Re: [RE-wrenches] Whole Home UPS, Generator Charging
Jason, We have had no demand for systems with no PV here in Hawaii but we are just a small outfit. As far as generators and Sol-Arks. We have always managed to get generators charging with Sol-Arks but it seems to be a challenge. I'll state the 2 obvious things which have tripped us up in the past which I am sure you have already tried. Battery Setup->Charge-> Amps (Our guys alway forget this is DC Amps) Always program the voltage setpoint in case closed-loop goes down In off-grid installs we always install on the grid-input with CTs. It seems to work better for us regardless of the size of the generator. Aloha, Lou Russo Owner l...@spreesolarsystems.com Office - 808 345 6762 Spree Solar Systems LLC CT-34322 On Mon, Oct 28, 2024 at 10:30 AM Jason Szumlanski via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > We are seeing an uptick in consumers looking for whole home battery backup > systems without solar panels for shorter grid outages. They either want > battery only or battery with generator charging capability, either portable > or fixed. > > I was planning on offering primarily Sol-Ark 15k for this scenario. But I > have had mixed results in getting any appreciable battery charging from > generators. I had a 48kW recently barely able to provide 3kW within the > Sol-Ark's parameters, and a 22kW that can charge at 18kW without breaking a > sweat. Portable generators are all over the map, too. I've used a Honda > 2200 inverter generator to charge at 1,500W, a piece of junk 8kW cage > rattler that was happy charging at 8kW, and a 5kW that didn't like giving > up even 500W. > > Is there any rhyme or reason to what generators are best or why this > happens? Sometimes I'm faced with clients that have existing generators and > I have to tell them that I can't promise how well it will work. That's not > a great sales pitch. > > Yes, I have adjusted the volt/freq windows and set the Sol-Ark to General > Standard. I have tried peak shaving with no real positive results for the > generators that performed poorly. > > Also, if Sol-Ark isn't the best answer, I'm open to alternatives. I also > considered installing these systems with separate 48V chargers connected to > the generator output, but I'm not sure how much better that will be and if > there are adjustable chargers I can use on a range of generator outputs. > > Any advice would be appreciated, and I would also like to know if others > are seeing this trend for whole home UPS. It could just be hurricane > related here, of course. > > Jason Szumlanski > Florida Solar Design Group > ___ > List sponsored by Redwood Alliance > > Pay optional member dues here: http://re-wrenches.org > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > There are two list archives for searching. When one doesn't work, try the > other: > https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org > > List rules & etiquette: > http://www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > http://www.members.re-wrenches.org > > ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org
Re: [RE-wrenches] All-In-Ones / Sol-Ark fail
Aloha All, Thank you Jason. This is a huge and surprising issue. So much so that I dropped what I was doing and called Sol-Ark to confirm. Mind you this was level 1 support, but I was told this is what the Sol-Arks are supposed to do and it is a feature not a bug. Their take is if there is any fault on any one string, the Sol-Ark assumes the worst and shuts everything down. I wonder what solutions could be implemented on future installs to prevent this from happening? Aloha, Lou Russo Owner l...@spreesolarsystems.com Office - 808 345 6762 Spree Solar Systems LLC CT-34322 On Thu, Oct 10, 2024 at 11:45 AM Jason Szumlanski via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > I think it's more likely water in a J-box or possibly physical damage, but > someone passed by the property and did not observe any physical damage to > the array. > > Jason Szumlanski > Principal Solar Designer | Florida Solar Design Group > NABCEP Certified Solar Professional (PVIP) > Florida State Certified Solar Contractor CVC56956 > Florida Certified Electrical Contractor EC13013208 > > > On Thu, Oct 10, 2024 at 5:41 PM Jay wrote: > >> Jason >> What’s the possibllity it was a lighting strike? >> >> Jay >> >> On Oct 10, 2024, at 2:57 PM, Jason Szumlanski via RE-wrenches < >> re-wrenches@lists.re-wrenches.org> wrote: >> >> >> We have been talking a lot recently about all-in-ones. I just had a >> massive fail during Hurricane Milton with a quad Sol-Ark 15K off-grid >> system that deserves some discussion about whether AIO is a good idea if it >> can't build in some resilience to errors. I'm not sure if the new Midnite >> unit is better in this respect, but this is what happened to the Sol-Ark >> system... >> >> Four inverters, each with 4 strings of PV paralleled to 2 MPPT per >> inverter. One of the slave units developed some sort of PV DC fault during >> the storm. This caused the slave inverter to shut down and throw an error, >> which in turn caused a parallel fault across all four inverters. Power >> output ceases at that point. Apparently the system keeps resetting because >> I have a cell modem that uploads data to Sol-Ark, but that cell modem is >> powered by the inverter outputs, so it must be getting power at least >> intermittently. The rest of the loads are basically flatlined according to >> the Sol-Ark data. It's mostly air conditioners, so they probably can't turn >> on fast enough before the PV fault causes another shutdown. >> >> So, in essence, one of 16 strings of PV develops a fault, and that causes >> all four inverters to malfunction? What is the point of redundancy if a >> fault of one results in a fault of all?! If there is a true PV input fault, >> shouldn't that just shut down that MPPT, or perhaps all of the PV DC input >> to that inverter? And why can't this inverter continue to invert power from >> the batteries and charge from a generator when there is a DC input fault >> that could be programmatically isolated and ignored? >> >> This is a bad design in my opinion, and something I hadn't considered. If >> the faulted inverter can't function with a DC input fault, it should just >> take itself out of the game. (This is 120/240 split phase, BTW). Is this >> how all AIO inverters work? One inverter fault on the DC side kills all >> paralleled units' AC output? Not good. >> >> This is a completely off-grid system on a remote island with no vehicle >> access, so it's not exactly easy to do a "truck roll" on this one, >> especially post-hurricane. To make matters worse, the generator was running >> at the time of the fault, as it was being signaled to run because the >> battery had reached the assigned charge voltage. The fault also killed the >> 2-wire start signal from the master, so the system also stopped passing >> through generator power to the loads. The house is dark. >> >> >> Jason Szumlanski >> Florida Solar Design Group >> >> ___ >> List sponsored by Redwood Alliance >> >> Pay optional member dues here: http://re-wrenches.org >> >> List Address: RE-wrenches@lists.re-wrenches.org >> >> Change listserver email address & settings: >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >> >> There are two list archives for searching. When one doesn't work, try the >> other: >> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ >> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org >> >> List rules & etiquette: >> http://www.re-wrenches.org/etiquette.htm >> >> Check out or update participant bios: >> http://www.members.re-wrenches.org >> >> ___ > List sponsored by Redwood Alliance > > Pay optional member dues here: http://re-wrenches.org > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > There are two list archives for searching. When
