On Jan 8, 2010, at 9:39:59 PM, frenergy frene...@psln.com wrote:

Don,
 
        Seems the benefit of using % charge would go out the window if your 
batteries were sulphatedjust when you would need the voltage based/temp 
comp logic the most.  No experience with your proposal though.
 
Bill
Feather River Solar Electric


Thanks Bill,


Ken's approach is interesting. ---Use the Pentamatic for bulking and voltage 
control less frequently for completing the charge cycle. You are right that we 
need to pay attention to both AH and finish voltage.

Don
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Square D DC disconnects

2010-01-11 Thread Peter Parrish
Can someone recommend a PV integrator on Kona area of the Big Island? I have
a friend who is in the early stages of designing his retirement home and he
wants to incorporate PV into his design. He is leaning towards a standing
metal roof and Unisolar PV laminate and of course SDHW. Any help would be
much appreciated.



- Peter

 

 


 

Peter T. Parrish, Ph.D., President
California Solar Engineering, Inc.
820 Cynthia Ave., Los Angeles, CA 90065
CA Lic. 854779, NABCEP Cert. 031806-26
peter.parr...@calsolareng.com  
Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885


 

image001.gif___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Square D DC disconnects

2010-01-11 Thread Kirpal Khalsa
Thanks, Mr Brearley..i have looked into the Solar Bos disconncecting
combiners and also the Blue Oak..both look very well designed and we
look forward to using them when we have a project where it makes
sense.small and medium residential projects dont pencil out for us based
on the price of these productsI encouraged both companies to come up
with a smaller version which has a price more in line with the smaller sized
systems..
Luckily the latest inverters from most manufacturers take care of this need
with their included/integrated but seperated fused DC disconnects.
However seems to me that in the nearer future we need to be moving towards
having disconnects located as close as possible to the array..
My dream combiner for all you manufacturers out there would be similar to
the readywatt 3 or 4 circuit, fused,  rail mountable, combiner with
disconnect integrated
I am still pondering how square D could have overlooked this important
listing requirement..makes me wonder!?!?!?


-- 
Sunny Regards,
Kirpal Khalsa
NABCEP Certified Solar PV Installer
Renewable Energy Systems
www.oregonsolarworks.com
541-218-0201 m
541-592-3958 o

On Mon, Jan 11, 2010 at 11:41 AM, David Brearley 
david.brear...@solarprofessional.com wrote:

 (Unless, of course, you are working with a transformerless inverter and an
 ungrounded array, in which case both the positive and negative conductors
 would need to be switched, since both are ungrounded.)



 On 1/10/10 9:10 AM, Drake Chamberlin 
 drake.chamber...@redwoodalliance.org wrote:

   At 05:14 PM 1/9/2010, you wrote:

 I recently came across a revised technical bulletin from square D (
 http://ecatalog.squared.com/pubs/Electrical%20Distribution/Safety%20Switches/Heavy%20Duty/3110DB0401.pdf)..

 We would need to use method D with the three pole. Method C would break
 the negative, leaving it ungrounded.


 Drake Chamberlin
 Athens Electric
 OH License 44810
 CO License 3773
 NABCEP TM Certified PV Installer
 Office - 740-448-7328

 Mobile - 740-856-9648

 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Square D DC disconnects

2010-01-11 Thread William Miller

Kirpa:

Have you considered using the Outback PSPV combiner with the 600 VDC 
touch-safe fuse holders and appropriate fuses?  I belive this configuration 
meets the 600 VDC rating.


William Miller




At 12:08 PM 1/11/2010, you wrote:
Thanks, Mr Brearley..i have looked into the Solar Bos disconncecting 
combiners and also the Blue Oak..both look very well designed and we 
look forward to using them when we have a project where it makes 
sense.small and medium residential projects dont pencil out for us 
based on the price of these productsI encouraged both companies to 
come up with a smaller version which has a price more in line with the 
smaller sized systems..
Luckily the latest inverters from most manufacturers take care of this 
need with their included/integrated but seperated fused DC disconnects.
However seems to me that in the nearer future we need to be moving towards 
having disconnects located as close as possible to the array..
My dream combiner for all you manufacturers out there would be similar to 
the readywatt 3 or 4 circuit, fused,  rail mountable, combiner with 
disconnect integrated
I am still pondering how square D could have overlooked this important 
listing requirement..makes me wonder!?!?!?
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Square D DC disconnects

2010-01-11 Thread David Brearley
Thanks, Bill.

Glad to hear you think the HU series is still a good option.

When I was making the rounds at SPI, I stopped by the Eaton booth and got
the sense that they were gunning for Square D. They made light of Square D¹s
self-certification of the HU series discos. The rep also made a statement
about the new Eaton dc discos being the only ones designed to meet UL1741
requirements. When I got home, the first thing I looked up was 690.4(D).
This doesn¹t say anything about dc disconnects needing to be listed to some
special PV standard.

Is there a movement in this direction? Is there a UL1741 standard for dc
discos that is somehow different that the standard used for other dc
disconnects?

Best,

David 

On 1/11/10 5:28 PM, Bill Brooks billbroo...@yahoo.com wrote:

 David and Kirpal,
  
 It is ultimately up to the AHJ whether or not they accept the Schneider/Square
 D self certification. That is a judgment call the installer needs to clear
 with the AHJ. That being said, having Square D behind the rating of a switch
 is a whole lot more than any one of the smaller companies making equipment for
 the PV industry. 
  
 I will continue to use the 30, 60, and 100-amp versions in the way recommended
 by the manufacturer because it is a huge saving in cost and they are well made
 switches. I will also check with the local AHJ before installing them in case
 they are not going to pass it. You have to remember you are working with one
 of the largest electrical suppliers in the world. They have a huge reputation
 with local jurisdictions.
  
