[RE-wrenches] Magnum MS4448AE Compatibility Question

2009-02-09 Thread Allan Sindelar
Wrenches,
We have an unusual problem, and I need to know if anyone else has had this
or a related problem, and what to do about it.
This concerns a new off-grid residential system, very conventional: 1,800W
PV, Midnite E-Panel with Magnum MS4448-AE inverter, MX60, 16 S-460s,
installed summer 2008. This existing home is being extensively remodeled,
and the home is not yet occupied. A local mechanical contractor installed a
new infloor radiant (gypcrete) hydronic heating system using a
Netherlands-made (German company) Buderus GB142 high-efficiency boiler. The
problem is that the boiler won't start reliably on the inverter. It appears
that the hot-surface igniter does not get full AC voltage (it runs on
straight 120V AC, but is supplied through the boiler's control circuitry).
We tested the igniter by disconnecting it and plugging it straight into
inverter AC and it lit right up. 
The mechanical contractor has tried a replacement Buderus GB142 boiler with
the same result. I was told that they brought out a generator and it also
failed to ignite on generator AC, but not knowing the generator used or the
way it was wired (I believe an extension cord to a portable) I don't put
much weight on this data. They also took a Lochinvar Boiler to the site to
test the theory that a different manufacturer's boiler might work. The
Lochinvar boiler, which uses a different control and a spark ignition rather
than a hot surface igniter, worked on site without any problems.
I'm looking for solutions. Magnum tech support had not heard of this. Have
you? 
Also, if indeed we have an inverter that is incapable of running this load,
how do we make it right to the homeowner and the mechanical contractor? What
should be Magnum's obligation? What should be ours? This issue hasn't come
up here since the days when the Trace SW mod-sine series was the waveform
standard.
Thanks,
Allan Sindelar
allan_(at)_positiveenergysolar.com mailto:al...@positiveenergysolar.com 
NABCEP certified solar PV installer
Positive Energy, Inc.
3225A Richards Lane
Santa Fe NM 87507
505 424-1112

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Magnum MS4448AE Compatibility Question

2009-02-09 Thread Dana
I have hit this one a couple of times but not with the equipment you are
listing. It turned out to be how the sine wave crossed the X axis and the
controls did not like the wave form.

 

Thanks -

 

Dana Orzel

 

Great Solar Works, Inc

www.solarwork.com

E - d...@solarwork.com

V - 970.626.5253

F - 970.626.4140

C - 970.209.4076

I'd put my money on solar energy. I hope we don't have to wait 'til oil and
coal run out before we tackle that.

-Thomas Edison, in conversation with Henry Ford and Harvey Firestone, March
1931

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Allan
Sindelar
Sent: Monday, February 09, 2009 11:16 AM
To: RE Wrenches
Subject: [RE-wrenches] Magnum MS4448AE Compatibility Question

 

Wrenches, 
We have an unusual problem, and I need to know if anyone else has had this
or a related problem, and what to do about it.

This concerns a new off-grid residential system, very conventional: 1,800W
PV, Midnite E-Panel with Magnum MS4448-AE inverter, MX60, 16 S-460s,
installed summer 2008. This existing home is being extensively remodeled,
and the home is not yet occupied. A local mechanical contractor installed a
new infloor radiant (gypcrete) hydronic heating system using a
Netherlands-made (German company) Buderus GB142 high-efficiency boiler. The
problem is that the boiler won't start reliably on the inverter. It appears
that the hot-surface igniter does not get full AC voltage (it runs on
straight 120V AC, but is supplied through the boiler's control circuitry).
We tested the igniter by disconnecting it and plugging it straight into
inverter AC and it lit right up. 

The mechanical contractor has tried a replacement Buderus GB142 boiler with
the same result. I was told that they brought out a generator and it also
failed to ignite on generator AC, but not knowing the generator used or the
way it was wired (I believe an extension cord to a portable) I don't put
much weight on this data. They also took a Lochinvar Boiler to the site to
test the theory that a different manufacturer's boiler might work. The
Lochinvar boiler, which uses a different control and a spark ignition rather
than a hot surface igniter, worked on site without any problems.

