Re: [RE-wrenches] intermittent battery problem; ...Battery Sulfation

2011-11-16 Thread Ron Young
Hi Larry, no amp hour meter installed yet as the customer is penny pinching. 
We're trying to solve the problem first and I've been out there twice, once to 
do general diagnostics and check all connections, try to load test the 
batteries, and so on; the second time I 'dropped in' to try a different load 
test on the batteries to see if I could replicate the problem and to resolve 
some other problems with a Whisper controller that had given up the ghost when 
disconnected  re-connected to the batteries (all precautions taken). It's a 
seven hour round trip and with time spent on the job makes for an expensive 
service call. I only charged for one call and I have to go back at least once 
more. So customer wanted to save some money on the installation of the 
TriMetric until the spring... sorry for the long winded reply. I know, it's 
false economy. So I'm thinking I'll just put the meter in and tell them to pay 
me when they feel like it. It'll help solve the problem and get some of the 
Wrenches off my back ... ;-)

Ron Young

On 2011-11-13, at 8:26 AM, la...@starlightsolar.com 
la...@starlightsolar.com wrote:

 Ron,
 I stick by my evaluation as seen here: 
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/msg10694.html
 
 The #1 reason for my opinion is that you can NOT drive up voltage on a 
 healthy bank that size in just 5 minutes. It is impossible with a 2500 watt 
 generator.
 
 Here is the pertinent part from my post:
 You mentioned that the the battery drops to 24.5 in the early AM without any 
 heavy loads on. For the 4KS25 battery this equates to about 800AH at the 72 
 hour rate. Then you said that the customer ran a 2500 watt generator for 5 
 minutes and drove the voltage up to 29 volts. Here's the Ah-Ha moment: That 
 is EXACTLY the behavior of a heavily sulfated battery bank. A fast rise in 
 voltage indicates sulfation. It is impossible for that tiny generator, or any 
 charge source they own for that matter, to replace the hundreds of AH it 
 would take to drive a healthy battery up to the absorb voltage of 29 volts. 
 The bank is about 45,000 watt hours (72h rate). There would have to be over 
 20,000 Wh removed to be at that voltage. How many Wh's are replaced in 5 
 minutes by a 2500 watt genny? I'm sure you are getting the picture. 
 
 Also, why have you not installed a battery monitor yet? It will give you 
 eyes into the battery and spare countless hours of time diagnosing the 
 problem.
 
 Larry
 
  Original Message 
 Subject: Re: [RE-wrenches] intermittent battery problem; ...Battery
 Sulfation
 From: Ron Young solarea...@solareagle.com
 Date: Sat, November 12, 2011 9:57 pm
 To: RE-wrenches re-wrenches@lists.re-wrenches.org
 
 Folks, this one really has me puzzled. The client has done regular two hour 
 EQ's, at least once a month. When did a site visit and I topped up the 
 electrolyte (they'd been starving the batteries for water but always just 
 above the plates) the problem seemed to go away. They were satisfied that the 
 problem was solved but I wasn't and I told them what I had been hearing from 
 this group - essentially that the batteries needed a deep EQ, discharge, 
 recharge and EQ again two or three times to scrub the sulphates. They 
 declined until just a few days ago when they said the rapid voltage drop was 
 back. Here's a quote:
 
 We had another rapid voltage loss this morning ---it was 25.2 when we got up 
 and it dropped rapidly to 22.8.  We turned on the generator and charged the 
 batteries until our display showed 30.2  for awhile with the generator 
 running.  We turned off the generator and the voltage settled at about 26.4.  
 We turned off all loads and wind and solar.
   
 At 9.15 our batteries were at 26.4
 At 9:16 we turned on an 8W light bulb, a1600W hair dryer, and a 1.5HP (120V 
 5.75A) shop vac
 The display showed a load of 1.9kw
 At 9:40 the inverter shut down---display showed batteries at 18.4
 By 9.47 the display showed the batteries at 25.2the solar and wind were 
 still shut down.
 We turned everything back on (a light, Sunfrost RF16, phone)  and all seems 
 to be normal.
 
 They agreed to do the EQ process but only have a 3kw generator so we started 
 with 8 hours with the EQ voltage set for 32v (24v system). They completed 
 that yesterday and here's what resulted:
 
 Before starting EQ the batteries were at 25.8, hydrometer reading 1283 with 
 temp. correction
 Began EQ32.6 v
  Buying 1.5 kw
 Hour 1  32.4 v
 1283  with temp. correction   Buying  1.4
 Hour 2  32.4 v
   1285  with temp. correction  Buying 1.5
 Hour 3  32.2 v
  

Re: [RE-wrenches] intermittent battery problem; ...Battery Sulfation

2011-11-16 Thread Ron Young
Hi Daryl. I've got other KS25's in hybrid systems (wind gen  solar) that seem 
to do fine over the last several years. The Ouback 3524 has an 85 amp charger.  
There was no problem getting to 32 v and holding it for eight hours. This has 
been done twice now.  Larry and others attribute the ability to get to 32v to a 
sulphated battery condition and I'm thinking that a healthy battery could get 
to 32v as well, especially one that's been regularly EQ'd... am I wrong?

I'm listening to every opinion here and trying to sort it out but I think John 
may be on the right track with an intermittent failure of one cell. I just 
can't seem to find it.