 Eaton has been in the process of trying to make a big deal out of this issue
 since they want a piece of the market. Fortunately, they are starting to build
 products specifically for the PV industry, which I applaud. However, they need
 to be given a hard time for the way they have tried to imply that all Square D
 switches are not properly listed. They won¹t admit to that because they would
 end up in a legal battle, but that is essentially what they have been doing.
 Square D still has the largest selection of dc-rated equipment on the market.
 Eaton has a long way to go.
  
 In a recent project that I reviewed, the engineer pulled the Square D 400-amp
 disconnect and replaced it with an Eaton disconnect at the insistence of the
 Eaton rep. The Eaton product was not properly rated or listed for the voltage
 while the Square D product was. This is the insanity that needs to stop.
  
 Bill.
  
  
 
 From: re-wrenches-boun...@lists.re-wrenches.org
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of David Brearley
 Sent: Monday, January 11, 2010 11:39 AM
 To: RE-wrenches
 Subject: Re: [RE-wrenches] Square D DC disconnects
  
 Kirpal,
 
 Have you checked out the SolarBOS disconnecting combiners? Their 28A version
 might be ideal for large resi or small commercial applications. For larger
 projects, Blue Oak PV Products and AMtec Solar also have disconnecting
 combiners.
 
 Thanks for sharing the updated Square D tech note. I had no idea that the
 Square D HU Series disconnects were not UL-listed when used as described in
 the older tech notes. The fact that this is not a UL-listed use of the heavy
 duty safety switch, pretty much means that it is not an option for
 integrators. As far as I know, there is no other product that is listed for
 this use. 
 
 David Brearley, Senior Technical Editor
 SolarPro magazine
 NABCEP Certified PV Installer 
 david.brear...@solarprofessional.com
 
 
 On 1/9/10 4:14 PM, Kirpal Khalsa solarwo...@gmail.com wrote:
 Hi All..
  
 I recently came across a revised technical bulletin from square D (
 http://ecatalog.squared.com/pubs/Electrical%20Distribution/Safety%20Switches/H
 eavy%20Duty/3110DB0401.pdf )..we have for years been using the Square D DC
 Disconnect of various amperages (30, 60, 100) as disconnects leading upto the
 inverter from the array.we have frequently wired one string to each of the
 three poles of the disconnect..we have had this configuration inspected by
 inspectors regularly with approval everytime..this new revision of the
 document from Square D shows this is no longer a UL listed method.they are
 now stating in this document that they are self certifying this
 technique...have any of you come across this or know why Square D has back
 tracked? 
  
 Something else I noticed is that they have raised the amperage rating on the
 30A disconncect per pole by 2 amps from 18 to 20 which is good especially when
 using higher amperage modules like Evergreen ES-A series which would not have
 ben allowed to use the 30A disconnect as the short circuit current rating was
 too high for the derated poles.
 
 This is not a huge concern as more and more of the inverters we are using
 these days have an appropriate disconnect included with the inverter negating
 the need for an additional stand alone disconnect.
  
 On a side noteAre there any other manufacturers making listed
 muiti 

Re: [RE-wrenches] DC disconnects

2010-01-11 Thread Rebecca Lundberg
In response to this: Luckily the latest inverters from most manufacturers
take care of this need with their included/integrated but seperated fused DC
disconnects.

I actually wish the integrated disconnects for the new inverters were an
option when purchasing, i.e. when I order the inverter it comes with it
automatically, and is therefore reflected in the price. Where I live the AHJ
and utlities are requiring the handled-lockable-'regular' AC and DC
disconnects regardless of whether or not there is a UL-listed integrated
disconnect with the inverter. Alas, for me it is redundancy and extra cost
for materials and electrical work either way. I can either have the
electrician wire it up and pay their cost, or I can leave the integrated
inverter out (when it is listed as optional in the installation manual) but
now I have a non-returnable part sitting around, which is wasteful too.
Alas, the best solution is more solar so everyone becomes more familiar with
it!

Keep Shining!
Rebecca Lundberg
Powerfully Green, Minnesota
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Square D DC disconnects

2010-01-11 Thread Kirpal Khalsa
William.we love the Outback FWPV12 and 8...a good improvement
over the PSPV..we use them high voltage apps, but alas..don't
open fuse under load.thats why we need a version which is
disconnectable..
Cheers,

-- 
Sunny Regards,
Kirpal Khalsa
NABCEP Certified Solar PV Installer
Renewable Energy Systems
www.oregonsolarworks.com
541-218-0201 m
541-592-3958 o


On Mon, Jan 11, 2010 at 12:16 PM, William Miller
will...@millersolar.com wrote:
 Kirpa:

 Have you considered using the Outback PSPV combiner with the 600 VDC
 touch-safe fuse holders and appropriate fuses?  I belive this configuration
 meets the 600 VDC rating.

 William Miller




 At 12:08 PM 1/11/2010, you wrote:

 Thanks, Mr Brearley..i have looked into the Solar Bos disconncecting
 combiners and also the Blue Oak..both look very well designed and we
 look forward to using them when we have a project where it makes
 sense.small and medium residential projects dont pencil out for us based
 on the price of these productsI encouraged both companies to come up
 with a smaller version which has a price more in line with the smaller sized
 systems..
 Luckily the latest inverters from most manufacturers take care of this need
 with their included/integrated but seperated fused DC disconnects.
 However seems to me that in the nearer future we need to be moving towards
 having disconnects located as close as possible to the array..
 My dream combiner for all you manufacturers out there would be similar to
 the readywatt 3 or 4 circuit, fused,  rail mountable, combiner with
 disconnect integrated
 I am still pondering how square D could have overlooked this important
 listing requirement..makes me wonder!?!?!?