I'm looking for solutions. Magnum tech support had not heard of this. Have
you? 
Also, if indeed we have an inverter that is incapable of running this load,
how do we make it right to the homeowner and the mechanical contractor? What
should be Magnum's obligation? What should be ours? This issue hasn't come
up here since the days when the Trace SW mod-sine series was the waveform
standard.

Thanks, 
Allan Sindelar 
 mailto:al...@positiveenergysolar.com allan_(at)_positiveenergysolar.com 
NABCEP certified solar PV installer 
Positive Energy, Inc. 
3225A Richards Lane 
Santa Fe NM 87507 
505 424-1112 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Magnum MS4448AE Compatibility Question

2009-02-09 Thread John Raynes
I second Dana's response.  I have observed that the MS4448 waveform 
quality degenerates quite rapidly with imbalanced loading of one or 
the other of the 120 volt output legs.  I can't give a quantitative 
(% distortion/amps) number to it, but I would classify it as 
severe.  I first noticed it when doing some test measurements in the 
shop, and found large discrepancies between various current metering 
devices I was using, as some of the meters were not measuring RMS, 
and the distortion was throwing them way off.  And when using 120 
volt motors, even though their surge may be well within specified 
load limits, count on things not going well.


I'm generally satisfied with the Magnum MS4448, but this is one the 
two key shortcomings that I see with the product.  The other is the 
idle power draw when not in search.


John Raynes
RE Solar
Torrey, UT


At 11:16 AM 2/9/2009, you wrote:


Wrenches,
We have an unusual problem, and I need to know if anyone else has 
had this or a related problem, and what to do about it.


This concerns a new off-grid residential system, very conventional: 
1,800W PV, Midnite E-Panel with Magnum MS4448-AE inverter, MX60, 16 
S-460s, installed summer 2008. This existing home is being 
extensively remodeled, and the home is not yet occupied. A local 
mechanical contractor installed a new infloor radiant (gypcrete) 
hydronic heating system using a Netherlands-made (German company) 
Buderus GB142 high-efficiency boiler. The problem is that the boiler 
won't start reliably on the inverter. It appears that the 
hot-surface igniter does not get full AC voltage (it runs on 
straight 120V AC, but is supplied through the boiler's control 
circuitry). We tested the igniter by disconnecting it and plugging 
it straight into inverter AC and it lit right up.


The mechanical contractor has tried a replacement Buderus GB142 
boiler with the same result. I was told that they brought out a 
generator and it also failed to ignite on generator AC, but not 
knowing the generator used or the way it was wired (I believe an 
extension cord to a portable) I don't put much weight on this data. 
They also took a Lochinvar Boiler to the site to test the theory 
that a different manufacturer's boiler might work. The Lochinvar 
boiler, which uses a different control and a spark ignition rather 
than a hot surface igniter, worked on site without any problems.


I'm looking for solutions. Magnum tech support had not heard of 
this. Have you?
Also, if indeed we have an inverter that is incapable of running 
this load, how do we make it right to the homeowner and the 
mechanical contractor? What should be Magnum's obligation? What 
should be ours? This issue hasn't come up here since the days when 
the Trace SW mod-sine series was the waveform standard.


Thanks,
Allan Sindelar
mailto:al...@positiveenergysolar.comallan_(at)_positiveenergysolar.com
NABCEP certified solar PV installer
Positive Energy, Inc.
3225A Richards Lane
Santa Fe NM 87507
505 424-1112
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org


List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Xantrex GT remote display issues

2009-02-09 Thread ryan

I have a customed with a Xantrex gt inverter and the remote wired display he 
has repetetive problems of the display losing or dumping the Monthly and Yearly 
history.

It will go random lengths of time between losing this data sometimes 2 months 
sometime 1 month it varys. the remote was replaced once for this problem and 
the inverter has been replaced for a failure to wake up.

Any thoughts before i wait on hold with Xantrex?___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Xantrex GT remote display issues

2009-02-09 Thread Jason Lombard
I had this same issue about 2 years ago in CA. Xantrex replaced the
inverter.

