Re: [RE-wrenches] dual rated 600/1000v cable for HV battery application

2020-08-01 Thread Darryl Thayer
Also my supplier has XHHW rated at 1000 volts

On Sat, Aug 1, 2020, 9:18 PM Darryl Thayer  wrote:

> I would not worry as 1000 volt AC has a 1400 volt peak, voltage,
>
> On Sat, Aug 1, 2020, 10:33 AM Kirk Herander  wrote:
>
>> I need to spec battery cable for a nominal 850 vdc LFP bank. Several
>> brands of power cable list their rating at a dual 600/1000v. it is my
>> understanding that to be listed in this manner, the cable must pass a test
>> apply of over 600v for a short period  without breakdown. But under normal
>> operation IMO, the voltage is not to exceed 600v. And this test is done
>> with AC voltage, not DC.
>>
>> "*UL 1277: Power and Control Tray Cable*
>>
>> UL 1277, the standard for electrical power and control tray cable, was
>> recently updated, allowing manufacturers with UL approved tray cable to
>> market their product as 600V/1kV rated. To be dual rated, products must use
>> a recognized 1kV rated conductor and pass a higher voltage AC Hipot test on
>> the completed cable. This test requires each insulated conductor in
>> finished cable to withstand a specified voltage range for one minute
>> without breakdown. If a product passes the AC Hipot test, it is suitable
>> for 1kV use."
>>
>> Am I getting this right? And If so, one should not use this 600/1000v
>> wire if normal operating voltage is above 600v as is my case? Proper rating
>> should be dual 1000/2000v like PV wire?
>>
>> What do you experienced high voltage battery gurus use in my application?
>> Thanks.
>> ___
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] dual rated 600/1000v cable for HV battery application

2020-08-01 Thread Darryl Thayer
I would not worry as 1000 volt AC has a 1400 volt peak, voltage,

On Sat, Aug 1, 2020, 10:33 AM Kirk Herander  wrote:

> I need to spec battery cable for a nominal 850 vdc LFP bank. Several
> brands of power cable list their rating at a dual 600/1000v. it is my
> understanding that to be listed in this manner, the cable must pass a test
> apply of over 600v for a short period  without breakdown. But under normal
> operation IMO, the voltage is not to exceed 600v. And this test is done
> with AC voltage, not DC.
>
> "*UL 1277: Power and Control Tray Cable*
>
> UL 1277, the standard for electrical power and control tray cable, was
> recently updated, allowing manufacturers with UL approved tray cable to
> market their product as 600V/1kV rated. To be dual rated, products must use
> a recognized 1kV rated conductor and pass a higher voltage AC Hipot test on
> the completed cable. This test requires each insulated conductor in
> finished cable to withstand a specified voltage range for one minute
> without breakdown. If a product passes the AC Hipot test, it is suitable
> for 1kV use."
>
> Am I getting this right? And If so, one should not use this 600/1000v wire
> if normal operating voltage is above 600v as is my case? Proper rating
> should be dual 1000/2000v like PV wire?
>
> What do you experienced high voltage battery gurus use in my application?
> Thanks.
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] dual rated 600/1000v cable for HV battery application

2020-08-01 Thread Ray
I would look at Diesel Locomotive Cable  DLO, which is usually dual 
rated RHH/RHW-2 for us non locomotive folks.  2000 v rated. Its pretty 
easy to work with, flexible, but has a 2nd inner liner that gives it the 
higher volt rating.  Its also usually tinned conductors too.


https://www.awcwire.com/productspec.aspx?id=dlo

Ray Walters
Remote Solar
303 505-8760

On 8/1/20 7:09 AM, Kirk Herander wrote:
I need to spec battery cable for a nominal 850 vdc LFP bank. Several 
brands of power cable list their rating at a dual 600/1000v. it is my 
understanding that to be listed in this manner, the cable must pass a 
test apply of over 600v for a short period  without breakdown. But 
under normal operation IMO, the voltage is not to exceed 600v. And 
this test is done with AC voltage, not DC.