 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Square D DC disconnects

2010-01-11 Thread Marv Dargatz
Title: Re: [RE-wrenches] Square D DC disconnects




The testing for the HU series switches was
performed by Square D according to a procedure that I wrote when
working with SMA. The procedure was reviewed and accepted by UL as
valid for the dedicated purpose of PV disconnect when used with the SMA
SB2500.
See ya!

Marv
707 763-4784  x7016



David Brearley wrote:

  
  Thanks, Bill.
  
Glad to hear you think the HU series is still a good option.
  
When I was making the rounds at SPI, I stopped by the Eaton booth and
got the sense that they were gunning for Square D. They made light of
Square Ds self-certification of the HU series discos. The rep also
made a statement about the new Eaton dc discos being the only ones
designed to meet UL1741 requirements. When I got home, the first thing
I looked up was 690.4(D). This doesnt say anything about dc
disconnects needing to be listed to some special PV standard. 
  
Is there a movement in this direction? Is there a UL1741 standard for
dc discos that is somehow different that the standard used for other dc
disconnects?
  
Best,
  
David 
  
On 1/11/10 5:28 PM, "Bill Brooks" billbroo...@yahoo.com wrote:
  
  
  David and Kirpal,

It is ultimately up to the AHJ whether or not they accept the
Schneider/Square D self certification. That is a judgment call the
installer needs to clear with the AHJ. That being said, having Square D
behind the rating of a switch is a whole lot more than any one of the
smaller companies making equipment for the PV industry. 

I will continue to use the 30, 60, and 100-amp versions in the way
recommended by the manufacturer because it is a huge saving in cost and
they are well made switches. I will also check with the local AHJ
before installing them in case they are not going to pass it. You have
to remember you are working with one of the largest electrical
suppliers in the world. They have a huge reputation with local
jurisdictions.

Eaton has been in the process of trying to make a big deal out of this
issue since they want a piece of the market. Fortunately, they are
starting to build products specifically for the PV industry, which I
applaud. However, they need to be given a hard time for the way they
have tried to imply that all Square D switches are not properly listed.
They wont admit to that because they would end up in a legal battle,
but that is essentially what they have been doing. Square D still has
the largest selection of dc-rated equipment on the market. Eaton has a
long way to go. 

In a recent project that I reviewed, the engineer pulled the Square D
400-amp disconnect and replaced it with an Eaton disconnect at the
insistence of the Eaton rep. The Eaton product was not properly rated
or listed for the voltage while the Square D product was. This is the
insanity that needs to stop.

Bill.



From:
re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org]
On Behalf Of David Brearley
Sent: Monday, January 11, 2010 11:39 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Square D DC disconnects
 
Kirpal,

Have you checked out the SolarBOS disconnecting combiners? Their 28A
version might be ideal for large resi or small commercial applications.
For larger projects, Blue Oak PV Products and AMtec Solar also have
disconnecting combiners.

Thanks for sharing the updated Square D tech note. I had no idea that
the Square D HU Series disconnects were not UL-listed when used as
described in the older tech notes. The fact that this is not a
UL-listed use of the heavy duty safety switch, pretty much means that
it is not an option for integrators. As far as I know, there is no
other product that is listed for this use. 

David Brearley, Senior Technical Editor
SolarPro magazine 
NABCEP Certified PV Installer 
david.brear...@solarprofessional.com


On 1/9/10 4:14 PM, "Kirpal Khalsa" solarwo...@gmail.com wrote:

Hi All..
  
 
I recently came across a revised technical bulletin from square D ( http://ecatalog.squared.com/pubs/Electrical%20Distribution/Safety%20Switches/Heavy%20Duty/3110DB0401.pdf
)..we have for years been using the Square D DC Disconnect of
various amperages (30, 60, 100) as disconnects leading upto the
inverter from the array.we have frequently wired one string to each
of the three poles of the disconnect..we have had this
configuration inspected by inspectors regularly with approval
everytime..this new revision of the document from Square D shows
this is no longer a UL listed method.they are now stating in this
document that they are "self certifying" this technique...have any
of you come across this or know why Square D has back tracked? 

Something else I noticed is that they have raised the amperage rating
on the 30A disconncect per pole by 2 amps from 18 to 20 which is good
especially when using higher amperage modules like Evergreen ES-A
series which would not have ben 

Re: [RE-wrenches] Square D DC disconnects

2010-01-11 Thread Kent Osterberg
Title: Re: [RE-wrenches] Square D DC disconnects




David,

The NEC doesn't require UL listing. The most appropriate section of
the code about this is Article 110, Requirements for Electrical
Installations, it requires equipment to be approved. In many
jurisdictions, such as Oregon, that means evaluated and approved by a
testing lab such as UL.

Kent Osterberg
Blue Mountain Solar, Inc.


David Brearley wrote:

  
  Thanks, Bill.
  
Glad to hear you think the HU series is still a good option.
  
When I was making the rounds at SPI, I stopped by the Eaton booth and
got the sense that they were gunning for Square D. They made light of
Square Ds self-certification of the HU series discos. The rep also
made a statement about the new Eaton dc discos being the only ones
designed to meet UL1741 requirements. When I got home, the first thing
I looked up was 690.4(D). This doesnt say anything about dc
disconnects needing to be listed to some special PV standard. 
  
Is there a movement in this direction? Is there a UL1741 standard for
dc discos that is somehow different that the standard used for other dc
disconnects?
  
