2013-03-08 Thread Simon Whitehead
APC are based in Romsey, I had a faulty unit, there are fuses located inside
the unit as well as the normal screw in type on the back.

 

When my box became faulty I dropped in, I live very local and collected a
repaired unit later that day, for pocket change money too.

 

Simon

 

-- 
Please post to: Hampshire@mailman.lug.org.uk
Web Interface: https://mailman.lug.org.uk/mailman/listinfo/hampshire
LUG URL: http://www.hantslug.org.uk
--

Re: [Hampshire] APC UPS advice please

2013-03-08 Thread Paul Stimpson

On 08/03/13 11:25, Simon Whitehead wrote:


APC are based in Romsey, I had a faulty unit, there are fuses located 
inside the unit as well as the normal screw in type on the back.


When my box became faulty I dropped in, I live very local and 
collected a repaired unit later that day, for pocket change money too.


Simon






I'm certainly not without hope on this. I tend to prefer totally dead 
faults over misbehaviour ones as they often are easier to fix. Sounds 
like it's worth asking if the yjourney isn't too far.


Cheers,
Paul.
-- 
Please post to: Hampshire@mailman.lug.org.uk
Web Interface: https://mailman.lug.org.uk/mailman/listinfo/hampshire
LUG URL: http://www.hantslug.org.uk
--

[Hampshire] APC UPS advice please

2013-03-07 Thread Martin N

Hello,

I got a new but open boxed APC backup-ups rs 800 VA UPS off ebay.

Plugging it in there are no light when holding the power button down.
Measuring the voltage on the terminal plugs gives me 4.7V when it outputs 14V
when fully charged.

After an hours charge i get 4.8V but that could be corrosion on connectors or
my cheapo multimeter.

So if the UPS dead?
battery dead?

How long does the lead acid battery last in storage?

Any advice on how i can test things further?

thanks for your time

Martin N

Those who would give up essential Liberty, to 
purchase a little temporary Safety, deserve neither Liberty nor Safety.
Benjamin Franklin (1706–90) 



--
Please post to: Hampshire@mailman.lug.org.uk
Web Interface: https://mailman.lug.org.uk/mailman/listinfo/hampshire
LUG URL: http://www.hantslug.org.uk
--


Re: [Hampshire] APC UPS advice please

2013-03-07 Thread James Courtier-Dutton
On 7 March 2013 15:24, Martin N marti...@bluebottle.com wrote:
 Hello,

 I got a new but open boxed APC backup-ups rs 800 VA UPS off ebay.

 Plugging it in there are no light when holding the power button down.
 Measuring the voltage on the terminal plugs gives me 4.7V when it outputs
 14V
 when fully charged.

 After an hours charge i get 4.8V but that could be corrosion on connectors
 or
 my cheapo multimeter.

 So if the UPS dead?
 battery dead?

 How long does the lead acid battery last in storage?

 Any advice on how i can test things further?

 thanks for your time

 Martin N


For a new UPS, the battery will arrive disconnected.

It is probably a old battery or a failed unit.
Do any lights light on the unit?
Is there any indication that power is getting to it?

-- 
Please post to: Hampshire@mailman.lug.org.uk
Web Interface: https://mailman.lug.org.uk/mailman/listinfo/hampshire
LUG URL: http://www.hantslug.org.uk
--


Re: [Hampshire] APC UPS advice please

2013-03-07 Thread Martin N

Lo,

At 16:01 07/03/2013, you wrote:

On 7 March 2013 15:24, Martin N marti...@bluebottle.com wrote:
 Hello,

 I got a new but open boxed APC backup-ups rs 800 VA UPS off ebay.

 Plugging it in there are no light when holding the power button down.
 Measuring the voltage on the terminal plugs gives me 4.7V when it outputs
 14V
 when fully charged.

 After an hours charge i get 4.8V but that could be corrosion on connectors
 or
 my cheapo multimeter.

 So if the UPS dead?
 battery dead?

 How long does the lead acid battery last in storage?

 Any advice on how i can test things further?

 thanks for your time

 Martin N


For a new UPS, the battery will arrive disconnected.


Yes i have connected it myself.



It is probably a old battery or a failed unit.


The ups failed or failed battery?



Do any lights light on the unit?


No lights at all which worries me.



Is there any indication that power is getting to it?