On Mon, Feb 9, 2009 at 12:55 PM, r...@solar4maine.com wrote:


  I have a customed with a Xantrex gt inverter and the remote wired display
 he has repetetive problems of the display losing or dumping the Monthly and
 Yearly history.

 It will go random lengths of time between losing this data sometimes 2
 months sometime 1 month it varys. the remote was replaced once for this
 problem and the inverter has been replaced for a failure to wake up.

 Any thoughts before i wait on hold with Xantrex?

 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org





-- 
Jason Lombard
Open Hand Solar LLC.
Certified Sustainable Building Adviser
www.openhandsolar.com
505 795 8646

I'd put my money on solar energy… I hope we don't have to wait 'til oil and
coal run out before we tackle that.

—Thomas Edison
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] St Croix

2009-02-09 Thread Dana
Any random brown spots on the trace lines intersections? [on the back
encapsulate]

 

Thanks -

 

Dana Orzel

 

Great Solar Works, Inc

www.solarwork.com

E - d...@solarwork.com

V - 970.626.5253

F - 970.626.4140

C - 970.209.4076

I'd put my money on solar energy. I hope we don't have to wait 'til oil and
coal run out before we tackle that.

-Thomas Edison, in conversation with Henry Ford and Harvey Firestone, March
1931

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jason
Lombard
Sent: Monday, February 09, 2009 1:37 PM
To: RE-wrenches
Subject: [RE-wrenches] Interesting question

 

This is from an installer in St Croix about and issue he had. Any thoughts?

I have a client w/ an older solar array. They are at least
as old as 1991, and I installed 1 new panel and new SW4048 and L-16 bats in
Jan 2000. The 24 modules are Solarex SX 110 but they have a 2.1 Isc and
they measure 17.5 x 42  each  I believe they are @ 35W each.  They are
wired 4 modules  in series , 6panels@ 48V nom.  w/ 2 panels parallel in J
box on roof w/no fuse, or diode.  3 pos 

power leads go down to SQ D fused Disconnect (3, 10A FLNR fuses).  

After opening PV disconnect at array site,  and measuring Voc on each input
terminal (@ 75Voc each) I measured Isc . I got 3.9 on West, 1.9 in middle,
and 3.9 on east. After I had finished w/this measure, I Heard a loud pop,
and when we inspected array found 1 panel w/cracked glass and an electrical
blow out on underneath on back sheet of module. 

This was the East panel, and measuring Isc on all again, got 3.9 West, 1.9
Mid, and 1.9 Isc East. 

I did not wire the array, though I did rewire the j box w.new busses.
Interestingly, each 48 V panel has 2 Pos wires, each measuring 75 Voc .;
i.e. each output circuit (to 10A fuse) has 4 Pos wires coming into it.
Though I did not confirm w/isc test, I imagine that 2 wires were used for
Pos on each 48 V panel. There are also a total of 4 -ve wires for ea panel
as well, all -ve on 1 buss.

All panels were in direct sun when this blowout event occurred.  Also, all
modules had severe darkening of cells.

Care to  comment on this, what happened and why?



-- 
Jason Lombard
Open Hand Solar LLC.
Certified Sustainable Building Adviser
www.openhandsolar.com
505 795 8646

I'd put my money on solar energy. I hope we don't have to wait 'til oil and
coal run out before we tackle that.

-Thomas Edison

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Point of connection

2009-02-09 Thread Keith Cronin
Hello

With the growth of the solar industry coupled with the generous incentives now 
offered on fed part of the equation, we are seeing some trends here and 
wondering what the approach has been in other areas. What kind of feedback are 
you receiving from the AHJ?

There are some integrators who now are installing systems meaning, multiple 
small inverters that are married to smaller arrays as opposed to one large 
array with one large inverter. 

So, it is quite conceivable to have, for example, 3- 3000 W SMA inverters on a 
customers home. So, the point of connection issues arise. When you look at 
690.64B, it speaks to the 120% of the busbar rating.