Best,
  
David 
  
On 1/11/10 5:28 PM, "Bill Brooks" billbroo...@yahoo.com wrote:
  
  
  David and Kirpal,

It is ultimately up to the AHJ whether or not they accept the
Schneider/Square D self certification. That is a judgment call the
installer needs to clear with the AHJ. That being said, having Square D
behind the rating of a switch is a whole lot more than any one of the
smaller companies making equipment for the PV industry. 

I will continue to use the 30, 60, and 100-amp versions in the way
recommended by the manufacturer because it is a huge saving in cost and
they are well made switches. I will also check with the local AHJ
before installing them in case they are not going to pass it. You have
to remember you are working with one of the largest electrical
suppliers in the world. They have a huge reputation with local
jurisdictions.

Eaton has been in the process of trying to make a big deal out of this
issue since they want a piece of the market. Fortunately, they are
starting to build products specifically for the PV industry, which I
applaud. However, they need to be given a hard time for the way they
have tried to imply that all Square D switches are not properly listed.
They wont admit to that because they would end up in a legal battle,
but that is essentially what they have been doing. Square D still has
the largest selection of dc-rated equipment on the market. Eaton has a
long way to go. 

In a recent project that I reviewed, the engineer pulled the Square D
400-amp disconnect and replaced it with an Eaton disconnect at the
insistence of the Eaton rep. The Eaton product was not properly rated
or listed for the voltage while the Square D product was. This is the
insanity that needs to stop.

Bill.



From:
re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org]
On Behalf Of David Brearley
Sent: Monday, January 11, 2010 11:39 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Square D DC disconnects
 
Kirpal,

Have you checked out the SolarBOS disconnecting combiners? Their 28A
version might be ideal for large resi or small commercial applications.
For larger projects, Blue Oak PV Products and AMtec Solar also have
disconnecting combiners.

Thanks for sharing the updated Square D tech note. I had no idea that
the Square D HU Series disconnects were not UL-listed when used as
described in the older tech notes. The fact that this is not a
UL-listed use of the heavy duty safety switch, pretty much means that
it is not an option for integrators. As far as I know, there is no
other product that is listed for this use. 

David Brearley, Senior Technical Editor
SolarPro magazine 
NABCEP Certified PV Installer 
david.brear...@solarprofessional.com


On 1/9/10 4:14 PM, "Kirpal Khalsa" solarwo...@gmail.com wrote:

Hi All..
  
 
I recently came across a revised technical bulletin from square D ( http://ecatalog.squared.com/pubs/Electrical%20Distribution/Safety%20Switches/Heavy%20Duty/3110DB0401.pdf
)..we have for years been using the Square D DC Disconnect of
various amperages (30, 60, 100) as disconnects leading upto the
inverter from the array.we have frequently wired one string to each
of the three poles of the disconnect..we have had this
configuration inspected by inspectors regularly with approval
everytime..this new revision of the document from Square D shows
this is no longer a UL listed method.they are now stating in this
document that they are "self certifying" this technique...have any
of you come across this or know why Square D has back tracked? 

Something else I noticed is that they have raised the amperage rating
on the 30A disconncect per pole by 2 amps from 18 to 20 which is good
especially when using higher amperage modules like 

Re: [RE-wrenches] Square D DC disconnects

2010-01-11 Thread Bill Brooks
David,

 

The state by the Eaton guy at SPI shows that person's lack of understanding.
The person I talked to was adamant that all disconnects had to be tested to
the disconnect standard that assumes a high (10,000-amp) current source
behind any fault. Switch openings are also tested based on the inductance in
the circuit since that has a major impact on the size and duration of the
arc-especially in ac systems.

 

Square D did an evaluation based on the limited fault currents and
inductance in PV system circuit that has no batteries. I believe their
evaluation is valid. The issue is that there is no specific test at UL
yet-that's why UL did not list it (I'm pretty sure they were involved at
some level, but that is impossible to prove). It will probably be added to
UL1741. Perhaps that was what the Eaton rep was referring-we'll give him the
benefit of the doubt.

 

I still use my basic rule similar to the rule for politicians-how do you
know if a marketing guy is lying?== his lips are moving.

 

Bill.

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of David
Brearley
Sent: Monday, January 11, 2010 3:41 PM
To: RE-wrenches
Cc: 'Tim Townsend'
Subject: Re: [RE-wrenches] Square D DC disconnects

 

Thanks, Bill.

Glad to hear you think the HU series is still a good option.

When I was making the rounds at SPI, I stopped by the Eaton booth and got
the sense that they were gunning for Square D. They made light of Square D's
self-certification of the HU series discos. The rep also made a statement
about the new Eaton dc discos being the only ones designed to meet UL1741
requirements. When I got home, the first thing I looked up was 690.4(D).
This doesn't say anything about dc disconnects needing to be listed to some
special PV standard. 

Is there a movement in this direction? Is there a UL1741 standard for dc
discos that is somehow different that the standard used for other dc
disconnects?

Best,

David 

On 1/11/10 5:28 PM, Bill Brooks billbroo...@yahoo.com wrote:

David and Kirpal,
 
It is ultimately up to the AHJ whether or not they accept the
Schneider/Square D self certification. That is a judgment call the installer
needs to clear with the AHJ. That being said, having Square D behind the
rating of a switch is a whole lot more than any one of the smaller companies
making equipment for the PV industry. 
 
I will continue to use the 30, 60, and 100-amp versions in the way
recommended by the manufacturer because it is a huge saving in cost and they
are well made switches. I will also check with the local AHJ before
installing them in case they are not going to pass it. You have to remember
you are working with one of the largest electrical suppliers in the world.
They have a huge reputation with local jurisdictions.
 