Yes i have connected a radio to the surge outlets which works.
The battery outlets do not work though :(

Martin N

Owner of the bwfc yahoogroup and Co-Moderator of  MiniDisc and 
amithlonopen yahoo groups. 



--
Please post to: Hampshire@mailman.lug.org.uk
Web Interface: https://mailman.lug.org.uk/mailman/listinfo/hampshire
LUG URL: http://www.hantslug.org.uk
--


Re: [Hampshire] APC UPS advice please

2013-03-07 Thread James Courtier-Dutton
On 7 March 2013 16:07, Martin N marti...@bluebottle.com wrote:

 Do any lights light on the unit?


 No lights at all which worries me.



 Is there any indication that power is getting to it?


 Yes i have connected a radio to the surge outlets which works.
 The battery outlets do not work though :(


You might have to resort to reading the manual.
There is a reset switch on the back of the unit. Have you tried pressing it?
The problem is most likely a faulty APC unit, and not a faulty
battery. (reason: no lights on unit).
The manual says this:
 If the internal battery cartridge is not
connected (see Step 1 above), the green On
Line indicator and red Replace Battery
indicators will light. The Back-UPS will also
emit a chirping sound

-- 
Please post to: Hampshire@mailman.lug.org.uk
Web Interface: https://mailman.lug.org.uk/mailman/listinfo/hampshire
LUG URL: http://www.hantslug.org.uk
--


Re: [Hampshire] APC UPS advice please

2013-03-07 Thread Martin N

Hello,

At 16:26 07/03/2013, you wrote:

On 7 March 2013 16:07, Martin N marti...@bluebottle.com wrote:

 Do any lights light on the unit?


 No lights at all which worries me.



 Is there any indication that power is getting to it?


 Yes i have connected a radio to the surge outlets which works.
 The battery outlets do not work though :(


You might have to resort to reading the manual.
There is a reset switch on the back of the unit. Have you tried pressing it?



That is the sticking out pellet like button?
Its wobbly and loose.


The problem is most likely a faulty APC unit, and not a faulty
battery. (reason: no lights on unit).


The 2 surge ports work ok though.



The manual says this:
 If the internal battery cartridge is not
connected (see Step 1 above), the green On
Line indicator and red Replace Battery
indicators will light. The Back-UPS will also
emit a chirping sound



Hmm that does not sound good

Martin N

Those who would give up essential Liberty, to 
purchase a little temporary Safety, deserve neither Liberty nor Safety.
Benjamin Franklin (1706–90) 



--
Please post to: Hampshire@mailman.lug.org.uk
Web Interface: https://mailman.lug.org.uk/mailman/listinfo/hampshire
LUG URL: http://www.hantslug.org.uk
--


Re: [Hampshire] APC UPS advice please

2013-03-07 Thread James Courtier-Dutton
On 7 March 2013 16:35, Martin N marti...@bluebottle.com wrote:
 Hello,


 At 16:26 07/03/2013, you wrote:

 On 7 March 2013 16:07, Martin N marti...@bluebottle.com wrote:
 
  Do any lights light on the unit?
 
 
  No lights at all which worries me.
 
 
 
  Is there any indication that power is getting to it?
 
 
  Yes i have connected a radio to the surge outlets which works.
  The battery outlets do not work though :(
 

 You might have to resort to reading the manual.
 There is a reset switch on the back of the unit. Have you tried pressing
 it?



 That is the sticking out pellet like button?
 Its wobbly and loose.

Check this on how to reset it.
http://www.apcmedia.com/salestools/ASTE-6Z7V3K/ASTE-6Z7V3K_R0_EN.pdf

-- 
Please post to: Hampshire@mailman.lug.org.uk
Web Interface: https://mailman.lug.org.uk/mailman/listinfo/hampshire
LUG URL: http://www.hantslug.org.uk
--


Re: [Hampshire] APC UPS advice please

2013-03-07 Thread Martin N

Hello,

At 16:53 07/03/2013, you wrote:

On 7 March 2013 16:35, Martin N marti...@bluebottle.com wrote:
 Hello,


 At 16:26 07/03/2013, you wrote:

 On 7 March 2013 16:07, Martin N marti...@bluebottle.com wrote:
 
  Do any lights light on the unit?
 
 
  No lights at all which worries me.
 
 
 
  Is there any indication that power is getting to it?
 
 
  Yes i have connected a radio to the surge outlets which works.
  The battery outlets do not work though :(
 

 You might have to resort to reading the manual.
 There is a reset switch on the back of the unit. Have you tried pressing
 it?



 That is the sticking out pellet like button?
 Its wobbly and loose.

Check this on how to reset it.
http://www.apcmedia.com/salestools/ASTE-6Z7V3K/ASTE-6Z7V3K_R0_EN.pdf


After looking at that manual, I have tried pressing it in but it 
doesn't stick/latch on to anything.


Its not stiff so to me the circuit breaker is reset but i am 
inexperienced so cant be fully confident.


Martin N

Owner of the bwfc yahoogroup and Co-Moderator of  MiniDisc and 
amithlonopen yahoo groups. 



--
Please post to: Hampshire@mailman.lug.org.uk
Web Interface: https://mailman.lug.org.uk/mailman/listinfo/hampshire
LUG URL: http://www.hantslug.org.uk
--


Re: [Hampshire] APC UPS advice please

2013-03-07 Thread Paul Stimpson

Hi,

On 07/03/13 16:58, Martin N wrote:


After looking at that manual, I have tried pressing it in but it 
doesn't stick/latch on to anything.


Its not stiff so to me the circuit breaker is reset but i am 
inexperienced so cant be fully confident.


Martin N

Owner of the bwfc yahoogroup and Co-Moderator of  MiniDisc and 
amithlonopen yahoo groups.





This may be a really silly thing but my experience of UPS breakages on 
the road is that the most common fault is blown fuses. Most of our 
UPSes, in addition to the pop-breaker, have a small fuse holder built 
into the IEC inlet, the power cord and some also on the motherboard. If 
the USP gets seriously overloaded this fuse will often blow before (or 
at the same time as) the breaker pops.


The usual scenario is that the hotel cleaner comes in, can't find a 
socket for the Hoover, sees this power strip, plugs in... Pop. 
beep.beep. Sneaks out and you have a dead UPS that won't charge when you 
plug it in. I know it's daft but it fixes 90% of the broken units people 
bring to me.


Cheers,
Paul.


--
Please post to: Hampshire@mailman.lug.org.uk
Web Interface: https://mailman.lug.org.uk/mailman/listinfo/hampshire
LUG URL: http://www.hantslug.org.uk
--


Re: [Hampshire] APC UPS advice please

2013-03-07 Thread Tim Brocklehurst
On Thursday 07 Mar 2013 15:24:55 Martin N wrote:
 After an hours charge i get 4.8V but that could be corrosion on connectors
 or my cheapo multimeter.
 
 So if the UPS dead?
 battery dead?
 
 How long does the lead acid battery last in storage?
 
 Any advice on how i can test things further?
 
 thanks for your time
 
 Martin N


Martin,

I have aquired a Belkin unit with very identical symptoms. In my case one 
battery terminal had actually corroded and fallen off, so it was a pretty 
simple fault to find. Typically, the Lead acid batteries used will be 6Volt or 
12Volt, sometimes wired in series to give 24Volts. Disconnect the battery(ies) 
and measure the voltage across them. If you are move than about two volts from 
the typical values above, it's likely that the battery is dead and needs 
replacement.

There are places which sell replacement batteries on the web at reasonable 
prices.

Cheers,

Tim B. 
-- 
Hampshire Linux User Group Chairman

-- 
Please post to: Hampshire@mailman.lug.org.uk
Web Interface: https://mailman.lug.org.uk/mailman/listinfo/hampshire
LUG URL: http://www.hantslug.org.uk
--


Re: [Hampshire] APC UPS advice please

2013-03-07 Thread Martin N

Lo,

At 17:43 07/03/2013, you wrote:

Hi,

On 07/03/13 16:58, Martin N wrote:


After looking at that manual, I have tried pressing it in but it 
doesn't stick/latch on to anything.


Its not stiff so to me the circuit breaker is reset but i am 
inexperienced so cant be fully confident.


Martin N

Owner of the bwfc yahoogroup and Co-Moderator of  MiniDisc and 
amithlonopen yahoo groups.



This may be a really silly thing but my experience of UPS breakages 
on the road is that the most common fault is blown fuses. Most of 
our UPSes, in addition to the pop-breaker, have a small fuse holder 
built into the IEC inlet, the power cord and some also on the 
motherboard. If the USP gets seriously overloaded this fuse will 
often blow before (or at the same time as) the breaker pops.