What are folks doing in other areas, for this above example to address the 
mechanical/electrical challenges associated with this situation, when if you 
had 1- 200 amp residential service? There is alot of discussion, like 
installing a 125 amp rated subpanel; interuppting the feeder from the electric 
service and installing a 225 amp panel with a higher rated buss (hard to find 
or custom made thru Cutler Hammer or others) etc.

We can also see a trend using the enphase products as well, but not as much 
pronounced. It could be conceivable for a client to want to build their system 
up over a few years and have 15, 175 watt panels on a circuit (2P15 amp) and 
grow the system up to lets say, 45, 175 watt panels (3-2P15 amp). Same 
situation, different inverter manufacturer. My sense is this trend will 
continue for the forseeable future, and alot of wrenches will find orphaned 
systems out there and we should look at ways to address point of connection 
issues that are bound to present themselves.

Thanks

Keith



  ___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] On demand Electric with pre heated water

2009-02-09 Thread Karl Schwingel

Hi Wrenches,

Have any of you experience with on demand electric water heaters?  I 
have a large space heating system I'm putting in a cramped utility room, 
and the on demand water heater might be the only option.  family of 4, 3 
bath house.  marathon 105 gal  solar storage tank. 

I'm looking for any information or suggestions on which if any electric 
on demand heater will manage pre heated water.  The other option is to 
use a marathon 40 gal backup and use a variable speed well pump, and 
therefore a tiny pressure tank. (#15)

that'd be my preferred, but I want to give the customer options.

thanks in advance,
karl

--
Karl Schwingel
NABCEP Certified Solar Thermal Installer
NorthWind Renewable Energy LLC

PO Box 723 Stevens Point, WI 54481
k...@northwindre.com
Cell: 715 209 0446
Fax : 715 952 4501


This e-mail message is confidential, is intended only for the named
recipient(s) above, and may contain information that is privileged or
exempt from disclosure under applicable law. If you have received this
message in error, or are not a named recipient(s), you are hereby notified
that any dissemination, distribution or copying of this e-mail is strictly
prohibited. If you have received this message in error, please immediately
notify the sender by return e-mail and delete this e-mail message from
your computer. Thank you.


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] On demand Electric with pre heated water

2009-02-09 Thread wlbryce
Hi karl

We are trying a HeatPump heater as backup for a solar hotwater system.
Trying to get away from propane.

http://www.airgenerate.com/products/specs.html

http://www.toolbase.org/TechInventory/TechManufacturers.aspx?ContentDetailID=862

Time will tell it it works.

Logan


 Hi Wrenches,

 Have any of you experience with on demand electric water heaters?  I
 have a large space heating system I'm putting in a cramped utility room,
 and the on demand water heater might be the only option.  family of 4, 3
 bath house.  marathon 105 gal  solar storage tank.

 I'm looking for any information or suggestions on which if any electric
 on demand heater will manage pre heated water.  The other option is to
 use a marathon 40 gal backup and use a variable speed well pump, and
 therefore a tiny pressure tank. (#15)
 that'd be my preferred, but I want to give the customer options.

 thanks in advance,
 karl

 --
 Karl Schwingel
 NABCEP Certified Solar Thermal Installer
 NorthWind Renewable Energy LLC

 PO Box 723 Stevens Point, WI 54481
 k...@northwindre.com
 Cell: 715 209 0446
 Fax : 715 952 4501


 This e-mail message is confidential, is intended only for the named
 recipient(s) above, and may contain information that is privileged or
 exempt from disclosure under applicable law. If you have received this
 message in error, or are not a named recipient(s), you are hereby notified
 that any dissemination, distribution or copying of this e-mail is strictly
 prohibited. If you have received this message in error, please immediately
 notify the sender by return e-mail and delete this e-mail message from
 your computer. Thank you.


 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Magnum MS4448AE Compatibility Question

2009-02-09 Thread robert ellison
I wonder if a work around might be to run the igniter off a relay activated
by the original board and fed by the inverter direct?

I have seen things not start when the charger was drawing off the generator,
not Magnums but old Hearts.