Eaton has been in the process of trying to make a big deal out of this issue
since they want a piece of the market. Fortunately, they are starting to
build products specifically for the PV industry, which I applaud. However,
they need to be given a hard time for the way they have tried to imply that
all Square D switches are not properly listed. They won't admit to that
because they would end up in a legal battle, but that is essentially what
they have been doing. Square D still has the largest selection of dc-rated
equipment on the market. Eaton has a long way to go. 
 
In a recent project that I reviewed, the engineer pulled the Square D
400-amp disconnect and replaced it with an Eaton disconnect at the
insistence of the Eaton rep. The Eaton product was not properly rated or
listed for the voltage while the Square D product was. This is the insanity
that needs to stop.
 
Bill.
 
 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of David
Brearley
Sent: Monday, January 11, 2010 11:39 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Square D DC disconnects

Kirpal,

Have you checked out the SolarBOS disconnecting combiners? Their 28A version
might be ideal for large resi or small commercial applications. For larger
projects, Blue Oak PV Products and AMtec Solar also have disconnecting
combiners.

Thanks for sharing the updated Square D tech note. I had no idea that the
Square D HU Series disconnects were not UL-listed when used as described in
the older tech notes. The fact that this is not a UL-listed use of the heavy
duty safety switch, pretty much means that it is not an option for
integrators. As far as I know, there is no other product that is listed for
this use. 

David Brearley, Senior Technical Editor
SolarPro magazine 
NABCEP Certified PV Installer T
david.brear...@solarprofessional.com


On 1/9/10 4:14 PM, Kirpal Khalsa solarwo...@gmail.com wrote:

Hi All..


I recently came across a revised technical bulletin from square D (
http://ecatalog.squared.com/pubs/Electrical%20Distribution/Safety%20Switches
/Heavy%20Duty/3110DB0401.pdf )..we have for years 

Re: [RE-wrenches] Square D DC disconnects

2010-01-11 Thread David Brearley
Right, Kent, but 690.4(D) does require the use of products ³identified and
listed for the application.² So, for example, UL-listed combiner boxes are
required per NEC 2008, whereas integrators could previously site build
combiners using UL-listed parts. The appropriate listing for a PV combiner,
everyone agrees, is UL1741. This code article lists most major components in
a PV system, but not discos. I¹m simply wondering if there is some activity
I am unaware of seeking to add dc discos to this list or to the UL1741
standard. Just curious.


On 1/11/10 6:27 PM, Kent Osterberg k...@coveoregon.com wrote:

 David,
 
 The NEC doesn't require UL listing.  The most appropriate section of the code
 about this is Article 110, Requirements for Electrical Installations, it
 requires equipment to be approved.  In many jurisdictions, such as Oregon,
 that means evaluated and approved by a testing lab such as UL.
 
 Kent Osterberg
 Blue Mountain Solar, Inc.
 
 
 David Brearley wrote:
  Re: [RE-wrenches] Square D DC disconnects Thanks, Bill.
  
 Glad to hear you think the HU series is still a good option.
  
 When I was making the rounds at SPI, I stopped by the Eaton booth and got the
 sense that they were gunning for Square D. They made light of Square D¹s
 self-certification of the HU series discos. The rep also made a statement
 about the new Eaton dc discos being the only ones designed to meet UL1741
 requirements. When I got home, the first thing I looked up was 690.4(D). This
 doesn¹t say anything about dc disconnects needing to be listed to some
 special PV standard.
  
 Is there a movement in this direction? Is there a UL1741 standard for dc
 discos that is somehow different that the standard used for other dc
 disconnects?
  
 Best,
  
 David 
  
 On 1/11/10 5:28 PM, Bill Brooks billbroo...@yahoo.com wrote:
  
   
 David and Kirpal,
  
 It is ultimately up to the AHJ whether or not they accept the
 Schneider/Square D self certification. That is a judgment call the installer
 needs to clear with the AHJ. That being said, having Square D behind the
 rating of a switch is a whole lot more than any one of the smaller companies
 making equipment for the PV industry.
  
 I will continue to use the 30, 60, and 100-amp versions in the way
 recommended by the manufacturer because it is a huge saving in cost and they
 are well made switches. I will also check with the local AHJ before
 installing them in case they are not going to pass it. You have to remember
 you are working with one of the largest electrical suppliers in the world.
 They have a huge reputation with local jurisdictions.
  
 Eaton has been in the process of trying to make a big deal out of this issue
 since they want a piece of the market. Fortunately, they are starting to
 build products specifically for the PV industry, which I applaud. However,
 they need to be given a hard time for the way they have tried to imply that
 all Square D switches are not properly listed. They won¹t admit to that
 because they would end up in a legal battle, but that is essentially what
 they have been doing. Square D still has the largest selection of dc-rated
 equipment on the market. Eaton has a long way to go.
  
 In a recent project that I reviewed, the engineer pulled the Square D
 400-amp disconnect and replaced it with an Eaton disconnect at the
 insistence of the Eaton rep. The Eaton product was not properly rated or
 listed for the voltage while the Square D product was. This is the insanity
 that needs to stop.
  
 Bill.
  
  
  
  From: re-wrenches-boun...@lists.re-wrenches.org
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of David
 Brearley
  Sent: Monday, January 11, 2010 11:39 AM
  To: RE-wrenches
  Subject: Re: [RE-wrenches] Square D DC disconnects
   
  Kirpal,
  
 Have you checked out the SolarBOS disconnecting combiners? Their 28A version
 might be ideal for large resi or small commercial applications. For larger
 projects, Blue Oak PV Products and AMtec Solar also have disconnecting
 combiners.
  
