume you are referring to the circuit prospective
current.  (I am not familiar with the proposal to 
WG8.)

[R_Hughes >] I know it as prospective short-circuit current, but maybe I go
boldly whereas you boldly go?

RN> However, I believe that the circuit prospective
current is of little or no consequence when testing
a robust earthing circuit complying with the 
constructional requirements.  (Of course we should
test this hypothesis.)
 
[R_Hughes >] Exactly the point I made in WG8. 


Best regards,
Richard 










This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Re: The transformer screen/shield conundrum

2003-06-28 Thread John Woodgate

I read in !emc-pstc that Rich Nute  wrote (in
<200306271743.kaa29...@epgc264.sdd.hp.com>) about 'The transformer
screen/shield conundrum' on Fri, 27 Jun 2003:

>The screen/shield must be capable of carrying
>the full fault current and is often tested 
>using the 25-amp test.  

C.2 of Annex C of IEC/EN 60950-1:2001 says, in the Notes:

' an overload device [should be 'protective device', I think] will
open the circuit before the screen is destroyed.'  If the product is
fitted with an internal fuse, say 5 A, I don't see any need for the
screen to withstand 25 A. 

I certainly would not want to design a transformer with a screen that
would withstand 25 A unless the cost and difficulty of manufacture were
amply justified. At 25 A, the current divergence from the fault point
and convergence to the lead out could well have significant effects.
There are ways of dealing with that, but it's bothersome.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Re: The transformer screen/shield conundrum

2003-06-28 Thread John Woodgate

I read in !emc-pstc that Rich Nute  wrote (in
<200306271956.maa00...@epgc264.sdd.hp.com>) about 'The transformer
screen/shield conundrum' on Fri, 27 Jun 2003:

>I would agree that this current, at a very small 
>contact area, is the driver for the hole in the
>screen/shield.  

OK, the trade secret is to use two layers of foil. Only the first one
gets the hole. 
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Re: The transformer screen/shield conundrum

2003-06-28 Thread Rich Nute




Hi Richard:


>   You mention a few times the 25 Amp test. The designs I have seen that try
>   and use this approach (and I don't ever recall seeing a design I was happy
>   with) were all switch mode power supplies where there was an input fuse of
>   about 2A, meaning that the test would be performed at 3A in the past (and
>   will be performed at 4A in the future, if the CDs go through un-changed).

I'm surprised that, today, a SMPS would used screen/
shield construction.  

The effectiveness of a SMPS transformer is a function
of the physical proximity of primary and secondary
windings.  All of the SMPS transformers that I have
been involved with over the past 10 years or so use
reinforced/double-insulation between primary and 
secondary.

While I mentioned the 25-amp test, I fully concur 
that the test current is a function of the relevant
overcurrent device.  

>   problem I am not convinced that it is the whole story.  For me, another
>   chapter in this story is the part played by the very high surge current
that
>   flows for a very short period of time.  It is here where we could usefully

I presume you are referring to the circuit prospective
current.  (I am not familiar with the proposal to 
WG8.)

I would agree that this current, at a very small 
contact area, is the driver for the hole in the
screen/shield.  

However, I believe that the circuit prospective
current is of little or no consequence when testing
a robust earthing circuit complying with the 
constructional requirements.  (Of course we should
test this hypothesis.)


Best regards,
Rich






This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



re: The transformer screen/shield conundrum

2003-06-28 Thread richhug...@aol.com

Rich,
 
Thanks for the Email in which you mention many of the points already
discussed in IEC TC74.  So what are we going to do with the new hazard based
standard?  Are we going to permit constructions that have been in IEC 60065
and IEC 60950 for years or are we going to introduce a test that is rather
more realistic of the actual failure condition than simply running an earth
bond test?
 
You mention a few times the 25 Amp test. The designs I have seen that try
and use this approach (and I don't ever recall seeing a design I was happy
with) were all switch mode power supplies where there was an input fuse of
about 2A, meaning that the test would be performed at 3A in the past (and
will be performed at 4A in the future, if the CDs go through un-changed).
 
You mention that current density caused by a small point of contact is the
reason why a short from the winding to the earthed foil will cause the
formation of a hole in the foil.  Although I agree that it is part of the
problem I am not convinced that it is the whole story.  For me, another
chapter in this story is the part played by the very high surge current that
flows for a very short period of time.  It is here where we could usefully
apply the surge test proposed in WG8 by Taylor and Bahra, but rejected as
being not sufficiently well thought through.

So there you have it, some of us Brits just like having a good discussion
(what you call an argument).  Unfortunately there were no Americans around
to argue with in our morning so we just had to make do with arguing with one
another!  Glad to see you've joined the fray!
 
Richard



From: ri...@sdd.hp.com [mailto:ri...@sdd.hp.com] 
Sent: Saturday, June 28, 2003 5:43 AM
To: j...@jmwa.demon.co.uk; richhug...@aol.com
Cc: emc-p...@majordomo.ieee.org
Subject: The transformer screen/shield conundrum







Hi John and Richard:


The transformer screen/shield between primary
and secondary windings is intended to carry
the fault current in the event of a failure 
of basic insulation between the primary and
the screen/shield.

The screen/shield must be capable of carrying
the full fault current and is often tested 
using the 25-amp test.  

The object of the test is to connect to the
screen/shield, and then pass the 25 amps 
through the shield to its transformer terminal 
and then to the PE terminal.

The difficult part is how to connect the
tester to the screen/shield.  When the screen/
shield is a copper foil, a special transformer 
must be wound with a wire connected (soldered) 
to the foil screen/shield and brought out for 
connection to the 25-amp source.  If this 
cannot be done, then a wire is soldered to the 
edge of the foil screen/shield by forcefully 
separating the sheet insulation that extends 
beyond the edge of the shield, inserting the
soldering iron tip, and soldering the wire.  

(A constructional problem is that the screen/
shield must extend BEYOND the primary winding
so that no part of the primary winding is 
"exposed" to the secondary winding.) 

(Another constructional problem is that the
ends of the foil must be overlapped, but with 
insulation inserted between the overlaps;
otherwise, the screen/shield would constitute 
a shorted turn and cause all kinds of 
electrical, magnetic, and thermal problems.)

The connection of the tester to the foil
screen/shield typically has a very large 
contact area.  Any thickness of foil screen/
shield passes the test.

The conundrum is that the failure of basic
insulation could result in a point contact
between the primary winding and the shield.
The point-contact, because of its small area,
has very high current density, and will blow
a hole in thin foil (that otherwise passes
the 25-amp test).  

With the hole in the screen/sheild, the fault 
to the foil opens, and the fault no longer 
exists -- even though there is a failure of 
basic insulation.  The connection of the foil 
to the PE remains intact, and there is no 
shock hazard.

(Of course, the heat of the point-contact 
fault may very well cause failure of the foil 
screen/shield-to-secondary functional
insulation, which might very well result in a 
shock hazard from the secondary SELV circuit.)

The point is that the test does not 
necessarily test what can occur within the
transformer, yet will pass the transformer
screen/shield construction.

Nevertheless, when the basic insulation fault 
occurs, the hole in the screen/shield may very 
well end the event safely.


Best regards,
Rich










This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri.