[RE-wrenches] XW connection to PC?

2008-12-10 Thread design

Fellow Wrenches,

	I am looking to see if there is a way to connect the Xantrex XW  
inverters to a PC for data acquisition and/or control.  The cabling  
is familiar enough, but I can find no reference in Xantrex literature  
mentioning a PC link.  With the old SW, they offered an interface  
box.  I though at first that the XW control panel may accommodate the  
connection, but it is not mentioned.  Have any of you found a way to  
do this?  OR have any of you come to the conclusion that it is not  
possible?


Thanks,

Jim Grundy
NABCEP Certified Solar PV Installer™
Vermont Solar Specialist Plumber PS-279
Elemental Energy, Inc.
1750 Clark Rd
E. Montpelier, VT   05651
802-476-3441 (p)
802-476-5680 (f )
802-272-8933 (c)


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] XW connection to PC?

2008-12-10 Thread Jon Haeme

Hi Jim,

Xantrex has a XW configuration tool with a USB to Xanbus adapter and  
XW config software that is used for firmware upgrades and adjusting  
settings on connected devices. I don't know if it can be used for  
data acquisition. I haven't used one yet so I can't tell you how it  
works.


Jon

Jon Haeme Innovations
NABCEP certified Solar PV installer
Kempton, IL


On Dec 10, 2008, at 7:34 AM, design wrote:


Fellow Wrenches,

	I am looking to see if there is a way to connect the Xantrex XW  
inverters to a PC for data acquisition and/or control.  The cabling  
is familiar enough, but I can find no reference in Xantrex  
literature mentioning a PC link.  With the old SW, they offered an  
interface box.  I though at first that the XW control panel may  
accommodate the connection, but it is not mentioned.  Have any of  
you found a way to do this?  OR have any of you come to the  
conclusion that it is not possible?


Thanks,

Jim Grundy
NABCEP Certified Solar PV Installer™
Vermont Solar Specialist Plumber PS-279
Elemental Energy, Inc.
1750 Clark Rd
E. Montpelier, VT   05651
802-476-3441 (p)
802-476-5680 (f )
802-272-8933 (c)


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re- 
wrenches.org


List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] XW connection to PC?

2008-12-10 Thread mick abraham
Here's a link to follow:

http://www.xantrex.com/web/id/269/p/1/pt/5/product.asp

I do not know if the Communications Gateway is shipping or not, but it's close 
anyway.

Mick Abraham, Proprietor 
www.abrahamsolar.com 
Voice: 970-731-4675

-- Original Message ---
From: design [EMAIL PROTECTED] 
To: re-wrenches@lists.re-wrenches.org 
Sent: Wed, 10 Dec 2008 08:34:29 -0500 
Subject: [RE-wrenches] XW connection to PC?

 Fellow Wrenches,
  
  I am looking to see if there is a way to connect the Xantrex XW inverters to 
 a PC for data acquisition and/or control.  The cabling is familiar enough, 
 but I can find no reference in Xantrex literature mentioning a PC link.  With 
 the old SW, they offered an interface box.  I though at first that the XW 
 control panel may accommodate the connection, but it is not mentioned.  Have 
 any of you found a way to do this?  OR have any of you come to the conclusion 
 that it is not possible?
 
 Thanks,
 
 
 Jim Grundy
 NABCEP Certified Solar PV [WINDOWS-1252?]Installer™
 Vermont Solar Specialist Plumber PS-279
 Elemental Energy, Inc.
 1750 Clark Rd
 E. Montpelier, VT   05651
 802-476-3441 (p)
 802-476-5680 (f )
 802-272-8933 (c) 
--- End of Original Message ---
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] XW connection to PC?

2008-12-10 Thread Wind-sun.com
You might want to take a look at http://www.righthandeng.com/ - our experience 
with Xantrex made software has been less than .. gratifying.


..
Northern Arizona Wind  Sun - Electricity From The Sun
..
  - Original Message - 
  From: mick abraham 
  To: RE-wrenches 
  Sent: Wednesday, December 10, 2008 8:24 AM
  Subject: Re: [RE-wrenches] XW connection to PC?


  Here's a link to follow: 

  http://www.xantrex.com/web/id/269/p/1/pt/5/product.asp 

  I do not know if the Communications Gateway is shipping or not, but it's 
close anyway. 

  Mick Abraham, Proprietor 
  www.abrahamsolar.com 
  Voice: 970-731-4675 

  -- Original Message --- 
  From: design [EMAIL PROTECTED] 
  To: re-wrenches@lists.re-wrenches.org 
  Sent: Wed, 10 Dec 2008 08:34:29 -0500 
  Subject: [RE-wrenches] XW connection to PC? 

   Fellow Wrenches, 
   
   I am looking to see if there is a way to connect the Xantrex XW inverters 
to a PC for data acquisition and/or control.  The cabling is familiar enough, 
but I can find no reference in Xantrex literature mentioning a PC link.  With 
the old SW, they offered an interface box.  I though at first that the XW 
control panel may accommodate the connection, but it is not mentioned.  Have 
any of you found a way to do this?  OR have any of you come to the conclusion 
that it is not possible? 
   

   Thanks, 
   
   
   Jim Grundy 
   NABCEP Certified Solar PV [WINDOWS-1252?]InstallerT 
   Vermont Solar Specialist Plumber PS-279 
   Elemental Energy, Inc. 
   1750 Clark Rd 
   E. Montpelier, VT   05651 
   802-476-3441 (p) 
   802-476-5680 (f ) 
   802-272-8933 (c) 

  --- End of Original Message --- 



--


  ___
  List sponsored by Home Power magazine

  List Address: RE-wrenches@lists.re-wrenches.org

  Options  settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

  List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

  List rules  etiquette:
  www.re-wrenches.org/etiquette.htm

  Check out participant bios:
  www.members.re-wrenches.org

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] building permits for PV

2008-12-10 Thread Joel Davidson
Dana,

See http://lomaprieta.sierraclub.org/global_warming/fee_study.htm

I think there were other lists of permit requirements on this list but I can 
not find them. Perhaps someone can suggest a search method.

Joel Davidson

  - Original Message - 
  From: Andrew Truitt 
  To: RE-wrenches 
  Sent: Tuesday, December 09, 2008 9:05 PM
  Subject: Re: [RE-wrenches] building permits for PV


  Dana,

  Washington DC, Baltimore MD, San Francisco, Berkeley and Oakland CA - none 
require roof footing inspections.  However, one of our local AHJs does 
require a letter on company letterhead stating our roof guarantee - maybe 
something you could try.  We are also required to get structural engineer 
stamped drawings in most jurisdictions in Maryland.  

  This document has some info you might find useful:

  http://www.solartech.org/index.php/about/29-objectives/18-buildingpermits

  But when faced with unreasonable AHJs I don't think any way foreword is 
better than just sitting down with the Head of Permitting and explaining 
exactly how you install, preferably with visual aids.  And since yours seems to 
be especially worried about leaks make sure you have a good counterflashed 
waterproofing solution to show him.  Tell him you want to work with him but 
that many solar installs are completed in a day or two and to accommodate an 
inspection in the middle severely impacts your project timeline.

  And of course it couldn't hurt to bring a box of donuts.

  Good luck!


  Andrew Truitt
  Standard Solar





  On Tue, Dec 9, 2008 at 6:13 PM, Dana Brandt [EMAIL PROTECTED] wrote:

Thanks for all the feedback. Sounds like there's a ton of variation from 
one jurisdiction to another. Would you all be willing to send me a list of 
large cities you've worked in that do not require a building permit? I'd like 
to use that to make a case against the requirement.

I just got back from the inspection which verified that - yes indeed, there 
are L-feet and rails on the roof. Seems pretty silly...

Thanks again,


Dana

-- 
Dana Brandt
Ecotech Energy Systems, LLC
www.ecotechenergy.com
[EMAIL PROTECTED]
360.510.0433



On Tue, Dec 9, 2008 at 8:11 AM, Paul Israel [EMAIL PROTECTED] wrote:

  Dana, 



  Firstly we all truly sympathize, I have never heard of that one!   



  Not one building department - has required that.  We have installed in 
Oregon, Connecticut, Rhode Island, Reno - Nevada, and Massachusetts. 



  We are inspected consistently for concrete pours (rebar/pads/ground 
mounts/pole mounts).  For most roofs in CT we are usually required to have an 
Engineers Stamp for the layout relative to the rafter loading.   It depends on 
the jurisdiction or whether they had their coffee.  It is random.



  I would try and push the manufacturer's installation instructions or get 
a local engineering stamp on the layout as an alternative.



  On a lighter note, make sure to leave some exposed wet caulk.   After 
messing up their car, paperwork, and a couple layers of skin they surely won't 
want to do that again. 



  Good luck and let us know how it works out. 





   

  Paul N. Israel, President

  [EMAIL PROTECTED]

  www.sunlightsolar.com

  541/389-3480 (Oregon)

  203/878-9123 x103 (CT)

  860/617-6527 (Cell)


--

  From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Dana Brandt
  Sent: Monday, December 08, 2008 5:46 PM
  To: RE-wrenches
  Subject: [RE-wrenches] building permits for PV



  Hi all,

  Until recently, we've only been required to have an electrical permit for 
flush-mounted PV systems. The city has now decided to require building permits 
for all PV systems and wants to come out and inspect our L-feet attachments and 
rails before the modules can go up. This seems crazy to me. What are other 
jurisdictions requiring? I'd love some information I can take to the city 
showing that other jurisdictions aren't requiring this type of process.

  Thanks a lot,

  Dana

  -- 
  Dana Brandt
  Ecotech Energy Systems, LLC
  www.ecotechenergy.com
  [EMAIL PROTECTED]
  360.510.0433



  ___
  List sponsored by Home Power magazine

  List Address: RE-wrenches@lists.re-wrenches.org

  Options  settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

  List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

  List rules  etiquette:
  www.re-wrenches.org/etiquette.htm

  Check out participant bios:
  www.members.re-wrenches.org







___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:

Re: [RE-wrenches] XW connection to PC?

2008-12-10 Thread Mark Edmunds
Hi All - yes the XW Gateway unit is shipping, and gives you either a
wired or wireless connection to a local Ethernet network. The XW-Config
tool is also available and provides a USB connection and software for
set up and monitoring via a PC. (I don't think the Config tool is on the
web site yet, but can be ordered through the tech support group)

 

The built in com ports on the XW system devices use CAN bus hardware,
with a proprietary communication protocol, so either one of the above
devices is the best way to make your connection from this to a computer.

 

Cheers,

 

Mark

 

 

Mark Edmunds

Xantrex Technology Inc.

 

From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of mick
abraham
Sent: Wednesday, December 10, 2008 7:25 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] XW connection to PC?

 

Here's a link to follow: 

http://www.xantrex.com/web/id/269/p/1/pt/5/product.asp 

I do not know if the Communications Gateway is shipping or not, but it's
close anyway. 

Mick Abraham, Proprietor 
www.abrahamsolar.com http://www.abrahamsolar.com/  
Voice: 970-731-4675 



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] XW connection to PC?

2008-12-10 Thread mick abraham
Thanks, Mark~

Did the T-tap device ever materialize? You had written about this as a way to 
get power onto the Xanbus network if an inverter/charger was absent from the 
system.

I think part number 865-1057 had been assigned. Please advise if this can now 
be ordered through distributor channels.

Mick Abraham, Proprietor 
www.abrahamsolar.com 
Voice: 970-731-4675

-- Original Message ---
From: Mark Edmunds [EMAIL PROTECTED] 
To: RE-wrenches re-wrenches@lists.re-wrenches.org 
Sent: Wed, 10 Dec 2008 09:07:39 -0800 
Subject: Re: [RE-wrenches] XW connection to PC?

 Hi All – yes the XW Gateway unit is shipping, and givesyou either a wired or 
 wireless connection to a local Ethernet network. The XW-Configtool is also 
 available and provides a USB connection and software for set up andmonitoring 
 via a PC. (I don’t think the Config tool is on the web siteyet, but can be 
 ordered through the tech support group)
  
 The built in com ports on the XW system devices use CAN bushardware, with a 
 proprietary communication protocol, so either one of the abovedevices is the 
 best way to make your connection from this to a computer.
  
 Cheers,
  
 Mark
  
  
 Mark Edmunds
 Xantrex Technology Inc.
  
 
 From: [EMAIL PROTECTED]:[EMAIL PROTECTED] On Behalf Of mickabraham
 Sent: Wednesday, December 10, 2008 7:25 AM
 To: RE-wrenches
 Subject: Re: [RE-wrenches] XW connection to PC?
  
 Here's a link to follow: 
 
 http://www.xantrex.com/web/id/269/p/1/pt/5/product.asp 
 
 I do not know if the Communications Gateway is shipping or not, but it's 
 closeanyway. 
 
 Mick Abraham, Proprietor 
 www.abrahamsolar.com
 Voice: 970-731-4675 
 
 
--- End of Original Message ---
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] voltage drop

2008-12-10 Thread R. Walters
I have a volt drop spreadsheet on our website as well at http:// 
www.solarray.com/TechGuides/TGmain_T.php
It uses NEC temp correction for resistance, and another temp  
correction for ampacity. One is based on ambient air temp, and one is  
wire temp. All calculations are taken directly from the 2005 NEC 
( don't think wire changed in 2008) Also, it lets you look at various  
wires at the same time like William's. I don't currently have AC on  
it, but it's getting cold here, so maybe I'll add that this winter.
I hid the ampacity stuff I attempted, since NEC has so many factors  
to consider, but its still on there, if you unhide all the rows.  I  
also tried to do a sizing based on wire cost thing, but when wire  
pricing shot up, it threw all that off too.
You can still use that, you just have to enter your per ft cost for  
each wire size. The idea was to not spend $1000 putting in 4/0 cable  
to save $100 worth of solar power.



Ray

On Dec 10, 2008, at 8:16 AM, Wind-sun.com wrote:

The NEC values are for 75C, but not everything operates at that  
temperature (167F), nor or all uses of wire under NEC codes. I  
understand why the spreadsheet is set up for NEC since that covers  
probably 98% of all uses.


At room temperature (25C), the resistance values are almost 20%  
less - the standard physics value of #10 AWG is almost exactly 1  
ohm per 1000 feet at 26C.


http://en.wikipedia.org/wiki/American_wire_gauge

.. 


Northern Arizona Wind  Sun - Electricity From The Sun
.. 



- Original Message - From: William Miller  
[EMAIL PROTECTED]

To: RE-wrenches re-wrenches@lists.re-wrenches.org
Sent: Tuesday, December 09, 2008 11:48 PM
Subject: Re: [RE-wrenches] voltage drop



Dear Wind  Sun:

What standard are you referring to?  We are using the 75C values  
from the NEC in order to assure code compliance.  We need to have  
a direct link to the NEC in case of compliance or liability issues.


Thanks for asking.

William Miller


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re- 
wrenches.org


List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



R. Walters
Solarray.com
NABCEP # 04170442   



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Module Voltage Question for Off-Grid Designers

2008-12-10 Thread Allan Sindelar
Wrenches,
Here's an issue I haven't seen directly addressed, and I would like to know
what the rest of you are doing.
It's getting harder to get 24V nominal modules. Because the bulk of industry
growth is high-voltage grid-tied applications, modules no longer have to be
a standard voltage. Just pick the number of modules to best fit the chosen
inverter's string voltage range.
But for off-grid, the odd cell counts and resulting nontraditional DC
input voltages challenge the traditional rules of off-grid design. I may be
fighting a losing battle here, as the industry changes so rapidly and
fundamentally. I have been trying to stay with 72-cell modules for offgrid,
as this most readily combines with existing systems with 36-cell modules
(12V) and 72-cell modules (24V). 
For example, I will use the new Canadian Solar 170-200W modules. They are
60-cell modules, with a Vmppt of around 28 volts - too low to charge 24V
batteries with a standard charge controller. We can use them in any new
systems with an MX60 or similar voltage-converting MPPT controller. Two or
three in series would charge a 24V battery; 3 in series would charge 48V.
Four in series would violate Code, as low-temp voltage would easily exceed
150V. 
Unless 60-cell modules remain a standard in the future, any future array
additions would have to be on their own charge controller, in order to match
a different I-V curve and MPP voltages into the same battery bank. Is this
prohibitive? No, it just runs counter to the longstanding standards of
off-grid design that allow modules to be added in the future: these modules
will not add well to existing systems, and will not easily allow additional
dissimilar modules to be added later. 
I had this same objection to using Day4 modules, although they were better
at 16Vnom. Three made up a standard 48V array, so strings could be combined
with two-module strings of similar 24Vnom modules.
Who else is trying to stay with 24V modules? Anyone still using 12V modules
in off-grid (residential-scale, not little apps) designs? Who has a crystal
ball and knows what modules will be like in 20 years, or even two years? Wat
are the rest of you doing?
Thanks, as usual.
Allan
Allan Sindelar
allan_(at)_positiveenergysolar.com mailto:[EMAIL PROTECTED] 
NABCEP certified solar PV installer
Positive Energy, Inc.
3225A Richards Lane
Santa Fe NM 87507
505 424-1112

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] solar hot water penetration flashing

2008-12-10 Thread troy Harvey
Any thoughts on how to flash a copper pipe roof penetration on a metal  
roof. The brazed copper flashing we typically use would cause  
corrosion with the steel roof I'm afraid. WHat have others used in  
this situation?


Troy Harvey
-
Heliocentric
801-453-9434
[EMAIL PROTECTED]


On Dec 10, 2008, at 11:07 AM, R. Walters wrote:


I have a volt drop spreadsheet on our website as well at 
http://www.solarray.com/TechGuides/TGmain_T.php
It uses NEC temp correction for resistance, and another temp  
correction for ampacity. One is based on ambient air temp, and one  
is wire temp. All calculations are taken directly from the 2005  
NEC( don't think wire changed in 2008) Also, it lets you look at  
various wires at the same time like William's. I don't currently  
have AC on it, but it's getting cold here, so maybe I'll add that  
this winter.
I hid the ampacity stuff I attempted, since NEC has so many factors  
to consider, but its still on there, if you unhide all the rows.  I  
also tried to do a sizing based on wire cost thing, but when wire  
pricing shot up, it threw all that off too.
You can still use that, you just have to enter your per ft cost for  
each wire size. The idea was to not spend $1000 putting in 4/0 cable  
to save $100 worth of solar power.



Ray

On Dec 10, 2008, at 8:16 AM, Wind-sun.com wrote:

The NEC values are for 75C, but not everything operates at that  
temperature (167F), nor or all uses of wire under NEC codes. I  
understand why the spreadsheet is set up for NEC since that covers  
probably 98% of all uses.


At room temperature (25C), the resistance values are almost 20%  
less - the standard physics value of #10 AWG is almost exactly 1  
ohm per 1000 feet at 26C.


http://en.wikipedia.org/wiki/American_wire_gauge

..
Northern Arizona Wind  Sun - Electricity From The Sun
..

- Original Message - From: William Miller [EMAIL PROTECTED] 


To: RE-wrenches re-wrenches@lists.re-wrenches.org
Sent: Tuesday, December 09, 2008 11:48 PM
Subject: Re: [RE-wrenches] voltage drop



Dear Wind  Sun:

What standard are you referring to?  We are using the 75C values  
from the NEC in order to assure code compliance.  We need to have  
a direct link to the NEC in case of compliance or liability issues.


Thanks for asking.

William Miller


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



R. Walters
Solarray.com
NABCEP # 04170442   



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Module Voltage Question for Off-Grid Designers

2008-12-10 Thread mick abraham
Call me old school, but the only modules I keep in stock are 36 cell. I would 
consider 72 cell modules for stock but otherwise I just say no to all of the 
screwball cell counts that are out there. It's not that I refuse to sell 
anything else...but if I go goofy on the cell count I just order those modules 
as I need them.

Why go goofy?, I ask myself. My occasional string inverter sale can often 
be accommodated with 36 cell modules...ditto for pumps...and of course a 36 
cell module fits right in to battery charging setups regardless of whether the 
solar array is wired classic or at elevated voltage. Cost per watt for my 
preferred 36's is about the same as everything else, so again I ask: Why go 
goofy?

The main thing that causes me now to consider 72 cell modules for stock is the 
Enphase M175 inverter. My preferred 36 cell modules are a little too big on 
amperage to work well in pairs with the Enphase 175. If anyone has a surplus 
batch or used batch of Enphase appropriate modules with 72 cell count, 
contact me off list for a possible cash sale.

Mick Abraham, Proprietor 
www.abrahamsolar.com 
Voice: 970-731-4675

-- Original Message ---
From: Allan Sindelar [EMAIL PROTECTED] 
To: 'RE-wrenches' re-wrenches@lists.re-wrenches.org 
Sent: Wed, 10 Dec 2008 13:16:26 -0700 
Subject: [RE-wrenches] Module Voltage Question for Off-Grid Designers

 Wrenches,
 Here's an issue I haven't seen directly addressed, and I would like to know 
 what the rest of you are doing.
 It's getting harder to get 24V nominal modules. Because the bulk of industry 
 growth is high-voltage grid-tied applications, modules no longer have to be a 
 standard voltage. Just pick the number of modules to best fit the chosen 
 inverter's string voltage range.
 But for off-grid, the odd cell counts and resulting nontraditional DC input 
 voltages challenge the traditional rules of off-grid design. I may be 
 fighting a losing battle here, as the industry changes so rapidly and 
 fundamentally. I have been trying to stay with 72-cell modules for offgrid, 
 as this most readily combines with existing systems with 36-cell modules 
 (12V) and 72-cell modules (24V). 
 For example, I will use the new Canadian Solar 170-200W modules. They are 
 60-cell modules, with a Vmppt of around 28 volts - too low to charge 24V 
 batteries with a standard charge controller. We can use them in any new 
 systems with an MX60 or similar voltage-converting MPPT controller. Two or 
 three in series would charge a 24V battery; 3 in series would charge 48V. 
 Four in series would violate Code, as low-temp voltage would easily exceed 
 150V. 
 Unless 60-cell modules remain a standard in the future, any future array 
 additions would have to be on their own charge controller, in order to match 
 a different I-V curve and MPP voltages into the same battery bank. Is this 
 prohibitive? No, it just runs counter to the longstanding standards of 
 off-grid design that allow modules to be added in the future: these modules 
 will not add well to existing systems, and will not easily allow additional 
 dissimilar modules to be added later. 
 I had this same objection to using Day4 modules, although they were better at 
 16Vnom. Three made up a standard 48V array, so strings could be combined with 
 two-module strings of similar 24Vnom modules.
 Who else is trying to stay with 24V modules? Anyone still using 12V modules 
 in off-grid (residential-scale, not little apps) designs? Who has a crystal 
 ball and knows what modules will be like in 20 years, or even two years? Wat 
 are the rest of you doing?
 Thanks, as usual.
 Allan
 Allan Sindelar
 allan_(at)_positiveenergysolar.com
 NABCEP certified solar PV installer
 Positive Energy, Inc.
 3225A Richards Lane
 Santa Fe NM 87507
 505 424-1112
--- End of Original Message ---
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Module Voltage Question for Off-Grid Designers

2008-12-10 Thread Starlight Solar, Yuma, AZ

Allan,

Because many MPPT controllers convert to any battery voltage, new  
installations allow you to use just about any solar module. When I  
install any higher voltage module on RV's (12 volt battery), I design  
series strings up to the max design voltage to minimize voltage drop.  
No more 6 gauge wire runs. Now I can install Sanyo's or even Kaneka's  
and charge 12 volt batteries with up to 97% conversion efficiency.


If you are trying to add to an existing array it may be harder to  
match up your Vmp for parallel strings. I would not be worried about a  
few volts. The voltages will average out somewhere in the middle. For  
instance, I have customers in Mexico that have very old systems (think  
Arco). They want to keep the PV modules they have and add more while  
upgrading to MPPT. I have done this by re-stringing the old modules in  
series and try to get close to the published Vmp of the new modules.  
Some power will be lost in this parallel setup as it is difficult to  
estimate the Vmp of a 20 year old module. I have done this for several  
customers and so far it has worked well.


Kindest Regards,

Larry Crutcher
Starlight Solar
11279 S. Glenwood Ave #4
Yuma, AZ 85367
(928) 941-1660

[EMAIL PROTECTED]
www.starlightsolar.com

Retail Store: 2998 Shari, Yuma, AZ

Renewable Energy Products, Service and Installation





On Dec 10, 2008, at 1:16 PM, Allan Sindelar wrote:


Wrenches,
Here's an issue I haven't seen directly addressed, and I would like  
to know what the rest of you are doing.
It's getting harder to get 24V nominal modules. Because the bulk of  
industry growth is high-voltage grid-tied applications, modules no  
longer have to be a standard voltage. Just pick the number of  
modules to best fit the chosen inverter's string voltage range.


But for off-grid, the odd cell counts and resulting nontraditional  
DC input voltages challenge the traditional rules of off-grid  
design. I may be fighting a losing battle here, as the industry  
changes so rapidly and fundamentally. I have been trying to stay  
with 72-cell modules for offgrid, as this most readily combines with  
existing systems with 36-cell modules (12V) and 72-cell modules (24V).


For example, I will use the new Canadian Solar 170-200W modules.  
They are 60-cell modules, with a Vmppt of around 28 volts - too low  
to charge 24V batteries with a standard charge controller. We can  
use them in any new systems with an MX60 or similar voltage- 
converting MPPT controller. Two or three in series would charge a  
24V battery; 3 in series would charge 48V. Four in series would  
violate Code, as low-temp voltage would easily exceed 150V.


Unless 60-cell modules remain a standard in the future, any future  
array additions would have to be on their own charge controller, in  
order to match a different I-V curve and MPP voltages into the same  
battery bank. Is this prohibitive? No, it just runs counter to the  
longstanding standards of off-grid design that allow modules to be  
added in the future: these modules will not add well to existing  
systems, and will not easily allow additional dissimilar modules to  
be added later.


I had this same objection to using Day4 modules, although they were  
better at 16Vnom. Three made up a standard 48V array, so strings  
could be combined with two-module strings of similar 24Vnom modules.


Who else is trying to stay with 24V modules? Anyone still using 12V  
modules in off-grid (residential-scale, not little apps) designs?  
Who has a crystal ball and knows what modules will be like in 20  
years, or even two years? Wat are the rest of you doing?


Thanks, as usual.
Allan
Allan Sindelar
allan_(at)_positiveenergysolar.com
NABCEP certified solar PV installer
Positive Energy, Inc.
3225A Richards Lane
Santa Fe NM 87507
505 424-1112




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Module Voltage Question for Off-Grid Designers

2008-12-10 Thread Matt Tritt
My favorite is the Sharp 175 for off-grid and solar pumping 
applications; a sturdy, well built and consistent module for most 
applications. You can even get them fairly often!


Matt T

Kirpal Khalsa wrote:

Allen..Greetingsyes indeed it is an issue. we have been addressing 
with multiple charge controllers per system. we don't fight the 
current (not electrical).  In the future the way i see it- the 
electronics will be more flexible and be able to handle the larger 
variety of string voltages.  For example the long long long awaited 
apollo solar t100 which will allow voltages to exceed the 150V limit 
we have had for a long time.  They have apparently even lined up some 
breakers which will work with these greater voltages.  3 modules in a 
series will no longer be a maximum.  I understand midnite solar also 
has a charge controller which will allow the 150V max to go by the way 
side.  We are trying to be flexible as modules become less standard 
and hope that the electronics will allow us to address thesee 
challanges as time goes by.


One thing that we would love to see is more large wattage modules with 
j boxes rather than pre-wired MC cables.  In many of our off grid 
systems the array is located in readily accesible locations and 
crafting a fence or sticking the array over 8 feet of the ground is a 
big hassle/extra expense.  This has proven to be a bigger concern for 
us rahter than the voltage variety.  If you know of any 72 cell or for 
that matter 60 cell modules  which allow flex conduit between j boxes 
we would love some info...



--
Sunny Regards,
Kirpal Khalsa
NABCEP Certified Solar PV Installer
Renewable Energy Systems LLC


On Wed, Dec 10, 2008 at 12:16 PM, Allan Sindelar 
[EMAIL PROTECTED] mailto:[EMAIL PROTECTED] 
wrote:


Wrenches,
Here's an issue I haven't seen directly addressed, and I would
like to know what the rest of you are doing.
It's getting harder to get 24V nominal modules. Because the bulk
of industry growth is high-voltage grid-tied applications, modules
no longer have to be a standard voltage. Just pick the number of
modules to best fit the chosen inverter's string voltage range.

But for off-grid, the odd cell counts and resulting
nontraditional DC input voltages challenge the traditional rules
of off-grid design. I may be fighting a losing battle here, as the
industry changes so rapidly and fundamentally. I have been trying
to stay with 72-cell modules for offgrid, as this most readily
combines with existing systems with 36-cell modules (12V) and
72-cell modules (24V).

For example, I will use the new Canadian Solar 170-200W modules.
They are 60-cell modules, with a Vmppt of around 28 volts - too
low to charge 24V batteries with a standard charge controller. We
can use them in any new systems with an MX60 or similar
voltage-converting MPPT controller. Two or three in series would
charge a 24V battery; 3 in series would charge 48V. Four in series
would violate Code, as low-temp voltage would easily exceed 150V.

Unless 60-cell modules remain a standard in the future, any future
array additions would have to be on their own charge controller,
in order to match a different I-V curve and MPP voltages into the
same battery bank. Is this prohibitive? No, it just runs counter
to the longstanding standards of off-grid design that allow
modules to be added in the future: these modules will not add well
to existing systems, and will not easily allow additional
dissimilar modules to be added later.

I had this same objection to using Day4 modules, although they
were better at 16Vnom. Three made up a standard 48V array, so
strings could be combined with two-module strings of similar
24Vnom modules.

Who else is trying to stay with 24V modules? Anyone still using
12V modules in off-grid (residential-scale, not little apps)
designs? Who has a crystal ball and knows what modules will be
like in 20 years, or even two years? Wat are the rest of you doing?

Thanks, as usual.
Allan
Allan Sindelar
_allan_(at)_positiveenergysolar.com_
mailto:[EMAIL PROTECTED]
NABCEP certified solar PV installer
Positive Energy, Inc.
3225A Richards Lane
Santa Fe NM 87507
505 424-1112






___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

 





Internal Virus Database is out of date.
Checked by AVG - 

[RE-wrenches] SS zip ties

2008-12-10 Thread jay peltz

Where do you get these SS zip ties.

I have seen them and think they would work in some applications.

thanks,

jay

peltz power
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] SDHW and High Mains Pressure

2008-12-10 Thread jay peltz

Hi Peter,

There are some hi end units that are really nice.