Ron Young

On 2011-11-13, at 3:51 AM, penobscotso...@midmaine.com wrote:

 Ron,
  What comes to mind for me is that Surrette 5000 series batteries like
 to have a regular charge of C10.  KS25 cells are rated for 1350 ah,
 creating a need for a somewhat regularly occurring charge of 135 amps.
 I do believe the batteries are not ever getting that, except for very
 rare occasions. We have seen this before in undersized systems.
  Is the bulk charge set to 29.6? I would try a couple more eq's over the
 next month to loosen likely sulfation. Get it up to as close to 32
 volts as possible and taper the charge down, then eq at that voltage
 for four or five hours, even more if the client will do it.
  That would be how we would deal with this. It does seem ultimately to
 be sulfation that is the problem.
 
 Daryl DeJoy
 NABCEP Certified PV installer
 Penobscot Solar Design
 
 
 
 
 Folks, this one really has me puzzled. The client has done regular two
 hour EQ's, at least once a month. When did a site visit and I topped up
 the electrolyte (they'd been starving the batteries for water but always
 just above the plates) the problem seemed to go away. They were satisfied
 that the problem was solved but I wasn't and I told them what I had been
 hearing from this group - essentially that the batteries needed a deep EQ,
 discharge, recharge and EQ again two or three times to scrub the
 sulphates. They declined until just a few days ago when they said the
 rapid voltage drop was back. Here's a quote:
 
 We had another rapid voltage loss this morning ---it was 25.2 when we got
 up and it dropped rapidly to 22.8.  We turned on the generator and charged
 the batteries until our display showed 30.2  for awhile with the generator
 running.  We turned off the generator and the voltage settled at about
 26.4.  We turned off all loads and wind and solar.
 
 At 9.15 our batteries were at 26.4
 At 9:16 we turned on an 8W light bulb, a1600W hair dryer, and a 1.5HP
 (120V 5.75A) shop vac
 The display showed a load of 1.9kw
 At 9:40 the inverter shut down---display showed batteries at 18.4
 By 9.47 the display showed the batteries at 25.2the solar and wind
 were still shut down.
 We turned everything back on (a light, Sunfrost RF16, phone)  and all
 seems to be normal.
 
 They agreed to do the EQ process but only have a 3kw generator so we
 started with 8 hours with the EQ voltage set for 32v (24v system). They
 completed that yesterday and here's what resulted:
 
 Before starting EQ the batteries were at 25.8, hydrometer reading 1283
 with temp. correction
 Began EQ32.6 v
  Buying 
 1.5 kw
 Hour 1  32.4 v
  1283  with temp. correction   Buying  1.4
 Hour 2  32.4 v
1285  with temp. correction  Buying 1.5
 Hour 3  32.2 v
  
 Buying 1.7
 Hour 4  32.2 v
1290  with temp correctionBuying 1.8
 HOur 5 32.0 v
   1290   with temp correctionBuying 1.8
 Hour 6  32.0 v
  Buying 
 1.9
 Hour 7  31.8 v
 1292 with temp correctonBuying 1.9
 Hour 8 complete---turned off Gen and turned on loads ---Batteries dropped
 to 25.4 within 30 minutes and stayed there until this morning---fridge was
 running, telephone, internet, wool carding machine, lights.  This morning
 hydrometer reading  was at 1290.
 
 
 
 Then today I just got this email:
 
 Just experienced another rapid voltage drop.  As soon as the voltage hits
 24.8 the voltage drops like a rock if we don't have any input (no solar or
 wind).
 
 This is not what I expected after a lengthy EQ. I'm getting them to do
 another one tomorrow after a discharge cycle and charge but I'm really
 beginning to think we have something else going on here, something
 electrical, not 

Re: [RE-wrenches] combiner bus bar for Sunny Tower DC input?

2011-11-16 Thread North Texas Renewable Energy Inc
You will need a fuse for each inverter for the same reason you would need a
fuse for 4 PV strings.
Jim Duncan
North Texas Renewable Energy


  -Original Message-
  From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org]On Behalf Of Glenn Burt
  Sent: Tuesday, November 15, 2011 7:57 PM
  To: 'RE-wrenches'
  Subject: Re: [RE-wrenches] combiner bus bar for Sunny Tower DC input?


  Are you sure you need to split them?

  IIR, there are only a pair of conductors going from each SB into the
tower. They must be combined on the SMA side of the touch-safe fuse holders
in some way.



  We opted to run all our source circuits from array through 6 external
discos then into the ST instead of combining them - the distance in our case
was around 150'.



  -Glenn



  From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kirk
Herander
  Sent: Tuesday, November 15, 2011 8:10 PM
  To: 'RE-wrenches'
  Subject: Re: [RE-wrenches] combiner bus bar for Sunny Tower DC input?



  But I don't believe the Sunny Tower internally  has single conductor lugs
leading to the respective SB it's wired to. The DC tower input/output to
each respective inverter is effectively a combiner box which combines all
fused inputs to a single positive prewired to the respective SB inverter. I
have already combined the strings in an external box and need to uncombine
them through the individual fused strings in the SunnyTower.



  Kirk Herander

  VT Solar, LLC

  dba Vermont Solar Engineering

  NABCEPTM Certified installer Charter Member

  NYSERDA-eligible Installer

  VT RE Incentive Program Partner



  From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Brian
Teitelbaum
  Sent: Monday, November 14, 2011 8:28 PM
  To: RE-wrenches
  Subject: Re: [RE-wrenches] combiner bus bar for Sunny Tower DC input?