Is this a black screw in thing?

I seem to remember seeing one on an old UPS at a place i worked.

There is not one on this unit but i could break it open and have a look.

Martin N

Running MorphOS v3.1 (July 2012) on a PowerPC Powerbook, Moderator of 
MiniDisc,amithlonopen,bwfc Yahoogroups




--
Please post to: Hampshire@mailman.lug.org.uk
Web Interface: https://mailman.lug.org.uk/mailman/listinfo/hampshire
LUG URL: http://www.hantslug.org.uk
--


Re: [Hampshire] APC UPS advice please

2013-03-07 Thread Martin N

Lo,

At 17:57 07/03/2013, you wrote:

On Thursday 07 Mar 2013 15:24:55 Martin N wrote:
 After an hours charge i get 4.8V but that could be corrosion on connectors
 or my cheapo multimeter.

 So if the UPS dead?
 battery dead?

 How long does the lead acid battery last in storage?

 Any advice on how i can test things further?

 thanks for your time

 Martin N


Martin,

I have aquired a Belkin unit with very identical symptoms.


Urgh this APC is to replace an old belkin 800VA unit that was badly designed.
You had to bend open a metal cage to insert a replacement battery.
Did it once and swore when the second battery went i would just get a new UPS.


 In my case one
battery terminal had actually corroded and fallen off, so it was a pretty
simple fault to find. Typically, the Lead acid batteries used will 
be 6Volt or
12Volt, sometimes wired in series to give 24Volts. Disconnect the 
battery(ies)
and measure the voltage across them. If you are move than about two 
volts from

the typical values above, it's likely that the battery is dead and needs
replacement.


Its 4.8V but they are not getting warm like i would expect a dead 
battery to do.

IIRC.



There are places which sell replacement batteries on the web at reasonable
prices.



Not really convinced yet that it is the battery.

Martin N

Running MorphOS v3.1 (July 2012) on a PowerPC Powerbook, Moderator of 
MiniDisc,amithlonopen,bwfc Yahoogroups




--
Please post to: Hampshire@mailman.lug.org.uk
Web Interface: https://mailman.lug.org.uk/mailman/listinfo/hampshire
LUG URL: http://www.hantslug.org.uk
--


Re: [Hampshire] APC UPS advice please

2013-03-07 Thread Paul Stimpson

On 07/03/13 18:23, Martin N wrote:


Is this a black screw in thing?

I seem to remember seeing one on an old UPS at a place i worked.

There is not one on this unit but i could break it open and have a look.



Most of the units I've come across recently have a small drawer built 
into the IEC socket, like this one 
http://www.sinolec.co.uk/iec-connectors/391-0717-cw.html


Please note that page is a random google, not a recommendation for this 
supplier as I've never used them.


Bests,
Paul.


--
Please post to: Hampshire@mailman.lug.org.uk
Web Interface: https://mailman.lug.org.uk/mailman/listinfo/hampshire
LUG URL: http://www.hantslug.org.uk
--


Re: [Hampshire] APC UPS advice please

2013-03-07 Thread Paul Stimpson

On 07/03/13 18:26, Martin N wrote:

Lo,

At 17:57 07/03/2013, you wrote:

On Thursday 07 Mar 2013 15:24:55 Martin N wrote:
 After an hours charge i get 4.8V but that could be corrosion on 
connectors

 or my cheapo multimeter.

 So if the UPS dead?
 battery dead?

 How long does the lead acid battery last in storage?

 Any advice on how i can test things further?

 thanks for your time

 Martin N


Martin,

I have aquired a Belkin unit with very identical symptoms.


Urgh this APC is to replace an old belkin 800VA unit that was badly 
designed.

You had to bend open a metal cage to insert a replacement battery.
Did it once and swore when the second battery went i would just get a 
new UPS.



 In my case one
battery terminal had actually corroded and fallen off, so it was a 
pretty
simple fault to find. Typically, the Lead acid batteries used will be 
6Volt or
12Volt, sometimes wired in series to give 24Volts. Disconnect the 
battery(ies)
and measure the voltage across them. If you are move than about two 
volts from

the typical values above, it's likely that the battery is dead and needs
replacement.