Re: [RE-wrenches] sol ark battery
Discover Rack Mount (you have to buy the outdoor rated enclosure separately) - Software is great and firmware is easily updated, standard rack mount aesthetics (not great looking) when installed without enclosure. HomeGrid (outdoor rated included) - Software is half baked and firmware is a pain to update, looks nice. Besides software we have not had any issues as of yet with either of these batteries. Aloha, Lou Russo Owner l...@spreesolarsystems.com Office - 808 345 6762 Spree Solar Systems LLC CT-34322 On Wed, Oct 9, 2024 at 8:39 AM MDElectricSolar via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Discover, Fortress, Simpliphi (briggs and > Stratton) > Michael D Nelson > MD Electric & Solar, Inc. > 707-684-0064 mobile > 707-884-1862 office > www.mdelectricsolar.com > www.facebook.com/mdelectricandsolar > > > > On Oct 9, 2024, at 11:32 AM, jay via RE-wrenches < > re-wrenches@lists.re-wrenches.org> wrote: > > > > HI All > > > > > > Wondering what people are using for lithium battery and sol ark? > > > > And no, LA is not a option for this system. > > > > Outdoor rated would be preferred, heated isn’t needed. > > > > thanks in advance > > > > jay > > > > > > > > ___ > > List sponsored by Redwood Alliance > > > > Pay optional member dues here: http://re-wrenches.org > > > > List Address: RE-wrenches@lists.re-wrenches.org > > > > Change listserver email address & settings: > > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > > > There are two list archives for searching. When one doesn't work, try > the other: > > https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ > > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org > > > > List rules & etiquette: > > http://www.re-wrenches.org/etiquette.htm > > > > Check out or update participant bios: > > http://www.members.re-wrenches.org > > > ___ > List sponsored by Redwood Alliance > > Pay optional member dues here: http://re-wrenches.org > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > There are two list archives for searching. When one doesn't work, try the > other: > https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org > > List rules & etiquette: > http://www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > http://www.members.re-wrenches.org > > ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org
Re: [RE-wrenches] UL3741
Derek is great and entertaining and has been on the UL3741 mission for a while now. Mayfield Renewables has a great video (1 hour long), though not as entertaining, that really digs into UL3741 https://youtu.be/FIPZibVbrus?si=LyI6TpLEMiV_8-GO On a side note, Mayfield Renewable is a great outfit to work with for your larger (greater the 100kW) installs. Aloha, Lou Russo Owner l...@spreesolarsystems.com Office - 808 345 6762 Spree Solar Systems LLC CT-34322 On Tue, Oct 8, 2024 at 5:55 PM david quattro wrote: > This is an excellent explanation of many aspects of 3741. > https://youtu.be/mgD0O9WfKVU?si=-SRdLuTd4XGDToKp > At the NABCEP conference in Raleigh earlier this year, there were > popular presentations about 3741. >I think it can be a great solution for some small commercial, but not > for residential. > > > > On Tue, Oct 8, 2024 at 12:41 PM Dave Tedeyan via RE-wrenches < > re-wrenches@lists.re-wrenches.org> wrote: > >> Hi Lou, >> >> It looks like Ironridge with the Midnite's MNSSR-600S-SS and some Solis >> Inverters (or Tesla) are compatible. But that is all I know of off the top >> of my head. >> >> https://www.ironridge.com/2024/02/27/flush-mount-systems-listed-to-ul-3741/ >> >> I have not actually pursued this yet, but would be curious to hear if >> others have and whether they like it. >> >> Cheers, >> Dave >> >> On Tue, Oct 8, 2024 at 3:01 PM Lou Russo via RE-wrenches < >> re-wrenches@lists.re-wrenches.org> wrote: >> >>> Hello Wrenches, >>> >>> We are researching UL3741 and NEC2020s Photovoltaic Hazard Control >>> System. Whether it is safe or not is a discussion for another time. >>> >>> After digging around a bunch it does not seem to be really geared toward >>> us residential (grid-tied and off-grid) and small commercial installers. >>> But I wanted to connect with folks who know the landscape better than us >>> before we disregard it for the foreseeable future. >>> >>> UL3741 listed racking systems and solar panels are not the limiting >>> factor, as there are enough manufacturers listed that we use regularly and >>> can get easily. It appears that Midnite's MNSSR-600S-SS may be a good path >>> for us as it has been tested with the Sol-Ark15k but from what I can tell >>> not to UL3741 standards. >>> >>> It seems the short list of compliant inverters with a compliant racking >>> system using Midnite's MNSSR-600S-SS is what would hold us back. As we >>> don't actively use any of the listed inverters. >>> >>> Has anyone heard from inverter manufacturers that are actively working >>> with a racking company on getting UL3741 or if they EVEN want to pursue it >>> (besides Tesla, Solis, SMA, GrowWatt)?Specifically battery based hybrid >>> inverters or charge controllers. I can't seem to find any. >>> >>> Thank you for your input. >>> >>> Aloha, >>> >>> Lou Russo >>> Owner >>> l...@spreesolarsystems.com >>> Office - 808 345 6762 >>> Spree Solar Systems LLC >>> CT-34322 >>> >>> ___ >>> List sponsored by Redwood Alliance >>> >>> Pay optional member dues here: http://re-wrenches.org >>> >>> List Address: RE-wrenches@lists.re-wrenches.org >>> >>> Change listserver email address & settings: >>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >>> >>> There are two list archives for searching. When one doesn't work, try >>> the other: >>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ >>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org >>> >>> List rules & etiquette: >>> http://www.re-wrenches.org/etiquette.htm >>> >>> Check out or update participant bios: >>> http://www.members.re-wrenches.org >>> >>> ___ >> List sponsored by Redwood Alliance >> >> Pay optional member dues here: http://re-wrenches.org >> >> List Address: RE-wrenches@lists.re-wrenches.org >> >> Change listserver email address & settings: >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >> >> There are two list archives for searching. When one doesn't work, try the >> other: >> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ >> http://lists.re-wrenches.