 Thanks for sharing the updated Square D tech note. I had no idea that the
 Square D HU Series disconnects were not UL-listed when used as described in
 the older tech notes. The fact that this is not a UL-listed use of the heavy
 duty safety switch, pretty much means that it is not an option for
 integrators. As far as I know, there is no other product that is listed for
 this use. 
  
 David Brearley, Senior Technical Editor
  SolarPro magazine
 NABCEP Certified PV Installer 
  david.brear...@solarprofessional.com
  
  
 On 1/9/10 4:14 PM, Kirpal Khalsa solarwo...@gmail.com wrote:
   
 Hi All..
  
   
 I recently came across a revised technical bulletin from square D (
 http://ecatalog.squared.com/pubs/Electrical%20Distribution/Safety%20Switches
 /Heavy%20Duty/3110DB0401.pdf )..we have for years been using the Square
 D DC Disconnect of various amperages (30, 60, 100) as disconnects leading
 upto the inverter from the array.we 

Re: [RE-wrenches] Square D DC disconnects

2010-01-11 Thread David Brearley
Thanks for the clarification, Bill. If they add this to UL1741, I hope they
will do so in a manner that recognizes the unique characteristics of PV
applications. Definitely easier to interrupt a 10A source than a 10,000A
one.


On 1/11/10 6:43 PM, Bill Brooks billbroo...@yahoo.com wrote:

 David,
  
 The state by the Eaton guy at SPI shows that person¹s lack of understanding.
 The person I talked to was adamant that all disconnects had to be tested to
 the disconnect standard that assumes a high (10,000-amp) current source behind
 any fault. Switch openings are also tested based on the inductance in the
 circuit since that has a major impact on the size and duration of the
 arc‹especially in ac systems.
  
 Square D did an evaluation based on the limited fault currents and inductance
 in PV system circuit that has no batteries. I believe their evaluation is
 valid. The issue is that there is no specific test at UL yet‹that¹s why UL did
 not list it (I¹m pretty sure they were involved at some level, but that is
 impossible to prove). It will probably be added to UL1741. Perhaps that was
 what the Eaton rep was referring‹we¹ll give him the benefit of the doubt.
  
 I still use my basic rule similar to the rule for politicians‹how do you know
 if a marketing guy is lying?== his lips are moving.
  
 Bill.
  
 
 From: re-wrenches-boun...@lists.re-wrenches.org
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of David Brearley
 Sent: Monday, January 11, 2010 3:41 PM
 To: RE-wrenches
 Cc: 'Tim Townsend'
 Subject: Re: [RE-wrenches] Square D DC disconnects
  
 Thanks, Bill.
 
 Glad to hear you think the HU series is still a good option.
 
 When I was making the rounds at SPI, I stopped by the Eaton booth and got the
 sense that they were gunning for Square D. They made light of Square D¹s
 self-certification of the HU series discos. The rep also made a statement
 about the new Eaton dc discos being the only ones designed to meet UL1741
 requirements. When I got home, the first thing I looked up was 690.4(D). This
 doesn¹t say anything about dc disconnects needing to be listed to some special
 PV standard. 
 
 Is there a movement in this direction? Is there a UL1741 standard for dc
 discos that is somehow different that the standard used for other dc
 disconnects?
 
 Best,
 
 David 
 
 On 1/11/10 5:28 PM, Bill Brooks billbroo...@yahoo.com wrote:
 David and Kirpal,
  
 It is ultimately up to the AHJ whether or not they accept the Schneider/Square
 D self certification. That is a judgment call the installer needs to clear
 with the AHJ. That being said, having Square D behind the rating of a switch
 is a whole lot more than any one of the smaller companies making equipment for
 the PV industry. 
  
 I will continue to use the 30, 60, and 100-amp versions in the way recommended
 by the manufacturer because it is a huge saving in cost and they are well made
 switches. I will also check with the local AHJ before installing them in case
 they are not going to pass it. You have to remember you are working with one
 of the largest electrical suppliers in the world. They have a huge reputation
 with local jurisdictions.
  
 Eaton has been in the process of trying to make a big deal out of this issue
 since they want a piece of the market. Fortunately, they are starting to build
 products specifically for the PV industry, which I applaud. However, they need
 to be given a hard time for the way they have tried to imply that all Square D
 switches are not properly listed. They won¹t admit to that because they would
 end up in a legal battle, but that is essentially what they have been doing.
 Square D still has the largest selection of dc-rated equipment on the market.
 Eaton has a long way to go.
  
 In a recent project that I reviewed, the engineer pulled the Square D 400-amp
 disconnect and replaced it with an Eaton disconnect at the insistence of the
 Eaton rep. The Eaton product was not properly rated or listed for the voltage
 while the Square D product was. This is the insanity that needs to stop.
  
 Bill.
  
  
 
 From: re-wrenches-boun...@lists.re-wrenches.org
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of David Brearley
 Sent: Monday, January 11, 2010 11:39 AM
 To: RE-wrenches
 Subject: Re: [RE-wrenches] Square D DC disconnects
 
 Kirpal,
 
 Have you checked out the SolarBOS disconnecting combiners? Their 28A version
 might be ideal for large resi or small commercial applications. For larger
 projects, Blue Oak PV Products and AMtec Solar also have disconnecting
 combiners.
 
 Thanks for sharing the updated Square D tech note. I had no idea that the
 Square D HU Series disconnects were not UL-listed when used as described in
 the older tech notes. The fact that this is not a UL-listed use of the heavy
 duty safety switch, pretty much means that it is not an option for
 integrators. As far as I know, there is no other product that is listed for
 this use. 
 