Its 4.8V but they are not getting warm like i would expect a dead 
battery to do.

IIRC.



If you unplug the UPS for a few minutes, connect the multimeter across 
the battery then power it up, do you see the terminal voltage rise? If 
the charger is charging, I would expect to see that.



Cheers,
Paul.


--
Please post to: Hampshire@mailman.lug.org.uk
Web Interface: https://mailman.lug.org.uk/mailman/listinfo/hampshire
LUG URL: http://www.hantslug.org.uk
--


Re: [Hampshire] APC UPS advice please

2013-03-07 Thread Paul Stimpson

Hi,

Is this the UPS you have? 
http://www.apc.com/resource/include/techspec_index.cfm?base_sku=br800itab=models


Does this look like the correct manual for it? 
http://www.apcmedia.com/salestools/ASTE-6Z7V5B/ASTE-6Z7V5B_R0_EN.pdf



I'm just going through what I would check. I'm not sure of your level of 
experience and I hope you don't feel I'm insulting you.



On 07/03/13 18:26, Martin N wrote:



Not really convinced yet that it is the battery.



Some times, batteries do go short and prevent gear from powering up. I 
recommend you disconnect the UPS then unplugging the battery. When 
you've done that, power the UPS up again. The manual says that if it is 
powered up with no battery, it should chirp and show the green (power) 
and red (replace battery) LEDs. If it doesn't do so with no battery 
connected, that eliminates a present battery short as the culprit.


Next, I would eliminate all the silly D'Oh! problems. Check things 
like there are volts on the end of the IEC cable and that you're 
pressing the power button for the right length or time. (You did mention 
holding the button down. The manual seems to suggest that a short press 
is on and a 10 second hold is programming mode)


When you press the power button, do you feel the switch behind it click? 
The switch is subject to mechanical force. Have the solder joints that 
fix the switch onto the board broken?


Next I would look for fuses inside and bad connections (also do a 
nose-test for brown smell). I always hope things like this are 
something simple like loose/corroded connections, broken wires fractured 
solder joints on things like the back of the IEC input. I know fault 
finding why a switched-mode inverter isn't oscillating is beyond me.


Cheers,
Paul.


--
Please post to: Hampshire@mailman.lug.org.uk
Web Interface: https://mailman.lug.org.uk/mailman/listinfo/hampshire
LUG URL: http://www.hantslug.org.uk
--


Re: [Hampshire] APC UPS advice please

2013-03-07 Thread Martin N

Hello,

At 19:00 07/03/2013, you wrote:

On 07/03/13 18:23, Martin N wrote:


Is this a black screw in thing?

I seem to remember seeing one on an old UPS at a place i worked.

There is not one on this unit but i could break it open and have a look.



Most of the units I've come across recently have a small drawer 
built into the IEC socket, like this one 
http://www.sinolec.co.uk/iec-connectors/391-0717-cw.html


Please note that page is a random google, not a recommendation for 
this supplier as I've never used them.


Thanks for that link it was interesting to see.

I have had a look and there is no fuse draw sadly.

This is the old link on amazon for my model:
http://www.amazon.co.uk/APC-Back-UPS-RS-800VA-UPS/dp/B00013MRS4/ref=sr_1_cc_1?s=apsie=UTF8qid=1362684739sr=1-1-catcorr

Sadly no rear view

Martin N

Owner of the bwfc yahoogroup and Co-Moderator of  MiniDisc and 
amithlonopen yahoo groups. 



--
Please post to: Hampshire@mailman.lug.org.uk
Web Interface: https://mailman.lug.org.uk/mailman/listinfo/hampshire
LUG URL: http://www.hantslug.org.uk
--


Re: [Hampshire] APC UPS advice please

2013-03-07 Thread Martin N

Lo,

At 19:02 07/03/2013, you wrote:

On 07/03/13 18:26, Martin N wrote:

Lo,

At 17:57 07/03/2013, you wrote:

On Thursday 07 Mar 2013 15:24:55 Martin N wrote:
 After an hours charge i get 4.8V but that 
could be corrosion on connectors

 or my cheapo multimeter.

 So if the UPS dead?
 battery dead?

 How long does the lead acid battery last in storage?

 Any advice on how i can test things further?

 thanks for your time

 Martin N


Martin,

I have aquired a Belkin unit with very identical symptoms.