[RE-wrenches] UL3741
Hello Wrenches, We are researching UL3741 and NEC2020s Photovoltaic Hazard Control System. Whether it is safe or not is a discussion for another time. After digging around a bunch it does not seem to be really geared toward us residential (grid-tied and off-grid) and small commercial installers. But I wanted to connect with folks who know the landscape better than us before we disregard it for the foreseeable future. UL3741 listed racking systems and solar panels are not the limiting factor, as there are enough manufacturers listed that we use regularly and can get easily. It appears that Midnite's MNSSR-600S-SS may be a good path for us as it has been tested with the Sol-Ark15k but from what I can tell not to UL3741 standards. It seems the short list of compliant inverters with a compliant racking system using Midnite's MNSSR-600S-SS is what would hold us back. As we don't actively use any of the listed inverters. Has anyone heard from inverter manufacturers that are actively working with a racking company on getting UL3741 or if they EVEN want to pursue it (besides Tesla, Solis, SMA, GrowWatt)?Specifically battery based hybrid inverters or charge controllers. I can't seem to find any. Thank you for your input. Aloha, Lou Russo Owner l...@spreesolarsystems.com Office - 808 345 6762 Spree Solar Systems LLC CT-34322 ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org
[RE-wrenches] 120/240V to 200V 3 phase (Japanese Electrical Scheme)
Aloha All, I have a project that requires powering 6 different pieces of equipment (mostly small motors) from East Japan that require 200V 3 phase (L-L-L) at 50Hz (though 60Hz appears to be OK), a unique electrical scheme for sure. The amp requirement for the various pieces of equipment ranges from 0.75A to 6A. For a total maximum load of 28 amps. The site is off-grid with standard 120/240V North American Electrical Scheme using a Sol-Ark 15kW. My initial plan was to use Digital Phase Converters from MYUNG YOUN ELECTRONICS for each device but after seeing the wiring in the control panel and power distribution box in person there is no room to do this. Plus the entire panel would need to be rewired. Ideally, I would have one device that converts the electricity appropriately (transformer, VFD, etc). I have reached out to several EEs and am awaiting responses. In the meantime I figured the hive mind of the Wrenches group may have some ideas or know somebody that would. As always, thanks for everyone's time. Aloha, Lou Russo Owner l...@spreesolarsystems.com Office - 808 345 6762 Direct Line - 808 731 1907 Spree Solar Systems LLC CT-34322 ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org
[RE-wrenches] N.C. - Wilmington area quality installers
Aloha All, I have a family member in the Wilmington North Carolina area (Carolina Beach specifically) that is wanting to go solar. Any wrenches out there in this area? or could you make a recommendation? Contact me off list. Aloha, Lou Russo Owner l...@spreesolarsystems.com 808 345 6762 Spree Solar Systems LLC CT-34322 ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org
Re: [RE-wrenches] Optics
I started poking through EnerSys's (The most recent owner of Outback) SEC filings in hopes to find who the new buyer is. I found nothing related to the sale but found this in their most recent quarterly report : On November 8, 2023, the Company's Board of Directors approved a plan to stop production and operations of residential renewable energy products, which include our OutBack and Mojave brands. Management determined that residential renewable energy products no longer fit with the company’s core strategy and resources will be better allocated toward commercial energy solutions for enterprise customers. The Company currently estimates that the total charges for these actions will amount to $23.5 million relating primarily to $22.6 million in non-cash charges primarily including inventory and an indefinite-lived intangible asset write-offs and $0.9 million in cash charges including employee severance and retention payments. The plan is expected to be completed in fiscal 2024. During the nine months of fiscal 2024, the Company recorded non-cash charges totaling $6.6 million primarily related to indefinite-lived intangible asset write-off and cash charges of $0.4 million related to severance costs. The Company also recorded a non-cash write off relating to inventories of $16.1 million, which was reported in cost of goods sold. To say I am curious about what is going on is an understatement. Aloha, Lou Russo Owner l...@spreesolarsystems.com 808 345 6762 Spree Solar Systems LLC CT-34322 On Sun, May 19, 2024 at 2:21 AM Jay via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > I agree with you William > > While there could be all sorts of valid reasons for the downtime. > > What’s not acceptable is the lack of communication and notification that > it was going to happen or had happened. > > If they do have new owners they are not starting well. > > Jay > > > > On May 18, 2024, at 9:42 PM, William Miller via RE-wrenches < > re-wrenches@lists.re-wrenches.org> wrote: > > > > Friends: > > > > I am sure you are all acutely aware, but this is not a trivial matter. We > depend on Optics for alerts and trouble shooting. We rely on Optics for > the history it records to analyze trends and evaluate production and > consumption. I doubt the data lost will back-fill. I sell Outback based in > great part on the Optics interface. For this system to be down for days at > a time is not a good sign at all. > > > > I will be lighting up the phone lines on Monday to find out what happened > and to emphasize this cannot become a