 David Brearley, Senior 

Re: [RE-wrenches] Square D DC disconnects

2010-01-11 Thread William Miller

Kirpal:

Can't you disconnect the load at the inverter and then go back to the array 
to disconnect the feeder?


William

At 04:01 PM 1/11/2010, you wrote:

William.we love the Outback FWPV12 and 8...a good improvement
over the PSPV..we use them high voltage apps, but alas..don't
open fuse under load.thats why we need a version which is
disconnectable..
Cheers,

--
Sunny Regards,
Kirpal Khalsa
NABCEP Certified Solar PV Installer
Renewable Energy Systems
www.oregonsolarworks.com
541-218-0201 m
541-592-3958 o


On Mon, Jan 11, 2010 at 12:16 PM, William Miller
will...@millersolar.com wrote:
 Kirpa:

 Have you considered using the Outback PSPV combiner with the 600 VDC
 touch-safe fuse holders and appropriate fuses?  I belive this configuration
 meets the 600 VDC rating.

 William Miller



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Square D DC disconnects

2010-01-11 Thread Marv Dargatz
Title: Re: [RE-wrenches] Square D DC disconnects




Not sure why the following reply which I posted a
couple of hours ago never got posted on the list. I can offer more
detail as to the considerations the test process must be given for this
application if anybody is interested.

Begin previous message:

The testing for the HU series switches was
performed by Square D according to a procedure that I wrote when
working with SMA. The procedure was reviewed and accepted by UL as
valid for the dedicated purpose of PV disconnect when used with the SMA
SB2500.
See ya!

Marv
707 763-4784  x7016



See ya!

Marv
707 763-4784  x7016



Bill Brooks wrote:

  
  
  
  

  
  David,
  
  The
state by the Eaton guy at SPI shows that persons lack
of understanding. The person I talked to was adamant that all
disconnects had
to be tested to the disconnect standard that assumes a high
(10,000-amp)
current source behind any fault. Switch openings are also tested based
on the
inductance in the circuit since that has a major impact on the size and
duration of the arcespecially in ac systems.
  
  Square
D did an evaluation based on the limited fault currents
and inductance in PV system circuit that has no batteries. I believe
their
evaluation is valid. The issue is that there is no specific test at UL
yetthats
why UL did not list it (Im pretty sure they were involved at some
level,
but that is impossible to prove). It will probably be added to UL1741.
Perhaps
that was what the Eaton rep was referringwell give him the
benefit of the doubt.
  
  I
still use my basic rule similar to the rule for politicianshow
do you know if a marketing guy is lying?== his lips are moving.
  
  Bill.
  
  
  
  From:
re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of David
Brearley
  Sent: Monday, January 11, 2010 3:41 PM
  To: RE-wrenches
  Cc: 'Tim Townsend'
  Subject: Re: [RE-wrenches] Square D DC disconnects
  
  
  
  Thanks,
Bill.
  
Glad to hear you think the HU series is still a good option.
  
When I was making the rounds at SPI, I stopped by the Eaton booth and
got the
sense that they were gunning for Square D. They made light of Square
Ds
self-certification of the HU series discos. The rep also made a
statement about
the new Eaton dc discos being the only ones designed to meet UL1741
requirements. When I got home, the first thing I looked up was
690.4(D). This
doesnt say anything about dc disconnects needing to be listed to some
special PV standard. 
  
Is there a movement in this direction? Is there a UL1741 standard for
dc discos
that is somehow different that the standard used for other dc
disconnects?
  
Best,
  
David 
  
On 1/11/10 5:28 PM, "Bill Brooks" billbroo...@yahoo.com
wrote:
  David
and Kirpal,

It is ultimately up to the AHJ whether or not they accept the
Schneider/Square
D self certification. That is a judgment call the installer needs to
clear with
the AHJ. That being said, having Square D behind the rating of a switch
is a
whole lot more than any one of the smaller companies making equipment
for the
PV industry. 

I will continue to use the 30, 60, and 100-amp versions in the way
recommended
by the manufacturer because it is a huge saving in cost and they are
well made
switches. I will also check with the local AHJ before installing them
in case
they are not going to pass it. You have to remember you are working
with one of
the largest electrical suppliers in the world. They have a huge
reputation with
local jurisdictions.

Eaton has been in the process of trying to make a big deal out of this
issue
since they want a piece of the market. Fortunately, they are starting
to build
products specifically for the PV industry, which I applaud. However,
they need
to be given a hard time for the way they have tried to imply that all
Square D
switches are not properly listed. They wont admit to that because they
would end up in a legal battle, but that is essentially what they have
been
doing. Square D still has the largest selection of dc-rated equipment
on the
market. Eaton has a long way to go. 

In a recent project that I reviewed, the engineer pulled the Square D
400-amp
disconnect and replaced it with an Eaton disconnect at the insistence
of the
Eaton rep. The Eaton product was not properly rated or listed for the
voltage
while the Square D product was. This is the insanity that needs to stop.

Bill.


  
  From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org]
  On Behalf Of David Brearley
  Sent: Monday, January 11, 2010 11:39 AM
  To: RE-wrenches
  Subject: Re: [RE-wrenches] Square D DC disconnects
  
  Kirpal,
  
Have you checked out the SolarBOS disconnecting combiners? Their 28A
version
might be ideal for large resi or small commercial applications. For
larger
projects, Blue Oak PV Products and AMtec Solar also have disconnecting
combiners.
  