  Hi Kirk,



  The Sunny Boy inverters also have a pair of lugs for a single conductor
pair coming in from the array. They are meant to be used if you have an
external combiner. No bus bars as you describe are needed.



  Brian Teitelbaum

  AEE Solar



  From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kirk
Herander
  Sent: Monday, November 14, 2011 2:57 PM
  To: RE-wrenches
  Subject: [RE-wrenches] combiner bus bar for Sunny Tower DC input?



  Hello,



  The Sunny Tower has four individual fuse holders on the DC input of each
inverter. I am combining the array output for each inverter in a combiner
box before the tower, so there is only a single positive, negative, and gnd
going to each inverter's DC input. I want to fan this input out to each of
the four dc fuses via a combiner bus with a single lug and prongs which fit
directly into each fuseholders' input, ala the Outback combiner bus. Is
there something similar made for the SunnyTower dc input? I have not been
able to talk to SMA yet about this. Thanks.



  Kirk Herander

  VT Solar, LLC

  dba Vermont Solar Engineering

  NABCEPTM Certified installer Charter Member

  NYSERDA-eligible Installer

  VT RE Incentive Program Partner


attachment: North Texas Renewable Energy Inc.vcf___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Sharp triangles

2011-11-16 Thread Marco Mangelsdorf
Does Sharp still make those quasi-triangular mods?

 

Thanks,

marco

 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] intermittent battery problem; ...Battery Sulfation

2011-11-16 Thread Larry Crutcher, Starlight Solar Power Systems
We are only on your back until you to do the advisable thing: Sell them a 
battery capacity monitor. It is a hard fact that NO off grid, battery based 
power system should be without a battery capacity monitor. They are cheap (only 
$150!) and not an option. Apparently, it is also hard learned fact. ;-)

Larry Crutcher
Starlight Solar Power Systems




On Nov 16, 2011, at 12:20 AM, Ron Young wrote:

 Hi Larry, no amp hour meter installed yet as the customer is penny pinching. 
 We're trying to solve the problem first and I've been out there twice, once 
 to do general diagnostics and check all connections, try to load test the 
 batteries, and so on; the second time I 'dropped in' to try a different load 
 test on the batteries to see if I could replicate the problem and to resolve 
 some other problems with a Whisper controller that had given up the ghost 
 when disconnected  re-connected to the batteries (all precautions taken). 
 It's a seven hour round trip and with time spent on the job makes for an 
 expensive service call. I only charged for one call and I have to go back at 
 least once more. So customer wanted to save some money on the installation of 
 the TriMetric until the spring... sorry for the long winded reply. I know, 
 it's false economy. So I'm thinking I'll just put the meter in and tell them 
 to pay me when they feel like it. It'll help solve the problem and get some 
 of the Wrenches off my back ... ;-)
 
 Ron Young
 
 On 2011-11-13, at 8:26 AM, la...@starlightsolar.com 
 la...@starlightsolar.com wrote:
 
 Ron,
 I stick by my evaluation as seen here: 
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/msg10694.html
 
 The #1 reason for my opinion is that you can NOT drive up voltage on a 
 healthy bank that size in just 5 minutes. It is impossible with a 2500 watt 
 generator.
 
 Here is the pertinent part from my post:
 You mentioned that the the battery drops to 24.5 in the early AM without any 
 heavy loads on. For the 4KS25 battery this equates to about 800AH at the 72 
 hour rate. Then you said that the customer ran a 2500 watt generator for 5 
 minutes and drove the voltage up to 29 volts. Here's the Ah-Ha moment: That 
 is EXACTLY the behavior of a heavily sulfated battery bank. A fast rise in 
 voltage indicates sulfation. It is impossible for that tiny generator, or 
 any charge source they own for that matter, to replace the hundreds of AH it 
 would take to drive a healthy battery up to the absorb voltage of 29 volts. 
 The bank is about 45,000 watt hours (72h rate). There would have to be over 
 20,000 Wh removed to be at that voltage. How many Wh's are replaced in 5 
 minutes by a 2500 watt genny? I'm sure you are getting the picture. 
 
 Also, why have you not installed a battery monitor yet? It will give you 
 eyes into the battery and spare countless hours of time diagnosing the 
 problem.
 
 Larry
 
  Original Message 
 Subject: Re: [RE-wrenches] intermittent battery problem; ...Battery
 Sulfation
 From: Ron Young solarea...@solareagle.com
 Date: Sat, November 12, 2011 9:57 pm
 To: RE-wrenches re-wrenches@lists.re-wrenches.org
 
 Folks, this one really has me puzzled. The client has done regular two hour 
 EQ's, at least once a month. When did a site visit and I topped up the 
 electrolyte (they'd been starving the batteries for water but always just 
 above the plates) the problem seemed to go away. They were satisfied that 
 the problem was solved but I wasn't and I told them what I had been hearing 
 from this group - essentially that the batteries needed a deep EQ, 
 discharge, recharge and EQ again two or three times to scrub the sulphates. 
 They declined until just a few days ago when they said the rapid voltage 
 drop was back. Here's a quote:
 
 We had another rapid voltage loss this morning ---it was 25.2 when we got up 
 and it dropped rapidly to 22.8.  We turned on the generator and charged the 
 batteries until our display showed 30.2  for awhile with the generator 
 running.  We turned off the generator and the voltage settled at about 26.4. 
  We turned off all loads and wind and solar.
   