Bob

On Mon, Feb 9, 2009 at 1:16 PM, Allan Sindelar 
al...@positiveenergysolar.com wrote:

  Wrenches,
 We have an unusual problem, and I need to know if anyone else has had this
 or a related problem, and what to do about it.

 This concerns a new off-grid residential system, very conventional: 1,800W
 PV, Midnite E-Panel with Magnum MS4448-AE inverter, MX60, 16 S-460s,
 installed summer 2008. This existing home is being extensively remodeled,
 and the home is not yet occupied. A local mechanical contractor installed a
 new infloor radiant (gypcrete) hydronic heating system using a
 Netherlands-made (German company) Buderus GB142 high-efficiency boiler. The
 problem is that the boiler won't start reliably on the inverter. It appears
 that the hot-surface igniter does not get full AC voltage (it runs on
 straight 120V AC, but is supplied through the boiler's control circuitry).
 We tested the igniter by disconnecting it and plugging it straight into
 inverter AC and it lit right up.

 The mechanical contractor has tried a replacement Buderus GB142 boiler with
 the same result. I was told that they brought out a generator and it also
 failed to ignite on generator AC, but not knowing the generator used or the
 way it was wired (I believe an extension cord to a portable) I don't put
 much weight on this data. They also took a Lochinvar Boiler to the site to
 test the theory that a different manufacturer's boiler might work. The
 Lochinvar boiler, which uses a different control and a spark ignition rather
 than a hot surface igniter, worked on site without any problems.

 I'm looking for solutions. Magnum tech support had not heard of this. Have
 you?
 Also, if indeed we have an inverter that is incapable of running this load,
 how do we make it right to the homeowner and the mechanical contractor? What
 should be Magnum's obligation? What should be ours? This issue hasn't come
 up here since the days when the Trace SW mod-sine series was the waveform
 standard.

 Thanks,
 Allan Sindelar
 ***allan_(at)_positiveenergysolar.com* al...@positiveenergysolar.com
 NABCEP certified solar PV installer
 Positive Energy, Inc.
 3225A Richards Lane
 Santa Fe NM 87507
 505 424-1112

 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] On demand Electric with pre heated water

2009-02-09 Thread Kurt Albershardt

On 2/9/09 12:24 PM, Karl Schwingel wrote:

Have any of you experience with on demand electric water heaters?
At the recommendation of someone on this list a few years back, we 
purchased a Stiebel-Eltron Tempra 36 for a project.  It seems quite 
happy with preheated water and is nicely engineered.






___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Heat pump water heaters (was: On demand Electric with pre heated water)

2009-02-09 Thread Kurt Albershardt

On 2/9/09 3:36 PM, wlbr...@pineridgeproducts.com wrote:

We are trying a HeatPump heater as backup for a solar hotwater system.
Trying to get away from propane.

http://www.airgenerate.com/products/specs.html
   
If that 7,000 BTU/hr rating is correct, it equates to 2kW of resistance 
heat, which is typical of under the sink bathroom applications in 
restaurants and gas stations.  Might work as makeup heat if you have a 
large enough tank.  The Stiebel-Eltron unit we used draws 36 kW (!)


The COP of compressor-driven heat pumps drops as output temperature 
increases (which is why they make such a nice pairing with radiant floor 
heat.)  Even at the lower COP that a 120-140F hot side produces, it 
would be a huge win in the southwest deserts if it pulled that heat from 
the interior air.  Remember that in the winter, you are stealing heat 
from the house to heat that water.   If you put the evaporater outside 
like Solahart does, you are then pulling heat from the outside in 
winter, which is harder work.  Ideally, you'd want a vented box that 
could use either inside or outside air depending on the season.


Better yet, find a source of waste heat like refrigeration or 
dehydration.  We are working on a commercial project where we will 
recover heat from the kitchen refrigeration systems (12-14 compressors 
overall) to heat domestic water.  I'd love to see this applied on a 
residential scale.






___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Magnum MS4448AE Compatibility Question

2009-02-09 Thread Ezra Auerbach
Have you tried a different SW inverter at the site? There is a  
difference between brands.


