Re: [RE-wrenches] automatic transfer switches

2019-11-25 Thread Jerry Shafer
There is the SMA Automatic transfer switch if you go with the SMA battery
inverter and SMA pv inverter, it can be located seperate of the battery and
inverter and will take up to 30 kwhrs. of capacity
Just a thought

On Mon, Nov 25, 2019, 10:52 PM Bill Hennessy  wrote:

> hi folks--
>
> We're installing a grid-tied, battery backup system on a farm where the
> service entrance is on a pole in the yard. At the single-phase, 240v,
> service entrance, there are two main breaker subpanels--one going to the
> house and one to the barn. The buildings are each about 100 feet away from
> the pole in opposite directions. The PV/battery system is located in the
> barn. When utility power is lost and the battery backup kicks in, we are
> looking for a way to bypass the house subpanel at the pole so it won't
> backfeed the grid.
>
> When the grid drops out, we need to tie the backup power coming from the
> barn to the line going to the house. We're thinking an automatic transfer
> switch installed at the pole will do the job, but the transfer switches
> seem to have built in delays to work with starting a generator. The
> switch does not have to be service entrance rated.
>
> It looks like the Asco 300 series has time delay adjustments, but it is
> pricey and has a seven-week lead time. (Thank-you PG)
>
> The battery backup system will switch over in milliseconds and we were
> hoping to find something similar for the transfer operation at the pole.  
> We're
> looking for something simple--hopefully a basic transfer switch that will
> quickly switch and drop out when grid power is restored.
>
> Would appreciate any thoughts or suggestions.
>
> regards, bill
>
> Bill Hennessy
> Berks Solar, LLC
> 371 Centennial Rd
> Mertztown, PA 19539
>
> o 610 682 4300
> c 484 560 4666
> NABCEP certified installer
> PA contractor #44411
> www.berkssolar.com
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



[RE-wrenches] automatic transfer switches

2019-11-25 Thread Bill Hennessy
hi folks--
We're installing a grid-tied, battery backup system on a farm where the service 
entrance is on a pole in the yard. At the single-phase, 240v, service entrance, 
there are two main breaker subpanels--one going to the house and one to the 
barn. The buildings are each about 100 feet away from the pole in opposite 
directions. The PV/battery system is located in the barn. When utility power is 
lost and the battery backup kicks in, we are looking for a way to bypass the 
house subpanel at the pole so it won't backfeed the grid. 

When the grid drops out, we need to tie the backup power coming from the barn 
to the line going to the house. We're thinking an automatic transfer switch 
installed at the pole will do the job, but the transfer switches seem to have 
built in delays to work with starting a generator. The switch does not have to 
be service entrance rated.

It looks like the Asco 300 series has time delay adjustments, but it is pricey 
and has a seven-week lead time. (Thank-you PG)

The battery backup system will switch over in milliseconds and we were hoping 
to find something similar for the transfer operation at the pole.  We're 
looking for something simple--hopefully a basic transfer switch that will 
quickly switch and drop out when grid power is restored.
Would appreciate any thoughts or suggestions. 

 regards, bill
Bill Hennessy
Berks Solar, LLC
371 Centennial Rd
Mertztown, PA 19539

o 610 682 4300
c 484 560 4666
NABCEP certified installer
PA contractor #44411
www.berkssolar.com___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Enphase

2019-11-25 Thread Bill Hennessy
And with all Enphase adapters, don't forget to check for continuity and 
connector seating before assembling. On occasion, we've found opens in the 
adapters.
bill

Bill Hennessy
Berks Solar, LLC
371 Centennial Rd
Mertztown, PA 19539

o 610 682 4300
c 484 560 4666
NABCEP certified installer
PA contractor #44411
www.berkssolar.com 

On Monday, November 25, 2019, 11:47:01 AM EST, Chris Schaefer 
 wrote:  
 
 Hi Jay,
Ran into the exact situation last install season with Enphase. After a lot of 
back and forth emails with pictures basically showing them I wasn't losing it, 
they finally deduced that they were packaging them wrong. So the package part 
number is correct but the adaptor inside the package is wrong. You'll have to 
dig deep into their engineering staff to clear this one up. I'm sorry but I 
couldn't find any emails on who I ended up dealing with on the issue.
Christopher
On Sat, Nov 23, 2019 at 10:45 AM Jay  wrote:

Hi all

I am replacing some old Enphase under the new replacement program. 
This one came with adapters to fit from the module Tyco ends to the 
inverterMC4. 

Except, the other end is Amphonel, not MC4. And the inverters are MC4. 

Is this the normal way from
Enphase or did The customer get something unusual/wrong. 

Thx 

Jay
Peltz power. 




___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org




-- 

Chris Schaefer’s

Tel/Fax585-229-2083 or Cell 585-748-1870 
5115South Hill Road ~ Canandaigua New York 14424
www.solarandwindfx.com ~ E-mail: ch...@solarandwindfx.com




Thomas Jefferson,the author of our great Constitution, once said, "democracy" 
willcease to exist when you take away from those who are willing to work and 
giveto those who would not."
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

  ___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Enphase

2019-11-25 Thread Chris Schaefer
Hi Jay,

Ran into the exact situation last install season with Enphase. After a lot
of back and forth emails with pictures basically showing them I wasn't
losing it, they finally deduced that they were packaging them wrong. So the
package part number is correct but the adaptor inside the package is wrong.
You'll have to dig deep into their engineering staff to clear this one up.
I'm sorry but I couldn't find any emails on who I ended up dealing with on
the issue.

Christopher

On Sat, Nov 23, 2019 at 10:45 AM Jay  wrote:

> Hi all
>
> I am replacing some old Enphase under the new replacement program.
> This one came with adapters to fit from the module Tyco ends to the
> inverterMC4.
>
> Except, the other end is Amphonel, not MC4. And the inverters are MC4.
>
> Is this the normal way from
> Enphase or did The customer get something unusual/wrong.
>
> Thx
>
> Jay
> Peltz power.
>
>
>
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>

-- 

Chris Schaefer’s


*Tel/Fax 585-229-2083 or Cell 585-748-1870 *
*5115 South Hill Road ~ Canandaigua New York 14424**www.solarandwindfx.com
 ~ E-mail: ch...@solarandwindfx.com
*


Thomas Jefferson, the author of our great Constitution, once said,
"democracy" will cease to exist when you take away from those who are
willing to work and give to those who would not."
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org