 At 9.15 our batteries were at 26.4
 At 9:16 we turned on an 8W light bulb, a1600W hair dryer, and a 1.5HP (120V 
 5.75A) shop vac
 The display showed a load of 1.9kw
 At 9:40 the inverter shut down---display showed batteries at 18.4
 By 9.47 the display showed the batteries at 25.2the solar and wind were 
 still shut down.
 We turned everything back on (a light, Sunfrost RF16, phone)  and all seems 
 to be normal.
 
 They agreed to do the EQ process but only have a 3kw generator so we started 
 with 8 hours with the EQ voltage set for 32v (24v system). They completed 
 that yesterday and here's what resulted:
 
 Before starting EQ the batteries were at 25.8, hydrometer reading 1283 with 
 temp. correction
 Began EQ32.6 v   
  

Re: [RE-wrenches] intermittent battery problem; ...Battery Sulfation

2011-11-16 Thread Larry Crutcher, Starlight Solar Power Systems
Ron, you have misquoted me so yes you are wrong. It is not about getting to 32 
volts. Go read it again.

On Nov 16, 2011, at 12:20 AM, Ron Young wrote:

 Hi Daryl. I've got other KS25's in hybrid systems (wind gen  solar) that 
 seem to do fine over the last several years. The Ouback 3524 has an 85 amp 
 charger.  There was no problem getting to 32 v and holding it for eight 
 hours. This has been done twice now.  Larry and others attribute the ability 
 to get to 32v to a sulphated battery condition and I'm thinking that a 
 healthy battery could get to 32v as well, especially one that's been 
 regularly EQ'd... am I wrong?
 
 I'm listening to every opinion here and trying to sort it out but I think 
 John may be on the right track with an intermittent failure of one cell. I 
 just can't seem to find it.
 
 Ron Young
 
 On 2011-11-13, at 3:51 AM, penobscotso...@midmaine.com wrote:
 
 Ron,
 What comes to mind for me is that Surrette 5000 series batteries like
 to have a regular charge of C10.  KS25 cells are rated for 1350 ah,
 creating a need for a somewhat regularly occurring charge of 135 amps.
 I do believe the batteries are not ever getting that, except for very
 rare occasions. We have seen this before in undersized systems.
 Is the bulk charge set to 29.6? I would try a couple more eq's over the
 next month to loosen likely sulfation. Get it up to as close to 32
 volts as possible and taper the charge down, then eq at that voltage
 for four or five hours, even more if the client will do it.
 That would be how we would deal with this. It does seem ultimately to
 be sulfation that is the problem.
 
 Daryl DeJoy
 NABCEP Certified PV installer
 Penobscot Solar Design
 
 
 
 
 Folks, this one really has me puzzled. The client has done regular two
 hour EQ's, at least once a month. When did a site visit and I topped up
 the electrolyte (they'd been starving the batteries for water but always
 just above the plates) the problem seemed to go away. They were satisfied
 that the problem was solved but I wasn't and I told them what I had been
 hearing from this group - essentially that the batteries needed a deep EQ,
 discharge, recharge and EQ again two or three times to scrub the
 sulphates. They declined until just a few days ago when they said the
 rapid voltage drop was back. Here's a quote:
 
 We had another rapid voltage loss this morning ---it was 25.2 when we got
 up and it dropped rapidly to 22.8.  We turned on the generator and charged
 the batteries until our display showed 30.2  for awhile with the generator
 running.  We turned off the generator and the voltage settled at about
 26.4.  We turned off all loads and wind and solar.
 
 At 9.15 our batteries were at 26.4
 At 9:16 we turned on an 8W light bulb, a1600W hair dryer, and a 1.5HP
 (120V 5.75A) shop vac
 The display showed a load of 1.9kw
 At 9:40 the inverter shut down---display showed batteries at 18.4
 By 9.47 the display showed the batteries at 25.2the solar and wind
 were still shut down.
 We turned everything back on (a light, Sunfrost RF16, phone)  and all
 seems to be normal.
 
 They agreed to do the EQ process but only have a 3kw generator so we
 started with 8 hours with the EQ voltage set for 32v (24v system). They
 completed that yesterday and here's what resulted:
 
 Before starting EQ the batteries were at 25.8, hydrometer reading 1283
 with temp. correction
 Began EQ32.6 v
 Buying 
 1.5 kw
 Hour 1  32.4 v
 1283  with temp. correction   Buying  1.4
 Hour 2  32.4 v
   1285  with temp. correction  Buying 1.5
 Hour 3  32.2 v
 
 Buying 1.7
 Hour 4  32.2 v
   1290  with temp correctionBuying 1.8
 HOur 5 32.0 v
  1290   with temp correctionBuying 1.8
 Hour 6  32.0 v
 Buying 
 1.9
 Hour 7  31.8 v
1292 with temp correctonBuying 1.9
 Hour 8 complete---turned off Gen and turned on loads ---Batteries dropped
 to 25.4 within 30 minutes and stayed there until this morning---fridge was
 running, telephone, internet, wool carding machine, lights.  This morning
 hydrometer reading  was at 1290.
 
 
 
 Then today I just got this email:
 
 Just experienced another rapid voltage drop.  As soon as the voltage hits
 24.8 the voltage drops like a rock if we don't have any input (no solar or
 wind).
 