Also, have you tried a clean wave form gennie like the Honda  
inverter series.


Finally I don't think that most manufacturers will guarantee that  
their wave form will power a specific load.


Regards,

Ezra Auerbach



On 9-Feb-09, at 4:18 PM, robert ellison reelli...@gmail.com wrote:

I wonder if a work around might be to run the igniter off a relay  
activated by the original board and fed by the inverter direct?


I have seen things not start when the charger was drawing off the  
generator, not Magnums but old Hearts.


Bob

On Mon, Feb 9, 2009 at 1:16 PM, Allan Sindelar al...@positiveenergysolar.com 
 wrote:

Wrenches,
We have an unusual problem, and I need to know if anyone else has  
had this or a related problem, and what to do about it.


This concerns a new off-grid residential system, very conventional:  
1,800W PV, Midnite E-Panel with Magnum MS4448-AE inverter, MX60, 16  
S-460s, installed summer 2008. This existing home is being  
extensively remodeled, and the home is not yet occupied. A local  
mechanical contractor installed a new infloor radiant (gypcrete)  
hydronic heating system using a Netherlands-made (German company)  
Buderus GB142 high-efficiency boiler. The problem is that the boiler  
won't start reliably on the inverter. It appears that the hot- 
surface igniter does not get full AC voltage (it runs on straight  
120V AC, but is supplied through the boiler's control circuitry). We  
tested the igniter by disconnecting it and plugging it straight into  
inverter AC and it lit right up.


The mechanical contractor has tried a replacement Buderus GB142  
boiler with the same result. I was told that they brought out a  
generator and it also failed to ignite on generator AC, but not  
knowing the generator used or the way it was wired (I believe an  
extension cord to a portable) I don't put much weight on this data.  
They also took a Lochinvar Boiler to the site to test the theory  
that a different manufacturer's boiler might work. The Lochinvar  
boiler, which uses a different control and a spark ignition rather  
than a hot surface igniter, worked on site without any problems.


I'm looking for solutions. Magnum tech support had not heard of  
this. Have you?
Also, if indeed we have an inverter that is incapable of running  
this load, how do we make it right to the homeowner and the  
mechanical contractor? What should be Magnum's obligation? What  
should be ours? This issue hasn't come up here since the days when  
the Trace SW mod-sine series was the waveform standard.


Thanks,
Allan Sindelar
allan_(at)_positiveenergysolar.com
NABCEP certified solar PV installer
Positive Energy, Inc.
3225A Richards Lane
Santa Fe NM 87507
505 424-1112


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Cost per kW of a 2 mega watt installation

2009-02-09 Thread tump
Can anyone out there give me this info or have a site that I can get these 
figures. How about the area required for a project of this size?  Thanks in 
advance. Tump
Sent via BlackBerry by ATT
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Point of connection

2009-02-09 Thread William Miller

Keith:

No matter how you slice it, every breaker panel and every conductor in the 
feeder from the inverter to the meter must meet the 120% rule.  You can not 
dedicate one panel as an AC Combiner and exceed the 120% rating on that 
panel only.  It does not matter if the source is one inverter or 10 
inverters.  You either meet the 120% requirement from section (B) or you 
supply a supply side tap as allowed in (A).


William Miller


At 02:40 PM 2/9/2009, you wrote:

Hello

With the growth of the solar industry coupled with the generous incentives 
now offered on fed part of the equation, we are seeing some trends here 
and wondering what the approach has been in other areas. What kind of 
feedback are you receiving from the AHJ?


There are some integrators who now are installing systems meaning, 
multiple small inverters that are married to smaller arrays as opposed to 
one large array with one large inverter.


So, it is quite conceivable to have, for example, 3- 3000 W SMA inverters 
on a customers home. So, the point of connection issues arise. When you 
look at 690.64B, it speaks to the 120% of the busbar rating.


What are folks doing in other areas, for this above example to address the 
mechanical/electrical challenges associated with this situation, when if 
you had 1- 200 amp residential service? There is alot of discussion, like 
installing a 125 amp rated subpanel; interuppting the feeder from the 
electric service and installing a 225 amp panel with a higher rated buss 
(hard to find or custom made thru Cutler Hammer or others) etc.