pattern. > > > > William > > > > Miller Solar > > 17395 Oak Road, Atascadero, CA 93422 > > 805-438-5600 > > www.millersolar.com > > CA Lic. 773985 > > > > > > *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On > Behalf Of *Lou Russo via RE-wrenches > *Sent:* Saturday, May 18, 2024 11:50 AM > *To:* RE-wrenches > *Cc:* Lou Russo > *Subject:* Re: [RE-wrenches] Optics > > > > All my sites are currently down. > > > > Not related but I tried to call tech support yesterday during business > hours and got message saying thank you for calling Outback Sales leave a > message. > > > > I do hope they are just in transition but I got a bad feeling about this. > I hope I am wrong. > > > > Has anyone heard for sure who bought them? I know they were bought from > talking to tech support but that is all I know and the Internet has 0 info > on a recent sale. > > > > On Sat, May 18, 2024, 6:48 AM Dan Fink via RE-wrenches < > re-wrenches@lists.re-wrenches.org> wrote: > > Mine all went down yesterday at noon MDT. I wonder if this has to do with > the sale of Outback? > > > Dan Fink > > Owner, Buckville Energy Consulting LLC > > IREC Certified Instructor for PV and Small Wind Installation > > NABCEP Certified PV System Inspector > > NABCEP PV Associate > > d anbo...@gmail.com > > 970-672-4342 > > > > > > > > > On Sat, May 18, 2024 at 10:17 AM William Miller via RE-wrenches < > re-wrenches@lists.re-wrenches.org> wrote: > > Friends: > > > > 100% of our Optics sites are down since 11 AM yesterday. Is it just us? > > William Miller > Miller Solar.com > 805-438-5600 > www.millersolar.com > > > > ___ > List sponsored by Redwood Alliance > > Pay optional member dues here: http://re-wrenches.org > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > There are two list archives fo
Re: [RE-wrenches] Optics
All my sites are currently down. Not related but I tried to call tech support yesterday during business hours and got message saying thank you for calling Outback Sales leave a message. I do hope they are just in transition but I got a bad feeling about this. I hope I am wrong. Has anyone heard for sure who bought them? I know they were bought from talking to tech support but that is all I know and the Internet has 0 info on a recent sale. On Sat, May 18, 2024, 6:48 AM Dan Fink via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Mine all went down yesterday at noon MDT. I wonder if this has to do with > the sale of Outback? > > Dan Fink > Owner, Buckville Energy Consulting LLC > IREC Certified Instructor for PV and Small Wind Installation > NABCEP Certified PV System Inspector > NABCEP PV Associate > d anbo...@gmail.com > 970-672-4342 > > > > > On Sat, May 18, 2024 at 10:17 AM William Miller via RE-wrenches < > re-wrenches@lists.re-wrenches.org> wrote: > >> Friends: >> >> 100% of our Optics sites are down since 11 AM yesterday. Is it just us? >> >> William Miller >> Miller Solar.com >> 805-438-5600 >> www.millersolar.com >> >> ___ > List sponsored by Redwood Alliance > > Pay optional member dues here: http://re-wrenches.org > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > There are two list archives for searching. When one doesn't work, try the > other: > https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org > > List rules & etiquette: > http://www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > http://www.members.re-wrenches.org > > ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org
Re: [RE-wrenches] REC modules - review?
We have installing REC for 15 years with no issues. George and his team have been nothing but awesome to work with. We have never had to file a warranty claims. As a certified installer the improved warranty and labor credit if there is a claim has been a great selling point for us as well. Their app for registering panels is easy. On Fri, May 17, 2024, 6:54 AM david quattro via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Hi everyone, > Does anyone have positive or negative experience with REC modules? > Specifically failure rate, and how the company acts when an RMA is > necessary. Thank you > > David Quattro > > CA License # 954020. C-10, C-46 > ph (415) 312-2661 > www.quattrosolar.com > > > ___ > List sponsored by Redwood Alliance > > Pay optional member dues here: http://re-wrenches.org > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > There are two list archives for searching. When one doesn't work, try the > other: > https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org > > List rules & etiquette: > http://www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > http://www.members.re-wrenches.org > > ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org
Re: [RE-wrenches] Sol-Ark 15kW 200A Load Breaker short-circuit rating?
6kA in case anyone ever needs it. Aloha, Lou Russo Owner l...@spreesolarsystems.com 808 345 6762 Spree Solar Systems LLC CT-34322 On Fri, Apr 12, 2024 at 5:26 AM Lou Russo wrote: > Aloha All, > > Sorry, I was confusing my terms. Coffee has yet to kick in. > > I am looking for the AIR rating. > > Aloha, > > Lou Russo > Owner > l...@spreesolarsystems.com > 808 345 6762 > Spree Solar Systems LLC > CT-34322 > > > > On Fri, Apr 12, 2024 at 4:57 AM Lou Russo > wrote: > >> Aloha All, >> >> Does anyone out there know the short-circuit rating of the 200A load >> breaker on the SOL-Ark 15kW Outdoor. >> >> The manual and spec sheet do not list it. Tech support did not know, >> which is concerning. >> >> Aloha, >> >> Lou Russo >> Owner >> l...@spreesolarsystems.com >> 808 345 6762 >> Spree Solar Systems LLC >> CT-34322 >> >> ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org
Re: [RE-wrenches] Sol-Ark 15kW 200A Load Breaker short-circuit rating?