Thanks for sharing the updated Square D tech note. I had no idea that
the

Re: [RE-wrenches] Square D DC disconnects

2010-01-11 Thread Kirpal Khalsa
Yes, we could do that...however during instances of testing, trouble
shooting, or in the event of a fire it can be helpful to have a wayto quikly
disconnect the inverter from the combiner/fusing *at* the array.  In most
standard electrical work having a disconnect located not in line of sight
from location of work leads to lock out/ tag out proceduresI see no
difference here.  It prevents one from having an inverter/disconnect from
accidentally being turned on when you are working on the roof out of sight
from a homeowner trying to help, or a co worker not paying attention.


Sunny Regards,
Kirpal


On Mon, Jan 11, 2010 at 5:39 PM, William Miller will...@millersolar.com
wrote:
 Kirpal:

 Can't you disconnect the load at the inverter and then go back to the
array
 to disconnect the feeder?

 William

 At 04:01 PM 1/11/2010, you wrote:

 William.we love the Outback FWPV12 and 8...a good improvement
 over the PSPV..we use them high voltage apps, but alas..don't
 open fuse under load.thats why we need a version which is
 disconnectable..
 Cheers,

 --
 Sunny Regards,
 Kirpal Khalsa
 NABCEP Certified Solar PV Installer
 Renewable Energy Systems
 www.oregonsolarworks.com
 541-218-0201 m
 541-592-3958 o


 On Mon, Jan 11, 2010 at 12:16 PM, William Miller
 will...@millersolar.com wrote:
 Kirpa:

 Have you considered using the Outback PSPV combiner with the 600 VDC
 touch-safe fuse holders and appropriate fuses?  I belive this
 configuration
 meets the 600 VDC rating.

 William Miller




 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] OB VFX3648 vs Munchkin?

2010-01-11 Thread dan
Heyall;I have a customer eyeing their new OB VFX3648 for their Boiler (Munchkin (sp?)) malfunction. anyone seen this or any similar issues? thanks. dbDan BrownPresidentFoxfire Energy Corp.Renewable Energy Systems(802)-483-2564www.Foxfire-Energy.comNABCEP #092907-44



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] OB VFX3648 vs Munchkin?

2010-01-11 Thread Darryl Thayer
I seem to remember someone having problems and it was that the voltage of the 
outback would sag when operating just very small control currents.  

--- On Mon, 1/11/10, d...@foxfire-energy.com d...@foxfire-energy.com wrote:

 From: d...@foxfire-energy.com d...@foxfire-energy.com
 Subject: [RE-wrenches] OB VFX3648 vs Munchkin?
 To: RE-wrenches re-wrenches@lists.re-wrenches.org
 Date: Monday, January 11, 2010, 9:35 PM
 Heyall;I
 have a customer eyeing their new OB VFX3648 for their Boiler
 (Munchkin (sp?)) malfunction. anyone seen this or any
 similar issues? thanks. db
 
 
 Dan Brown
 President
 Foxfire Energy Corp.
 Renewable Energy Systems
 (802)-483-2564
 www.Foxfire-Energy.com
 NABCEP #092907-44
 
 
 
 
  
 
 -Inline Attachment Follows-
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
 


  
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] OB VFX3648 vs Munchkin?

2010-01-11 Thread Howie Michaelson
Hey Dan,

I have had a persistent issue with a Boderus low mass boiler at one of my
off-grid clients (dual stack VFX3648's, FM80, FNDC, etc.  It goes into
error sporadically, perhaps after a longer generator (Kohler 12 kW
propane) charge run, maybe as it (the generator) shuts off.  We tried to
isolate the boiler's power supply with a small UPS with now luck.  Outback
couldn't help.  Seems Boderus may know something about this issue in
regards to generator/inverter setups, but the install base is so small
they choose to ignore it. Don't know if this is related, and I have no
solutions after many attempts at fixing it.  Sorry...

Howie
-- 
Howie Michaelson
NABCEP Certified Solar PV Installer™

Sun Catcher, LLC
Renewable Energy Systems Sales and Service
VT Solar  Wind Incentive Program Partner
http://www.SunCatcherVT.com
(cell) 802-272-0004
(home) 802-439-6096


On Mon, January 11, 2010 10:35 pm, d...@foxfire-energy.com wrote:
 I have a customer eyeing their new
 OB VFX3648 for their Boiler (Munchkin (sp?)) malfunction. anyone seen this
 or any similar issues? thanks. db


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] OB VFX3648 vs Munchkin?

2010-01-11 Thread Allan Sindelar




Dan,
Long-winded response compendium below. This is my record of a on-list
and off-list Wrenches discussion of a similar boiler issue on one of
our jobs, about a year ago. The issue never got resolved with Magnum or
Buderus, but when the customer's hydronic contractor changed to a
different boiler the problem disappeared and hasn't returned. Below the
thread is my email to Buderus, with a reply from engineering
acknowledging the problem. 
This isn't Munchkin, but you might find some material here to use in
your situation.








 
 

Re: [RE-wrenches] Square D DC disconnects

2010-01-11 Thread R Ray Walters
I got into that one a few years ago with an inspector. 
He cited 110.2.
Approved according to article 100 means: acceptable to the AHJ. 
So put article 100 into 110.2 and you get:
 Conductors and Equipment required or permitted shall be acceptable only if 
'acceptable to the AHJ' 

Basically I call these 2 sections of the code read together as the 'AHJ = The 
Man' ruling.
I guess there was some politics involved in NOT putting that together for all 
to see?

R. Walters
r...@solarray.com
Solar Engineer




On Jan 11, 2010, at 5:27 PM, Kent Osterberg wrote:

 David,
 
 The NEC doesn't require UL listing.  The most appropriate section of the code 
 about this is Article 110, Requirements for Electrical Installations, it 
 requires equipment to be approved.  

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org