We can also see a trend using the enphase products as well, but not as 
much pronounced. It could be conceivable for a client to want to build 
their system up over a few years and have 15, 175 watt panels on a circuit 
(2P15 amp) and grow the system up to lets say, 45, 175 watt panels (3-2P15 
amp). Same situation, different inverter manufacturer. My sense is this 
trend will continue for the forseeable future, and alot of wrenches will 
find orphaned systems out there and we should look at ways to address 
point of connection issues that are bound to present themselves.


Thanks

Keith


Please note new e-mail address and domain:

William Miller
Miller Solar
Voice :805-438-5600 Fax: 805-438-4607
email: will...@millersolar.com
http://millersolar.com
License No. C-10-773985
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Magnum MS4448AE Compatibility Question

2009-02-09 Thread David Katz

Hi Allan,
This is not an unusual problem.  i have seen it with conventional forced 
air heating systems.  The burner controls would not run on A Xantrex or 
Outback sine wave inverter.  There is something about waveforms from 
inverters designed by Trace legacy engineers.  I had to put in Exeltech 
or Studer inverters to operate the heating control system.  you can do 
this and still run larger pumps and fans on the Magnum.

David

David Katz

President

AEE Solar

1155 Redway Drive

P.O. Box 339

Redway, CA  95560

Tel (707) 825-1200

Fax (707) 825-1202

da...@aeesolar.com mailto:da...@aeesolar.com

www.aeesolar.com http://www.aeesolar.com



DISCLAIMER:
This communication, along with any documents, files or attachments, is 
intended for the use of only the addressee and contains privileged and 
confidential information. If you are not the intended recipient, you are 
hereby notified that any dissemination, distribution or copying of any 
information contained in or attached to this communication is strictly 
prohibited.  If you have received this message in error, please notify 
the sender immediately by e-mail reply and destroy the original 
communication and its attachments without reading, printing or saving in 
any manner.


P  Please consider the environment before printing this e-mail.



Allan Sindelar wrote:

Wrenches,
We have an unusual problem, and I need to know if anyone else has had this
or a related problem, and what to do about it.
This concerns a new off-grid residential system, very conventional: 1,800W
PV, Midnite E-Panel with Magnum MS4448-AE inverter, MX60, 16 S-460s,
installed summer 2008. This existing home is being extensively remodeled,
and the home is not yet occupied. A local mechanical contractor installed a
new infloor radiant (gypcrete) hydronic heating system using a
Netherlands-made (German company) Buderus GB142 high-efficiency boiler. The
problem is that the boiler won't start reliably on the inverter. It appears
that the hot-surface igniter does not get full AC voltage (it runs on
straight 120V AC, but is supplied through the boiler's control circuitry).
We tested the igniter by disconnecting it and plugging it straight into
inverter AC and it lit right up. 
The mechanical contractor has tried a replacement Buderus GB142 boiler with

the same result. I was told that they brought out a generator and it also
failed to ignite on generator AC, but not knowing the generator used or the
way it was wired (I believe an extension cord to a portable) I don't put
much weight on this data. They also took a Lochinvar Boiler to the site to
test the theory that a different manufacturer's boiler might work. The
Lochinvar boiler, which uses a different control and a spark ignition rather
than a hot surface igniter, worked on site without any problems.
I'm looking for solutions. Magnum tech support had not heard of this. Have
you? 
Also, if indeed we have an inverter that is incapable of running this load,

how do we make it right to the homeowner and the mechanical contractor? What
should be Magnum's obligation? What should be ours? This issue hasn't come
up here since the days when the Trace SW mod-sine series was the waveform
standard.
Thanks,
Allan Sindelar
allan_(at)_positiveenergysolar.com mailto:al...@positiveenergysolar.com 
NABCEP certified solar PV installer

Positive Energy, Inc.
3225A Richards Lane
Santa Fe NM 87507
505 424-1112


  



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

  
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org