Aloha All, Sorry, I was confusing my terms. Coffee has yet to kick in. I am looking for the AIR rating. Aloha, Lou Russo Owner l...@spreesolarsystems.com 808 345 6762 Spree Solar Systems LLC CT-34322 On Fri, Apr 12, 2024 at 4:57 AM Lou Russo wrote: > Aloha All, > > Does anyone out there know the short-circuit rating of the 200A load > breaker on the SOL-Ark 15kW Outdoor. > > The manual and spec sheet do not list it. Tech support did not know, which > is concerning. > > Aloha, > > Lou Russo > Owner > l...@spreesolarsystems.com > 808 345 6762 > Spree Solar Systems LLC > CT-34322 > > ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org
[RE-wrenches] Sol-Ark 15kW 200A Load Breaker short-circuit rating?
Aloha All, Does anyone out there know the short-circuit rating of the 200A load breaker on the SOL-Ark 15kW Outdoor. The manual and spec sheet do not list it. Tech support did not know, which is concerning. Aloha, Lou Russo Owner l...@spreesolarsystems.com 808 345 6762 Spree Solar Systems LLC CT-34322 ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org
Re: [RE-wrenches] Plaques
Aloha Wrenches, Kirpal, I was looking at the Vision product line. What model did you purchase? We work out in the boonies and driving 35 minutes to town to pick up a $75 directory from the trophy shop is getting old. On Sat, Mar 30, 2024, 5:48 PM Kirpal Khalsa via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Hi Lou and all. > We dove all in and got a Vision Engraving machine. They offer several > models and the most basic version works just fine. It was a big investment > but we can make our own placatds in the same day. > We have a dedicated cheap laptop and a vacuum attachment they sell which > keeps the work area clean. There was a learning curve but we won after a > bit. > Its really nice to have and to have the flexibility makes that an aspect > of job management much less complicated. My guess is that it will take 3-4 > years to pay for itself. > We like having it and my only regret us that we didnt get one sooner. > > On Sat, Mar 30, 2024, 11:57 AM Lou Russo via RE-wrenches < > re-wrenches@lists.re-wrenches.org> wrote: > >> Aloha Wrenches, >> >> Anyone out there making their own engraved plaques and labels? >> If so, is it worth it and what machine are you using? >> Thanks for your time and insight, it is always appreciated. >> >> Aloha, >> >> Lou Russo >> Owner >> l...@spreesolarsystems.com >> 808 345 6762 >> Spree Solar Systems LLC >> CT-34322 >> >> ___ >> List sponsored by Redwood Alliance >> >> Pay optional member dues here: http://re-wrenches.org >> >> List Address: RE-wrenches@lists.re-wrenches.org >> >> Change listserver email address & settings: >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >> >> There are two list archives for searching. When one doesn't work, try the >> other: >> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ >> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org >> >> List rules & etiquette: >> http://www.re-wrenches.org/etiquette.htm >> >> Check out or update participant bios: >> http://www.members.re-wrenches.org >> >> ___ > List sponsored by Redwood Alliance > > Pay optional member dues here: http://re-wrenches.org > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > There are two list archives for searching. When one doesn't work, try the > other: > https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org > > List rules & etiquette: > http://www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > http://www.members.re-wrenches.org > > ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org
[RE-wrenches] Plaques
Aloha Wrenches, Anyone out there making their own engraved plaques and labels? If so, is it worth it and what machine are you using? Thanks for your time and insight, it is always appreciated. Aloha, Lou Russo Owner l...@spreesolarsystems.com 808 345 6762 Spree Solar Systems LLC CT-34322 ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org
[RE-wrenches] Schneider Insight Home and Insight Cloud
Aloha All, I recently installed 2 new off-grid systems using all Scneider products, Discover 7.4 batteries and the Insight Home all setup in Insight Cloud. Both systems are experiencing communications issues with Insight Cloud and a bit on the Xanbus. Though each in a different way. Before I go into specifics, has anyone else been having issues with Insight Cloud or the Xanbus recently? Just wondering if it is a me problem or a they problem. I have gone through all the standard tech support phone call instructions. All firmware updated, comms cables checked, internet speeds confirmed to be good, system set back to system defaults and reprogrammed, etc... Thanks for your time. Aloha, Lou Russo Owner l...@spreesolarsystems.com 808 345 6762 Spree Solar Systems LLC CT-34322 ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org
Re: [RE-wrenches] Automatic load control
Aloha Howie, The Lumin Smart Panel has worked well for us. https://www.luminsmart.com/ Software is simple and tech support was on point. The app works well also. Bonus...you can remotely monitor power consumption on each controlled load. Two minor hang ups: 1. Having to run a separate "grid sense" circuit. This circuit has to be pulled from a location that is on the grid side of the Sol-Ark. This can be in a pain when the load you wanna dump is on sub panel clear across the property from the inverter. I am sure this the case with all these load shedding type devices. 