 This is not what I expected after a lengthy EQ. I'm getting them to 

[RE-wrenches] 90 degree wire bends

2011-11-16 Thread Marco Mangelsdorf
Some electricians have great fun in making 90 degree wire bends to try and
make their enclosure wiring look so purdy.

 

Given the importance of maintaining wiring radiuses, this can't be a good
idea, can it?  Is the issue greater resistance when the wire is bent at a
straight 90 degrees (or more)?

 

Thanks,

marco

 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Sizing 3 phase OCPD - main

2011-11-16 Thread Rebekah Hren
Hi wrenches, 

I have a
question about sizing the main OCP breaker for a panel combining the output of
several true three-phase output inverters. To be precise - 10 of the  Refusol 
20kW, which connect to  480V/277 Y with a max output of 24.1 amps, each
inverter has a 3 pole breaker, line a, b, c and a neutral, which doesn’t
apparently carry any current. 
 
Recommended
interconnection breaker is 35 Amps. Ok fine, but what should the main breaker 
and
main panel busbar rating be? 
 
What I’m not
sure about is if this is the right equation for the main breaker in a panel 
combining all ten inverter outputs: 
10  x 24.1A x √3
x 1.25  = 521.8 A
 
or is this the
right equation:
10 x 24.1A x
1.25 = 301.25 A
 
The busbar
rating should be easy, once I get the main disco OCPD figured out. 
Main OCPD + (10
x 35)  ≤ 120% busbar rating


Thanks for the help!
Rebekah Hren___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Sizing 3 phase OCPD - main

2011-11-16 Thread Mark Frye
Rebekah,
 
If you knew only the power and voltage, then you would use the root of 3 to
determine the amps. But since you know the amps, you don't need to use the
root.
 
The second equation would be the correct one.
 
Mark Frye 
Berkeley Solar Electric Systems 
303 Redbud Way 
Nevada City,  CA 95959 
(530) 401-8024 
 http://www.berkeleysolar.com/ www.berkeleysolar.com  
 

  _  

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Rebekah Hren
Sent: Wednesday, November 16, 2011 9:36 AM
To: RE-wrenches@lists.re-wrenches.org
Subject: [RE-wrenches] Sizing 3 phase OCPD - main


Hi wrenches, 


I have a question about sizing the main OCP breaker for a panel combining
the output of several true three-phase output inverters. To be precise - 10
of the  Refusol 20kW, which connect to  480V/277 Y with a max output of 24.1
amps, each inverter has a 3 pole breaker, line a, b, c and a neutral, which
doesn't apparently carry any current. 
Recommended interconnection breaker is 35 Amps. Ok fine, but what should the
main breaker and main panel busbar rating be? 
What I'm not sure about is if this is the right equation for the main
breaker in a panel combining all ten inverter outputs: 
10  x 24.1A x v3 x 1.25  = 521.8 A
or is this the right equation:
10 x 24.1A x 1.25 = 301.25 A
The busbar rating should be easy, once I get the main disco OCPD figured
out. 
Main OCPD + (10 x 35)  ? 120% busbar rating


Thanks for the help!
Rebekah Hren
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 90 degree wire bends

2011-11-16 Thread Ray Walters
It seems that if the strands were stretched and therefore thinned, that 
that would increase resistance, some. I think more importantly, the 
insulation  bunchs up and cracks, and is definitely compromised.  Also 
with strain hardening of copper, I'm sure some strands could break 
internally with a tight enough bend. I've heard at least for bare ground 
wires that lightning will jump off to the case at tight bends, but I've 
never actually seen that.
Aside from all that, is there actually an increased impedance from a 
tight bend (like in plumbing)? I don't know.
I've had to stop more than one journeyman from violating 300.34. I just 
tell them the bends should look like the long sweeps in conduit relative 
to the diameter of the wire: also purdy.


Aloha,

Ray

On 11/16/2011 10:35 AM, Marco Mangelsdorf wrote:


Some electricians have great fun in making 90 degree wire bends to try 
and make their enclosure wiring look so purdy.


Given the importance of maintaining wiring radiuses, this can't be a 
good idea, can it?  Is the issue greater resistance when the wire is 
bent at a straight 90 degrees (or more)?


Thanks,

marco



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] SW4048 AC Coupling

2011-11-16 Thread Richard L Ratico
Fellow Wrenches,

I would welcome some feedback on this one:

I may be adopting an eleven year old, Y2K, grid tie with battery back-up
system. It consists of 12 - Astro-Power 120 modules, installed in 2000, 12 -
Evergreen  EC-110 modules installed in 2004, only one MX60, which controls BOTH
sub-arrays, one SW4048 in SELL mode through a dedicated load sub-panel.
Existing, seven year old battery is shot (8-Trojan L-16). Initial bank of
unknown batteries was replaced after only four years.

Recent long, nearby, utility outages have the client requesting a proposal to
include a new back-up generator and to restore the system selling to the grid.
Client may decide go straight grid tie to eliminate the batteries. They have
found the maintenance to be a hassle.

My thoughts so far: 

1)To take advantage of most of the existing hardware, I wonder if it makes sense
to try to improve the system efficiency by relegating the SW to a manual back-up
mode only, where, say, by means of a timer controlling grid availability through
AC1, it would only charge a smaller battery bank, once a week. The bank would be
a single string of either, sealed gel units or T-105s with the new Trojan
watering system. 
2) Provide new grid-tie inverter/s to handle the net metering. 
3) Provide a way to AC couple the new inverter/s to the SW in the event of an
outage.
4) Provide a new Honda 3000 inverter type generator connected to AC2 in the SW.
5)Provide a way to lockout the grid tie inverter/s when the generator is
operating.