Urgh this APC is to replace an old belkin 800VA unit that was badly designed.
You had to bend open a metal cage to insert a replacement battery.
Did it once and swore when the second battery 
went i would just get a new UPS.



 In my case one
battery terminal had actually corroded and fallen off, so it was a pretty
simple fault to find. Typically, the Lead acid 
batteries used will be 6Volt or
12Volt, sometimes wired in series to give 
24Volts. Disconnect the battery(ies)
and measure the voltage across them. If you 
are move than about two volts from

the typical values above, it's likely that the battery is dead and needs
replacement.


Its 4.8V but they are not getting warm like i 
would expect a dead battery to do.

IIRC.


If you unplug the UPS for a few minutes, connect 
the multimeter across the battery then power it 
up, do you see the terminal voltage rise? If the 
charger is charging, I would expect to see that.


The battery is very well insulated and the only 
contacts are with the captive cable plugging into a socket in the UPS.
There are no exposed terminals on the battery and 
the socket is recessed so i cant get my probes down there.


Thanks for the ideas though

Martin N

Those who would give up essential Liberty, to 
purchase a little temporary Safety, deserve neither Liberty nor Safety.
Benjamin Franklin (1706–90) 



--
Please post to: Hampshire@mailman.lug.org.uk
Web Interface: https://mailman.lug.org.uk/mailman/listinfo/hampshire
LUG URL: http://www.hantslug.org.uk
--


Re: [Hampshire] APC UPS advice please

2013-03-07 Thread Martin N

hi,

At 19:27 07/03/2013, you wrote:

Hi,

Is this the UPS you have? 
http://www.apc.com/resource/include/techspec_index.cfm?base_sku=br800itab=models


Yes that is correct although it does say RS on 
mine which is present on the imag if not the title.

The layout at the back and front is the same.


Does this look like the correct manual for it? 
http://www.apcmedia.com/salestools/ASTE-6Z7V5B/ASTE-6Z7V5B_R0_EN.pdf



I'm just going through what I would check. I'm 
not sure of your level of experience and I hope 
you don't feel I'm insulting you.


No problem, I could of missed something obvious 
so I rather be insulted than miss something :)





On 07/03/13 18:26, Martin N wrote:



Not really convinced yet that it is the battery.


Some times, batteries do go short and prevent 
gear from powering up. I recommend you 
disconnect the UPS then unplugging the battery. 
When you've done that, power the UPS up again. 
The manual says that if it is powered up with no 
battery, it should chirp and show the green 
(power) and red (replace battery) LEDs. If it 
doesn't do so with no battery connected, that 
eliminates a present battery short as the culprit.


done and no leds light or chirping.


Next, I would eliminate all the silly D'Oh! 
problems. Check things like there are volts on 
the end of the IEC cable and that you're 
pressing the power button for the right length 
or time. (You did mention holding the button 
down. The manual seems to suggest that a short 
press is on and a 10 second hold is programming mode)


When you press the power button, do you feel the 
switch behind it click? The switch is subject to 
mechanical force. Have the solder joints that 
fix the switch onto the board broken?


No click.
The button feels ok and doesnt wobbly too much for a cheaply made UPS.


Next I would look for fuses inside and bad 
connections (also do a nose-test for brown 
smell). I always hope things like this are 
something simple like loose/corroded 
connections, broken wires fractured solder 
joints on things like the back of the IEC input. 
I know fault finding why a switched-mode 
inverter isn't oscillating is beyond me.


I could break it open but googling seems to say 
it requires a lot of force as click snap plastic

rather than screws for the front panel.
It also says not too hard as you will remove the led cable.

Leaving me not knowing how hard to try.
I guess with the surge working I dont want to 
kill it completely as I can always use it for that.
(I would expect the surge protection on the 2 
outlets are better quality than surge on a standard

extension block)
The led cable being detached shouldnt affect the surge protection it provides.

Probably worth a try prizing it  off.

thanks for your time

Martin N

Those who would give up essential Liberty, to 
purchase a little temporary Safety, deserve neither Liberty nor Safety.
Benjamin Franklin (1706–90) 



--
Please post to: Hampshire@mailman.lug.org.uk
Web Interface: https://mailman.lug.org.uk/mailman/listinfo/hampshire
LUG URL: http://www.hantslug.org.uk
--