2. You have to do a training to install them. It was a short webinar. Super easy. On Fri, Dec 15, 2023, 2:28 AM William Miller via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Howie: > > Segregated load distribution. Simple, automatic. > > I don’t get why they put 200 amp pass-through on an inverter that can only > produce 62.5 amps. > > > William Miller > Miller Solar.com > 805-438-5600 > www.millersolar.com > > > On Thu, Dec 14, 2023 at 6:37 PM Howie Michaelson via RE-wrenches < > re-wrenches@lists.re-wrenches.org> wrote: > >> Hi all, >> >> I am trying to figure out best options to control loads in a Sol-Ark15k >> battery backup residential system. It's been quite a few years since I've >> set up an automatic load control, and never with a Sol-Ark. The Sol-Ark >> will output to the main breaker panel, so no separate "backed up" panel - >> all house loads will likely be on the Sol-Ark's load side. >> >> What do folks like to use in this type of circumstance to automatically >> shed loads when the grid is down, either sequentially as the battery bank >> drops down or more simply triggered by loss of grid? Are they pieces of >> equipment that work specifically with the Sol-Ark? >> I'd also be open to considering Fortress's Envy, if there is an option >> that would work well specifically with it. >> I'm interested in the range of options from simple to complicated, as >> long as it is automated. All automated ideas/options appreciated. >> Thanks! >> Howie Michaelson >> Sun Catcher >> ___ >> List sponsored by Redwood Alliance >> >> Pay optional member dues here: http://re-wrenches.org >> >> List Address: RE-wrenches@lists.re-wrenches.org >> >> Change listserver email address & settings: >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >> >> There are two list archives for searching. When one doesn't work, try the >> other: >> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ >> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org >> >> List rules & etiquette: >> http://www.re-wrenches.org/etiquette.htm >> >> Check out or update participant bios: >> http://www.members.re-wrenches.org >> >> ___ > List sponsored by Redwood Alliance > > Pay optional member dues here: http://re-wrenches.org > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > There are two list archives for searching. When one doesn't work, try the > other: > https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org > > List rules & etiquette: > http://www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > http://www.members.re-wrenches.org > > ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org
[RE-wrenches] Looking for software platforms
Aloha All, We are exploring software platforms to manage service calls (HouseCall Pro, Service Titan, etc...) The feature set on these service call related platforms seem to be great for that component of our business but we also need to manage the full installation side of the business and every growing paperwork flow to make sure things don't slip through the cracks. Ideally these 2 needs would be met by one platform and allow us to move on from the Google Workspace kludge, which has been great up until now. I don't know if it is even possible! I am wondering if you all are currently using any software platforms to meet these needs (separately or together) and what your experience has been. Thanks! Aloha, Lou Russo Owner l...@spreesolarsystems.com 808 345 6762 Spree Solar Systems LLC CT-34322 ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org
Re: [RE-wrenches] XW Pro failures
I had a 7 year-old one die 1.5 months ago. F41 APS Under Voltage. No ugly sounds. Just no power. I don't have many out there but this is the first. Aloha, Lou Russo (808) 345 6762 On Fri, Oct 13, 2023 at 4:47 AM Michael Morningstar via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Funny you should say that. One that I just installed is acting weird and > sounds horrible. Waited an hour on the phone for tech support to no avail. > Will be a really long drive back to sort things out. Never had an XW with > issues before. > > On Thu, Oct 12, 2023 at 9:29 PM Kevin Pegg via RE-wrenches < > re-wrenches@lists.re-wrenches.org> wrote: > >> Hello Wrenches, >> >> >> >> Curious if anyone else is dealing with failed Schnieder XW PRO6848’s this >> year? In recent months I’ve had 2 DOA (one producing 180/360VAC; one >> charger had this nasty building THD and ugly noise until it tripped out), >> and 2 fail after few weeks in service. One charger just failed, and another >> have yet to take the long drive to figure out but it’s gone dark. >> >> >> >> I’ve sold, serviced, and installed 100’s of XW’s starting with Beta 001 >> and can’t think of any that just failed like of recent. Unplanned return >> service calls are costly as we all know. Tech support has been wildly >> inconsistent and presently unresponsive. >> >> >> >> Thanks, >> >> >> >> Kevin Pegg >> >> EA Energy Alternatives Ltd. >> >> Telkwa, BC V0J 2X2 >> >> >> >> >> ___ >> List sponsored by Redwood Alliance >> >> Pay optional member dues here: http://re-wrenches.org >> >> List Address: RE-wrenches@lists.re-wrenches.org >> >> Change listserver email address & settings: >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >> >> There are two list archives for searching. When one doesn't work, try the >> other: >> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ >> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org >> >> List rules & etiquette: >> http://www.re-wrenches.org/etiquette.htm >> >> Check out or update participant bios: >> http://www.members.re-wrenches.org >> >> > > -- > > Michael Morningstar > > > Morningstar Electric > > PO Box 1494 > > Mount Shasta, CA 96067 > > 530-921-0560 > > mjmornings...@gmail.com > > > ___ > List sponsored by Redwood Alliance > > Pay optional member dues here: http://re-wrenches.org > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > There are two list archives for searching. When one doesn't work, try the > other: > https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org > > List rules & etiquette: > http://www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > http://www.members.re-wrenches.org > > ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org
Re: [RE-wrenches] SOK Batteries