I think a few of you are still running your original SW inverters in grid tie
mode. Any upgrades? Am I going off the deep end here? 

Dick Ratico
Solarwind Electric
Bradford, VT
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] intermittent battery problem; ...Battery Sulfation

2011-11-16 Thread Ron Young
You're correct Larry, my apologies. Been burning the candle at both ends. 
Thanks for your input.

On 2011-11-16, at 9:04 AM, Larry Crutcher, Starlight Solar Power Systems wrote:

 Ron, you have misquoted me so yes you are wrong. It is not about getting to 
 32 volts. Go read it again.
 
 On Nov 16, 2011, at 12:20 AM, Ron Young wrote:
 
 Hi Daryl. I've got other KS25's in hybrid systems (wind gen  solar) that 
 seem to do fine over the last several years. The Ouback 3524 has an 85 amp 
 charger.  There was no problem getting to 32 v and holding it for eight 
 hours. This has been done twice now.  Larry and others attribute the ability 
 to get to 32v to a sulphated battery condition and I'm thinking that a 
 healthy battery could get to 32v as well, especially one that's been 
 regularly EQ'd... am I wrong?
 
 I'm listening to every opinion here and trying to sort it out but I think 
 John may be on the right track with an intermittent failure of one cell. I 
 just can't seem to find it.
 
 Ron Young
 
 On 2011-11-13, at 3:51 AM, penobscotso...@midmaine.com wrote:
 
 Ron,
 What comes to mind for me is that Surrette 5000 series batteries like
 to have a regular charge of C10.  KS25 cells are rated for 1350 ah,
 creating a need for a somewhat regularly occurring charge of 135 amps.
 I do believe the batteries are not ever getting that, except for very
 rare occasions. We have seen this before in undersized systems.
 Is the bulk charge set to 29.6? I would try a couple more eq's over the
 next month to loosen likely sulfation. Get it up to as close to 32
 volts as possible and taper the charge down, then eq at that voltage
 for four or five hours, even more if the client will do it.
 That would be how we would deal with this. It does seem ultimately to
 be sulfation that is the problem.
 
 Daryl DeJoy
 NABCEP Certified PV installer
 Penobscot Solar Design
 
 
 
 
 Folks, this one really has me puzzled. The client has done regular two
 hour EQ's, at least once a month. When did a site visit and I topped up
 the electrolyte (they'd been starving the batteries for water but always
 just above the plates) the problem seemed to go away. They were satisfied
 that the problem was solved but I wasn't and I told them what I had been
 hearing from this group - essentially that the batteries needed a deep EQ,
 discharge, recharge and EQ again two or three times to scrub the
 sulphates. They declined until just a few days ago when they said the
 rapid voltage drop was back. Here's a quote:
 
 We had another rapid voltage loss this morning ---it was 25.2 when we got
 up and it dropped rapidly to 22.8.  We turned on the generator and charged
 the batteries until our display showed 30.2  for awhile with the generator
 running.  We turned off the generator and the voltage settled at about
 26.4.  We turned off all loads and wind and solar.
 
 At 9.15 our batteries were at 26.4
 At 9:16 we turned on an 8W light bulb, a1600W hair dryer, and a 1.5HP
 (120V 5.75A) shop vac
 The display showed a load of 1.9kw
 At 9:40 the inverter shut down---display showed batteries at 18.4
 By 9.47 the display showed the batteries at 25.2the solar and wind
 were still shut down.
 We turned everything back on (a light, Sunfrost RF16, phone)  and all
 seems to be normal.
 
 They agreed to do the EQ process but only have a 3kw generator so we
 started with 8 hours with the EQ voltage set for 32v (24v system). They
 completed that yesterday and here's what resulted:
 
 Before starting EQ the batteries were at 25.8, hydrometer reading 1283
 with temp. correction
 Began EQ32.6 v
Buying 
 1.5 kw
 Hour 1  32.4 v
1283  with temp. correction   Buying  1.4
 Hour 2  32.4 v
  1285  with temp. correction  Buying 1.5
 Hour 3  32.2 v

 Buying 1.7
 Hour 4  32.2 v
  1290  with temp correctionBuying 1.8
 HOur 5 32.0 v
 1290   with temp correctionBuying 1.8
 Hour 6  32.0 v
Buying 
 1.9
 Hour 7  31.8 v
   1292 with temp correctonBuying 1.9
 Hour 8 complete---turned off Gen and turned on loads ---Batteries dropped
 to 25.4 within 30 minutes and stayed there until this morning---fridge was
 running, telephone, internet, wool carding machine, lights.  This morning
 hydrometer reading  was at 1290.
 
 
 
 Then today I just got this email:
 
 Just experienced another rapid voltage drop.  As 

Re: [RE-wrenches] intermittent battery problem; ...Battery Sulfation

2011-11-16 Thread Jeff Yago
Ron,

 

This reply a little late since I have been off line a few days.  I mentioned
in a similar thread last year that I had an off grid home client I designed
and installed in Idaho back in 1998 that had a Kohler 8.5 kw generator, a
Trace 4024 inverter, two separate solar arrays and Outback charge
controllers, and 16 Trojan L-16 batteries.  This system worked flawlessly
for 7 years and only required the generator a few hours per month, then it
was time to change the batteries.  I replaced the Trojans with the same size
battery made by Surrette and everything went to crap.  They had to run the
generator hours and hours to get them past an 80% charge and we had lots of
problems with overloading the generator even though we did not make any
program changes and used the same generator.  The generator was replaced 2
years later but this system  never worked like it did before the battery
replacement.