Takagi, Rennai  are the two that come to mind that are really  
amazing.  They have digital remote controlls and are are designed to  
mounted outside, which saves a lot of

interior space, cost of reworking the flue etc.

Jay

Peltz power
On Dec 7, 2008, at 3:22 PM, Peter Parrish wrote:

We are getting ready to install a SDHW system for a customer and we  
looked at a number of things regarding his current set up. I just  
posted a question about tankless heaters but I wanted this query to  
be a separate one. The customer’s mains water pressure is 88 psi on  
a Saturday afternoon and some time over the next 18 hours, the  
pressure went as high as 96 psi. I understand that 80 psi is the  
high end of the safe range in general and that 96 psi on a regular  
basis can/will damage valves and possibly trigger TP valves on  
water heaters.


At the recommendation of a plumber I know I looked into pressure  
reducers, specifically the Wilkins/Zurn line. All the Wilkins  
regulators produce zero pressure drop at zero flow. What good are  
these products in protecting plumbing systems from high mains  
pressures at night when pressures tend to be the highest and usage  
is at a minimum or even zero?


Are there products that will prevent system pressures from exceeding  
a set point (e.g. 60 psi) under any flow condition including zero?


- Peter
Peter T. Parrish, President
California Solar Engineering, Inc.
820 Cynthia Ave., Los Angeles, CA 90065
Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885
CA Lic. 854779, NABCEP Cert. 031806-26
[EMAIL PROTECTED]

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] solar hot water penetration flashing

2008-12-10 Thread Karl Schwingel
I use similar boots, and design the penetration so the insulation and 
wrap ( we use aluminum) nearly cover the whole boot by the time you're 
all done.  you're left with about 1/2 of boot showing all the way around. 


where can I get the coolie cap style brazed copper flashings?

karl

Todd Cory wrote:
I use accordion style rubber boots. These are typically attached to 
the roofing with a bead of silicone underneath and gasketed metal 
roofing screws on top. These are made for all kinds of metal roof 
penetrations and I have even seen them used for 6 metalbestos stove 
flues. One note of caution, the orange high temperature ones are (I 
think) rated only to 180 degrees F. so you want to make sure the SHW 
fluid never exceeds this. Also in time, like any rubber flashing on a 
roof the rubber will deteriorate from UV. I build a show shed over my 
system's plumbing which shades it so hopefully this will not be in 
issue in ~20 years.


Todd




troy Harvey wrote:
Any thoughts on how to flash a copper pipe roof penetration on a 
metal roof. The brazed copper flashing we typically use would cause 
corrosion with the steel roof I'm afraid. WHat have others used in 
this situation?


Troy Harvey
-
Heliocentric
801-453-9434
[EMAIL PROTECTED] mailto:[EMAIL PROTECTED]





___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

  


--
Karl Schwingel
NABCEP Certified Solar Thermal Installer
NorthWind Renewable Energy LLC

PO Box 723 Stevens Point, WI 54481
[EMAIL PROTECTED]
Cell: 715 209 0446
Fax : 715 952 4501


This e-mail message is confidential, is intended only for the named
recipient(s) above, and may contain information that is privileged or
exempt from disclosure under applicable law. If you have received this
message in error, or are not a named recipient(s), you are hereby notified
that any dissemination, distribution or copying of this e-mail is strictly
prohibited. If you have received this message in error, please immediately
notify the sender by return e-mail and delete this e-mail message from
your computer. Thank you.

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] SS zip ties

2008-12-10 Thread William Miller

Jay:


Waytekwire.com

William


At 04:15 PM 12/10/2008, you wrote:

Where do you get these SS zip ties.

I have seen them and think they would work in some applications.

thanks,

jay

peltz power
___



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] SS zip ties

2008-12-10 Thread William Miller

Kent:

To tighten:  1. Pull tie snug by hand.  2. Cut tail about 20 mm from 
clasp.  3. Roll tail with needle-nose pliers, like a sardine can lid.  This 
tightens tie and hides sharp end.


See 
http://mpandc.com/practices/Technical_Procedures/PV_wiring/PV_wiring.html 
for photos.


Do not over-tighten to avoid wire damage.

William


At 09:25 PM 12/10/2008, you wrote:

Fastenal has stainless ties is various lengths

http://www.fastenal.com/web/products/detail.ex?sku=0710242

For those that haven't used these before, beware that it is difficult to 
tighten them.


Kent Osterberg
Blue Mountain Solar



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org