I would call Current Connected in Nevada. They handle SOKs for the US market and I have found there tech support to be knowledgeable and timely. On Wed, Oct 11, 2023, 2:06 PM Jay via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Buy another SOK battery so that doesn’t happen. > > Or maybe happens less > > Jay > > > > On Oct 11, 2023, at 5:55 PM, Kristopher Schmid via RE-wrenches < > re-wrenches@lists.re-wrenches.org> wrote: > > > Hello brain trust, > > Anyone have experience with SOK lithiums? Here's my issue. Client has a > tiny home and bought their system online (I know, run away...). Whenever > they start a larger load (power tool, hair dryer) it pulls too much current > and causes the BMS to shut down the battery output. Not necessarily a huge > issue, but I cannot get the app (ABC-BMS) to reset the batteries. I log in > with the password and it gives me the reset option, but it will not allow > me to click OK. Hooking up an external battery charger has been my only > successful reset solution. > > Any help would be greatly appreciated. > > Thanks, > Kris > > Shine On! > > Kris Schmid > Legacy Solar, LLC > 137 West 1st Avenue > Luck, WI 54853 > www.legacysolar.com > 715-653-4295 > NABCEP Certified PV Installation Professional > Licensed Wisconsin Master Electrician > BSEE > ___ > List sponsored by Redwood Alliance > > Pay optional member dues here: http://re-wrenches.org > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > There are two list archives for searching. When one doesn't work, try the > other: > https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org > > List rules & etiquette: > http://www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > http://www.members.re-wrenches.org > > ___ > List sponsored by Redwood Alliance > > Pay optional member dues here: http://re-wrenches.org > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > There are two list archives for searching. When one doesn't work, try the > other: > https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org > > List rules & etiquette: > http://www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > http://www.members.re-wrenches.org > > ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org
Re: [RE-wrenches] Sol-Ark 15k Conduit Entries
Hello All, Super impressive install, Michael. Almost worth a flight, and a site visit! Back to Jason's initial question If you are using the 15kW Outdoor Sol-Ark they vent from the top and bottom with a required 6" minimum spacing on both the top and bottom. A 12kW Outdoor with 8x8 gutter and 1" offset nipples have worked great for us. Aloha, Lou Russo (808) 345 6762 On Thu, Aug 3, 2023 at 7:09 AM Michael Morningstar via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Hi Drake, > Those are single phase combiner panels. I would have loved to set this up > as a three phase system, but there was already a mile of underground single > phase run throughout the property. We ended up running a half mile 15KV > line from the power site to the estate. This is an aside, it's kind of hard > to see, but for seperation, we attached the pv circuits to the back of the > gutter using through bolted adhesive backed cable tie holders. Often we use > gutter dividers. They originate in the tall cabinet at the end which houses > controls, secondary PV disconnects, AC and DC egauges, Tigo hub, Battery > hub and (Lynk II). On the opposite end is a similar cabinet for the > collection and distribution of AC circuits. Also, above and below the > batteries are small gutters for communications and CT wires that run from > the transfer switches to eguage. One transfer switch to alternate usage > (alternating relay) or bypass between Gen 1 and Gen 2, and the other switch > to select inverter or generator power, locally or remotely. In the AC > cabinet there is a 400a contactor and time delay relay to achieve a > generator cooldown as the janky Sol-Arks don't do that and it's hell on new > diesels not to have that function. > > On Thu, Aug 3, 2023 at 7:50 AM Drake Chamberlin via RE-wrenches < > re-wrenches@lists.re-wrenches.org> wrote: > >> That looks really nice. How were you able to put 8 Sol Arc inverters on a >> 3 phase panel? Tech support told me that inverters had to be connected in >> groups of 3. >> >> Thank you, >> >> Drake >> >> >> *Drake Chamberlin* >> >> *Athens Electric LLC* >> >> *Ohio Electrical Contractor’s License 44810* >> >> *CO Master Electrician’s License 4526* >> >> *NABCEP Certified PV Installation Professional* >> --- >> >> >> >> On 2023-08-02 14:19, Michael Morningstar via RE-wrenches wrote: >> >> 10x10 gutter. Notice within, a 2.5x2.5 gutter for comms. 1 x 2.5" nipples >> work well. Chase nipples wont due to door clearance. I've also cut the >> bottoms out of the Sol-Arks and a corresponding square window in the >> gutter, placed a 1/4" rubber gasket between the two. We do that when we >> have many VFD's over a gutter. Someone a while ago asked for a picture >> showing how we make long bussbars. This one is 24' long. >> >> On Wed, Aug 2, 2023 at 10:08 AM Jerry Shafer via RE-wrenches < >> re-wrenches@lists.re-wrenches.org> wrote: >> >> Jason >> In plenty of applications l will use couplers with chase nipples, height >> is one issue but installed working height is very important. I use a 8"x8"x >> X gutter and sometimes even off set that from the wall, l have had AHJ not >> want to see mixed cables LVDC and AC in the same conduit so pass through >> the battery conductors right out the bottom and to the battery. I just >> create a template for punching into the gutter, looks clean and is safe >> with easy access to the display >> Fun times >> >> On Wed, Aug 2, 2023, 8:04 AM Jason Szumlanski via RE-wrenches < >> re-wrenches@lists.re-wrenches.org> wrote: >> >> I see a lot of pictures with conduit nipples coming out of a gutter that >> are fairly long. I have a height limit issue and I'm wondering if there are >> any negative implications of using very short nipples between a wireway >> below and the inverter. I'm thinking about using close nipples or perhaps >> 2-in nipples if I have enough room. >> >> If there are any practical reasons that this will not work well, please >> let me know. >> >> Jason Szumlanski >> Florida Solar Design Group >> ___ >> List sponsored by Redwood Alliance >> >> Pay optional member dues here: http://re-wrenches.org >> >> List Address: RE-wrenches@lists.re-wrenches.org >> >> Change listserver email address & settings: >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >> >> There are two list archives for searching. When one doesn't work, try the >> other: >> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ >> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org >> >> List rules & etiquette: >> http://www.re-wrenches.org/etiquette.htm >> >> Check out or update participant bios: >> http://www.members.re-wrenches.org >> >> ___ >> List sponsored by Redwood Alliance >> >> Pay optional member dues here: http://re-wrenches.org >> >> List Address: RE-wrenches@lists.re-wrenches.org >> >> Change listserver email address & settings: >> h