 

When researching all this at that time I had talked with Surrette, Trojan,
and anyone else that might help and this is what I found out.  Of course
there are just my opinions based on these conversations, but it is my
understanding that Surrette is a much longer life battery with much less
water loss when comparing apples and apples, and I was told this was due to
a different lead composition that Surrette uses than any other battery
manufacturer.  However, this difference requires a much longer
absorption/taper off charge process or you will never get it past 80%
charged.  This of course is almost impossible to achieve with a generator or
undersized solar array, and you really need a grid connection to fully
charge these things.  No doubt these would be great in some standby grid
connected system but I no longer use them in off grid.  This was also at a
time when battery manufacturers were just discovering solar so maybe battery
designs have changed.  Again, I think Surrette is a good company and makes a
great battery, but just not sure you can fully recharge them with a
mid-sized generator.

 

I also do not like using parallel battery layouts as its hard to keep one
string from pulling down the other strings when there is a low performance
cell so you might do a cell by cell check.

 

Good Luck,

 

Jeff Yago

DTI Solar Inc.

 




---

This is not what I expected after a lengthy EQ. I'm getting them to do
another one tomorrow after a discharge cycle and charge but I'm really
beginning to think we have something else going on here, something
electrical, not chemical. The rapid voltage drop is puzzling. 

 

To review, it's an Outback 3524 on an Epanel, Whisper 100  controller, 6
4KS 25 Surrette batteries in 24v configuration - 4.5 years old, .7kw solar.
I know the charging end is undersized but they have been compensating with
the generator and they get lots of wind in the fall, winter, spring.

 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Sizing 3 phase OCPD - main

2011-11-16 Thread Darryl Thayer
Hi rebecca, I assume the inverters are all true 3 phase, to check 20 
kW/480/1.73 = 24 amps this is what you expect on each leg.  You have 10 of 
these therefore 240 amps on each leg.  Solar is continous so you need x1.25 
this is of course 301 amps you need to select a 301 breaker, but I think 
NEC 240.6 will allow a 300 amp.  ((sorry I do not have my code book and I am on 
the road))  
Good Luck
Darryl 



From: Mark Frye ma...@berkeleysolar.com
To: 'Rebekah Hren' bekahh...@yahoo.com; 'RE-wrenches' 
re-wrenches@lists.re-wrenches.org
Sent: Wednesday, November 16, 2011 11:43 AM
Subject: Re: [RE-wrenches] Sizing 3 phase OCPD - main


 
Rebekah, 
  
If you knew only the power and voltage, then you would use the 
root of 3 to determine the amps. But since you know the amps, you don't need to 
use the root. 
  
The second equation would be the correct 
one. 
 
Mark Frye 
Berkeley Solar Electric Systems 
303 Redbud Way 
Nevada City,  CA 
95959 
(530) 
401-8024 
www.berkeleysolar.com   




 From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Rebekah 
Hren
Sent: Wednesday, November 16, 2011 9:36 AM
To: RE-wrenches@lists.re-wrenches.org
Subject: [RE-wrenches] Sizing 3 
phase OCPD - main

  
Hi 
wrenches,  
 
I have a 
question about sizing the main OCP breaker for a panel combining the output of 
several true three-phase output inverters. To be precise - 10 of the  
Refusol 20kW, which connect to  480V/277 Y with a max output of 24.1 amps, 
each inverter has a 3 pole breaker, line a, b, c and a neutral, which doesn’t 
apparently carry any current.   
Recommended 
interconnection breaker is 35 Amps. Ok fine, but what should the main breaker 
and main panel busbar rating be?   
What I’m not 
sure about is if this is the right equation for the main breaker in a panel 
combining all ten inverter outputs:  
10  x 
24.1A x √3 x 1.25  = 521.8 A  
or is this the 
right equation: 
10 x 24.1A x 
1.25 = 301.25 A  
The busbar 
rating should be easy, once I get the main disco OCPD figured out.  
Main OCPD + 
(10 x 35)  ≤ 120% busbar 
rating 
 
 
Thanks for the help!
Rebekah Hren 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] 3-phase wire run considerations

2011-11-16 Thread Luke Christy

Hi Folks,
In several months we will be installing a 100kW ground mounted PV  
system for one of our commercial customers. I'm in the planning stage  
and am looking at the wire runs. The site requires a 700' underground  
wire run between the 480V service and the single central inverter  
located at the array (a PVP100kW unit). I have two related questions:
1: Given the significant cost of the AC cabling for this situation,  
what is the most appropriate number to use for current in running  
voltage drop calcs? The wiring is going to be significantly oversized  
to achieve a ~1% VD at this length. I could use the max rated output  
current of the inverter (120A), but that seems like it might be overly  
conservative. Opinions?


2: It looks like the most cost effective and manageable solution for  
this run will involve several paralleled sets of cables. How important  
are the considerations of careful cable bundling? ie: putting several  
conductors per phase willy nilly in a trench vs having separate  
triplexed bundles.


Thanks in advance for your thoughts.