"*UL 1277: Power and Control Tray Cable*

UL 1277, the standard for electrical power and control tray cable, was 
recently updated, allowing manufacturers with UL approved tray cable 
to market their product as 600V/1kV rated. To be dual rated, products 
must use a recognized 1kV rated conductor and pass a higher voltage AC 
Hipot test on the completed cable. This test requires each insulated 
conductor in finished cable to withstand a specified voltage range for 
one minute without breakdown. If a product passes the AC Hipot test, 
it is suitable for 1kV use."



Am I getting this right? And If so, one should not use this 600/1000v 
wire if normal operating voltage is above 600v as is my case? Proper 
rating should be dual 1000/2000v like PV wire?


What do you experienced high voltage battery gurus use in my 
application? Thanks.


___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



[RE-wrenches] dual rated 600/1000v cable for HV battery application

2020-08-01 Thread Kirk Herander
I need to spec battery cable for a nominal 850 vdc LFP bank. Several brands of 
power cable list their rating at a dual 600/1000v. it is my understanding that 
to be listed in this manner, the cable must pass a test apply of over 600v for 
a short period  without breakdown. But under normal operation IMO, the voltage 
is not to exceed 600v. And this test is done with AC voltage, not DC.

"UL 1277: Power and Control Tray Cable

UL 1277, the standard for electrical power and control tray cable, was recently 
updated, allowing manufacturers with UL approved tray cable to market their 
product as 600V/1kV rated. To be dual rated, products must use a recognized 1kV 
rated conductor and pass a higher voltage AC Hipot test on the completed cable. 
This test requires each insulated conductor in finished cable to withstand a 
specified voltage range for one minute without breakdown. If a product passes 
the AC Hipot test, it is suitable for 1kV use."

Am I getting this right? And If so, one should not use this 600/1000v wire if 
normal operating voltage is above 600v as is my case? Proper rating should be 
dual 1000/2000v like PV wire?

What do you experienced high voltage battery gurus use in my application? 
Thanks.___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Trace SW 4048

2020-08-01 Thread Rick Brown
Marco,

Can you be more specific when you say not producing PV power? Do you mean no AC 
output? Given that these are battery-based inverters they’re not dependent on 
the PV to be present in order to operate. What state are the batteries in? Is 
the voltage stable when the inverter is in invert mode?

> On Aug 1, 2020, at 12:37 AM, Marco Mangelsdorf  wrote:
> 
> Aloha all,
> 
> I’ve got a pair of Trace, yes Trace, 4048s in a NEM system circa 2001. 
> 
> While I can’t find anything demonstrably wrong after hours of 
> troubleshooting, these buggers just don’t seem to be producing PV power when 
> they should.
> 
> I’m looking for a greybeard out there who’s well steeped in this fine 
> dinosaur for additional guidance, please.
> 
> Please contact me off list.
> 
> Mahalo,
> marco 
> ___
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 

rick brown
SolShine Energy Alternatives, LLC
Electrical & Solar Contracting Services
www.SolShineEnergyAlternatives.com
Check, Virginia 24072
540.808.9502

VA Class A Contractor Lic# 2705147660
VA Master Electrician Lic# 2710062762
VA Alternative Energy Systems Installer  
NABCEP Certified PV Installation Professional 110112-21



___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



[RE-wrenches] Trace SW 4048

2020-08-01 Thread Marco Mangelsdorf
Aloha all,

I’ve got a pair of Trace, yes Trace, 4048s in a NEM system circa 2001.

While I can’t find anything demonstrably wrong after hours of
troubleshooting, these buggers just don’t seem to be producing PV power
when they should.

I’m looking for a greybeard out there who’s well steeped in this fine
dinosaur for additional guidance, please.

Please contact me off list.

Mahalo,
marco
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org