Re: [RE-wrenches] HomeGrid batteries
That was a bit of a cavalier statement on my part. On paper the tech specs look good. The warranty (60% after ten years or 3650 cycles) and initial track record is what I think is mediocre. . I guess in comparison to Blue Planet most battery warranties look mediocre. Aloha, Lou Russo (808) 345 6762 On Tue, Oct 11, 2022 at 3:09 AM Bradley Bassett wrote: > I'm curious what you consider mediocre about the HomeGrid? > > Brad > > On Mon, Oct 10, 2022 at 7:07 PM Lou Russo via RE-wrenches < > re-wrenches@lists.re-wrenches.org> wrote: > >> Aloha All, >> >> I am considering doing a job with one of these (14kWH) with a Sol-Ark >> 12kW for a client who is demanding them. Anyone have any recent >> experience with them? >> The price is good but all else is pretty mediocre. >> >> Aloha, >> >> Lou Russo >> (808) 345 6762 >> >> >> >> On Thu, Aug 18, 2022 at 4:46 PM Jerry Shafer via RE-wrenches < >> re-wrenches@lists.re-wrenches.org> wrote: >> >>> The cycle life sounds good the warranty cycle for off grid is far less >>> than blue planet and fortress. If you compare the fortress x 2, 18.5's with >>> a better warranty it comes out cheaper. I do see a display but l only see >>> volts. Pretty low surge, is there US warranty administration? Good luck, >>> >>> On Thu, Aug 18, 2022, 6:24 PM Kirpal via RE-wrenches < >>> re-wrenches@lists.re-wrenches.org> wrote: >>> >>>> Hi Yall! >>>> Anyone used HomeGrid batteries? We are just getting ready to pair them >>>> with some Outback and Sol Ark systems.. They have a compelling price, form >>>> and feature set. >>>> Hoping to hear of any issues before we jump in too deep with them.. >>>> 100 thanks for any thoughts! >>>> Cheers. >>>> Kirpal >>>> Oregon Solarworks >>>> >>>> ___ >>>> List sponsored by Redwood Alliance >>>> >>>> Pay optional member dues here: http://re-wrenches.org >>>> >>>> List Address: RE-wrenches@lists.re-wrenches.org >>>> >>>> Change listserver email address & settings: >>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >>>> >>>> There are two list archives for searching. When one doesn't work, try >>>> the other: >>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ >>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org >>>> >>>> List rules & etiquette: >>>> http://www.re-wrenches.org/etiquette.htm >>>> >>>> Check out or update participant bios: >>>> http://www.members.re-wrenches.org >>>> >>>> ___ >>> List sponsored by Redwood Alliance >>> >>> Pay optional member dues here: http://re-wrenches.org >>> >>> List Address: RE-wrenches@lists.re-wrenches.org >>> >>> Change listserver email address & settings: >>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >>> >>> There are two list archives for searching. When one doesn't work, try >>> the other: >>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ >>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org >>> >>> List rules & etiquette: >>> http://www.re-wrenches.org/etiquette.htm >>> >>> Check out or update participant bios: >>> http://www.members.re-wrenches.org >>> >>> ___ >> List sponsored by Redwood Alliance >> >> Pay optional member dues here: http://re-wrenches.org >> >> List Address: RE-wrenches@lists.re-wrenches.org >> >> Change listserver email address & settings: >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >> >> There are two list archives for searching. When one doesn't work, try the >> other: >> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ >> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org >> >> List rules & etiquette: >> http://www.re-wrenches.org/etiquette.htm >> >> Check out or update participant bios: >> http://www.members.re-wrenches.org >> >> ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org
Re: [RE-wrenches] HomeGrid batteries
Aloha All, I am considering doing a job with one of these (14kWH) with a Sol-Ark 12kW for a client who is demanding them. Anyone have any recent experience with them? The price is good but all else is pretty mediocre. Aloha, Lou Russo (808) 345 6762 On Thu, Aug 18, 2022 at 4:46 PM Jerry Shafer via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > The cycle life sounds good the warranty cycle for off grid is far less > than blue planet and fortress. If you compare the fortress x 2, 18.5's with > a better warranty it comes out cheaper. I do see a display but l only see > volts. Pretty low surge, is there US warranty administration? Good luck, > > On Thu, Aug 18, 2022, 6:24 PM Kirpal via RE-wrenches < > re-wrenches@lists.re-wrenches.org> wrote: > >> Hi Yall! >> Anyone used HomeGrid batteries? We are just getting ready to pair them >> with some Outback and Sol Ark systems.. They have a compelling price, form >> and feature set. >> Hoping to hear of any issues before we jump in too deep with them.. >> 100 thanks for any thoughts! >> Cheers. >> Kirpal >> Oregon Solarworks >> >> ___ >> List sponsored by Redwood Alliance >> >> Pay optional member dues here: http://re-wrenches.org >> >> List Address: RE-wrenches@lists.re-wrenches.org >> >> Change listserver email address & settings: >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >> >> There are two list archives for searching. When one doesn't work, try the >> other: >> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ >> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org >> >> List rules & etiquette: >> http://www.re-wrenches.org/etiquette.htm >> >> Check out or update participant bios: >> http://www.members.re-wrenches.org >> >> ___ > List sponsored by Redwood Alliance > > Pay optional member dues here: http://re-wrenches.org > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > There are two list archives for searching. When one doesn't work, try the > other: > https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org > > List rules & etiquette: > http://www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > http://www.members.re-wrenches.org > > ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org