Luke Christy

NABCEP Certified PV Installer™: Certification #031409-25 (Luke Christy)
NABCEP Certified Solar Thermal Installer™: Certification #ST032611-03
 CoSEIA Certified PV Installer (Luke Christy)

Solar Gain Services, LLC
Monte Vista, CO.
sgsrenewab...@gmail.com






___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 90 degree wire bends

2011-11-16 Thread Darryl Thayer
I have seen the lightening damage at tight bends, but in my electrical career 
of 60+ years I have not seen any other
problems. 
Darryl  



From: Ray Walters r...@solarray.com
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Sent: Wednesday, November 16, 2011 12:11 PM
Subject: Re: [RE-wrenches] 90 degree wire bends


It seems that if the strands were stretched and therefore thinned, that that 
would increase resistance, some. I think more importantly, the insulation  
bunchs up and cracks, and is definitely compromised.  Also with strain 
hardening of copper, I'm sure some strands could break internally with a tight 
enough bend. I've heard at least for bare ground wires that lightning will jump 
off to the case at tight bends, but I've never actually seen that. 
Aside from all that, is there actually an increased impedance from a
tight bend (like in plumbing)? I don't know.  
I've had to stop more than one journeyman from violating 300.34. I
just tell them the bends should look like the long sweeps in conduit
relative to the diameter of the wire: also purdy.

Aloha,

Ray

On 11/16/2011 10:35 AM, Marco Mangelsdorf wrote: 
 
Some electricians have great fun in making 90 degree wire bends to try and 
make their enclosure wiring look so purdy. 
  
Given the importance of maintaining wiring radiuses, this can’t be a good 
idea, can it?  Is the issue greater resistance when the wire is bent at a 
straight 90 degrees (or more)? 
  
Thanks, 
marco 
   
 

___
List sponsored by Home Power magazine List Address: 
RE-wrenches@lists.re-wrenches.org Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules  
etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: 
www.members.re-wrenches.org
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 3-phase wire run considerations

2011-11-16 Thread Darryl Thayer
y seem to be on top of the situation.  I would use the MPPT wattage of the 
array for my source wattage.  devide by 480 volts and 1.73 for three phase and 
you have the current per leg.to do your voltage drop calcs from.   IO have not 
always been carefull to keep similar phases apart, but you will probibly buy 
your direct burrial in the form of triplex so lay them like you buy them.  Of 
course do not runn through metal holes unless balanced currents.  Also any time 
you make a short run, KEEP the length the same.  
 
DT 



From: Luke Christy sgsrenewab...@gmail.com
To: re-wrenches@lists.re-wrenches.org
Sent: Wednesday, November 16, 2011 9:51 PM
Subject: [RE-wrenches] 3-phase wire run considerations


Hi Folks,
In several months we will be installing a 100kW ground mounted PV system for 
one of our commercial customers. I'm in the planning stage and am looking at 
the wire runs. The site requires a 700' underground wire run between the 480V 
service and the single central inverter located at the array (a PVP100kW unit). 
I have two related questions: 
1: Given the significant cost of the AC cabling for this situation, what is the 
most appropriate number to use for current in running voltage drop calcs? The 
wiring is going to be significantly oversized to achieve a ~1% VD at this 
length. I could use the max rated output current of the inverter (120A), but 
that seems like it might be overly conservative. Opinions?

2: It looks like the most cost effective and manageable solution for this run 
will involve several paralleled sets of cables. How important are the 
considerations of careful cable bundling? ie: putting several conductors per 
phase willy nilly in a trench vs having separate triplexed bundles.

Thanks in advance for your thoughts.


  

Luke Christy 

NABCEP Certified PV Installer™: Certification #031409-25 (Luke Christy)
NABCEP Certified Solar Thermal Installer™: Certification #ST032611-03    
 CoSEIA Certified PV Installer (Luke Christy)

Solar Gain Services, LLC
Monte Vista, CO.
sgsrenewab...@gmail.com







___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 3-phase wire run considerations

2011-11-16 Thread William Miller

Luke:

Maximum inverter output will occur rarely.  Most of the time the 
inverter(s) will be running at lesser output amps.  One approach is to size 
wiring for a certain percentage of the average operating amps.  What is the 
average operating amps?  One way I have found to calculate this is use PV 
Watts and invoke the tool that gives a data set of hour by hour 
results.  This includes night time hours.  Delete all values with a zero 
output and average the rest.  I found a daily bell curve that is about 50% 
of full power.  Your results may vary.


Good luck,

William Miller

At 07:51 PM 11/16/2011, you wrote:
1: Given the significant cost of the AC cabling for this situation, what 
is the most appropriate number to use for current in running voltage drop 
calcs? The wiring is going to be significantly oversized to achieve a ~1% 
VD at this length. I could use the max rated output current of the 
inverter (120A), but that seems like it might be overly conservative. Opinions?




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] intermittent battery problem; ...Battery Sulfation

2011-11-16 Thread toddcory

I digress but... the best battery for grid tie with backup is not lead 
antimony, but lead calcuum. Surrette makes these too and they use next to no 
water and have a much longer warrantied life.
 
Todd
 
 
 
On Wednesday, November 16, 2011 6:52pm, Jeff Yago jry...@dtisolar.com said:


 
 No doubt these would be great in some standby grid connected system but I no 
longer use them in off grid.  This was also at a time when battery 
manufacturers were just discovering solar so maybe battery designs have 
changed. 


Sent from Finest Planet WebMail.
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org